EinTopaz Posted December 26, 2025 Author Posted December 26, 2025 (edited) 1 hour ago, EinTopaz said: Hey, hope you all had a lovely Christmas. Ours was lovely despite the boiler still playing up after all this. I ran it yesterday with exactly the same settings as previous, got to target of 60'c in 25mins like last time. I had to nip out to go get the family, came back 10mins later and the boiler was down at 51c again, and a really low output % on the burner. I never got to witness it happen but in the past this is because it's exceeded the target temp by > the set threshold and turned the burner off for 2mins. It's annoying I never was logging the data for that run but i'll do another today and see if I can replicate it. If it did do that then the issue from my last post where it was taking a while to modulate down despite going 5c over target...appears to be getting worse, as in its going higher and higher over target each time, i'll confirm that today. EDIT: Infact looking at the settings, I did change one thing, I raised what I thought was the threshold before it would trip out, from 6c to 10c. I think that's what this setting is for anyway in the image below. Maybe I misunderstood it. Image didn't attach, its this one, i thought that meant "target can be exceeded by this many degrees before it turns the burner off" but on reading and testing again I dont think it means that. I think that threshold is hard coded to the boiler and what this option means is "after the burner has turned off from overshooting, how far do you want the temp to drop before the burner re-ignites?" I'm fairly confident it means that now. Edited December 26, 2025 by EinTopaz
John Carroll Posted December 26, 2025 Posted December 26, 2025 (edited) 24 minutes ago, EinTopaz said: HIVE. Just using the boost function it. As far as I know it doesn’t do any modulating itself. Just on/off im running the heating again now with a lower pump speed. It hasn’t tripped off this time which is annoying. Target still 60. It over shot to 65.5 and is still at 65.5 now 20 mins after reaching target With lower pump speed the flow / return dt was closer to 25 than 20 for the most part. It’s now at 18. Or so. No way should the boiler behave like this, under steady running conditions, like above, the only reason that the flowtemperature exceeds the targettemp up to the burner trip point and recycle is when/if the minimum boiler output is > than the rad(s) demand, can you repost that thumbimage above or just take a screenshot as I can't open it. OK see it now, above, I don't think that has anything to do with the burner tripping when the flowtemp exceeds the targettemp, its to do with the anticycle time, on at least some of these WBs you have two parameters for setting the anticycle time..... a time (minutes) and a (negative temperature hysteresis) where the "longest" one wins, it goes something like this, if the time is set to say 5 minutes and the hysteresis set to (-) 6C, if, after burner cut off, the 5 minutes time has elapsed but the flowtemp hasn't reac hed targettemp -6C then the burner will not refire until the flowtemp does reach targettemp -6C, if the flowtemp had reached targettemp - 6C, then the burner will not refire until the 5 minute time has elapsed, or something like that. Most burners will trip at targettemp+5C. Edited December 26, 2025 by John Carroll 1
JohnMo Posted December 26, 2025 Posted December 26, 2025 1 hour ago, EinTopaz said: threshold before it would trip out, from 6c to 10c So that is just the restart hysterisis. Doesn't the lower pump speed, just drive a lower output of the radiators, and then drive shorter boiler cycles, as there is less to take the boiler heat away? 1
EinTopaz Posted December 26, 2025 Author Posted December 26, 2025 (edited) 2 hours ago, JohnMo said: So that is just the restart hysterisis. Doesn't the lower pump speed, just drive a lower output of the radiators, and then drive shorter boiler cycles, as there is less to take the boiler heat away? id have thought so. But looking at the data I logged side by side with the previous test. It reached target temp around about the same time. All rads felt hot. The only difference was the dt was mostly around 25 rather than 20 in the test previous. Whether that’s better or worse. I couldn’t say. edit: previous test was pump setting 6 at 400mbar, this test was pump setting 4 at 300mbar Edited December 26, 2025 by EinTopaz
EinTopaz Posted December 26, 2025 Author Posted December 26, 2025 (edited) 2 hours ago, John Carroll said: No way should the boiler behave like this, under steady running conditions, like above, the only reason that the flowtemperature exceeds the targettemp up to the burner trip point and recycle is when/if the minimum boiler output is > than the rad(s) demand, can you repost that thumbimage above or just take a screenshot as I can't open it. OK see it now, above, I don't think that has anything to do with the burner tripping when the flowtemp exceeds the targettemp, its to do with the anticycle time, on at least some of these WBs you have two parameters for setting the anticycle time..... a time (minutes) and a (negative temperature hysteresis) where the "longest" one wins, it goes something like this, if the time is set to say 5 minutes and the hysteresis set to (-) 6C, if, after burner cut off, the 5 minutes time has elapsed but the flowtemp hasn't reac hed targettemp -6C then the burner will not refire until the flowtemp does reach targettemp -6C, if the flowtemp had reached targettemp - 6C, then the burner will not refire until the 5 minute time has elapsed, or something like that. Most burners will trip at targettemp+5C. Yep makes sense, I couldn’t get it to trip this time. I have a feeling the trip is +6c on this boiler. It went up to 65.6c in today’s test. When it does trip again though I’ll be able to confirm the 3-b3 setting above. I’ve set it to -2now. So I’m expecting the behavior to be… if/when it next trips above target, it’ll drop to 58 then fire up again. Where’s at -10 I suspect it waited all the way down to 50 before firing up again. That’d explain the gap where I wasn’t monitoring yesterday. But yeah the larger concern is… why is it exceeding target by nearly 10% at all?! Perhaps I should range rate it down too to maybe like 85% max and see if that affects heat up time / and / or helps this over shooting issue. Edited December 26, 2025 by EinTopaz
marshian Posted December 26, 2025 Posted December 26, 2025 4 minutes ago, EinTopaz said: Perhaps I should range rate it down too to maybe like 85% max and see if that affects heat up time / and / or helps this over shooting issue. I wouldn't expect range rating it down to impact the overshoot unless it was RR down to less than the circuit can accept in which case the temp wouldn't over shoot for a long time - equally the house would be also slower to warm up. Plus your "85%" might be fine for now but when it's -2 outside and you want to throw a bit of heat at the house it could potentially result in a lot slower warm up. IMO the only time you can be justified in RR a boiler is where the boiler capacity is massively in excess of the house heat loss and even then with a scheduled heating (or as and when you think it needs it in your case) you are going to need plenty in reserve to bring the house up to target temp so probably not much point RR'ing the boiler
John Carroll Posted December 26, 2025 Posted December 26, 2025 11 minutes ago, EinTopaz said: Yep makes sense, I couldn’t get it to trip this time. I have a feeling the trip is +6c on this boiler. It went up to 65.6c in today’s test. When it does trip again though I’ll be able to confirm the 3-b3 setting above. I’ve set it to -2now. So I’m expecting the behavior to be… if/when it next trips above target, it’ll drop to 58 then fire up again. Where’s at -10 I suspect it waited all the way down to 50 before firing up again. That’d explain the gap where I wasn’t monitoring yesterday. But yeah the larger concern is… why is it exceeding target by nearly 10% at all?! Perhaps I should range rate it down too to maybe like 85% max and see if that affects heat up time / and / or helps this over shooting issue. Can you post a E link to a exact copy of your paper MIs?.
marshian Posted December 26, 2025 Posted December 26, 2025 20 minutes ago, EinTopaz said: id have thought so. But looking at the data I logged side by side with the previous test. It reached target temp around about the same time. All rads felt hot. The only difference was the dt was mostly around 25 rather than 20 in the test previous. Whether that’s better or worse. I couldn’t say. I think I've said this before - be careful if you end up with a DT greater than 20 Deg at the boiler most modern condensing boilers really don't like this much and will do all sorts of things to try and protect themselves. If you are getting a wide DT with a slower pump speed then you could probably lower the flow temp to tighten the DT (at the expense of slightly cooler rads but I wouldn't think the difference in rad temp between 60 and say 55 would be detectable by touch)
EinTopaz Posted December 26, 2025 Author Posted December 26, 2025 23 minutes ago, John Carroll said: Can you post a E link to a exact copy of your paper MIs?. https://www.worcester-bosch.co.uk/support/literature/download/release/6720883858/45568 Goes into the settings from around Page 51. 1
SimonD Posted December 26, 2025 Posted December 26, 2025 29 minutes ago, EinTopaz said: But yeah the larger concern is… why is it exceeding target by nearly 10% at all?! The boiler is essentially dumb and slow to respond. It measures just flow temperature so by the time the return temperature has reached the point at which flow temperature increases the heat is already in the system, so there's always going to be some intertia. It's not sensible from a design perspective to make the system respond too rapidly as that affects operating efficiencies and can cause various unwanted attempted control oscillations within the system. The real issue here is that the focus at the moment is only on the boiler and not your controls together with your boiler. At present, even though they might call it a smart thermostat, it's actually pretty dumb because the Hive only provides relay control of your heating. To get this boiler modulating properly in relation to room temperature or outside temperature you need some decent controls that actually modulate the boiler - so either weather compensation, or if you want load compensation, something like the Worcester Easy Control which uses EMC Bus to communicate with the boiler. You can use Opentherm to do modulation, but only with a third party translation kit that you need to get from Europe. Get yourself some proper controls and the boiler will behave much better and can be refined from there.
marshian Posted December 26, 2025 Posted December 26, 2025 4 minutes ago, SimonD said: The real issue here is that the focus at the moment is only on the boiler and not your controls together with your boiler. At present, even though they might call it a smart thermostat, it's actually pretty dumb because the Hive only provides relay control of your heating. To get this boiler modulating properly in relation to room temperature or outside temperature you need some decent controls that actually modulate the boiler - so either weather compensation, or if you want load compensation, something like the Worcester Easy Control which uses EMC Bus to communicate with the boiler. You can use Opentherm to do modulation, but only with a third party translation kit that you need to get from Europe. Get yourself some proper controls and the boiler will behave much better and can be refined from there. The issue there is the dumb controls are all @EinTopaz requires for the way he uses the heating system
John Carroll Posted December 26, 2025 Posted December 26, 2025 3 hours ago, EinTopaz said: Target still 60. It over shot to 65.5 and is still at 65.5 now 20 mins after reaching target It doesn't matter what kind of fancy controls or otherwise it may have, maintaining a alleged targettemp+5.5C for 20 minutes smacks surely of some boiler control problem, especially since the boiler minimum output is way below the steady state rad demand.
EinTopaz Posted December 26, 2025 Author Posted December 26, 2025 What would be reasonable next steps then guys? get WB out again and show them that it's going way beyond target and fingers crossed I can get it to trip out on the day? As it stands they have swapped out the pump, sensors, Hex, and they did the board last Monday too. Not sure what else to do other than keep running it with slower pump speeds and seeing if that fixes anything. I have noticed a whole bunch of weird inconsistencies in the manual, particularly in the L2 hydraulic settings, the settings on my boiler are not consistent with the ones in the manual. But WB told me because i simply have flow/return/Gas and no cylinder or diverter etc, then it doesnt really matter about L2.... again not sure if im being palmed off there again or they're right on that one.
marshian Posted December 26, 2025 Posted December 26, 2025 3 minutes ago, EinTopaz said: What would be reasonable next steps then guys? get WB out again and show them that it's going way beyond target and fingers crossed I can get it to trip out on the day? As it stands they have swapped out the pump, sensors, Hex, and they did the board last Monday too. Not sure what else to do other than keep running it with slower pump speeds and seeing if that fixes anything. I have noticed a whole bunch of weird inconsistencies in the manual, particularly in the L2 hydraulic settings, the settings on my boiler are not consistent with the ones in the manual. But WB told me because i simply have flow/return/Gas and no cylinder or diverter etc, then it doesnt really matter about L2.... again not sure if im being palmed off there again or they're right on that one. What are your L2 settings? I would have thought it was pretty important to have the correct parameters?? 1
John Carroll Posted December 27, 2025 Posted December 27, 2025 I would suggest, under steady state running, get the flow/return dT to less than 20C, say 18C, assuming the target & flow temps are equal, take readings, then slowly decrease the pump speed, (you can use your max clamping method to achieve this), the dT will keep rising, see if the flowtemp starts to exceed the target temp as the dT increases, keep reducing the pump speed until the flowtemp exceeds the target temp by 5.5C (trip point?), note all readings. Before doing, (if) I would increase the anti cycle time to 5/6 minutes again. 1
John Carroll Posted December 29, 2025 Posted December 29, 2025 @EinTopaz, any update on that pesky boiler of yours? 1
EinTopaz Posted December 29, 2025 Author Posted December 29, 2025 10 hours ago, John Carroll said: @EinTopaz, any update on that pesky boiler of yours? Hey guys, sorry ive been away for a few days. Yes one more update, i've been running it at different pump speeds to see which I like best. First set of data logging I tried was pump speed 6 (400mbar constant pressure). This was the setting it tripped on on Xmas day. I since tried pump speed 4 (300mbar constant pressure) it didn't trip out on this setting and didn't seem to take much longer to heat the rads up. Though the dt was 5c greater for most of the operation compared to pump speed 6. Yesterday I tried pump speed 3 (250mbar constant pressure), the flow still got to 60c in 25mins, but the radiators did take notably longer to get hot. Like a good 10-15mins longer, and even more so for the triple column ones. It did not trip out on this setting either, got to 65.5c, and modulated down at a slightly quicker rate than the tests previous. So it is still overshooting target massively, and sometimes tripping out, but mostly taking 30-45mins of time to get from its overshot of target, back to target. With regards to the L2 settings, it's a bit of a saga. I'll make a separate post of it, because its a head scratcher. Though TLDR is i've tried all the obvious configurations in there and it hasnt appeared to make too much of a difference. Will post below.
EinTopaz Posted December 29, 2025 Author Posted December 29, 2025 On 26/12/2025 at 18:23, marshian said: What are your L2 settings? I would have thought it was pretty important to have the correct parameters?? Ok, so First things first, when The boiler is set back to factory defaults, my defaults are not the same as what's in the manual. My defaults are 2-A1 = 0 2-A2 = 1 In this configuration I don't get the option for 2-A3 or 2-A4. 2-A1 makes sense, I don't have a LLH. But 2-A2 have manually set to 0 because i dont have any hot water linked up to this boiler, no cylinder, no DHW, just central heating. When I set 2-A2 to 0, Magically I get the option then of 2-A3 being available. But it only gives me the options 0 and 1 in there. Which is completely inconsistent with the manual. in the manual there isnt even an option for setting "1" in 2-A3 Also, in 2-A2, i get the options of 0, 1 or 3..... which again is inconsistent with the manual, no idea what option 3 is in 2-A2 2-A4, no matter what I set in 2-A1, A2 or A3.... I can never get 2-A4 to appear, so I simply ignore it. SO yes, its a complete and utter mess. WB have told me to just try different configurations with it. And I have. But its never made any sense to me any of this. I've tried these configs below A1 - 0 A2 - 1 ------ A1- 0 A2 - 0 A3 - 0 ------ A1-0 A2-0 A3-1 None seemed to make a massive difference. 1
John Carroll Posted December 29, 2025 Posted December 29, 2025 Irrespective of any of those pump settings then, as stated previously, (especially) under steady state conditions the target&flow temperatures should be almost identical, as long as the minimum boiler output is less than the heat (rad) output. The flow/return dT increases (correctly) with decreasing pump head, does this have any effect on the targettemp/flowtemp dT?. You said, I think, in one post that the boiler HEX only was replaced but a (the) card wasn't because it was for a older type boiler but in a later post you said, again I think, that a card was replaced??. Did WB advise you to try these different pump settings after the senior engineers visit??. I certainly wouldn't be happy with the above "performance" so back to WB I would go.
John Carroll Posted December 30, 2025 Posted December 30, 2025 13 hours ago, EinTopaz said: Ok, so First things first, when The boiler is set back to factory defaults, my defaults are not the same as what's in the manual. My defaults are 2-A1 = 0 2-A2 = 1 In this configuration I don't get the option for 2-A3 or 2-A4. 2-A1 makes sense, I don't have a LLH. But 2-A2 have manually set to 0 because i dont have any hot water linked up to this boiler, no cylinder, no DHW, just central heating. When I set 2-A2 to 0, Magically I get the option then of 2-A3 being available. But it only gives me the options 0 and 1 in there. Which is completely inconsistent with the manual. in the manual there isnt even an option for setting "1" in 2-A3 Also, in 2-A2, i get the options of 0, 1 or 3..... which again is inconsistent with the manual, no idea what option 3 is in 2-A2 2-A4, no matter what I set in 2-A1, A2 or A3.... I can never get 2-A4 to appear, so I simply ignore it. SO yes, its a complete and utter mess. WB have told me to just try different configurations with it. And I have. But its never made any sense to me any of this. I've tried these configs below A1 - 0 A2 - 1 ------ A1- 0 A2 - 0 A3 - 0 ------ A1-0 A2-0 A3-1 None seemed to make a massive difference. Can, if you have "pump setting proportional to thermal output" take a few sets of readings in this mode, to see what effect it has, if any, on the targettemp/flowtemp dT. 1
EinTopaz Posted December 30, 2025 Author Posted December 30, 2025 2 hours ago, John Carroll said: Can, if you have "pump setting proportional to thermal output" take a few sets of readings in this mode, to see what effect it has, if any, on the targettemp/flowtemp dT. Yep, I’m trying it on pump 5 for today’s tests and have rated the boiler down to 90% just to see if it helps the over shooting / taking ages to modulate down…. will do pump 0 “proportional” tomorrow. though looking at the manual again I wonder if there’s an error here. In the diagram it clearly shows that the “max” pump rate (A) is far higher than pump setting 6. Though when I ran it on 6 last time. The pump % output constantly read at 100%. So it’s just another thing I’m confused by honestly. 400mbar and 700mbar is a huuuge difference if we’re to believe this diagram.
John Carroll Posted December 30, 2025 Posted December 30, 2025 (edited) I have a fair idea I think of how those curves "work" A (&B) are just the installed pump curves, A being the one at 100% speed. All the dotted lines are the pump head remaining (residual) after the head loss through the boiler, mainly the HEX, so we'll call it that, HEX loss = boiler loss and RAD (+pipes etc) loss = residual head required or remaining. A 36kW boiler at 20C flow/returm dT requires a flowrate of 25.8LPM,1548LPH, so a flowrate of 25LPM, 1500LPH will give a dT of 20C with the boiler at 34.9kW output so we'll use that 1500LPH number. You can see that the pump head at 1500LPH is 650mb and the residual head (on 6,) is 400mb so HEX loss=650-400,250mb and the Rad loss is 400mb. If you use your "average" of 20.0LPM,1200LPH then, by calculation, the HEX loss is now, 250*sq(1200/1500), 160mb and the RAD loss is 400*sq(1200/1500), 256mb, so total (pump) head required is 160+256, 416mb (4.16M) the pump will deliver 1500LPH at 6.50M so at the required head of 4.16M should reduce its speed to ~ 100*sqroot(4.16/6.5), 80%, I havn't the exact pump curve but the above is the gist of how I think this works, of course if your RADs/pipework has sludge then the pump may still continue to run at 100% Edited December 30, 2025 by John Carroll
John Carroll Posted December 30, 2025 Posted December 30, 2025 I have a feeling that it all revolves around the flowtemperature measurement or what the boiler's PCB perceives the actual flowtemp is, even though the boiler does eventually return to "normal" and your measured readings correspond to the displayed reading. If, for whatever reason, the flowtemp is sometimes perceived to be as much as 5C below the targettemp then the burner output will be outputting as much as +7.53kW (21%) more than that required to satisfy the actual targettemp, even a error of 2/3C is a substantial increase in firing of ~ 3.8kW (10.6%).
John Carroll Posted 18 hours ago Posted 18 hours ago (edited) On 30/12/2025 at 10:08, EinTopaz said: Yep, I’m trying it on pump 5 for today’s tests and have rated the boiler down to 90% just to see if it helps the over shooting / taking ages to modulate down…. will do pump 0 “proportional” tomorrow. though looking at the manual again I wonder if there’s an error here. In the diagram it clearly shows that the “max” pump rate (A) is far higher than pump setting 6. Though when I ran it on 6 last time. The pump % output constantly read at 100%. So it’s just another thing I’m confused by honestly. 400mbar and 700mbar is a huuuge difference if we’re to believe this diagram. Happy New Year to all. The max rad output seems to be ~ 18kW with the present target/flow temp of 60C and because the boiler isn't range rated then at times it is inputting 15kW more than required which will lead to overshoot but IMO should still modulate down before targettemp+6C and burner trip? is reached, maybe range rate the boiler to say 20kW, 56% and see what effect this has on heat up from cold and overshoot temp. Eventually, if required, to speed up the heating period from cold, you can keep increasing the range rating until it doesn't overshoot by say targettemp+4C and leave it like that. I would also leave the pump speed high at 90/100%. Edited 18 hours ago by John Carroll
EinTopaz Posted 15 hours ago Author Posted 15 hours ago (edited) 2 hours ago, John Carroll said: Happy New Year to all. The max rad output seems to be ~ 18kW with the present target/flow temp of 60C and because the boiler isn't range rated then at times it is inputting 15kW more than required which will lead to overshoot but IMO should still modulate down before targettemp+6C and burner trip? is reached, maybe range rate the boiler to say 20kW, 56% and see what effect this has on heat up from cold and overshoot temp. Eventually, if required, to speed up the heating period from cold, you can keep increasing the range rating until it doesn't overshoot by say targettemp+4C and leave it like that. I would also leave the pump speed high at 90/100%. I’ll give that a try. But I know already from testing that the 90% range rated test I tried yesterday took 5 mins longer to get To target. Still overshot but only by 3.6c this time. But then weirdly never did make its way down to 60. It settled at 62.5 with a modulated output of 54% I assume the higher modulated % was because it was a colder day and the pipes are in the subfloor with the ventilated air bricks etc. so assume it was just working a little harder to keep them at temp. Or above! EDT ^ this was all on pump setting 5, which was essentially locking it at 87% pump speed Edited 15 hours ago by EinTopaz