Russdl Posted Friday at 10:01 Posted Friday at 10:01 (edited) During my mid year service of the house it turns out that the second Willis Heater we hardly ever use doesn’t work anyway. After a bit of investigation it became pretty clear why that was. The neutral from the Willis Heaters fused spur into the contactor was trying to catch fire, it had actually melted and stuck to the outer casing of the junction box. The neutral was in the right hand No.3 terminal - kinda. I found that pretty disturbing, especially as there was no indication of when this had happened (nothing tripped off, no smoke alarm) or how long ago it happened. On closer inspection I think it’s clear what has happened, the terminal screw seems to be cross threaded so I guess it felt like it was done up tight but clearly it wasn’t. Stuff clearly needs replacing, like the contactor and the Wago. The obviously burnt twin and earth needs replacing, can I just cut out the burnt sections and splice in new cable with these? Or should I replace the whole length to the fused spur? The T&E appearing above the contactor is directly from the distribution board and looks slightly heat damaged, I guess that all needs replacing as well? As a side note, I’m going to be sourcing another smoke detector for this area. There is a smoke detector in the room and also an MVHR extract. The problem is with the relative positions the MVHR extract will effectively prevent any air from the area of the distribution board passing over the smoke detector. Edited Friday at 10:03 by Russdl Changed the first photo
Kelvin Posted Friday at 10:07 Posted Friday at 10:07 If you can replace the whole length why wouldn’t you do that? 2
Russdl Posted Friday at 11:10 Author Posted Friday at 11:10 Good point, I’ve not had a good look at what that would entail, replacing the T&E from the contactor to the fused spur, but I suspect I could do that with relative ease. 1
ProDave Posted Friday at 18:43 Posted Friday at 18:43 I would not hesitate having a junction inside the contactor box. Always give new terminations a tug to see if they are really tight. I have found MK sockets especially bad at having poor binding screws that feel tight before the screw even touches the wire, yet plenty of people still think they are the best. 1
Russdl Posted Friday at 21:02 Author Posted Friday at 21:02 2 hours ago, ProDave said: I would not hesitate having a junction inside the contactor box Just so I’m clear on that advice you say the Wago would be fine? 2 hours ago, ProDave said: Always give new terminations a tug to see if they are really tight I do. But I guess the electrician that did the original install didn’t. However tugging upwards against the distribution board would have been difficult I guess.
BotusBuild Posted Friday at 22:20 Posted Friday at 22:20 If you are replacing the damaged contactor (bad screw) - you're doing that! - then replace the whole T&E at the same time. IMHO 1
Russdl Posted Saturday at 04:42 Author Posted Saturday at 04:42 That’s what I’m here for, “HO’s”. I’m no electrician so I’m seeking advice. I’m definitely going to replace the contactor, I’ve no idea how damaged that is internally but it has most definitely got very hot and, on balance, it would seem that the whole length of T&E should be replaced as well, so I’ll do that.
BotusBuild Posted Saturday at 08:34 Posted Saturday at 08:34 3 hours ago, Russdl said: I’m no electrician Don't be too afraid. Photograph what you are going to replace, particularly connections. Turn everything off, then check nothing is live. Replace the cable. Replace the connector. Make the connections (refer ro earlier photos) Tighten and tug test. Apply volts. You got this 1
Russdl Posted Saturday at 11:46 Author Posted Saturday at 11:46 Thanks 🤣. Im not afraid, I can’t do any worse than the professional that went before me! I just want to ensure that any rectification/replacement I do is done according to best practice.