JohnMo Posted 2 hours ago Posted 2 hours ago 1 hour ago, NetTechie said: 5kW or so does seem low to me That's because everyone is brain washed by plumbers wanting to install 30kW+ boilers. 1 hour ago, NetTechie said: Total heat loss for room 272, 18W/m2 Doesn't that far out. MCS start doing 2 or 3 ach which soon racks up the heat loss. Your calculations assumes the room above is also heated, which is fine if it is. And should be with ASHP anyway.