Hey everyone, I'm new to this place. I've been lurking for a while so, by way of introduction; I'm an electrician by trade and I decided to undertake a lowerground/basement conversion and extension at my own house with the vast majority of the work being undertaken at weekends. I'm over two years down the road in this journey and I'm at UFH design and pipe installation prior to getting screed down.
The extension has access to the garden, all walls aren't underground but the majority of the existing house walls are. I'm going to internally insulating the walls.
My floor build up is a 150mm ground bearing reinforced concrete slab, cavity drainage membrane, 100mm PIR insulation, UFH, sand/cement screed.
As for heat loss calculations, I've been playing a lot with a few options. My first port of call was heatpunk, I found it intuitive and managed to define all of the different elements I required such as the differing wall build ups. I've also played with the famous Jeremy's heat loss calculator spreadsheet and Copilot. They are all within 10% of each other so I'm confident the heat loss figures look reasonable.
That brings me onto LoopCAD, I've struggled with the materials and insulation details to reflect what I have and therefore achieve similar heat loss figures the three methods above have indicated. Hopefully I've managed to put the right figures in and have something approximating a pipe layout. Pipework is 16mm PEX-AL-PEX, I'm sure I saw a recommendation for 20mm, would it make sense to use bigger pipes?
The area directly above the manifold is the stairs, so I need to tidy up the pipes leaving the small cupboard to get to each room. Have I missed anything obvious? Seeing as this is my first system I'm mindful I might have missed something crucial. The cupboard and hallway are both shown as being too cold but from what I've read on this forum it should be fine considering the circuits are running through the areas.
Any observations, comments, feedback would be greatly appreciated.
First not enough insulation really
You either do no insulation and use ground as a heat store, then run heating low and slow for the whole heating season, or at least 150mm PIR, but the more the better. This limits heat seeping downwards never to return.
16mm PEX-AL-PEX
Do yourself a favour and swop to Pert-Al-Pert, easier to manipulate. 16mm is the size to use.
Flow dT is likely to either 4 or 7 rather than 10.
Layout looks good, making use of pipe to and from rooms to heat halls etc.
Easy way to fix that, pull the hall pipes closer together then use a longer pipe length for room A-02 and make an addition loop or two in the hall.
As @JohnMo says, more floor insulation.
Once you know the total, worse case, heat losses, it is relatively easy to work out the pipe spacing.
I cannot think of a good reason to go greater than 16mm tubes. I think 20mm is for very long runs and lots of tight bends.
Check you can do the full loop with one length, you really only want joints at the manifold.
Edited by SteamyTea
Balls, I'm too far down the track to change that now, I think. I wish I'd ask the question before going off the architects bloody drawings. I should have known, I've already ignored a lot of his other details after researching them myself. Will it have a major impact on the comfort levels of the rooms?
I have 75mm screed/floor finish after the original 100mm insulation, not much to play with.
Cheers, I'll be ordering that later today.
I'll make a note of that, does that mainly affect flow rates?
I've played around with the spacings and layouts and it appears there isn't much difference in performance between 150 and 200mm spacing. Is there a general consensus of what it should be? Looking at LoopCAD, if I change the pipe centres it still performs as required.
I've seen the chart with lines to draw between mean water temp and spacings. Seems like what I've drawn so far with 150mm centres is too much. I have a 2734W loss in the space and around 72m2, which works out at 38w/m2. Would it be feasible to install at 150/200mm centres and if its too hot, turn down the flow for the circuit?
No just you wallet as you will loose heat downwards
Be careful with the lengths you order as it can get a lot of waste
It affects flow rates and flow temp. UFH output is governed by the mean flow temp, the smaller the dT the lower the flow temp needs to be.
Once you get fairly well insulated the flow temp has very little impact on floor heat output.  What is changes is reaction time, so how long you need to allow for the floor to impact room temp. I have a loose 300mm spacing (but much lower heat loss per m2), it's a glacial time scale from cold floor to hot house, but that only occurs once per year.  Rest of the time its running weather compensation, so only has to react to daily changes in the weather.
You can either use 150mm or relax the spacing slightly, but with your heat loss I would stick to 150mm.
Is this an add on to an existing system, boiler or heat pump?
The underfloor heating in this thread is going to be on a boiler until the day I get the entire house upto spec. Its a long term project 😅
Its an old pre 1930's house, solid brick walls, that will eventually be externally insulated complete with lots of airtightness improvements and MVHR. But I've started from the bottom and am going to work my way up, once this level is complete the ground level gets a garage conversion and modernisation throughout. I'm looking at the ground level having underfloor heating too.
If it all goes wrong I'll just stick massive radiators in 🫣
I bought a roll of PEX-AL-PEX 16mm and PERT-AL-PERT 16mm to test, and found zero difference in flexibility.
  • 4 weeks later...
If I'm not too late...
We had planned for 200mm PIR then 60mm screed.  It turned out that once the upstand walls were built we had 280mm to play with (my error).  So I toyed with 80mm liquid screed but an extra 20mm PIR proved cheaper than the extra screed! (100+120, rather than 2 x 100mm).  Ok it only moved our floor u-value from 0.101 to 0.092 but it cost less to install anyway.
My point is, if you have not already laid your pipes you could add another 20mm of PIR and reduce your screed to 55mm.  Might be cheaper to install and save running costs.  Just a thought.
Far too late I'm afraid. The screed has been down for a couple of weeks now.
I'm going to be internally insulating the walls shortly. I need to get that moving, might be another thread.
  • 6 months later...
A small update.
I'm onto connecting this underfloor heating install onto my existing boiler but with a view to an ASHP in the future, once the rest of the house is sufficiently thermally performant.
I've done some watching of videos and very dodgy calculations, it appears 28mm copper or 32mm MLCP for the flow and return. This will pipework will also likely end up feeding the manifold for the ground floor, eventually.
Any thoughts? Have I asked in the right part of the forum?
41 minutes ago, Adrock said:
A small update.
What's the heat load being carried by the primary pipes?
Do you have a plan where the heat pump will be going and its relationship to existing boiler and pipework?
Using heatpunk to design my house in it's finished state, just under 4kW is the heat loss of the building when it's complete.
As for heat pump location, at the moment I'm not sure as that part hasn't been designed yet. I suspect the primary pipework from the heat pump to the basement will be around 18-20m to get to the basement and then an additional 8-9m in the basement to get to the manifold. The ground floor manifold will be teed off within the first couple of meters within the basement.
So minimum is going to be 28mm piping. Ideally in copper, Hep2O should be ok, 22mm the pressure drops will be too high. Depending on heat pump you may need to add a boost pump. MLCP in 32mm I would check the cost of pipe insulation - min wall thickness 19mm it could cost quite a bit.
Assuming that you have full load to your manifold and therefore lets say 30m from heat pump to manifold and 22mm copper pipe - assuming 5C delta T-  will give you:
Pressure drop of 9kPA (.92 Meters head)
Flow rate of 0.191l/s (or approx 0.688m3/h)
And a velocity of 0.61m/s
This includes a 20% allowance for fittings and a water temperature of 35C (viscosity of water changes with temperature).
With pipe sizing you don't really want to drop your velocity below the industry figure of 0.5m/s due to risk of debris settling in the pipework and you would do this if you used 28mm or 32mm MLCP. You could use 25 or 26mm MLCP and have roughly the same results as with the 22mm copper.
This means that you could get away with 22mm copper and just make sure the nearly 1m head is okay with the rest of your system index circuit pressure drop and the pump residual head.
It's so common for installers to think you need much bigger pipes. I've recently installed a 9kW heat pump (that can put out over 10kW) with a 25m long header to the house using 32mm MLCP and that's currently running a scop of 5.4. In this instance my header pressure drop is 1.1m head and flow rate of 0.8m/s well within the limits of the max 1 or 1.2 m/s maximum depending on which brand of MLCP used. Index circuit is just over 2m head with a pump with residual of 7m so really no problems at all.
In your case, at 4kW the figures for 32mm MLCP would be:
Velocity 0.36m/s
Pressure drop 2.59kPa
So even with 22mm copper you have some headroom if the heat pump can output more than 4kW and it'll save you a good few quid v 28mm.
Edited by SimonD
adding delta T
But you may have issues doing DHW - I say this from experience, the heat pump circulation pump runs full speed in most situations. My system drops from 28mm to 22mm for the run to the cylinder - around 10m each way and it needs an additional pump to get adequate flow.
That's a good point. You always need to know the full load the pipework is going to carry as well as pump curve and heat pump drop offs. I always get these from manufacturer technical as part of a design if it's a new product for me. So to illustrate in @Adrock's situation. Lets for arguments sake say the output of the heat pump is 6.5kW in DHW mode. That same 22mm pipe, still assuming a total length of 30m (which it probably won't be as this  pipework includes the section to the ufh manifold) This time I've adjusted water temperature to a conservative 40C. The figures are:
Pressure drop: 19.69 kPa (2.01 meters head)
Flow rate: 0.311 l/s
Velocity: 0.97 m/s
So the velocity is almost spot on for copper design purposes and you've got a doubling of the pressure drop, but if there's sufficient residual head at the pump, this should be no problem at all. My calcs include a 20% addition for fittings and if I remove fittings it drops to 16.40 kPa (1.67 meters head). If you used 25mm MLCP you could probably do the run without many fittings at all.
So even in this scenario, providing there is sufficient residual head, which their should be from a decent heat pump as the pumps are now getting pretty big, even with DHW you're very well within a comfort zone.
If I take this to 28mm.
Pressure Drop: 5.69 kPa (0.58 m head)
Velocity: 0.58 m/s
So here, you're only just within the 0.5m/s velocity limit on dhw.
As a real world example, I have one heat pump with a 6.5kW output at -5  installed with about 15m of 22mm polybutylene push-fit pit as the owner did not want to rip it all out and upgrade due to the extent of works required through the house. Yes, it's on the flow velocity limit of 1.2m/s on DHW but there are no issues at all with flow rates or function and efficiency is extremely good.
The question is whether you want to incur the costs of 28mm pipework and a low flow velocity regime when for the vast majority of the time flow requirements are going to be nowhere near.
Thank you very much everyone. @SimonD you've given me an insight into what it takes to design heating and dhw pipework. I should have probably expected that considering my day job is similar, just on the electrical (better 😁) side of the game.
So, my take away from this recent discussion is 22mm copper is sufficient for the actual load of the building. I just need to work out the index circuit and see how those figures all sit together.
If the pressure drop is too high a bigger pipe would reduce that but the velocity would still be low, right?
I would suspect for 90% of the year velocity will below min rates anyway. Most heat pumps will modulate circulation pump flow to match heat demand, heat demand will vary and only duty demand rate being required on the coldest days. The rest of the time heat pump should be running close to minimum modulation.
Example -my heat pump this morning was circulating at 7L/min, so pretty much well below and min velocity rates.