JohnMo Posted January 31 Author Posted January 31 19 minutes ago, SteamyTea said: Does it do internal and external temperatures? It does external and assumes 20 deg internal.
JohnMo Posted January 31 Author Posted January 31 34 minutes ago, SimonD said: One piece of kit for helping with this, that I'm seriously looking at is Adia That's an interesting bit of kit A video here https://youtu.be/9sHmHa5ha_4?si=mir2dQesUXf0Aqgn 1
JohnMo Posted January 31 Author Posted January 31 1 hour ago, SimonD said: seriously looking at is Adia Just found a price, £1500, smart but... if offsetting getting new radiators, new plumbing and paying for an engineer to optimise your system, then small beer. New build where you should know exactly wall, floor and roof buildup and get heat losses quite accurate and your installing new piping and radiators anyway, not really needed. But would idiot proof a lot of installs, assuming heat pump is massively oversized.
SimonD Posted January 31 Posted January 31 24 minutes ago, JohnMo said: Just found a price, £1500, smart but... if offsetting getting new radiators, new plumbing and paying for an engineer to optimise your system, then small beer. New build where you should know exactly wall, floor and roof buildup and get heat losses quite accurate and your installing new piping and radiators anyway, not really needed. But would idiot proof a lot of installs, assuming heat pump is massively oversized. Yes, absolutely, it could be a game changer in that context. From discussions one of the ideas behind it is that it's about taking the guesswork out of the system design so instead you put in the Adia with the heat pump to get a proper understanding of how the system works and then propose essential changes based on real world measurements. The only issue and question I've got about this approach in retrofits is the application of VAT because the VAT examption on installs is defined as single supply. Technically you could probably get away with it but I do wonder how the conversation with the HMRC might go if they questioned you.
JohnMo Posted January 31 Author Posted January 31 1 hour ago, SimonD said: the heat pump to get a proper understanding of how the system works and then propose essential changes based on real world measurements. I've seen that way of doing things mentioned several times and the real world a lot of building could get away without much in the way of radiator changes. VAT, include a contingency (deposit) to return assess and make x pre priced changes - fully refundable, less second visit service charge? Explain you could remove that charge, but full VAT, plus any grant funding, that was too have been included, would be payable for the second visit.
SimonD Posted January 31 Posted January 31 27 minutes ago, JohnMo said: VAT, include a contingency (deposit) to return assess and make x pre priced changes - fully refundable, less second visit service charge? Explain you could remove that charge, but full VAT, plus any grant funding, that was too have been included, would be payable for the second visit. This is certainly a contender for how to manage it as there are already jobs where installing a volumiser, for example, might be priced but in the end it's unecessary so reduce the final invoice. The thing about single supply is that it depends on perspective. So if a customer considers all of the job as a reasonable single supply, then that is permitted at least in theory, even if there are several invoices.
Beelbeebub Posted January 31 Posted January 31 If the goal is accurate capture of the radiator/heat loss situation could the unit be plumbed in as part of the survey - left for a week to do it's thing and then report what radiators need upgrading, what the flow balance situation is etc. Removed with the install.
JohnMo Posted January 31 Author Posted January 31 1 hour ago, Beelbeebub said: If the goal is accurate capture of the radiator/heat loss situation could the unit be plumbed in as part of the survey - left for a week to do it's thing and then report what radiators need upgrading, what the flow balance situation is etc. Removed with the install. It's sold on the basis that no radiator or piping changes are needed. After a few weeks of capturing data, the home owners gets the options - stay as you are, and possibly upgrade radiators, for a given cost v cost saving on running cost. Suppose the idea is for £4k plus a day or two labour you get a heat pump. If you have a cylinder already they can use that as well.
Beelbeebub Posted January 31 Posted January 31 I do wonder why they include the pumo. With the exception of g6 Samsung pretty much all heatpump have a fairly powerful pump built in. The heat meter already has a flow meter (and some HPs also do). All you really need is a heat meter, possibly a pressure sensor, and then the ability to incrementally change each radiator flow. That would save a couple of hundred quid on thr BOM, which would translate to a hefty saving on the final price - at the cost of losing hydraulic separation, which you normally don't want anyway.
JohnMo Posted February 1 Author Posted February 1 14 hours ago, Beelbeebub said: I do wonder why they include the pumo Think it's there to cover all bases. Use the installed pump of the ASHP to overcome heat exchanger and piping to house. The secondary pump is there to push though micro bore if you need to. It's a one box to cover a lot of situations. Still not seen anything on how it works with UFH. It says one flow temperature systems including UFH are doable. But not seen any details.
SimonD Posted February 1 Posted February 1 (edited) 16 hours ago, Beelbeebub said: I do wonder why they include the pumo. With the exception of g6 Samsung pretty much all heatpump have a fairly powerful pump built in. The heat meter already has a flow meter (and some HPs also do). All you really need is a heat meter, possibly a pressure sensor, and then the ability to incrementally change each radiator flow. That would save a couple of hundred quid on thr BOM, which would translate to a hefty saving on the final price - at the cost of losing hydraulic separation, which you normally don't want anyway. There's a lot more to it than that. As I understand it at the moment, the pump is a modulating pump which is just there to boost head where necessary, which is becoming less common with the current crop of pumps, but there are still heat pumps that require external circulators. The issue with the radiators is that if you use standard balancing approaches, they're only correct at certain flow/pressure situations, and other than pressure independent flow regulating valves, there aren't any other tools that are a reliable way to balance the flow through radiators for all operating conditons. Most of the industry still uses standard lockshields and some are now starting to use the flow regulating valves, just like the UFH ones. The Adia unit has its own valves and room stats that feedback information to the system to understand the local climate situation at each radiator and it can also adjust flow temps and flow rates etc. to those based on this information. Nothing else on the market can do this. However, the flow temps are still global ones. What's also handy is the ability to control the system according to tou tariffs which I know customers really struggle with. But I do agree with you that having a box that includes everything, where you need it or not, may be unecessary. 2 hours ago, JohnMo said: Think it's there to cover all bases. Use the installed pump of the ASHP to overcome heat exchanger and piping to house. The secondary pump is there to push though micro bore if you need to. It's a one box to cover a lot of situations. Still not seen anything on how it works with UFH. It says one flow temperature systems including UFH are doable. But not seen any details. My thinking is that its position is really for retrofits with primarily radiator circuits and at the moment there are limited heatpumps it can work with - I have one project I'm completing the design for right now with a troublesome heating area fed by inadequate pipe sizes but the customer is adamant they don't want any disruptive work, so pipes have to stay the same. My worry about all these things is that it is a startup with unknown reserve capital and it largely seems like it's still in a development stage. They proudly display the venture capital firms, but having worked in the tech startup scene for about 10 years, I'm always cautious about this. This is an add-on product with currently limited compatibility with heat pump manufacturers living in the hope of an open protocol to be agreed across the industry. Looking at their team, they've clearly got a lot of very clever people on board, but other than a small number of testimonials, I can't see any real-world test evidence to back up their cost saving claims - and that always worries me. I also wonder whether some of the benefits they're selling are really as valuable as made out because they are suggesting forms of zoning, which we know in practise aren't great and don't necessarily improve efficiencies or save on running costs. For me, this is another of those 'solutions' being introduced to the market in the attempt to overcome common objections to installing heatpumps and trying to make it out like it's no different from installing a gas boiler, a bit like the new Zero disrupt scheme by Heat Geek. I'm taking the cynical view here, but I am thinking about how it might work very well for some projects, but it still doesn't and shouldn't detract from the fundamentals of good design and the long term benefit of designing and installing a system to run on good old low flow temperatures. Edited February 1 by SimonD
JohnMo Posted February 1 Author Posted February 1 The other way to it, is borrow ideas for the Adia system and simplify. Have heat pump on its own loop, CCT and additional pump for secondary loop, flow rate and match flow rate with secondary pump. Choose pump with enough head to go through existing pipes as required. Use flow setters on the existing rads at a dT to suit room and flow temps. Heat pump will modulate as needed to meet the heat extracted from the primary loop. Primary pump pulling almost zero Watts as no real head is needed. Whether you actually need to include the CCT is questionable, you just install an additional pump on the piping to produce the additional head required on fixed duty (then there is no fight with 2x modulating pumps), to push though the existing pipes. Then do what you normally do to the system.
SimonD Posted February 1 Posted February 1 9 hours ago, JohnMo said: The other way to it, is borrow ideas for the Adia system and simplify. Yes, absolutely. The Adia came to mind mostly because of the continuous monitoring and adapting of the heat pump output etc. as well as the additional pump. The customer wants monitoring of the system they can access and see. I'd sketched up a pipe system to first try it with the single pump and then if necessary switch to CCT with a small additional circulator should it be needed.
JohnMo Posted February 5 Author Posted February 5 So final update on commissioning. 1. Circulation pump has 3 modes AUTO/ON/OFF. In AUTO mode, the pump speed modulates and it goes off when no call for heat. In ON mode pump runs full speed all the time even when no call for heat. With thick screed and a fan coil, AUTO mode for pump does not work well, flow rate goes down to circa 6L/min and controller can't cope and under and overshoots modulation. It cannot find find the correct running mode. In OFF mode ASHP trip with flow error. Have set to ON and it seems to work well. 2. Control mode can be either dT mode, fixed speed (speed can be selected), or dT control with circulation pump in full speed fixed speed (depending on point 1. and setting to ON above). Have set to dT control. 3. Target dT is selectable, best one my heating setup is to target dT 4. dT2, 3 and 5 didn't respond as well. dT actually sits nearer 2 to 3 but controller seems happy with that. 4. Restart hysterisis, found the controller reacts badly to a premature restart, found I was chasing issues due to forcing a start early. dT4 for restart was acceptable, dT 3 lead to unstable running as the heat couldn't dump heat well. 5. Volumiser in, out or part out of system doesn't make much difference, have left in place. 6. Heat meter reads 0.6 degs higher temperatures, than the Haier controller 7. Final WC curve is 12 OAT 22 flow, -5 OAT 31 flow. 8. Controller set up to use 3rd party thermostat, this allow a 'stove on' over ride, to switch heat pump off when stove is on. It also allows a single switch to move between heat and cool on ASHP and thermostat. It also allows cooling to be temperature driven. Wiring is, from house to wiring centre - 2 core cable for winter/summer change over, wireless switch from thermostat Then from wiring centre to heat pump a 2 core cable to heat pump. No DHW connected. 4 degs outside delivering an average CoP so far today of 5, currently doing 5.2. 2
Beelbeebub Posted February 5 Posted February 5 On 01/02/2026 at 11:31, SimonD said: The issue with the radiators is that if you use standard balancing approaches, they're only correct at certain flow/pressure situations, and other than pressure independent flow regulating valves, My understanding is the Adia kit replaces the TRV and you wind the lock shield fully open ie all thr flown adjustment is via moving the TRV plunger up and down. The TRV valve isn't really designed for this but it will work. The key is very pricise control of the plunger. Adia use a. "TRV" than can move the plunger in 1% increments (sonoff do one - might even be the same unit rebadged) I tried (before I moved) controlling thr flow temp of my ufh system by using a similar approach. It worked OK, but because I was using a thermal wax valve, precise control.was very difficult. I had to pwm the power to the valve to start to melt the wax, then when the desired opening level was reached, back off the pwm so the melting stopped. The level of pwm needed to hold at a specific opening % was very variable as factors like ambient temperature, flow temperature and heat soaking of the assembly all varied. If I had access to the Adia style valves back then it would ha e been a lot easier. So for UFH I would say the flow setting valves would be wound open and the regular thermal actuators replaced with Adia units the system would then treat them as radiators.
JohnMo Posted February 5 Author Posted February 5 19 minutes ago, Beelbeebub said: So for UFH I would say the flow setting valves would be wound open and the regular thermal actuators replaced with Adia units the system would then treat them as radiators The trouble with that, is the long delay in room temp dropping and floor warming enough to recover room temperature - especially on a low temp thick screed system. But it is strange that a self learning linear actuator doesn't exist for UFH. Self balancing exist, but they don't do what you describe, they just change flow rate to maintain dT, not room temperature.
Beelbeebub Posted February 5 Posted February 5 2 hours ago, JohnMo said: The trouble with that, is the long delay in room temp dropping and floor warming enough to recover room temperature - especially on a low temp thick screed system. But it is strange that a self learning linear actuator doesn't exist for UFH. Self balancing exist, but they don't do what you describe, they just change flow rate to maintain dT, not room temperature. That was what I was toying with.
SimonD Posted February 6 Posted February 6 20 hours ago, Beelbeebub said: My understanding is the Adia kit replaces the TRV That's what I said: On 01/02/2026 at 11:31, SimonD said: The Adia unit has its own valves and room stats that feedback information to the system to understand the local climate situation at each radiator and it can also adjust flow temps and flow rates etc. to those based on this information. Nothing else on the market can do this. However, the flow temps are still global ones. 20 hours ago, Beelbeebub said: So for UFH I would say the flow setting valves would be wound open and the regular thermal actuators replaced with Adia units the system would then treat them as radiators. I think you're better off simply using weather compensation for UFH and not trying to mess with flow rates at the UFH manifold as that just adds another unecessary variable and will impact Delta P across the system, so just get rid of your actuators.
JohnMo Posted February 6 Author Posted February 6 14 minutes ago, SimonD said: another unecessary variable and will impact Delta P across the system, so just get rid of your actuators Plus additional cost and more to go wrong than needed. Did find a system than messed with flow rates rather than on/off valves, but by the time you finished, it add a £1000 just in parts. What benefit is questionable.
JohnMo Posted May 14 Author Posted May 14 On 05/02/2026 at 08:13, JohnMo said: So final update on commissioning. 1. Circulation pump has 3 modes AUTO/ON/OFF. In AUTO mode, the pump speed modulates and it goes off when no call for heat. In ON mode pump runs full speed all the time even when no call for heat. With thick screed and a fan coil, AUTO mode for pump does not work well, flow rate goes down to circa 6L/min and controller can't cope and under and overshoots modulation. It cannot find find the correct running mode. In OFF mode ASHP trip with flow error. Have set to ON and it seems to work well. 2. Control mode can be either dT mode, fixed speed (speed can be selected), or dT control with circulation pump in full speed fixed speed (depending on point 1. and setting to ON above). Have set to dT control. 3. Target dT is selectable, best one my heating setup is to target dT 4. dT2, 3 and 5 didn't respond as well. dT actually sits nearer 2 to 3 but controller seems happy with that. 4. Restart hysterisis, found the controller reacts badly to a premature restart, found I was chasing issues due to forcing a start early. dT4 for restart was acceptable, dT 3 lead to unstable running as the heat couldn't dump heat well. 5. Volumiser in, out or part out of system doesn't make much difference, have left in place. 6. Heat meter reads 0.6 degs higher temperatures, than the Haier controller 7. Final WC curve is 12 OAT 22 flow, -5 OAT 31 flow. 8. Controller set up to use 3rd party thermostat, this allow a 'stove on' over ride, to switch heat pump off when stove is on. It also allows a single switch to move between heat and cool on ASHP and thermostat. It also allows cooling to be temperature driven. Wiring is, from house to wiring centre - 2 core cable for winter/summer change over, wireless switch from thermostat Then from wiring centre to heat pump a 2 core cable to heat pump. No DHW connected. 4 degs outside delivering an average CoP so far today of 5, currently doing 5.2. Due to instability caused by heat pump hunting, I had to make some slight changes. Using the thermostat for heat pump permissive, the hysterisis was widened to 0.3 degs, the WC curve was changed also, 26 flow at 10 degs and 29 at -5. This seems to give a good balance house temperature and running stability leading to great CoP. Have run cooling also, have set target flow temperature to be 14.5, this was giving a CoP of around 7 in the warm spell a few weeks ago and zero condensation. Overall with cold spell over the last week, we got an average CoP of 5.4.
PhilT Posted May 14 Posted May 14 Haier is a very good heat pump, but unfortunately Chinese. I would rather buy closer to home. Ideal make one of the most efficient heat pumps available, the HP290, made in UK. Support british industry!!!
JohnMo Posted May 14 Author Posted May 14 1 hour ago, PhilT said: Haier is a very good heat pump, but unfortunately Chinese. I would rather buy closer to home. Ideal make one of the most efficient heat pumps available, the HP290, made in UK. Support british industry!!! True, but Ideal don't do cooling, so that was eliminated. Vaillant, just too expensive, but they do seem to perform well in real life. Mitsubishi never really liked and most don't cool. There are a few other British made heat pumps, but none of them do cooling or are stupidly expensive. My driver for a heat pump was cooling, heating is a bonus.