Yesterday at 09:061 day SITUATION. Systems all checked:Pipes flushed, a sparky has checked electrics, new combi boiler (£7.5k ouch) and providing water to required temperature, thermostat calls for heat, a new actuator (replaced 1 week ago), mixing valve checked, pump checked (set at III or II), flow meters showing 1.5, temperature showing 32 degrees. PROBLEM. Water supply pipes up to manifolds hot but tepid once in manifold. Floor tiles not warming (chill taken off). I believe too much cold water being mixed.QUESTION. How do I increase temperature of water going under tiles?
Yesterday at 09:141 day Is the room up to temperature? And how how have you given it to heat up?UFH doesn't or shouldn't have a hot floor. 32 degs is below body temperature so it will only feel tempid.
23 hours ago23 hr That 32 degrees on the manifold is the clue for me. I would check the blending valve on the manifold first and nudge it up in small steps, as it sounds like it is mixing in too much return water before the loops. Also compare the flow and return temperatures on a loop and make sure the actuators are actually lifting, because a stuck pin will leave a loop cold even when the pump is running. Tiles will still only feel mildly warm at normal UFH temperatures, so give it a good few hours after any change before judging it.
13 hours ago13 hr Author 12 hours ago, JohnMo said:Is the room up to temperature? And how how have you given it to heat up?UFH doesn't or shouldn't have a hot floor. 32 degs is below body temperature so it will only feel tempid.Thanks, l give it three hours. I have felt the tiles mildly warm before but tepid is with just above chilled tiles. The room temp is 19 and I have thermo set at 21. the water temp does go up to 36 but its inconsistent.
12 hours ago12 hr 17 minutes ago, Adrian Clark said:Thanks, l give it three hours. I have felt the tiles mildly warm before but tepid is with just above chilled tiles. The room temp is 19 and I have thermo set at 21. the water temp does go up to 36 but its inconsistent.Depending on screed depth or floor buildup, warm up times can be way longer than 3 hours with UFH.20 minutes ago, Adrian Clark said:the water temp does go up to 36 but its inconsistent.That sounds like your boiler is cycling, one of the issues with zoning central heating. Is this the only part of the heating system on? What is the rest of the heating system and how is it controlled?More info you can provide the better
2 hours ago2 hr Author 8 hours ago, JohnMo said:Depending on screed depth or floor buildup, warm up times can be way longer than 3 hours with UFH.That sounds like your boiler is cycling, one of the issues with zoning central heating. Is this the only part of the heating system on? What is the rest of the heating system and how is it controlled?More info you can provide the betterThis morning's situation. I checked the system which was flowing had been running for 2.5 hrs. Sequence of checks:The ufh is the only zone on the two upstairs radiators are on a separate thermostat. This morning the copper pipes were hot up to the mixing manifold. The return and outbound manifolds were tepid as were the pipes going into the floor.Water temperature 30 degrees.Then the system clicked, stopped calling for hot water with the room temp at 20 degrees and thermo set at 21 degrees.I turned the thermo up, see photo, it called for heat but the combi boiler did not respond (water ufh temperature dropped to 26 degrees).I turned up the seperate radiator thermostat the boiler responded.I observed the combi boiler heating system which consistently responds rapidly rises to the 53 degrees setting after gradually dropping to 43 degrees. As I write the ufh water temp is 28 degrees with the system just incomprehensibly clicked off with room temp 20 degrees and thermo at 21 degrees. It then clicked back on. It seems haphazard. Stevenlee is right about too much cold water being mixed. I dont know what a blending valve is (unless its the white knob i call a mixing valve).(this help to figure out the problem is priceless I am grateful).
1 hour ago1 hr I wouldn't put too much faith in the calibration of that thermo head, a couple of degrees higher might sort it for you
1 hour ago1 hr Think your issue is more than setting the UFH flow temp.With only 3 loops of UFH on, your boiler cannot get the heat away quick enough and goes in to self protection mode, switching off and letting the system cool for x minutes and try again. Easy anolagy is a kettle with below minimum water level and a full kettle. The full kettle has a nice controlled run, the kettle with too little water boils and doesn't trip off the element when it's hot. The boiler is seeing to little water and seeing a rapid rise in temperature and saying something not right I will stop.So to get this all working well you need to look wider and at the whole CH system. Still way more information needed So assuming radiators elsewhere all with trvs? Yes or no, if no what exactly do you have?How many thermostats do you have?How many radiators per thermostat or are they all on TRVs?What boiler do you have and it's sizeHow big is your house and how old is itAnything else I have missed?
30 minutes ago30 min And to add to the above post, are you trying to heat just the UFH while doing these tests, or the radiators as well?If just UFH and radiators are off, then it is indeed very likely the boiler is unhappy and shutting down. Try it with radiators running and UFH on at the same time, the radiator load should keep the boiler happy.Turn up that big white dial on the left of the bottom manifold. That is what sets the temperature going into the UFH loops.UFH does take a long time to warm up. Every year when we turn the heating on, later that same day SWMBO says "the heating's not working in the En-Suite" Next morning it is toasty warm and then stays warm with very little heat input.
Just now1 min Author Thank you. More information:So assuming radiators elsewhere all with trvs? Yes. Only upstairs, See photos.How many thermostats do you have? Two, the previous photo for the ufh and the one for the radiators, see photo. How many radiators per thermostat or are they all on TRVs? One thermostat serves our two radiators, they are efficient. What boiler do you have and it's size. Greenstar Heatslave II, see photo (eighteen months old)How big is your house and how old is it. Small 2 bed cottage, roughly 40 sq metres footprint, 200 years old. Renovated with underfloor heating installed downstairs some time after 2009 (no paperwork discovered).Anything else I have missed? When I do the tests I have only run the UFH.
Just now1 min 27 minutes ago, ProDave said:UFH does take a long time to warm up. Every year when we turn the heating on, later that same day SWMBO says "the heating's not working in the En-Suite" Next morning it is toasty warm and then stays warm with very little heat input.We are about 24 hours from a coke start, tried doing setbacks once, and ended up switching the heat off at lunch time to get a night time set back. But restarting the heating about midnight to catch for the next morning. UFH is very slow, time scheduling is just a waste of time in my experience.