1 hour ago, NetTechie said:
5kW or so does seem low to me
That's because everyone is brain washed by plumbers wanting to install 30kW+ boilers.
Total heat loss for room 272, 18W/m2
Doesn't that far out. MCS start doing 2 or 3 ach which soon racks up the heat loss.
Your calculations assumes the room above is also heated, which is fine if it is. And should be with ASHP anyway.
4 hours ago, NetTechie said:
What's wrong with PIR cavity insulation?  It has a much better u value than rock wool, am I missing something?
The combination of EWI and cavity is due to the extensions and current building regs, whilst getting the external finish flush with a complete thermal envelope. I don't need to but then the extended walls will stick out on the side which I don't want.
I would also sack the PIR off as a bad job, the U value will only be good on paper - it’s a nightmare to detail correctly and any mistake will undo your hard work and then some by all the air flowing through the gaps and around the PIR sheets.
There are enough horror stories on these boards to chill your spine both literally and figuratively with regard to PIR as cavity wall insulation.
Fill with EPS bonded beads/full fill mineral wool.
Edited by IGP
Missed word
23 hours ago, NetTechie said:
the 5kW or so does seem low to me
how many people will be living in this house? 5kW is too low to keep up with family hot water demand in a property of this size. I have an oversized heat pump (11kW vs 6kW at -3degC) and it's great, I never have to worry about not being warm or getting hot water quickly. My experience, backed up by the data tables, is that oversized heat pumps are no less efficient overall, and more efficient during the coldest periods like we have been having over the last few weeks. Some headroom is essential for all sorts of reasons especially those situations where a strong recovery is needed - defrosts, power cuts, all the family off work and school with the flu, and any other situation where you need extra warmth, or the house temperature drops significantly and you need a fast recovery.
a typical family of 4, with a couple of guests staying over say once a month.
This isn't the heat pump size, it's the property heat loss. A proper heat pump design would also look at DHW cylinder and re heat times in the context of property size and occupancy numbers.
These assessment have to be considered in the round. Whilst it is sensible to consider heat pump size in relation to defrost, the coldest periods are usually very short so I would suggest the selected heat pump needs to be considered in light of the mean temperature it's going to be running at most of the time as well as its ability to cope with cold snaps. A heat pump twice the size may have poorer modulation. There's also the infrastructure costs where if you double the size of the heat pump, your pipe sizing will inevitably need to be upsized with consequential costs - a double in heat pump size can easily add £2k to the heat pump unit price itself. Input power is also likely to be higher with a bigger heat pump.
A properly sized heat pump is always going to provide the best overall efficiencies and balance with infrastructure costs.
All depends on modulation and demand. A heat pump that runs without cycling will always be more efficient than one that cycles. First a heat pump that doesn't need to cycle can run a lower temperature - mine I am looking at 5 degs cooler at 8 to 10 degs outside. That's a big chunk of CoP increase. Then there is the needless heating of big chunks of metal at the start of each cycle. So basically I don't agree, unless of cause the large heat pump can modulate down to meet the 7 to 10 Deg outside temp with undue cycling, then there is just capital expenditure and large pipework etc to accommodate it.
Cylinder heating isn't a big issue, 210L from an indicator temperature of 6 degs only takes 50 mins with a 6kW heat pump to get to 50. Heat twice per day, no real impact on house temps, one heat is likely when your asleep anyway.
I have actually found heating by immersion has barely changed overall electricity consumption. On paper ASHP heating gives me a CoP of 3, but in practice the immersion does a good job, maybe due to the long pipe runs on my install.
Our house has a calculated heat loss of 8.5 kw at -2 but we put in a 7kw HP on the basis that it would be more efficient as the days of sub zero temps are few and far between and we could always run a fan heater or switch over to an LPG boiler if the HP couldn't cope. The HP has done 100% of the space heating since september and through the few cold snaps we've had recently with temps getting down to a degree or 2 below freezing. It worked very hard and guzzled eleccy whilst it was freezing but I'm hoping that the undersizing will pay efficiency dividends for the rest of the year??
An MCS umbrella/HP supplier wanted to sell us a 12kw unit!!
The data tables published by Mitsubishi and Vaillant, as examples, an 11.2kW vs an 8.5kW Ecodan, or a 10kW vs a 7kW Vaillant Arotherm+, indicate that the extra efficiency of the larger, slower revving scroll compressors* outweighs any inefficiencies in warmer times, but why would there be any significant losses for modern oversized scroll compressors cycling at reasonable intervals of no more than once or twice per hour in the warmer months anyway? Long gone are the days of fixed speed reciprocating compressors. Isn't the oversized low modulation inefficiency paradigm something of an urban myth now?
*(friction losses rise only in direct proportion to surface area, but rise exponentially with RPM)
Nope. Fact any cycling requires a higher flow temperature to compensate. Example my install is cycling 4 degs outside, runs for 1.5 hours off for a hour. Flow temp max 29.4 degs. Overall CoP so far today is 4.55, but heat input is approx 500W higher than it should be (2.5 compared to 2kW).
Steady state running flow temp required is 23-24, also need 2kW heat input, reduced flow temp increases CoP to around 5.2 to 5.5, reduced electricity input by 500W, so should yield something like a 30% reduction in running cost, just by a using a heat pump that covers full heating range by modulation.  Apply that to 80% of the heating season it's not small change.
The data tables don't support this. For a house with a theoretical heat loss of 7kW at ΔT of 22°C, if you compare a 10kW Vaillant Arotherm+ with a 7kW version, the 10kW will give lower operating costs across a whole year, because it is so much more efficient during the coldest days, when energy use is at its highest. In the real world of (hopefully) common heat pump ownership this is likely to be even more relevant as the larger pump will be far more forgiving of less-than-optimal operation by non expert users during the coldest months of the year.
Can you share the data tables you're using please?
But I think it's also useful to have a clear understanding of what exactly you mean by oversizing. By how much, proportionally are you proposing oversizing is more efficient? At the beginning you gave an example of almost 100% (6kW - 11kW) now it's more in the order of 40%. This distinction is important I think.
Heat output is governed by mean floor temperature or mean radiator temperature. A heat pump that can modulate down to match heat energy required and not cycle, the target flow temp will always be lower as it can run steady state. So to deliver a mean flow of say 30 degs with a delivery temp of say 32 and return of 28.
A cycling ASHP no matter how minor, to deliver the same mean flow temp will have to operate a higher target flow temp to compensate for the periods when the compressor is off, so CoP takes a hit.
Also data table assume steady state running not any cycling. So do not take account of any energy wasted reheated cooled down components.
But as previously mentioned, if a oversized heat pump has a suitable depth of modulation your only hit is capital costs. Which could be in the thousands as everything becomes bigger to accommodate the increased flow rates and electrical loads.
Which aren't the dominant use case. The coldest days are the few and more average 7 degs days are the many.
It's the Czech Vaillant tables - this is a good resource to access and understand them https://energy-stats.uk/vaillant-arotherm-performance-data/#:~:text=The Czech tables give you,your system should be doing. Taking a simple example, for a nominal spec of -2°C / 7kW heat requirement, at 35°C flow temp, the 7kW model has a COP of 3.3 but the 10kW model has a COP of 4.0 - a 21% advantage. At those power levels, the 10kW compressor is revving at 50rps vs the 7kW compressor at 90rps (see my previous comment about how friction loss is affected by rotational speed compared to surface area).
In answer to the other comment, I was trying to explain, rather poorly, that my heat pump is an 11.2kW model, but the power requirement at -2°C is only 6kW. The Mitsubishi data tables show a similar picture to Vaillant, in that the next size down (8.5kW) is less efficient at similar power levels.
Edited by PhilT
What would those same comparative figures be for a more normal winter time of say 7 degrees with a load on both pumps of 3kw?
That's the avoided answer - it's cycling because it's too big. If I'm reading the numbers correctly the 10kW at 7 degs and 35 flow a min output of 5.8kW. When running cop will be 5.8, but then the impact of cycling will bring this down.
The 7kW min output at 7 degs is 3.2kW, so will still cycle but only a couple timescale day, the chart indicates a cop of 4.9. which is pretty rubbish.
By way of comparison a Haier R290
35 flow, for a max 6kW demand at -2 and at 3kW at 7 degs
A 6kW is suitable putting out 6.4kW at -2, at a CoP of 4.17, at 7 degs CoP is 5.4 and is mid range of it's output, it's min modulation at 15 degs is 1.8kW at a cop of 7.24. So should run none stop from start of heating season to the end for almost any house.
Back to the heat pump compatible fan coils….
Does anyone have any recommendations???
or with the „fan assisted radiators” (basically a fan coil so far as I can see)?
Or is running AC split system more effective? If so, I’m assuming heatpump could be downsized to offset capacity provided by AC heating/cooling
Panasonic, Daikin, I'm using a Myson iVector. You need one with adjustable water flow temp fan start permission. Some only really designed for gas boiler so have a fan start permission of say 45 degs - which is no good.
These fit in the none adjustable fan permission category, in most and are designed to allow cooling.
On 12/01/2026 at 11:56, SimonD said:
If yours is really going to be 12kW, you could also consider 2 smaller units in cascade to provide the modulation you need for the shoulder months, in particular when you have a great deal of solar gain.
Could that be designed a bit differently with one dealing with the majority of the space heating i.e. lower temp output, and the other predominantly for DHW and occasional higher temperature input to the space heating.
It depends on the control system, some of which are pretty advanced where you can specify which heat pump delivers what proportion of heating and how they share DHW demand. With Nibe systems you can even integrate ASHP with GSHP.