Friday at 15:131 day There are lots of loopcad layouts here on BH with room-by-room loops. Figure heat loss per room etc...Now supposing I have PH-level insulation and a thickish slab - can I just slather my slab below the screed with a regular loop design, ignoring the individual rooms? My thinking is that concrete/screed is a good thermal conductor and, for that reason, I won't really be able to control the temperature in individual rooms anyhoo. The screed will pretty much all be at the same temperature, and the heat output to the individual rooms will be governed by that temperature, whatever I try to do?p.s. my place has 3 rectangular slabs roughly the same size. Edited Friday at 15:161 day by Alan Ambrose
Friday at 15:351 day I believe for 16mm pipe, loops should not exceed 100m length.About 16 sqm ? - have I got that right for 150mm spacing ?
Friday at 15:501 day I think you'd struggle to pump through a much longer small diameter pipe and even if you could, most of the heat would be dumped into your screed in the earlier part of the run so heating would be very uneven.I agree you can ignore zoning exactly to individual rooms and not much point trying to control their temperature separately, but you'll still need a manifold and ideally similar length loops to even out the heat distribution and keep flow through the pipes easier.
Friday at 15:591 day Many of us with passive-type slabs treat the whole thing as one zone.That said, there could be a benefit to at least trying to keep each loop to one or a couple of rooms with similar heating needs. That way, you can tweak per-room heating by adjusting flow rates at the manifold. You'd do that entirely passively - tweak the flow rates when you first move in to get the room temps you want, then probably never look at the manifold again.As it happens, running all loops completely open worked fine for us. The one carpeted room downstairs is a little cool in winter, but it isn't used that much, and when it is, it's generally the kids gaming or watching TV, so it heats up fast enough. I haven't touched our manifold in over a decade.As @torre says, there's probably an advantage in keeping all loops about the same length. I think each loop in our system is nominally 100 m long (one might be a little shorter).
Friday at 17:311 day We're not PH level, but very well insulated with UFH in a 70mm slab over Hanson Jetfloor. We have a total of 12 circuits grouped in 7 thermostatically controlled zones. This enables us to set and maintain comfort levels to suit the use of each zone, and for relevant times of day.Surely, a single loop/zone risks losing such control, even if you could deliver even heat distribution across the entire circuit/slab?
17 hours ago17 hr Author Sorry, I wasn’t being quite exact - I meant one logical loop, ignoring the room layout - sure it would need to be split for flow reasons.@nss - that’s what I’m asking - is it even possible to adjust the temperature in each room given that comcrete is such a good thermal conductor? It’s a bit like trying to have different temperatures across a frying pan. Edited 17 hours ago17 hr by Alan Ambrose
16 hours ago16 hr Concrete is a good thermal conductor but is also stores loads of heat. Have loops in each room does allow some fine tuning of room temperature, just by flow rate variation, so localise output can be manipulated. Having a bunch or random loops that cover the space is fine also, but you are more likely to an even output across all rooms, depending on floor covering, which has a direct impact on floor output, carpet is pants, ceramic tiles are great. So if you have multiple floor coverings a room by room approach may be better or add flexibility for the future.The other thing is you say thickish slab, that doesn't really mean much. We have 100mm and was concerned about internal wall fixings or drilling for them, puncturing through my pipe, so I kept a wide berth from the internal walls, so that could not occur, also ran all pipe through doorways for that reason also
16 hours ago16 hr Author Yeah, I think, on reflection that you’re right - so the conventional room layout thing - which means I need to make up my mind on the room boundaries…I might also avoid the drilling problem by sticking the wall plates down.
Just now1 min I would go with what Spinny and torre said and keep the loops fairly even and under that 100m sort of length. A thick slab will even the heat out a lot, so one logical zone can work, but it does make fault finding much harder later. If one loop ever drops pressure you want to be able to isolate it at the manifold, so pressure test each loop on its own before the screed goes down and keep a simple sketch of where each loop runs.