Oz07 Posted 21 hours ago Posted 21 hours ago Talking to a plumber tonight. He is F gas certified. He was explaining the difference with these heat pumps to the standard ones to me. It's all a bit beyond my understanding. Anyway I was asking him if I could have wet UFH on GF then air to air units upstairs to do heating if needed and cooling in summer, also probably 1 or 2 air units downstairs to cool. All off 1 outdoor unit. I think he is more in with Daikin and said they are bringing out something soon, however Samsung appear to do the perfect solution with the TDM plus / climate hub. Outdoor pump, pre plumbed cylinder and air to air units. It looks good, no doubt very costly?! Does anyone have any experience with this set up. Seems simpler to a luddite like me. I suppose cost will be the trade off for simplicity i've no doubt others like @JohnMo can knock something up just as good performance wise for a lot less dough, maybe even have 2 seperate outdoor units. It's just beyond my pay grade though. I wonder what cost would be for this and 5 or 6 indoor air con units and the cylinder. https://samsung-climatesolutions.com/gb/b2c/our-solutions/home/heat-pump-solutions/heating-cooling/tdm-plus.html
SimonD Posted 21 hours ago Posted 21 hours ago Lots of ifs and buts on this one. There are only really three practical ways of moving the heat into and out of the building: water, air, refrigerant. Air specific heat capacity is poor so you need lots of volume and flow, refrigerant needs its own specific pipework, qualifications etc. with lots of limitations to things like pipework length. Water is definitely the most effective way to move the heat. The aircon units will probably also need condensate drainage so added complexity there. I don't think the solution is that simple, or not as simple as the Samsung marketing department makes it look. Maybe okay for a new build, but for a retrofit? I'm not so sure. Like with all these things, the complexity lies more in the cooling than in the heating, especially if you want aircon type cold. 1
JohnMo Posted 20 hours ago Posted 20 hours ago The F gas solution doesn't look cheap, may be wrong. Could be a good system, but I would go A2W and have fan coils (water to air) in bedrooms and normal wet UFH. A pragmatic design could be pretty simple. Design for heating, accept cooling may not be perfect but way better than not having cooling. UFH will make house feel way cooler than the air temperature is. The fan coils in bedrooms will leave rooms for a comfortable sleep. First job is looking at heat loss and sizing an outdoor unit. Then room by room heat loss. Design UFH (not some cut and paste job by UFH suppliers). Size fan coils to provide room heating at under 30 degs. Then run everything as a single zone. Fan coils will modulate fan speed to keep room temperature stable. The above assumes you are talking about a low energy house. 1
Oz07 Posted 11 hours ago Author Posted 11 hours ago The build will be relatively low energy, not approaching passive but certainly lower than most. I have to admit the air con type cooling does appeal to us. After I built our last house I said i'd never build another without aircon. It's a small luxury that I'd be happy to pay for. I suppose what I need to do is compare prices of a normal ashp for 1500 odd sq ft house versus this f gas system. I'm sure fan coils and UFH would have ok cooling capacity but would it be as good as a2a air con?! I think with the umbrella scheme the grant could be claimed either way. I asked AI and I think it was estimating the installation at 12-20k with the cost for the samsung gear estimated at 7-12k. I did ask AI about the distances of air con units from the pump and it was saying quite long, 7.5-10m. I imagine they are decent if Samsung market this as 1 unit can serve whole house. I'm a fair way off heat calcs yet as resubmitting a new planning app but will deffo be one to keep an eye on. The plumber was saying to me that with the f gas you don't get any heat loss from the pipework to the unit whereas with the A2W you do?
JohnMo Posted 10 hours ago Posted 10 hours ago 1 hour ago, Oz07 said: think with the umbrella scheme the grant could be claimed either way Maybe not, A2A is ok for £2.5k only and almost no one is approved, so don't hold your breath on that one. If you assume UFH is just part of house build cost. It all doesn't have to cost a lot to build a good performance system. I never bothered with the grants, would rather pay myself than get ripped off. Simple direct UVC for DHW, cheap as chips, save around £1000 compared to pre plumbed heat pump one. Charge on time off use tariff. Would be surprised if you need more than a 4kW heat source, from size of house and assuming better than Building Regs. If you want Aircon performance add a mixing valve to system and run fan coils at 6 degs, or just oversize the fan coils, decent fan coils have the output data for different flow temps. Or do everything A2A, don't bother with UFH. Still do direct water heating. Spend the money saved on a good system with good airflow regulation. Having lived in hot countries a number of years, the airflow became a thing of hate, once the novelty wore off.
Nickfromwales Posted 9 hours ago Posted 9 hours ago 11 hours ago, SimonD said: Lots of ifs and buts on this one. There are only really three practical ways of moving the heat into and out of the building: water, air, refrigerant. Air specific heat capacity is poor so you need lots of volume and flow, refrigerant needs its own specific pipework, qualifications etc. with lots of limitations to things like pipework length. Water is definitely the most effective way to move the heat. The aircon units will probably also need condensate drainage so added complexity there. I don't think the solution is that simple, or not as simple as the Samsung marketing department makes it look. Maybe okay for a new build, but for a retrofit? I'm not so sure. Like with all these things, the complexity lies more in the cooling than in the heating, especially if you want aircon type cold. 2 hours ago, Oz07 said: The build will be relatively low energy, not approaching passive but certainly lower than most. I have to admit the air con type cooling does appeal to us. After I built our last house I said i'd never build another without aircon. It's a small luxury that I'd be happy to pay for. I suppose what I need to do is compare prices of a normal ashp for 1500 odd sq ft house versus this f gas system. I'm sure fan coils and UFH would have ok cooling capacity but would it be as good as a2a air con?! I think with the umbrella scheme the grant could be claimed either way. I asked AI and I think it was estimating the installation at 12-20k with the cost for the samsung gear estimated at 7-12k. I did ask AI about the distances of air con units from the pump and it was saying quite long, 7.5-10m. I imagine they are decent if Samsung market this as 1 unit can serve whole house. I'm a fair way off heat calcs yet as resubmitting a new planning app but will deffo be one to keep an eye on. The plumber was saying to me that with the f gas you don't get any heat loss from the pipework to the unit whereas with the A2W you do? For a current (MBC PH TF) project, the decision has been made to go for fa refrigerant based setup for domestic heating / cooling (via UFH) plus DHW (all via a plate heat exchanger), and a second setup for all of the first floor space heating and cooling. There is some considerable distance between the external units (x2) and the internal units, and to overcome this it has been suggested that a manifolded system is utilised. This is outside my wheelhouse as I mostly do wet (hydronic) systems, so am learning here too, but this certainly overcomes distance issues without a problem. Sizeable dwelling, circa 400m2, but (apparently) the proposed Daikin setup will perform perfectly well here; I think the furthest 2/3 units are >20m from A-B. Going for remote mounted chassis tucked into newly (purposefully created) closet / plant spaces vs units on the walls. 1
SimonD Posted 8 hours ago Posted 8 hours ago 2 hours ago, Oz07 said: The plumber was saying to me that with the f gas you don't get any heat loss from the pipework to the unit whereas with the A2W you do? This is pretty much irrelevant tbh. The 'losses' aren't really losses as they go into the heated envelope of the house, so do their bit on contribution. Honestly, I'd wait and see what your heat loss calc says and then review from there as they may be so small if you're going near ph that even a 4kW heat pump would be too big. The other ball to chuck into the mix for a highly efficient house for heating is an exhaust air heat pump, which simultaneously deals with your heating, MVHR and DHW. The you can go multi-split for your air-con. Just make sure that the person doing your heat loss actually understands whole house MVHR and models the heat loss accordingly - lots don't and then calculate normal ventilation losses.
joth Posted 6 hours ago Posted 6 hours ago 1 hour ago, SimonD said: This is pretty much irrelevant tbh. The 'losses' aren't really losses as they go into the heated envelope of the house, so do their bit on contribution. It's relevant for any external pipework. I think this is more common in F-Gas installs as they tend to be retrofits (in domestic installs at least), and tends to be easier by running pipes all over the outside of the building. (Ugly for sure, but easier & cheaper). I expect retrofits to increasingly use a2a for this very reason. 4 hours ago, Oz07 said: ... I have to admit the air con type cooling does appeal to us. After I built our last house I said i'd never build another without aircon. It's a small luxury that I'd be happy to pay for This is the key decision point. If you're happy to pay for it, then an a2a (i.e. some sort of refrigerant based) system is the only way to get the "arctic gale" of an aircon system. Whether you combine one system with UFH & DHW or do two systems (potentially one exhaust air for UFH & DHW) comes down to shopping about, supplier selection and what they are comfortable working with. Cost wise it's probably a wash (one complex system vs two more conventional ones). A a2w heat pump with FCUs is likely cheaper to install and can perform very well (comfort and cost wise) if setup correctly. And is much more DIY-able if that's your truck. But it will never give the same frozen air blast of a2a
Bancroft Posted 6 hours ago Posted 6 hours ago Have a word with CoolEnergy in Grimsby - they might be able to provide the sort of solution you're looking for.
Oz07 Posted 59 minutes ago Author Posted 59 minutes ago 9 hours ago, JohnMo said: Maybe not, A2A is ok for £2.5k only and almost no one is approved, so don't hold your breath on that one. If you assume UFH is just part of house build cost. It all doesn't have to cost a lot to build a good performance system. I never bothered with the grants, would rather pay myself than get ripped off. Simple direct UVC for DHW, cheap as chips, save around £1000 compared to pre plumbed heat pump one. Charge on time off use tariff. Would be surprised if you need more than a 4kW heat source, from size of house and assuming better than Building Regs. If you want Aircon performance add a mixing valve to system and run fan coils at 6 degs, or just oversize the fan coils, decent fan coils have the output data for different flow temps. Or do everything A2A, don't bother with UFH. Still do direct water heating. Spend the money saved on a good system with good airflow regulation. Having lived in hot countries a number of years, the airflow became a thing of hate, once the novelty wore off. The plumber was telling me he knows some guy who is accredited who wants to do business with him. I think the idea is this guy finds the leads, gives the plumber the install job and this guy does the heat loss and mcs side. From my brief research I think the samsung option would qualify for the 7.5k grant as its doing A2W UFH, or would the cooling option on A2A rule it out? I know you never bothered with grants as you can DIY, unfortunately that is beyond me. I don't want to go to a full bells and whistles firm and pay massive overheads which wipe out the saving from the grant but I might be able to find a happy medium one man band / small firm installer and claim the grant somehow.
Oz07 Posted 53 minutes ago Author Posted 53 minutes ago 5 hours ago, joth said: It's relevant for any external pipework. I think this is more common in F-Gas installs as they tend to be retrofits (in domestic installs at least), and tends to be easier by running pipes all over the outside of the building. (Ugly for sure, but easier & cheaper). I expect retrofits to increasingly use a2a for this very reason. This is the key decision point. If you're happy to pay for it, then an a2a (i.e. some sort of refrigerant based) system is the only way to get the "arctic gale" of an aircon system. Whether you combine one system with UFH & DHW or do two systems (potentially one exhaust air for UFH & DHW) comes down to shopping about, supplier selection and what they are comfortable working with. Cost wise it's probably a wash (one complex system vs two more conventional ones). A a2w heat pump with FCUs is likely cheaper to install and can perform very well (comfort and cost wise) if setup correctly. And is much more DIY-able if that's your truck. But it will never give the same frozen air blast of a2a He was deffo on about external pipework but realistically my unit would be adjacent to the house so i suppose it's a red herring. I have seen some naff pipework all up the side of houses today which have had aircons fitted. I've just got to do the numbers. If I was happy to spunk say 5k on 2 aircon units, but I can get a combined A2W and A2A system for the same price or cheaper than 2 seperate systems then I suppose it's a goer. What would a realistic figure be for an A2W system with UFH GF and 4 or 5 FCU upstairs, installed, no DIY. 10k? lower? I was pretty set on using UFH on GF but would running whole house on A2A be a good idea? You don't see this much. If I can get an A2W set up with the FCU which performs very well cheaper then i'm happy to forgo the frost blast of AC. As long as it performs and cools the house then happy days. Would this option work out cheaper?
Oz07 Posted 50 minutes ago Author Posted 50 minutes ago 8 hours ago, Nickfromwales said: For a current (MBC PH TF) project, the decision has been made to go for fa refrigerant based setup for domestic heating / cooling (via UFH) plus DHW (all via a plate heat exchanger), and a second setup for all of the first floor space heating and cooling. There is some considerable distance between the external units (x2) and the internal units, and to overcome this it has been suggested that a manifolded system is utilised. This is outside my wheelhouse as I mostly do wet (hydronic) systems, so am learning here too, but this certainly overcomes distance issues without a problem. Sizeable dwelling, circa 400m2, but (apparently) the proposed Daikin setup will perform perfectly well here; I think the furthest 2/3 units are >20m from A-B. Going for remote mounted chassis tucked into newly (purposefully created) closet / plant spaces vs units on the walls. I think Samsung offer a charged unit or manifold or god knows what if you exceed the distance. Can't see it being needed on mine with clever placement of outside unit and pipework runs. It's only 1500 sq ft ish. Mine will be nowhere approaching Passive, but better than building regs. I've done the numbers on passive and it just doesn't work for me i'm happy to spend a few extra quid running the place and have the bandwidth free to think about other things.