Bco git


Pocster

Recommended Posts

Just when I thought I was at the sign off finish line …

bco has magically requested exposed steels are painted fire resistant.

These steels have been easily accessible and visible for literally years - with never a mention .

The ceiling is up and is fire rated for 30 mins .

Needless I’m somewhat pissed off !

Nothing ever in writing “ paint steels “ but presumably from his own notes casually mentions it now as I’ve applied for sign off .

Ignoring bco’s incompetence does the fact I have a fire rated ceiling over the steels support my case to avoid taking down the entire ceiling ? I.e is that not fire resistant enough ????

 

Link to comment
Share on other sites

25 minutes ago, Pocster said:

.... is that not fire resistant enough ????

 

It may or may not be. 

 

You @Pocster are a legend. We all  know that, you know that. But the BCO doesn't.

Convince him of your legendary status as somebody who conserves energy - nervous energy - and just bloody does it instead of worrying about it.

Better put  JustBloodyDoIt - JBDI

  • Thanks 1
Link to comment
Share on other sites

Well - as the legend I am I recorded the conversation from the last visit .

So been listening to that …

He does indeed mention fire resistance of the exposed steels . But seemed convinced that if the ceiling tile system could provide 30 mins fire rating then it might be ok .

The conversation by the bco is all non commit on his side I.e no “ yes “ or “ that’s acceptable “ .

So , need to be careful not too mention that too much …

Are steels ( standard red/brown coating ) not fire rated anyway ???

Link to comment
Share on other sites

36 minutes ago, joe90 said:

Surely if covered in a 30 min fire retardant ceiling the steels are not exposed ? Was this not specified in your architects drawings? What does your ceiling consist of?

Further listening to his conversation suggests the concern was fire say by cabling above the ceiling and below the steels .

Going to find steel spec 

  • Sad 1
Link to comment
Share on other sites

1 minute ago, Pocster said:

Further listening to his conversation suggests the concern was fire say by cabling above the ceiling and below the steels .

That’s fair enough, however the BCO should have given you a definitive answer on his previous visit, not “it may do”

Link to comment
Share on other sites

No luck with original steel company. They don't have any spec that covers fire rating and don't fire coat their steels.

The steel guy thought the BCO was just being pedantic.

 

BCO also wants " We still also require sign off (from G3 ‘Registered operative’) for the unvented hot water tank" - which I assume is just a magic bit of paper.

Link to comment
Share on other sites

What's the steel doing? Strictly only needs protection if it's supporting a means of escape.

 

But otherwise, your BCO is correct, 30mins fire protection needed. Are you ceiling panels not easy to remove to get access?

Link to comment
Share on other sites

17 minutes ago, Conor said:

What's the steel doing? Strictly only needs protection if it's supporting a means of escape.

 

But otherwise, your BCO is correct, 30mins fire protection needed. Are you ceiling panels not easy to remove to get access?

What about if no mains cabling crosses under the steel ? I.e no chance of a fire above the ceiling under the steel ? . My low voltage lighting goes direct to the perimeter I.e ring main for lighting is around the edge - so technically lighting wiring ( only thing above the ceiling ) doesn’t go under steel . That sound valid argument? 🤔

Link to comment
Share on other sites

19 minutes ago, Conor said:

What's the steel doing? Strictly only needs protection if it's supporting a means of escape.

The steels are used to create the stairwell . So you could argue a means of escape . But equally there are nice sliding doors to permit escape in the event of fire .

I always wonder what type of fire we’re expecting that will cause structural steel rated at 350% over spec by SE to fail …

Link to comment
Share on other sites

Are all you electric cables wired in to a modern consumer unit with RCBOs etc? Then I'd argue the risk of electrical file is minimal and if the ceiling is 30min rated then you're golden. We've only painted two of our steels, the main mezzanine steels are protected by 30min rated ceiling. 

 

The point of fire protecting steels is to ensure that the building stays up long enough for escape. A smouldering electrical cable isn't going to bother an RSJ.

  • Like 2
Link to comment
Share on other sites

5 minutes ago, Conor said:

Are all you electric cables wired in to a modern consumer unit with RCBOs etc? Then I'd argue the risk of electrical file is minimal and if the ceiling is 30min rated then you're golden. We've only painted two of our steels, the main mezzanine steels are protected by 30min rated ceiling. 

 

The point of fire protecting steels is to ensure that the building stays up long enough for escape. A smouldering electrical cable isn't going to bother an RSJ.

Yep all modern rcbo , cu etc etc .

Might see if I can get electrician to write something …

Not played this card with bco yet …

Link to comment
Share on other sites

5 minutes ago, Super_Paulie said:

cant you just lash it with intumescent paint as it is and its job done? Rawlins will give you a certificate regardless of how well its been applied and that will be enough to satisfy BC.

Yeah I could . But it is a pita . Ceilings a pain to access across the entire width of the property. Just trying to avoid work !

Whats this Rawlings certificate?? I need to look into that ….

Link to comment
Share on other sites

19 minutes ago, Super_Paulie said:

cant you just lash it with intumescent paint as it is and its job done? Rawlins will give you a certificate regardless of how well it’s been applied and that will be enough to satisfy BC.

Just spoke to Rawlings . They won’t issue a certificate unless a professional contractor has applied it . Not for “ diy “ use ….

Edited by Pocster
  • Sad 1
Link to comment
Share on other sites

Winner winner chicken dinner !

 

Sent an appropriate email about poor service , lack of work required list after bco viewings etc etc etc 

Said once I get the G3 thing in then all passed and completion certificate issued .

 

@ToughButterCup just checked the dictionary..

 

Legend = Pocster 

 

Pocster = ( see Legend ) .

  • Like 5
  • Thanks 3
Link to comment
Share on other sites

4 hours ago, ToughButterCup said:

 

It may or may not be. 

 

You @Pocster are a legend. We all  know that, you know that. But the BCO doesn't.

Convince him of your legendary status as somebody who conserves energy - nervous energy - and just bloody does it instead of worrying about it.

Better put  JustBloodyDoIt - JBDI

Get the wheelbarrow !

 

Why ?

 

Got to get my extra large testies in there !

 

Legends aren’t born . They are made !

 

Party !!

 

Legend !

 

🍾🍷

 

Party on !!! L-E-G-E-N-D !

  • Like 1
  • Haha 2
Link to comment
Share on other sites

2 hours ago, Pocster said:

Just spoke to Rawlings . They won’t issue a certificate unless a professional contractor has applied it . Not for “ diy “ use ….


thats weird, that never used to be the case at all.
Still, good news on the sign off.

Edited by Super_Paulie
  • Thanks 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...