john0wingnut Posted July 30 Posted July 30 Afternoon all I have just had an inspection visit for my timber frame rear extension. It is a single storey 6x2 timber frame, 400 centres, 11mm OSB on the outside, breather membrane and is to be finished with vertical thermo pine, on batten / counter batten. The BCO has advised I need to put intumescent cavity closers in at the top / bottom and around the windows and doors, which is not something I thought was required for ventilated cladding; I've just got mesh top and bottom. Windows / doors have a cladding cheek to finish, so are closed already. Can anyone on here enlighten me? John
Alan Ambrose Posted July 30 Posted July 30 The intumescent strips seem to be accepted practice. Alternatives are 0.5mm steel / wood of a given thickness (I forget how much). There’s a fair amount of discussion on this on ‘t ‘ub. My BC seemed to be more open-minded - I forget his exact words. We used the steel strip as it was cheaper, but it did take a while to put up.
G and J Posted July 30 Posted July 30 OK, I can’t help feeling I should know this, but how does a steel strip stop the ventilation behind the cladding act like a chimney during a fire whilst still allowing the chimney effect to dry the cladding under normal conditions? 1
john0wingnut Posted July 30 Author Posted July 30 Hi all So having done some reading, document B refers to a cavity as a sealed entity, vs what I would call a ventilated void behind my cladding as it isn’t sealed. I understand strips would be useful preventing fire spreading from first to second storey for example, but, if my cladding or the timber frame catches fire, no intumescent strip sealing the ventilated area is going to stop it; and given the soffit is 10mm above where the cladding finishes, it won’t stop that catching fire either. My front extension is TF with brick veneer, and drawings for that clearly advise fire proof closures at the top of the cavity and around the windows / doors which makes sense.
john0wingnut Posted Friday at 08:39 Author Posted Friday at 08:39 11 hours ago, john0wingnut said: Hi all So having done some reading, document B refers to a cavity as a sealed entity, vs what I would call a ventilated void behind my cladding as it isn’t sealed. I understand strips would be useful preventing fire spreading from first to second storey for example, but, if my cladding or the timber frame catches fire, no intumescent strip sealing the ventilated area is going to stop it; and given the soffit is 10mm above where the cladding finishes, it won’t stop that catching fire either. My front extension is TF with brick veneer, and drawings for that clearly advise fire proof closures at the top of the cavity and around the windows / doors which makes sense. Cant seem to edit the above. I misread the regs. Cavity is a considered a concealed space. Not sealed!! So that statement above is incorrect.
Alan Ambrose Posted Sunday at 10:50 Posted Sunday at 10:50 Following @G and J comments, I've been researching this again. It's not completely obvious - NHBC doesn't go into a lot of detail re timber cladding & cavities, nor the building regs. They say a bit but a picture or two would have been nice. My current thinking is that 0.5mm steel is fine around windows & doors but intumescent might be required at the top of the cavity. I've not figured out the bottom yet.
G and J Posted Sunday at 18:50 Posted Sunday at 18:50 I can imagine steel cavity closures round penetrations. I think the key thing is to close off the chimney (behind the cladding) when there is a fire.
Owain1602 Posted Sunday at 20:47 Posted Sunday at 20:47 (edited) The regs say 0.8mm steel (or thicker) and 38mm wide timber (or thicker). I agree, this can be quite a confusing topic. Whatever you do, don’t try and read the STA documents seeking clarity….it will confuse you even more! The cavity barrier element of the regs doesn’t have anything to do with the fire rating of your cladding, that’s a separate topic. They want to see how you will stop a fire from using the external cavity behind the cladding as a means of bypassing the internal fire resisting elements. There are numerous arguments and nuances that can be put forward such that the guidance as read do not apply in certain sections. Obviously, a lot of this came out after Grenfell. My understanding is that the fire service couldn’t understand at the time how fire was spreading throughout the building, especially from floor to floor so quickly. They couldn’t see the fact that fire was spreading inside the cavity behind the cladding. We had two different external claddings, one for the ground and another for the first floor, both had ventilated cavities. I specified a steel drip flashing between the two (which ended up 3mm thick). The ground floor cavity ventilates at the underside of the drip, and the start of the first floor cavity is above the drip. In the event of a fire, we wouldn’t fully close off either cavity, just that fire in the ground floor cavity would come up against a 3mm steel plate. It would have to come out of the ground floor cavity at the drip, come out 100mm to get around the drip then turn back on itself to get back to the first floor cavity. That is the detail around a lot of the house. at the heads of windows we have intumescent strips, side and bottom of windows is fully closed with 38mm or bigger timber. I had agreement from the BCO that the detail and argument I put forward for the eaves to roof was okay. But as I was doing the cladding, I had to change something to better attach the gutter. Rather than go through the whole approval loop again, I just ran intumescent strips around the whole of the eaves (not at the gables). Value my time and sanity more than about £500’s worth of strips. If you can post a bit more detail, I’m sure that we can come up with more specific suggestions. Edited Sunday at 20:48 by Owain1602 1
Alan Ambrose Posted Monday at 06:42 Posted Monday at 06:42 Think 0.5mm steel rather than 0.8mm. @G and J & @Owain1602 Can I ask - did you do intumescent strip at the bottom of the cladding cavity? @Owain1602 - interested on why you didn't do the gables - did it not have the same circumstances as the eaves? BTW this is what my BCO said on this subject: Fire stopping cavity barriers are not enforceable under building regulations for individual domestic dwellings. Only enforceable in buildings with separate compartment ie flats or semi’s. Although I do think the fire stopping strip is a good idea it is your choice in this circumstance. 1
Owain1602 Posted Monday at 07:12 Posted Monday at 07:12 Apologies @Alan Ambrose, you are right, it is 0.5mm steel. We don’t have anything on the bottom of the cavity. I’m not sure what situation would be helped by a closure at the bottom, since the strips need fire to activate them. Nothing was needed at the wall to roof junction at the gables since this was completely sealed with timber, as the roof is ventilated from eaves to ridge. The comment from your BCO is similar to what I was referring to by being able to argue your case for not needing them in certain scenarios.
G and J Posted Monday at 07:25 Posted Monday at 07:25 Our sides are within a meter of our boundaries and so we have to demonstrate reasonable precautions to prevent fire spreading from one property to another. Whilst they aren’t technically enforceable it would seem odd to me to be willing to spend money on things like a robot vacuum (a similar cost level) and not on something that might save a life. In my mind once a fire is bad enough to operate the strips the house is in real trouble, the key drive is to slow stuff down long enough for everyone to get out and the fire service to prevent spread between buildings. As for positioning, I’d agree that they will be less effective at ground level, but I’d also argue that one wouldn’t want a single strip atop a 6m cladding ‘chimney’.
Alan Ambrose Posted Monday at 11:24 Posted Monday at 11:24 >>> As for positioning, I’d agree that they will be less effective at ground level, but I’d also argue that one wouldn’t want a single strip atop a 6m cladding ‘chimney’. That's an interesting point. For a highish single storey like we have (our eaves are at ~3.5m) maybe it would make sense to have it, say, 2/3rds up. If it's right at the top, the fire has to get all the way up before it operates.
G and J Posted Monday at 13:31 Posted Monday at 13:31 Some will be better than none, even if it isn’t in the perfect place. Let’s hope they are never tested.
kandgmitchell Posted Monday at 18:49 Posted Monday at 18:49 Don't conflate the requirement for cavity closures as required by Requirement B3 - Internal Fire Spread which says: 5.18 Cavity barriers should be provided at all of the following locations. a.) At the edges of cavities, including around openings (such as windows, doors and exit/entry points for services). with Requirement B4 - External Fire spread which says: External walls on, and within 1000mm of, the relevant boundary Unprotected areas should meet the conditions in Diagram 11.5, and the rest of the wall should be fire resisting from both sides. External surface materials facing the boundary should be class B-s3, d2 or better. You will need to consider both (and both are complex and cannot be explained simply here) 1
G and J Posted Monday at 20:41 Posted Monday at 20:41 1 hour ago, kandgmitchell said: with Requirement B4 - External Fire spread which says: No sure if you were referring to our comment, but just for completeness (in case helpful to others) we are bound by B4, so the relevant walls have cement board over our timber frame and fire treated cladding, in addition to the appropriate cavity closures and intumescent strip.
Gus Potter Posted Monday at 22:42 Posted Monday at 22:42 15 hours ago, Alan Ambrose said: BTW this is what my BCO said on this subject: Fire stopping cavity barriers are not enforceable under building regulations for individual domestic dwellings. Only enforceable in buildings with separate compartment ie flats or semi’s. Although I do think the fire stopping strip is a good idea it is your choice in this circumstance. Fire protection in timber frames is very tricky. But I have to say that for a BCO to make a statement such as this is astounding, given that you have timber frame construction. To make such a statement is not in alignment with current design understanding and the law. I suspect that the person that made this statement is less experienced and has just made a mistake in the way they have written. Just say they have. The bottom line, if you look at the fine print, you’ll find that they have little or no liability. The real liability rests with either you or you designer.
Nickfromwales Posted Monday at 23:55 Posted Monday at 23:55 1 hour ago, Gus Potter said: The real liability rests with either you or you designer. The designer will follow the law, the BCO will enforce it. 1 hour ago, Gus Potter said: To make such a statement is not in alignment with current design understanding and the law. You would need to support this with written evidence to the contrary, do you have such reference material? I find it difficult to accept that a practicing BCO would make such a bold statement, post Grenfell, if it wasn't valid. 17 hours ago, Alan Ambrose said: Fire stopping cavity barriers are not enforceable under building regulations for individual domestic dwellings. I can accept this in principle, because at the point where these would become effective, circa 55-57 degrees C of flames licking around them, the sad reality is that the occupants (remaining inside) would have likely already expired due to smoke inhalation. Almost nobody dies from being 'burned alive'; they would have already succumbed to the toxic smoke. At that point, your external cavity fire prevention would be doing absolutely feck all for these lost souls. So, that being my personal opinion, the above BCO makes a valid statement in actuality, but I cannot say that it was lawful for them to say so, as I am not completely fluent with these regs personally. Common sense should prevail here; for my current and subsequent 2 self-build clients, I raised the subject of "automatic fire suppression". It wasn't "needed", but the client chose to adopt this anyways, at reasonable cost, to safeguard his family. In addition, I routinely add 2 - 3x the required number of smoke / heat / multi-sensor detectors for the best line of defence, aka 'early warning', as this is hands-down the one thing that saves lives. External cavity measures are borderline irrelevant for a regular domestic dwelling of 1 or 2 stories, in my own opinion.
ADLIan Posted Tuesday at 04:48 Posted Tuesday at 04:48 22 hours ago, Alan Ambrose said: Think 0.5mm steel rather than 0.8mm. @G and J & @Owain1602 Can I ask - did you do intumescent strip at the bottom of the cladding cavity? @Owain1602 - interested on why you didn't do the gables - did it not have the same circumstances as the eaves? BTW this is what my BCO said on this subject: Fire stopping cavity barriers are not enforceable under building regulations for individual domestic dwellings. Only enforceable in buildings with separate compartment ie flats or semi’s. Although I do think the fire stopping strip is a good idea it is your choice in this circumstance. 'Cavity barriers' and 'fire stopping' are totally different items and are noted as such in Appr Doc B. Fire stopping is normally related to compartment walls and floors found in blocks of flats, semi detached and terraced houses. Even the BCO is confused! 1
Alan Ambrose Posted Tuesday at 11:39 Posted Tuesday at 11:39 (edited) >>> I raised the subject of "automatic fire suppression". Would be interested to hear about that. FYI, just spoke to Envirograf - they asked what the BCO said and actually agreed with him ... but said that for belt-and-braces a strip under the eaves and gables and at the bottom of the cladding was good. Also the windows etc. But then they are selling the stuff. 😀 p.s. Envirograf said there was a v good illustration on the NHBC website. Envirograf couldn't / wouldn't send me a link or copy. And I can't find it. Think I'm going with a strip at the top of the cladding only. >>> External cavity measures are borderline irrelevant for a regular domestic dwelling of 1 or 2 stories, in my own opinion. Might depend on how generally flammable the build is, but kind of agree - esp. as we're one storey and all rooms except bathrooms have a door to the outside. Edited Tuesday at 11:44 by Alan Ambrose
Owain1602 Posted Tuesday at 13:59 Posted Tuesday at 13:59 I feel at the eaves is a sensible approach, but it does depend on the rest of the construction. What are you going to do at the heads of the windows? In my mind, the only real risk of fire getting behind the external cladding is from an internal fire escaping through an open window (hence why they like to see them at the heads of windows, for a ventilated cavity). Your external walls presumably have a 30 min fire rating on the inside?
john0wingnut Posted Tuesday at 16:27 Author Posted Tuesday at 16:27 Interesting reading everyone’s replies. BCO for me has stated it’s required and sent me a letter to that effect. Hopefully the picture uploads. My issue is I have a tiny amount of room for batten / counter batten above the window, so I have no idea how I am going to run an intumescent strip along the top with ventilation mesh all while leaving a gap to the soffit. I’ll see if I can find this NHBC guide, but as it stands agree with others that none of the guides are clear cut
Alan Ambrose Posted Tuesday at 16:52 Posted Tuesday at 16:52 @Owain1602 >>> What are you going to do at the heads of the windows? We used thin stainless strip as per an earlier ‘ub discussion. Quite a bit of work, but done now. Much cheaper than intumescent of course and seems to me anything fireproof will work (maybe not in the regs though) as you don’t need the expandability of intumescent.
Alan Ambrose Posted Tuesday at 17:44 Posted Tuesday at 17:44 @john0wingnut >>> how I am going to run an intumescent strip along the top with ventilation mesh Envirograf do a combined mesh / intumescent product if that helps.
Great_scot_selfbuild Posted Tuesday at 17:55 Posted Tuesday at 17:55 57 minutes ago, Alan Ambrose said: Am I correct in thinking that for ventilation behind the cladding here (assuming it’s timber), you rely on the horizontal battens providing lateral air movement? (love the detail in this thread - exactly what makes buildhub so useful!)