Insulating window reveal timber frame new build


benben5555

Recommended Posts

Is insulated plasterboard the way to go here? Any suggestions on thickness? Also shall I advise the timber frame company to widen the structural opening to allow for the insulation? I.e. for the timber frame opening to be wider than the brickwork to allow for the extra thickness of insulation?

Link to comment
Share on other sites

What are your window frames made from?

 

If it's something thermally good like UPVC or a properly thermally broken Wooden frame the gains are very marginal if not negligible. 

 

Increasing the opening size, you'll end up with a slightly better psi value at the window wall join at the expense of a larger area of structural headers, jambs, and sills. 

 

I would concentrate on making sure all headers are thermally broken and all jambs and sills are continuously externally insulated or internally insulated.  

 

 

Link to comment
Share on other sites

PIR to the reveals and then plasterboard on top. Much better chance of getting a continuous insulation layer and less waste too. Airtightness trumps any thermal bridging however. 

 

Have you committed to this wall build-up? @Thorfun did similar recently and I think would have changed their mind given the labour involved. 

 

 

I'll have a pop at a therm model tomorrow if I get a chance. 

Link to comment
Share on other sites

Here are some mock-ups. 80mm thick simplified window. 30mm in the brick, 50mm in the cavity. 

 

No insulation inside or out. U value 0.6985. Lots of heat loss at the corner. 

 

 

image.thumb.png.9911a2667f93ef990f7064b03c88b568.png

image.thumb.png.10ea8ef34dc31495d4f4672210ed5a79.png

 

No insulation inside or out. 

 

 

Edited by Iceverge
Link to comment
Share on other sites

2 minutes ago, benben5555 said:

I've never seen these kind of models before. Really helpful in showing the best approach. What is the software called?

 

THERM. It's a PITA to setup and use but it is free for PC's. it gives a good idea graphically of what actually makes much difference if nothing else. 

 

From above from best to worse. 

 

1. 150mm sock and pir cheek.  0.5946 

2. 75mm sock and pir cheek. 0.6037  = best - 0.0091

3. pir cheek only 0.6285 = best -0.0292

4. 75mm sock only. 0.6275 = best -0.0329

5. Nothing. 0.6985 = best 0.0091 -0.1039  

 

 

All figures in W/mK. 

 

So if you have 100m of window perimeter to consider on a cold day with temp outside of 0 and inside of 20

 

Your difference in heat loss will be 100m*20deg*0.1039W/mK = 208watts of extra heating. 

 

At a guesstimate using 100 heating days per year and an average outside temp of 9 deg and gas heating

 

It'll equate to. 

 

100days*24hrs*9deg*208*15p per unit *80 % boiler efficiency........ = £93.60 extra per year going from no insulation to best insulation.  

 

  • Like 1
  • Thanks 1
Link to comment
Share on other sites

Sorry but that model is wrong - therefore the numbers for the psi-value (not U-value) are probably wrong too. THERM is not particularly intuitive when pulling together the basic model (in fact it's downright difficult), the numbers generated need further manipulation to generate the psi-value and the calculation  must follow set conventions. Depending upon the geometry, cavity closer and position of the window I would expect a psi-value for the jamb to be approx 0.07 - 0.10 W/mK 

Link to comment
Share on other sites

Hi @ADLIan. I'm only trial and erroring here so don't take any of the above for gospel. What have I got wrong?

 

The big numbers above are only U-values for the total 2m section of wall using a simple window. I used these as it's easy to read off the numbers from THERM. 

 

I didn't try to calculate any psi values but just the different overall U values between each buildup which should be representative of the different heat loss with and without insulation. 

 

 

 

 

 

 

 

 

 

 

Link to comment
Share on other sites

@ADLIan @benben5555

 

Looking back over those THERM drawings yesterday I had a completely b*llocks value for the thermal conductivity of the window. Almost an order or magnitude worse than reality. 

 

Cover as much of the frame with insulation as possible remains the mantra. 

 

I'll try to post a better drawing shortly. 

 

 

 