Marvin Posted May 28, 2023 Share Posted May 28, 2023 Does the electrician need to put a breaker in the tails as they are 4 meters long? Different DNO's seem to say different things. Also told that Tails must be surface mounted in trunking. Client doesn't want this!! Oh happy days. Link to comment Share on other sites More sharing options...
TonyT Posted May 28, 2023 Share Posted May 28, 2023 Not a breaker a fuse Dno fuse protects tails for the first 3 m anything else your own fuse is required. 2 Link to comment Share on other sites More sharing options...
Temp Posted May 28, 2023 Share Posted May 28, 2023 1 hour ago, Marvin said: Also told that Tails must be surface mounted in trunking. Client doesn't want this!! I believe tails buried less than 50mm would need to be RCD protected in the meter cabinet. Many houses (mine included) have them run in the cavity but I don't think that's really allowed if you go by the book. Might be possible to use SWA tails not buried over 50mm but I'm not an electrician. 1 Link to comment Share on other sites More sharing options...
TonyT Posted May 28, 2023 Share Posted May 28, 2023 Yes would need 30mA RCD protection if under 50mm. so make the wall thicker at this point 😁or as Temp says run Swa surface to forgo the RCD protection. 1 Link to comment Share on other sites More sharing options...
Marvin Posted May 28, 2023 Author Share Posted May 28, 2023 1 hour ago, TonyT said: Not a breaker a fuse DNO fuse protects tails for the first 3 m anything else your own fuse is required. Hi @TonyT Thanks for this. Does this mean a 30ma RCD can be in the meter box at the start of the 4 meter tails? Link to comment Share on other sites More sharing options...
dpmiller Posted May 28, 2023 Share Posted May 28, 2023 depends, might need to be 100mA time delay to give sufficient discrimination 1 1 Link to comment Share on other sites More sharing options...
Marvin Posted May 28, 2023 Author Share Posted May 28, 2023 18 minutes ago, dpmiller said: depends, might need to be 100mA time delay to give sufficient discrimination Between the inline and the consumer box one?? Link to comment Share on other sites More sharing options...
Nickfromwales Posted May 28, 2023 Share Posted May 28, 2023 49 minutes ago, dpmiller said: depends, might need to be 100mA time delay to give sufficient discrimination Only required if 2 differing RCD's are employed pre-CU? I've only ever installed an 80a switch-fuse at the meter when conveying tails of 3+m and above, and this is never a problem (no RCD required for the last few) but I'm not over the 18th edition like a rash tbh. If run in SWA there should be no requirement for RCD, but it may be requisite where the tails are sub 50mm from surface. You can screw into a live tail and make the fixing live, but with a SWA you'd have to short live to steel armour, so the tails need to be further away from 'attack' and the SWA less so. 1 Link to comment Share on other sites More sharing options...
Mattg4321 Posted May 29, 2023 Share Posted May 29, 2023 10 hours ago, dpmiller said: depends, might need to be 100mA time delay to give sufficient discrimination This won’t comply. If cables are run less than 50mm within the wall they need 30mA RCD protection. Either run swa, bury the tails deeper, or cover them with something impenetrable by sds drill - 3mm steel plate etc. 2 Link to comment Share on other sites More sharing options...
Nickfromwales Posted May 29, 2023 Share Posted May 29, 2023 3 hours ago, Mattg4321 said: 3mm steel plate etc. That's what I did on a build in Gravenhill. MBC TF so only a 35mm service cavity to lose the tails within, and SWA just would have been impossible to get where I needed it to go. Flat bar from B&Q iirc, and shows up well with a stud / metal finder. Link to comment Share on other sites More sharing options...
dnb Posted May 30, 2023 Share Posted May 30, 2023 It depends on the earthing scheme to a point as well. I'm on a TT earth so ended up with SWA and a 100mA RCD + 80A switch fuse box. (But my tails were a slightly silly 20 metres...) Suspect you are on TNCS earth so you'll only need SWA or RCD. I do have a blue book, but I left it on site - @Marvin happy to let you have a read of it and the on-site guide if you want since you're local to me. I might even have a spare length of 25mm2 SWA getting in the way, although it might be a fraction too short. 1 1 Link to comment Share on other sites More sharing options...