Crofter Posted November 18, 2025 Posted November 18, 2025 OK I'm not a total newbie, I've designed and built a couple of off grid systems. But this is different. I've got a small all-electric newly built property which needs essentially no heating at all through the summer months. There's a 200l direct UVC in there which currently heats up from an E7 tariff. I'm considering installing a PV system with a diverter, primarily aimed at covering that DHW demand. I'm going to assume that I need about 8kwh/day to heat the tank (incoming 10°, outgoing 60°, two seven minute showers at 10l/min). As it's a holiday let, it's primarily occupied from April-September inclusive. So I'm looking to design a system that can deliver close to 8kwh/day over that period. What I've come up with so far is: 6x 500w panels (£450) 3kw inverter (£300) Diverter (£300) Plus obviously mounting hardware, cabling, isolators, fuses, etc. So I should be looking at not too much north of £1k, plus any labour and fees. I'm considering getting it signed off by a qualified but non MCS sparky. I believe I still need DNO approval though? If I go down this route, would there be anything wrong with using secondhand gear? The panels would probably be either ground mounted, or on a south facing gable (or possibly a combination of both). Playing around with PVGIS, I've learned that my optimal angle is 39° for total annual output, and 74° for the best winter production. Somewhere in-between would give me the greatest number of months which hit my target of 240kwh. All academic if I end up putting panels on the gable, of course. I could think about roof mount as well, but the roof is E-W. It's corrugated steel over timber battens. Anyway like I say, I'm new to this, I might be overlooking something, or overthinking things. Feedback and suggestions would be much appreciated.
Dillsue Posted November 18, 2025 Posted November 18, 2025 With a 3kw G98 certified inverter you don't need to ask permission from your DNO, just tell them afterwards, but...... Maybe I'm thinking of someone else but is this Buildings supply piggy backed off another buildings supply?? That might impact DNO permissions. Nothing wrong with secondhand gear but you cant legitimately use an old inverter in a new installation without the inverter complying with current standards.
ProDave Posted November 18, 2025 Posted November 18, 2025 For your DNO sign off, with a G98 inverter you will need to fill in a form and provide some drawings including location of equipment and a wiring diagram. as well as an Electrical Installation Certificate from the sparky. Make sure the sparky can provide the wiring diagram as well as the EIC. for G98 you notify the DNO afterwards. The G98 application is linked to your electricity meter's MPAN number. If as hinted both properties share a single supply and meter, you will only be allowed one G98 application. If you want solar PV for both, you might have to get a second supply installed so each building has their own supply and meter. If buying secong hand inverters, make SURE they are not so old that they pre date the present G98/G99/G100 types. 1
Crofter Posted November 18, 2025 Author Posted November 18, 2025 Thanks both. The property has a completely separate supply with an E7 meter. Random example of a secondhand inverter (hope this isn't in breach of any forum rules, I have no idea who the seller is) https://www.ebay.co.uk/itm/306596178881?_skw=grid+tied+inverter&itmmeta=01KABNM23RJZP4ZYC7R6XJWNQR&hash=item47628e6bc1%3Ag%3Alq0AAeSwWNRpG1Si&itmprp=enc%3AAQAKAAAA8FkggFvd1GGDu0w3yXCmi1eDtXN4tIIR6UuOxc%2FS0lIttlUJ0Z7JI8%2BWN6xaqUGAYWWoFtcYpBGviBiu9ELNmvH7YU6aU%2BaBBT3OZ%2FmvQ9XFTDopJQNPu%2FXvJL4716s1gHyn4Jyz6PFu8rGn20ohVw77ZkKLTwxBZt5kHTHuWr7Qh%2FcgOvxjp1dsXSnEoQCVFTtCUgMFnngx0DlpPVO%2FicepK6nrX7HcO6uE76fYuBhxxJttvCDWjrPDtAPGSw%2FcIsMhSKztfxfv0y4X0m4sgwtWgEPTaAC1c37eP83GP%2B0D4lF3%2BWqs%2FbFCZ9nR67Etlw%3D%3D|tkp%3ABk9SR5ai0PXSZg&LH_BIN=1 Likewise the diverters seem to go for about half price secondhand.
JohnMo Posted November 18, 2025 Posted November 18, 2025 2 hours ago, Crofter said: would there be anything wrong with using secondhand gear Nothing be careful with price, current adverts look more expensive than new for panels. I have a fully second hand system and bought a inverter the same as the the one above (just slightly bigger) second hand, no issues. cool energy do a diverter, it will drive two immersions one after the other. Other brand tags for the same item, selling lots cheaper, so do an image search - may have to wait for it come from China.
ProDave Posted November 18, 2025 Posted November 18, 2025 36 minutes ago, Crofter said: Thanks both. The property has a completely separate supply with an E7 meter. Random example of a secondhand inverter (hope this isn't in breach of any forum rules, I have no idea who the seller is) https://www.ebay.co.uk/itm/306596178881?_skw=grid+tied+inverter&itmmeta=01KABNM23RJZP4ZYC7R6XJWNQR&hash=item47628e6bc1%3Ag%3Alq0AAeSwWNRpG1Si&itmprp=enc%3AAQAKAAAA8FkggFvd1GGDu0w3yXCmi1eDtXN4tIIR6UuOxc%2FS0lIttlUJ0Z7JI8%2BWN6xaqUGAYWWoFtcYpBGviBiu9ELNmvH7YU6aU%2BaBBT3OZ%2FmvQ9XFTDopJQNPu%2FXvJL4716s1gHyn4Jyz6PFu8rGn20ohVw77ZkKLTwxBZt5kHTHuWr7Qh%2FcgOvxjp1dsXSnEoQCVFTtCUgMFnngx0DlpPVO%2FicepK6nrX7HcO6uE76fYuBhxxJttvCDWjrPDtAPGSw%2FcIsMhSKztfxfv0y4X0m4sgwtWgEPTaAC1c37eP83GP%2B0D4lF3%2BWqs%2FbFCZ9nR67Etlw%3D%3D|tkp%3ABk9SR5ai0PXSZg&LH_BIN=1 Likewise the diverters seem to go for about half price secondhand. Check with the seller it is G98 approved, It should be at only 2 years old. Susprised they don't state that, Only 1 input so all panels need to be on one string. 2 inputs is better if you want panels on different facing roof elevations etc.
Crofter Posted November 18, 2025 Author Posted November 18, 2025 25 minutes ago, JohnMo said: Nothing be careful with price, current adverts look more expensive than new for panels. I have a fully second hand system and bought a inverter the same as the the one above (just slightly bigger) second hand, no issues. cool energy do a diverter, it will drive two immersions one after the other. Other brand tags for the same item, selling lots cheaper, so do an image search - may have to wait for it come from China. I doubt I'd bother with secondhand panels, they're the cheap bit after all.
Crofter Posted November 18, 2025 Author Posted November 18, 2025 7 minutes ago, ProDave said: Check with the seller it is G98 approved, It should be at only 2 years old. Susprised they don't state that, Only 1 input so all panels need to be on one string. 2 inputs is better if you want panels on different facing roof elevations etc. Good point. I'm playing with PVGIS and wondering about putting two panels on each aspect of the roof. I hadn't considered that this could complicate things. I've heard of micro inverters, would those be useful in this situation? Or, can I just run panels in parallel? On my boat I have always done that, but that's a smaller system.
ProDave Posted November 18, 2025 Posted November 18, 2025 You wire the panels in series. I have 8 panels on each string and 2 strings, one facing east the other facing west. With only 4 panels that may not work as each string may not achieve the minimum input voltage. What is limiting you to 3kW? the default domestic install is 3.68kW (the max without prior approval under G98) That is probably where there is most choice.
Crofter Posted November 18, 2025 Author Posted November 18, 2025 15 minutes ago, ProDave said: You wire the panels in series. I have 8 panels on each string and 2 strings, one facing east the other facing west. With only 4 panels that may not work as each string may not achieve the minimum input voltage. What is limiting you to 3kW? the default domestic install is 3.68kW (the max without prior approval under G98) That is probably where there is most choice. So I looked up that Solis and it's got a 60v startup. I'm used to boat stuff which will kick in at much lower voltages. So 60v means I need to put two panels in series to get above startup. Presumably that means I could have a pair of panels on each elevation, but I'd ideally want separate inverters for them? Nothing is limiting me to 3kw, I'm just trying to keep this system small, simple, and low cost. Anything above what's needed to heat the UVC is likely just going to go to waste. As a holiday house, it is unoccupied throughout much of the day, and it has low heating demand. And as a non MCS install I wouldn't be getting anything for export. I'm a bit sceptical that the current export rates are sustainable tbh and I don't want to build a system based on them.
Crofter Posted November 18, 2025 Author Posted November 18, 2025 What prevents you from combining the inputs in parallel? Sorry if I'm missing something obvious. E.g. on my old boat I had two 260w panels in parallel, I just ran them to the same input terminals on the MPPT. I had another MPPT which had four 100w panels all in parallel. On a boat parallel is the way to go because of variable shading, the panels can end up with quite different levels of output.
ProDave Posted November 18, 2025 Posted November 18, 2025 Domestic grid tie inverters generate a high voltage output so need a high voltage dc input to do that, hence it is normal to connect the panels in series. forget all you know about boat inverters.
Crofter Posted November 18, 2025 Author Posted November 18, 2025 OK I get it now, I looked at the spec of that Solis and it's limited to an input current of 14A. The panels I'm looking at have Imp of 13.5, which seems awfully close. So any attempt to wire in parallel would go way above the max current.
JohnMo Posted November 18, 2025 Posted November 18, 2025 59 minutes ago, Crofter said: What prevents you from combining the inputs in parallel? Sorry if I'm missing something obvious. If doing that on two roofs, the amps produced follows the lowest output panel, so if you had a side in shade and the other in the sun, output of whole system would be equal to the shade side. You can get around it with optimisers, but not fully. Each side of roof needs it's own MTTP. Plenty of cheap string inverters with 2x MTTPs. City Plumbing is my go to, for solar.
-rick- Posted November 18, 2025 Posted November 18, 2025 4 minutes ago, JohnMo said: If doing that on two roofs, the amps produced follows the lowest output panel, so if you had a side in shade and the other in the sun, output of whole system would be equal to the shade side. You can get around it with optimisers, but not fully. Each side of roof needs it's own MTTP. Plenty of cheap string inverters with 2x MTTPs. City Plumbing is my go to, for solar. I'm pretty sure this is wrong. It is an manufacturer approved installation setup to install east + west facing panels in parallel so that the bulk of generation comes from the east in the morning and west in the afternoon. Current in parallel sums. https://www.fronius.com/~/downloads/Solar Energy/Technical Articles/SE_TA_Efficient_East_West_orientated_PV_systems_with_one_MPP_Tracker_EN.pdf
JohnMo Posted November 18, 2025 Posted November 18, 2025 That sounds good until you read the rules "Shading must be avoided" how do you avoid shade on the west panels in the morning?
-rick- Posted November 18, 2025 Posted November 18, 2025 6 minutes ago, JohnMo said: That sounds good until you read the rules "Shading must be avoided" how do you avoid shade on the west panels in the morning? They are talking within a string, not between strings in parallel. So they want to maintain each string at a similar voltage. Their document explains that the output voltage of panels doesn't vary that much by the amount of light, it's the current that moves more and that doesn't really matter. If the voltage of the two strings is mismatched then you will experience more loss. Electrically, the string with the higher voltage will dominate and less power will be drawn from the string with lower voltage (reducing yield). Significant shading of a panel will reduce voltage significantly, but the difference between direct and indirect light mostly appears in current generated.
Crofter Posted November 18, 2025 Author Posted November 18, 2025 As I've said, I'm familiar with off grid systems, but I think the principles are the same. Panels in series will run at the current of the lowest output panel on that string, and at the voltage of all the panels added together. Panels in parallel will run at the voltage of the lowest performing panel and the current of all panels added together. Panels in series give a higher system voltage, allowing smaller cable sizes and generally better efficiency. But shade on any one panel will drastically cut output of the others. Panels in parallel don't get the benefits of higher voltage, but they function independently and shade on one panel doesn't drag down the others. Panels put together in a string will act like one big panel, subject to the above rules. There's nothing to stop you from making up all sorts of combinations, so long as you stay within the specifications of the receiving charge controller. 1
ProDave Posted November 18, 2025 Posted November 18, 2025 6 minutes ago, Crofter said: There's nothing to stop you from making up all sorts of combinations, so long as you stay within the specifications of the receiving charge controller. That is the critical statement. I doubt a single or even 2 panels in series would achieve the minimum voltage to start most grid tie inverters.
Crofter Posted November 18, 2025 Author Posted November 18, 2025 Most panels seem to operate around 32-38v, and the grid-tie inverter I was looking at has a minimum of 60v, so yes you'd need two. But as I understand it you could wire up pairs in parallel, so long as the current didn't exceed the specs on the inverter. By the way I'm starting to mull over the possibility of switching tack and installing a system on the other house instead. I could just go ground mounted for optimum performance. It's a slightly bigger tank and the bills are generally higher, so it's probably more worthwhile. I read somewhere that permitted development for ground mounted solar in Scotland was to be increased from 9m2 to 12m2, but I haven't seen anything definitive about whether that change has come in to force.
-rick- Posted November 18, 2025 Posted November 18, 2025 4 minutes ago, Crofter said: Most panels seem to operate around 32-38v, and the grid-tie inverter I was looking at has a minimum of 60v, so yes you'd need two. But as I understand it you could wire up pairs in parallel, so long as the current didn't exceed the specs on the inverter. For voltage you want the string max voltage to be close to the inverter max voltage. That way you get startup to happen even in low light. If your startup voltage is too close to string voltage you will lose a lot of generation in lower light conditions. Up in scotland I'm guessing that is a very significant chunk of generation. The current spec you want to look at is short circuit current. The MPPT current can be exceeded as the MPPT won't draw more than it can handle. If you can supply more current you effectively cap generation once the current reachs the inverter limit. But this means you get more generation in less than ideal conditions with the trade off of limiting maximum generation. 1
Crofter Posted November 18, 2025 Author Posted November 18, 2025 OK I am settling on a design. Assuming that I can erect 12m2 of ground mounted PV within permitted development, I'd be putting up a structure that's 3m tall at the highest point, and which would have six 590w panels along the top at a 39° angle, plus another three horizontally along the front at 74°. I've arrived at these figures after spending a few hours farting about with PVGIS and I think they're optimal. It does take me slightly over the 12m2 footprint but I don't think anybody would notice, and if they did, I'd just have to bring those three extra panels all the way to vertical. I'd have a 3.68kw inverter for the top panels, and a 2kw one for the extra three. The array would be mounted out behind the house, at a distance of around 20m. Where's the best place to put the inverters? I could see it being fairly easy to build an enclosure under the panels. Then run SWA down to the house? Are there any rules that need to be followed about building the structure? I could obviously just use wood but perhaps unistrut would be longer lasting. Inevitably I'd be very tempted to box it in underneath, lots of people seem to do that. If fully boxed in, it would look something like this:
Dillsue Posted November 18, 2025 Posted November 18, 2025 Why 2 inverters? You'll need DNO permission with potentially more than 3.68kw of export. Put the lot on a single inverter. Most/lots of inverters can have way more DC input power than the headline power rating If you enclose the underside then it's no longer a ground mounted PV array but a building clad in solar panels so any planning limits would be those for a garden building rather than a PV array....not sure of Scottish rules though!! 1
JohnMo Posted November 18, 2025 Posted November 18, 2025 38 minutes ago, Crofter said: The array would be mounted out behind the house, at a distance of around 20m. You need to be careful with voltage drop on the AC side. The inverter can trip if grid voltage is high and you have a voltage drop. You are better taking the voltage drop on the DC side. Turn into a shed, then it's not a ground mount array. 1
Crofter Posted November 18, 2025 Author Posted November 18, 2025 48 minutes ago, Dillsue said: Why 2 inverters? You'll need DNO permission with potentially more than 3.68kw of export. Put the lot on a single inverter. Most/lots of inverters can have way more DC input power than the headline power rating If you enclose the underside then it's no longer a ground mounted PV array but a building clad in solar panels so any planning limits would be those for a garden building rather than a PV array....not sure of Scottish rules though!! I thought I'd need a second inverter because the extra three panels will see quite different conditions. Maybe I'm overthinking it. Tbh they don't add a huge amount, it would be easier just to stick to the main array of six.