September 12, 20251 yr Author I appreciate that the overnight power draw is not wasted but is heating the DHW tank, but my concern is the relatively 'short cycling' damaging the CoP and/or compressor life.
September 13, 20251 yr If all your scheduling is done within the Honeywell programmer can you turn that off overnight and see if the HP continues starting up? That will rule out the programmer. If you think it could be the HP topping up the buffer then can you turn the buffer set point temp right down before you go to bed? That should stop the buffer being topped up.
September 13, 20251 yr 8 hours ago, chris47 said: I appreciate that the overnight power draw is not wasted but is heating the DHW tank, Is it, or is it heating up the buffer? Given you are in Bristol its most unlikely to be frost protection because its (presumably) not yet cold enough. You may be able to adjust the frost protection settings to find out for sure, but its equally likely you cant, given that the freezing point of water is the same worldwide and frost protection is a safety measure to protect the equipment. Certainly my Vaillant, and several other heat pumps the manuals of which I have read, have no provision for adjusting the frost protection settings (neither did my boiler), for the simple reason that there is nothing really that it makes sense to adjust. Im still thinking its most likely the heat pump satisfying the buffer because it has no way to know that there isnt a call for heat. @Dillsue is suggesting ruling out the programmer, but I think you have already done this. He is also suggesting turning down the buffer target temperature to detect whether its the heat pump satisfying the buffer. If you can do that he is right it is a good way to confirm. Alternatively trace the route from the receiver end of the wireless thermostat. Does it only switch the secondary pump, in which case what I suspect is the cause is guaranteed to happen, or does it also switch the call for heat contact on the heat pump? Or just ask your installer! Although you are right to be concerned about the short cycling, probably more significantly long term is your mode of operation. In most houses heat pumps are most efficient run 24*7 on weather compensation and without a buffer, with all or most of the TRVs and thermostats turned up a couple of degrees above the desired set point. Depending on what your flow temperature is, the buffer alone will increase your running costs by 15%. Running at a flow temperature 5 degrees too high and bouncing off thermostats could easily be another 15%. And, depending on your house characteristics part time running another 15% (unless your heat pump is well oversized in which case you may be incurring the penalty anyway). Really your installer should come back, replumb the buffer as a 2 port volumiser in the flow, attach the Honeywell to the call for heat from the heat pump, operate it 24*7 then turn up all the TRVs/Thermostats and adjust the WC so it just heats the house. That's generally a good starting point from which to tweak. Of course there are always exceptions to the general rule, but in a well insulated house (you say yours is reasonably well insulated) with a reasonably right-sized heat pump the general rule is almost always the right starting point. Edited September 13, 20251 yr by JamesPa
September 14, 20251 yr Author On 13/09/2025 at 08:40, JamesPa said: Is it, or is it heating up the buffer? Given you are in Bristol its most unlikely to be frost protection because its (presumably) not yet cold enough. You may be able to adjust the frost protection settings to find out for sure, but its equally likely you cant, given that the freezing point of water is the same worldwide and frost protection is a safety measure to protect the equipment. Certainly my Vaillant, and several other heat pumps the manuals of which I have read, have no provision for adjusting the frost protection settings (neither did my boiler), for the simple reason that there is nothing really that it makes sense to adjust. Im still thinking its most likely the heat pump satisfying the buffer because it has no way to know that there isnt a call for heat. @Dillsue is suggesting ruling out the programmer, but I think you have already done this. He is also suggesting turning down the buffer target temperature to detect whether its the heat pump satisfying the buffer. If you can do that he is right it is a good way to confirm. Alternatively trace the route from the receiver end of the wireless thermostat. Does it only switch the secondary pump, in which case what I suspect is the cause is guaranteed to happen, or does it also switch the call for heat contact on the heat pump? Or just ask your installer! Although you are right to be concerned about the short cycling, probably more significantly long term is your mode of operation. In most houses heat pumps are most efficient run 24*7 on weather compensation and without a buffer, with all or most of the TRVs and thermostats turned up a couple of degrees above the desired set point. Depending on what your flow temperature is, the buffer alone will increase your running costs by 15%. Running at a flow temperature 5 degrees too high and bouncing off thermostats could easily be another 15%. And, depending on your house characteristics part time running another 15% (unless your heat pump is well oversized in which case you may be incurring the penalty anyway). Really your installer should come back, replumb the buffer as a 2 port volumiser in the flow, attach the Honeywell to the call for heat from the heat pump, operate it 24*7 then turn up all the TRVs/Thermostats and adjust the WC so it just heats the house. That's generally a good starting point from which to tweak. Of course there are always exceptions to the general rule, but in a well insulated house (you say yours is reasonably well insulated) with a reasonably right-sized heat pump the general rule is almost always the right starting point. Dillsue said 'If all your scheduling is done within the Honeywell programmer can you turn that off overnight and see if the HP continues starting up........' The Honeywell programmer is for CH only; DHW is controlled by the LG programmer. Rather than running 24/7 I'm timing my start/stops for DHW to match Octopus Cosy tariff that gives me 3 daily cheap rate slots totalling 8 hours @ 12.9p/kWh. The other rates are 3 day rate slots totalling 13 hours @ 26.31p/kWh & a 3 hour slot @ 39.46p/kWh. I'm timing my start/stops for CH using all the above slots but avoiding the expensive slot of 39.46p/kWh During my 'first' winter coming up using an AWHP I will balance the radiator temps using the lockshields (TRV's fully open) & then adjust the TRV's as you suggested. I also have a Give Energy battery backup which I can charge with solar PV & Octopus Cosy cheap rate to help reduce the running costs of the AWHP. I think this coming winter is going to be a lot of 'trial & error' & a steep learning curve. ps I turned OFF the main AWHP isolator switch Friday night between 01:00 & 07:00 & all the power draw spikes disappeared; proving it was the AWHP & or an internal AWHP electrical heater running that caused these 'spikes'. I noticed from the installation manual that their is a reference to 2 DIP switches that control an 'electrical heater' but it doesn't say whether it's the buffer tank heater (which I don't have) or some other heater (like the Willis heater referred to earlier in this post). I shall be installing a wireless temperature sensor in the DHW tank to help determine whether CH or DHW heating is being supplied by the AWHP. I've sent the initial data from the start of this post to LG support & will report back their suggestions/comments if any! Thanks to everyone for you input & I will post again when I have something to report.
September 14, 20251 yr @chris47 All above makes sense. I didn't realise you had cosy which does make the picture of how best to operate the heat pump a tad more complex (unless you also have a battery of course) Have you discounted the possibility that the ashp is simply satisfying the buffer then? There is another thread on this forum discussing alternative ways to wire controls when a buffer is present, and the installer in question is advocating (he claims for efficiency) doing it in the way that is guaranteed to cause the symptoms you observe. Given that one installer favours this it's likely that others do, so quite possible yours did. Edited September 14, 20251 yr by JamesPa
September 14, 20251 yr Author 4 hours ago, JamesPa said: @chris47 All above makes sense. I didn't realise you had cosy which does make the picture of how best to operate the heat pump a tad more complex (unless you also have a battery of course) Have you discounted the possibility that the ashp is simply satisfying the buffer then? There is another thread on this forum discussing alternative ways to wire controls when a buffer is present, and the installer in question is advocating (he claims for efficiency) doing it in the way that is guaranteed to cause the symptoms you observe. Given that one installer favours this it's likely that others do, so quite possible yours did. I do have a battery - Give Energy 9.6kWh with 3.1kW AC coupled inverter:) I haven't discounted the possibility that the AWHP is simply satisfying the buffer; I intend fitting a wireless temp sensor to the buffer feed pipe so I can determine if indeed the heating of the buffer is the cause of the spikes. Do you know the link to 'ways to wire controls when a buffer is present' you referred to above?
September 15, 20251 yr Remember, the LG doesn’t have a dedicated buffer sensor, it just uses an internal temp sensor in the outdoor unit to sense flow. Same as the Samsung. On an LG there’s no way to separate the two sides of a buffer system from a call-for-heat perspective (unless you’ve done a terrible job installing it) - the 3rd party room thermostat wires back to the outdoor unit. They’re literally designed to have a room stat by default. Good heat pump, complex and can do lots of things. But a good unit. p.s. On the gen4 there isn’t a heater in the outdoor unit. Edited September 15, 20251 yr by HughF
September 15, 20251 yr 1 hour ago, HughF said: On an LG there’s no way to separate the two sides of a buffer system from a call-for-heat perspective (unless you’ve done a terrible job installing it) - the 3rd party room thermostat wires back to the outdoor unit. They’re literally designed to have a room stat by default. Isnt the default set up to use the room temp sensor built into the remote controller?? An external/3rd party thermostat, if fitted, has to be enabled with a DIP switch
September 15, 20251 yr 21 minutes ago, Dillsue said: Isnt the default set up to use the room temp sensor built into the remote controller?? An external/3rd party thermostat, if fitted, has to be enabled with a DIP switch Yes. I have mine set for external room thermostat input which is actually the call for heat contact from the UFH manifold controller. Mine is an early one and the supplied controller is the most complicated, non intuitive thing I have met, I did not want to be using that to schedule on and off times etc, so I have a perfectly ordinary central heating controller for that, something which most people understand, and the heat pump is purely under control of the room thermostat input. Doing the same for DHW was more of a challenge. There is no official way to remotely turn DHW on or off. So my hack was use the same central heating controller so switch a relay. The relay contact then either connects the thermistor temperature probe to the controller (DHW on) or switches to a fixed resistor chosen to mimic the thermistor value at a high temperature. So fixed resistor in circuit = DHW off because it always thinks the water temperature is way above the set point. I am still waiting for some clever person to post details of the frost protection settings they found. We all know water freezes at 0C buy my experience is mine starts it's water circulation thing when the water temperature gets down to just 10C which I think is way too soon and I would love to be able to adjust it to say 5C
September 15, 20251 yr 10 hours ago, chris47 said: Do you know the link to 'ways to wire controls when a buffer is present' you referred to above? Point 3 on the post by d438a1. Interestingly triggered a disagreement between MCS inspector and installer apparently 2 hours ago, HughF said: On an LG there’s no way to separate the two sides of a buffer system from a call-for-heat perspective (unless you’ve done a terrible job installing it) - the 3rd party room thermostat wires back to the outdoor unit. They’re literally designed to have a room stat by default. Surely you can just leave out the room stat as far as the LG is concerned, it will then satisfy the buffer based on return temp and its WC curve. Im not saying this is a good thing to do, just saying that the plumber may have done it if, like the one in the reference above, they prefer to do it this way. Edited September 15, 20251 yr by JamesPa
September 15, 20251 yr 26 minutes ago, JamesPa said: Surely you can just leave out the room stat as far as the LG is concerned, it will then satisfy the buffer based on return temp and its WC curve. That's my understanding of how things can be configured. I'm in the throws of setting ours up and currently have it configured to run and stop on a volt free contact which is the same as an on/off stat. Once all the hydraulics are sorted I'll be moving onto WC(AI in LGs world) with the volt free contact acting as a temperature limiter or to disable the HP for other reasons. I could leave the volt free contact/stat disabled with a dip switch and the HP would just pump water as required by WC/AI
September 15, 20251 yr 16 hours ago, chris47 said: During my 'first' winter coming up using an AWHP I will balance the radiator temps using the lockshields (TRV's fully open) & then adjust the TRV's as you suggested. Balancing and WC setup can be done now. I wouldn't wait til winter to set things up in case you hit problems.....I couldn't balance the whole house and have had to shut the heating down to add a pump and control for it. Potentially could have been without heat for a couple of days which isn't a problem now but would have been in the winter
September 15, 20251 yr 4 minutes ago, Dillsue said: Balancing and WC setup can be done now. I wouldn't wait til winter to set things up in case you hit problems.....I couldn't balance the whole house and have had to shut the heating down to add a pump and control for it. Potentially could have been without heat for a couple of days which isn't a problem now but would have been in the winter Interesting, presumably to boost a high resistance leg. Was it just plumbed in series or did you employ any separation?
September 15, 20251 yr The original part of the house had 8mm copper drops from ceiling to floor on 5 rads and I couldn't get any flow to 3 of them without shutting down the lockshield on the rest of the house. A small pump on the 22mm pipe feeding them has sorted that. Still got another rad with a long 10mm run to get flowing but Im confident Ill get that with balancing. Everything is plumbed direct so no separation
September 15, 20251 yr TL;DR We looked at phantom power draw a while back with regard to crankcase heaters, has this been ruled out?
September 15, 20251 yr Our series two has a built in immersion in the heat pump unit in a very small horizontal 'cylinder' which we have both disabled via dip switches and physically disconnected. There is a downside that this is part of the de-icing mechanism and we did have some issues when there was a 3 day hoar frost earlier in the year. WE also run a secondary circulating pump due to undersized internal plumbing but have to be careful it does not generate too much flow through the HP during start up as the heat pump sees this as the flow sensor being stuck open and errors out.
September 23, 20251 yr Author see attached 22/9/25 graph; is this an example of 'short cycling'? According to online AI: The LG Therma V R32 monobloc air-to-water heat pump does not have a built-in immersion heater (IH). The monobloc unit is designed as a self-contained outdoor unit for heating and hot water that connects directly to the domestic water system. I noticed that the WC kicks in when outside temp drops below 12°C. During overnight period, between 00:00 & 05:00, schedules for DHW & CH are OFF so it seems that the power draw is to satisfy the buffer using WC (AI). Since there is no IH available for use, I have to assume the AWHP is running at these times at a low (modulated) level. If this is an example of 'short cycling' what can I change to help reduce the effect? My World Heat DHW cylinder has a built in buffer tank at the base. There are 4 connections to this buffer tank which seems to indicate it is a 'hydronic seperator' preventing the AWHP's internal pump interfering with the CH pump attached the the CH circuit of the DHW tank. There is no IH fitted to this buffer tank. My 'sterilisation' IH is switched OFF permanently. My Octopus Cosy tariff has 3 daily cheap rate slots but the AWHP seems to be able to run at any time, contolled by WC. This means it could run during the most expensive time between 16:00 & 19:00 (3 times cheap rate!). Is there any way to mitigate this effect? Still no response from LG!
September 23, 20251 yr 18 minutes ago, chris47 said: My Octopus Cosy tariff has 3 daily cheap rate slots but the AWHP seems to be able to run at any time, contolled by WC. This means it could run during the most expensive time between 16:00 & 19:00 (3 times cheap rate!). Is there any way to mitigate this effect? Im struggling with interpretation of the graph but it looks like short cycling to me. At least 3 ways I can think of to mitigate: Take out the buffer and secondary pump(s) or turn it into a 2 port volumiser in the flow Logically 'or' the call for heat from any stats and connect it (via a relay) to the master call for heat from the heat pump (assuming there is one - which there usually is) Turn the stats up to say 2C above the target and run it on pure WC turned down as low as possible consistent with heating the house, balancing on the LSVs or loop flow regulating valves (heat pump may still short cycle at moderate temperatures if oversized). (1) + (3) is almost certainly the best solution. (1) on its own the next best, (2) involves least disruption but retains the disadvantage of buffer and control-by-thermostat. Edited September 23, 20251 yr by JamesPa
September 23, 20251 yr Author 20 minutes ago, JamesPa said: Im struggling with interpretation of the graph but it looks like short cycling to me. At least 3 ways I can think of to mitigate: Take out the buffer and secondary pump(s) or turn it into a 2 port volumiser in the flow Logically 'or' the call for heat from any stats and connect it (via a relay) to the master call for heat from the heat pump (assuming there is one - which there usually is) Turn the stats up to say 2C above the target and run it on pure WC turned down as low as possible consistent with heating the house, balancing on the LSVs or loop flow regulating valves (heat pump may still short cycle at moderate temperatures if oversized). (1) + (3) is almost certainly the best solution. (1) on its own the next best, (2) involves least disruption but retains the disadvantage of buffer and control-by-thermostat. Thanks for that; I'll try the LSV route first
September 23, 20251 yr 17 minutes ago, chris47 said: short cycling Short cycling occurs when the heat source cannot get the heat away quick enough, or there is little or no demand, or flow rate is too low, or all three conditions. As the heat source goes through a start cycle the target temperature is exceeded by enough margin to cause the heat source to shut down, this repeats. To eliminate it, you can raise the target flow temp, add a couple degrees to the existing target temp. Then fine tune down. Or increase the system volume or flow rate. If you have the parameter available you can increase/decrease the PI integral time. This changes the reaction time of the controller. The way your system is setup can actually cause short cycling. If I run heat pump, so the circulation pump runs periodically, the temperature of the water close to the heat pump cools quicker than that inside the house, so heat pump thinks it needs to start up, but in reality it doesn't, heat pump starts, the warm water from house hits the heat pump it shutdown. This is fixed by running the heat pumping it's default mode of circulation when there is a demand for heat. The heat pump control then knows exactly when to restart - no short cycling.
September 23, 20251 yr 55 minutes ago, chris47 said: Thanks for that; I'll try the LSV route first Actually thinking about it this isnt guaranteed to stop it coming on during peak periods. It will make it less likely because the buffer will almost certainly be warm before the 'switch off', but its not guaranteed to stop it. Its good practice anyway and, by turning down the WC, you will also reduce consumption if the heat pump does come on during peak. Sorry about this. Edited September 23, 20251 yr by JamesPa
September 23, 20251 yr 1 hour ago, JohnMo said: To eliminate it, you can raise the target flow temp, add a couple degrees to the existing target temp. Then fine tune down. Or increase the system volume or flow rate. If you have the parameter available you can increase/decrease the PI integral time. This changes the reaction time of the controller. I think (if I understand him correctly) that the cycling OP is concerned about is when the HP comes on yet there is no call for heat from the thermostats. This is almost certainly caused by satisfying a tiny buffer in a buffered system. This being the case is raising the LWT really going to make much difference? Certainly it wont guarantee that the system doesnt come on during peak cosy periods when call for heat on the secondary has been disabled. Edited September 23, 20251 yr by JamesPa
September 23, 20251 yr 16 minutes ago, JamesPa said: I think (if I understand him correctly) that the cycling OP is concerned about is when the HP comes on yet there is no call for heat from the thermostats. This is almost certainly caused by satisfying a tiny buffer in a buffered system. This being the case is raising the LWT really going to make much difference? Certainly it wont guarantee that the system doesnt come on during peak cosy periods when call for heat on the secondary has been disabled. 22-09 electric chart would certainly indicate short cycling almost all day. So as you say trying to keep a small buffer happy isn't working. But everything I stated are the reason for the cycling. Mentioned above by @HughF was that the buffer has no control system or feedback. So firing the compressor based on return temperature most likely. Cosy tariff - Would certainly look to dump the buffer in the short to medium term, convert to volumiser on the return side, remove secondary side pump(s). This can be done with or without buffer - either run pure WC (so call for heat 24/7) or a time based running in Cosy periods with WC flow temperature (maybe slightly elevated to compensate for some off periods). Set thermostat so you have no call for heat during really expensive period. Then set thermostat to 23 in cheap periods and a more tolerant temp in normal rate periods, say 19.5. This would encourage most running in cheap periods, coast in normal rate off in expensive rates, but internal temps could swing about if on radiators, less so on UFH. Ideally if you can run a second setpoint that would be better than a thermostat set point. I have (but don't currently use) a second set point setup, this add 5 degs to normal WC curve, so this would allow running elevated temps in cheap periods and normal WC at all other times. Net result is runs hard during cheap periods, pretty much off for several hours. Observation - the intermittent running to keep buffer happy is possibly costing as much as it would to run WC 24/7, as to run intermittently via time control, you have to run a higher flow temperature. Plus running WC allows you generally have a cooler house and still be comfortable. So current operating strategy is costing you not saving you money.
September 23, 20251 yr 2 hours ago, chris47 said: My Octopus Cosy tariff has 3 daily cheap rate slots but the AWHP seems to be able to run at any time, contolled by WC. This means it could run during the most expensive time between 16:00 & 19:00 (3 times cheap rate!). Is there any way to mitigate this effect? Not sure what series HP you have but on our series 3 I could use a timed contact to switch the thermostat input to turn the HP off during peak cost periods. Although Ive not used it yet, the Energy State function seems to allow you to turn off or set back heating and hot water setpoint temperatures by switching a pair of digital inputs. If it's available on your HP you could use that feature to set back flow temp during peak times and boost flow temp during the Cosy periods
September 23, 20251 yr 3 hours ago, Dillsue said: Not sure what series HP you have but on our series 3 I could use a timed contact to switch the thermostat input to turn the HP off during peak cost periods. Although Ive not used it yet, the Energy State function seems to allow you to turn off or set back heating and hot water setpoint temperatures by switching a pair of digital inputs. If it's available on your HP you could use that feature to set back flow temp during peak times and boost flow temp during the Cosy periods Mine is an early version but the thermostat input only works for turning heating on and off. There is no official way on mine to turn DHW on and off via an external switch or thermostat.
Create an account or sign in to comment