1 hour ago, SimonD said:

 

I think it's worth testing pump setting 0 to see what happens. Who knows, it may not work at all but if it were me, I'd like to see variation in flow rate proportional to burner and DT and then see what happens through the system. 

 

It was, on this very boiler, but in another Site/Thread, "Bypass Valve" in DIYnot.com, the pump speed fell to 30% which by my calcs meant a flowrate of 6.3LPM at a head of only 0.35M, shared through 11 Type22 & 4 Triple rads.

This was before the boiler HEX was changed, so yes, would be interesting to see a full set of data if tried again.

Edited by John Carroll

  • 2 weeks later...
  • Replies 233
  • Views 21.1k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • I have to say, John, that I try to avoid WB boilers like the plague. I think their designs are awful, I hate working on them and I would definitely never install one (although I have installed one, on

  • Readings boiler / flow  target 65 boiler / flow actual 66.5 return actual 52.3 burner output 54% pump output 87%   Strange, but the flowrate has hardly changed from

  • Happy Christmas to all.   I have a 20kW oil fired boiler that fires either flat out or not at all, with ~ 15kw of rads & ~ 85L system contents, and a circ pump flowrate of a measured (sm

Posted Images

  • Author
On 25/02/2026 at 20:55, SimonD said:

I wonder what happens when these things are installed with weather compensation, or maybe nobody ever does and they build these things for relay controls only for the UK market, just like other manufacturers like to reduce specs for us?

 

Hey all sorry was away for a bit on holiday... lovely not having to stress about heating when you're in a warm country eh. 

I ran some more tests and logged the data. I may have mentioned already but I have a mix of type 22 and triple column rads in this system too. Those triple column rads always take a lot longer to warm up because of the amount of water content in them, its maybe 70L just in those as they're huge. So i wanted to do an A/B test with all rads on Vs all rads on bar the triple column ones. To see if it would affect the ramp up time by much. My thinking was, if the heat up time is very similar then the issue is likely that the pipes in the subfloor are losing lots of heat (as they're maybe 50-60meters of piping down there in total). 

Also taking your advice from the forum I ran both of the tests in pump setting 0 (proportional to burner mode), in which the range min was set to 60% and the max set to 100% Test A was all rads on, Test B was all rads on Bar the triple column ones. Note: i've set the target to 68c now rather than 60 just to see if it helped speed the ramp up too.

 

image.thumb.png.e84d88e2268993f7615a2b39cb685fb3.png

 

image.thumb.png.0c53a3c0924967a84a0c7ff3003d31b2.png

 

On test B it did heat up quicker, but also tripped the burner out at 27minute mark....I imagine because without the triple column rads TRV's on, it was just too much heat for the system.

 

 


I've got a few other things i want to try in my next set of runs.... but before I speak to them, what do you think of the above? On Test A i'm still a little baffled that the boiler is reacting so slowly to modulating down. 

 

Edited by EinTopaz

22 hours ago, EinTopaz said:

I've got a few other things i want to try in my next set of runs.... but before I speak to them, what do you think of the above? On Test A i'm still a little baffled that the boiler is reacting so slowly to modulating down. 

 

I'm not that surprised. Sometimes it's better to have a system that is not too reactive and reactivity can significantly reduce efficiency. I think the figures in test A are okay. But I also caution against focusing too much on just the boiler temperatures and consider radiator temperatures and room temperature changes in relation to room volume. That way you'll properly know if the whole system you've got is in the right ball park. What are your expectations of what your heating system should be doing - specifically in regard to heating the space?

 

I'm still of the belief that to get this thing running properly, you need to add some decent modulating controls, like weather compensation - but that, I know, is not what you want.

 

 

  • Author
3 hours ago, SimonD said:

 

I'm not that surprised. Sometimes it's better to have a system that is not too reactive and reactivity can significantly reduce efficiency. I think the figures in test A are okay. But I also caution against focusing too much on just the boiler temperatures and consider radiator temperatures and room temperature changes in relation to room volume. That way you'll properly know if the whole system you've got is in the right ball park. What are your expectations of what your heating system should be doing - specifically in regard to heating the space?

 

I'm still of the belief that to get this thing running properly, you need to add some decent modulating controls, like weather compensation - but that, I know, is not what you want.

 

 

That's fair re: boilers not being too reactive, but it does seem awful slow to react this one. Like it carries on way past the target at nearly full strength output. I'll do a longer test next time to show you but it really does take a while for it to come back down to target.  That doesn't seem efficient to me and means it does sometimes turn the burner off if it exceeds the target too much. None of that seems like its doing what it should to me. Maybe 10minutes to react and load its self down would be fine, but in my case its way longer.

My expectations and frustrations are two fold with this boiler, they were three until the hex got fixed, now just the two. They are - I want the rads to get hot sooner, and, I want the thing to run efficiently and modulate down correctly. (the overshooting stuff above bothers me regarding efficiency). If it fixes both the frustrations; I am prepared to put the boiler in the bin if I need to and go for a larger Vaillant conventional type. This one is 35kw and doing 28kw-ish of rads at T50

Perfomance wise, i want it run more like the other boiler I have at this property. I'll put the data log of that one below. Its 41kw CDI conventional (with grundfos 25-55 pump) and powers around 22kw of rads. i've no issues with that boiler. It warms up fast, Runs exactly as I want it to. im sure it is overpowered for that system but again, no issues with overshooting or anything like that. Just works (tm). I wish the greenstar 8000 life in question here ran more like that.

 

image.thumb.png.3807139a0fdd0c09232c1024e9e73a00.png

1 hour ago, EinTopaz said:

That doesn't seem efficient to me

Sorry confused - the way you want to operate isn't efficient anyway. So are you fussed about efficiency? You seem willing to spend thousands to get a poor efficiency system anyway. I'm not even convinced you need you need two boilers, but hay ho.

 

I keep looking at this thread and I shouldn't.

  • Author
1 hour ago, JohnMo said:

Sorry confused - the way you want to operate isn't efficient anyway. So are you fussed about efficiency? You seem willing to spend thousands to get a poor efficiency system anyway. I'm not even convinced you need you need two boilers, but hay ho.

 

I keep looking at this thread and I shouldn't.

 

I'll spend thousands for a thing to function correctly and me not have to fanny around with it, yes. In simple terms it takes too long to heat up my system and its not running cheaply enough to outweigh the time i have to wait for it to heat up. Id rather go for a commercial boiler at this point.

it was on one system at one point but its been extended many times now. I cant be bothered linking it all back together now, rather have 2 boilers. I just need my downstairs one to be less shit. Incase I hadn't mentioned 🙂 

On 08/03/2026 at 13:24, EinTopaz said:

 

Hey all sorry was away for a bit on holiday... lovely not having to stress about heating when you're in a warm country eh. 

I ran some more tests and logged the data. I may have mentioned already but I have a mix of type 22 and triple column rads in this system too. Those triple column rads always take a lot longer to warm up because of the amount of water content in them, its maybe 70L just in those as they're huge. So i wanted to do an A/B test with all rads on Vs all rads on bar the triple column ones. To see if it would affect the ramp up time by much. My thinking was, if the heat up time is very similar then the issue is likely that the pipes in the subfloor are losing lots of heat (as they're maybe 50-60meters of piping down there in total). 

Also taking your advice from the forum I ran both of the tests in pump setting 0 (proportional to burner mode), in which the range min was set to 60% and the max set to 100% Test A was all rads on, Test B was all rads on Bar the triple column ones. Note: i've set the target to 68c now rather than 60 just to see if it helped speed the ramp up too.

 

image.thumb.png.e84d88e2268993f7615a2b39cb685fb3.png

 

image.thumb.png.0c53a3c0924967a84a0c7ff3003d31b2.png

 

On test B it did heat up quicker, but also tripped the burner out at 27minute mark....I imagine because without the triple column rads TRV's on, it was just too much heat for the system.

 

 


I've got a few other things i want to try in my next set of runs.... but before I speak to them, what do you think of the above? On Test A i'm still a little baffled that the boiler is reacting so slowly to modulating down. 

 

The boiler's behaviour in reaching 100% output seems quite reasonable IMO, 5 minutes to reach 75% and a further 5 minutes to reach 100%, my daughters Vokera Vision 20S is pretty similar except, as it states, in the MIs.... it takes another 10 minutes to increase the output from 75% to 100%., it probably doesn't take quite 5 minutes to reach 75% but ~ 2 or 3, not a whole not different. But it certainly behaves much differently once the targettemp is reached, it immediately ramps down to maintain the targettemp very accurately, if one zone is switched off, the flowtemp might rise by a max of 2C and then returns to exactly its targettemp. This would be my bone of contention with WB. It shouldn't matter where the "flow" temperature is being measured, the controller is looking at this temperature and should modulate the boiler output to maintain the targettemp.

 

What is the offset now between the Boiler displayed flowtemperature and the targettemp? and how does your temperature sensor, (if installed),  compare with the boiler displayed one?.

 

If you change the targettemp up or down by say 3C, is the boiler sluggish in responding and is there overshoot and undershoot?.

 

I seem to remember that before the HEX replacement that the targettemp and boler displayed flotemp were withim a degree or so even though way higher than the actual flowtemp?.

 

Edited by John Carroll

  • Author
8 hours ago, John Carroll said:

The boiler's behaviour in reaching 100% output seems quite reasonable IMO, 5 minutes to reach 75% and a further 5 minutes to reach 100%, my daughters Vokera Vision 20S is pretty similar except, as it states, in the MIs.... it takes another 10 minutes to increase the output from 75% to 100%., it probably doesn't take quite 5 minutes to reach 75% but ~ 2 or 3, not a whole not different.

Yep, from monitoring i think this is just standard behaviour from modern boilers. Though as part of the test yesterday I did try setting the burner min output% to 45% (default is 14%). It did shave a few minutes off reaching 60c, but i think it also caused further problems with the boiler not being able to properly modulate down once it had hit/exceeded target temp. I need to confirm that today with another test, may've been a coincedence.

 

8 hours ago, John Carroll said:

But it certainly behaves much differently once the targettemp is reached, it immediately ramps down to maintain the targettemp very accurately, if one zone is switched off, the flowtemp might rise by a max of 2C and then returns to exactly its targettemp. This would be my bone of contention with WB

 

Yes exactly, thats the behaviour i'd expect to see. If the system doesnt demand as much power as the boiler can give, ie if some of the TRV temps get hit and the radiators turn off, i'd expect the boiler to modulate down, not just carry on and overshoot the temp at 100% output. That just seems ignorant and primitive to me, I agree with you that this doesn't seem like its part of normal programming, this boiler doesnt have a return temp that i can monitor on the LCD, but it must have a sensor inside thats being checked to determine the modulation beyond the flow temp? From memory they have changed a couple sensors already but that was to try and fix the massive difference we had back when the HEX was screwed. Maybe theres more sensors on there that need to swap thats causing this?

 

8 hours ago, John Carroll said:

What is the offset now between the Boiler displayed flowtemperature and the targettemp? and how does your temperature sensor, (if installed),  compare with the boiler displayed one?.

When i run it now with all the radiators fully on, ive got the target set at 68c, it will overshoot this by 4c, very occasionally it will overshoot it by more and turn the burner off. But that's more rare when all the radiators TRVS are on. When it doesn't trip off, as mentioned previously it will take as long as 30-45 mins to come back down to target. Modulating verrrry slowly as it goes. 

 

My own sensor is now 1C difference to the boiler LCD display. 

 

 

8 hours ago, John Carroll said:

If you change the targettemp up or down by say 3C, is the boiler sluggish in responding and is there overshoot and undershoot?.

 

That's a good question, do you mean if i change it once the target temp has been reached and everything is stable? i'll give that a try. From memory i dont think it reacts at all to this.

 

8 hours ago, John Carroll said:

I seem to remember that before the HEX replacement that the targettemp and boiler displayed flotemp were withim a degree or so even though way higher than the actual flowtemp?.

 

Before hex replacement i cant recall, I feel it was still overshooting back then.... it must've been as it was going quite high on the LCD display, why do you ask? do you suspect theres been a problem since they swapped the hex and thats causing the overshooting? 

Edited by EinTopaz

1 hour ago, EinTopaz said:

Yep, from monitoring i think this is just standard behaviour from modern boilers. Though as part of the test yesterday I did try setting the burner min output% to 45% (default is 14%). It did shave a few minutes off reaching 60c, but i think it also caused further problems with the boiler not being able to properly modulate down once it had hit/exceeded target temp. I need to confirm that today with another test, may've been a coincedence.

I would never increase the minimum output, 14%, the default = 5.0kW, your total heat demand might very occasionally fall below this leading to burner cutout and boiler recycling.

 

 

Yes exactly, thats the behaviour i'd expect to see. If the system doesnt demand as much power as the boiler can give, ie if some of the TRV temps get hit and the radiators turn off, i'd expect the boiler to modulate down, not just carry on and overshoot the temp at 100% output. That just seems ignorant and primitive to me, I agree with you that this doesn't seem like its part of normal programming, this boiler doesnt have a return temp that i can monitor on the LCD, but it must have a sensor inside thats being checked to determine the modulation beyond the flow temp? From memory they have changed a couple sensors already but that was to try and fix the massive difference we had back when the HEX was screwed. Maybe theres more sensors on there that need to swap thats causing this?

You only have to look at your other boiler's data to show how any boiler should and does control/modulate, this boiler, targettemp 55C, only overshot by 1.3C to 56.3C, it then reduced the flowtemp to 56.3C and the average flowtemp averaged 55.42C over the next 25 minutes or so, a difference of 0.42C from the targettemp.

 

When i run it now with all the radiators fully on, ive got the target set at 68c, it will overshoot this by 4c, very occasionally it will overshoot it by more and turn the burner off. But that's more rare when all the radiators TRVS are on. When it doesn't trip off, as mentioned previously it will take as long as 30-45 mins to come back down to target. Modulating verrrry slowly as it goes. 

No good, not acceptable.

 

My own sensor is now 1C difference to the boiler LCD display. 
 

That's a good question, do you mean if i change it once the target temp has been reached and everything is stable? i'll give that a try. From memory i dont think it reacts at all to this.

Yes, and it should, next time the other boiler is running steadily and stable, do this test also on this boiler and note or film both boilers and show it to WB.

 

 

Before hex replacement i cant recall, I feel it was still overshooting back then.... it must've been as it was going quite high on the LCD display, why do you ask? do you suspect theres been a problem since they swapped the hex and thats causing the overshooting? 

I'd say, based on the (your) above, that  the problem has been there before renewing the HEX, but hard to imagine that all these boilers are behaving in this manner.

 

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.