richo106 Posted September 8, 2022 Share Posted September 8, 2022 Hi All At the beginning of our project is was simply to convert a bungalow into a house and then after speaking to few people I became a lot more aware of air tightness and the use of MVHR At the minute the plan is to make the house as airtight as possible and have a MVHR installed. Going triple glazed throughout and a good level of insulation...floor 0.11, ceilings 0.13, walls 0.18 We will be adding another floor to our existing bungalow What are the key things to consider and make sure I do when it comes to air tightness? I will be parge coating all my walls before insulating internally/plasterboarding Is it best to get it routinely tested for air tightness at certain parts of the build? And a big question...is it worth it going down the air tightness and MVHR route? Thanks in advance Link to comment Share on other sites More sharing options...
joe90 Posted September 8, 2022 Share Posted September 8, 2022 17 minutes ago, richo106 said: And a big question...is it worth it going down the air tightness and MVHR route? Yes, if your insulation is up to a decent level as well. Link to comment Share on other sites More sharing options...
SteamyTea Posted September 8, 2022 Share Posted September 8, 2022 You have to make sure that your insulation cannot be wind washed. That would bypass all advantages. Then you have to consider condensation risk. 1 sheet of glass or 3 in the windows does not affect airtightness, it is the seals and joint to the openings that is important. There is thermal bridging to take into account here. Frequent testing is important if it can be done cheaply. If you get to 1 ACH then MVHR is important. I think there is a limit where forced ventilation becomes compulsory (<3 ACH?). Can you improve the U-Value the walls and ceilings? Ceiling especially, walls depend on the total exposed area. Link to comment Share on other sites More sharing options...
richo106 Posted September 8, 2022 Author Share Posted September 8, 2022 Unfortunately with our design the only way to improve u values of the walls is internal insulation (already planning to have 50mm PIR in the existing bungalow) Ceilings I can What do you mean by wind washed? The more I look into ACH and MVHR the more I think i could be wasting my time and money trying to achieve it Thanks again Link to comment Share on other sites More sharing options...
jayc89 Posted September 8, 2022 Share Posted September 8, 2022 17 minutes ago, richo106 said: Unfortunately with our design the only way to improve u values of the walls is internal insulation (already planning to have 50mm PIR in the existing bungalow) Ceilings I can What do you mean by wind washed? The more I look into ACH and MVHR the more I think i could be wasting my time and money trying to achieve it Thanks again I'm in a similar boat. We'll likely reach 0.15 floor, 0.10 loft, but walls will be nearer 0.18, given our size constraints, due to being internal wall insulation. I plan on addressing airtightness as a matter of course when fitting the IWI, however I don't think I can justify a full MVHR system, so will likely replace windows with trickle vents and dMEV in certain rooms for ventilation. Not perfect, but I'm beginning to accept it as a "happy medium" for our property. It will significant reduce our energy usage regardless. Link to comment Share on other sites More sharing options...
SteamyTea Posted September 8, 2022 Share Posted September 8, 2022 (edited) 22 minutes ago, richo106 said: What do you mean by wind washed? If cold outside air can blow around, or though, insulation. This is a particular problem with mineral wool insulation. Edited September 8, 2022 by SteamyTea Link to comment Share on other sites More sharing options...
jayc89 Posted September 8, 2022 Share Posted September 8, 2022 17 minutes ago, SteamyTea said: If cold outside air can blow around, or though, insulation. This is a particular problem with mineral wool insulation. I guess that's the benefit of parging before fitting insulation to the internal face of brick walls. Link to comment Share on other sites More sharing options...
SteamyTea Posted September 8, 2022 Share Posted September 8, 2022 2 minutes ago, jayc89 said: guess that's the benefit of parging before fitting insulation to the internal face of brick walls. Yes, integral face of the external brickwork. There are also cavity closers for openings, they need to be fitted well. Link to comment Share on other sites More sharing options...
richo106 Posted September 8, 2022 Author Share Posted September 8, 2022 Thanks all for the comments I really am stuck in two minds what to do I will still be insulating as much as I can and will be mindful of Air tightness but as I will be renovating/extending and existing bungalow I am thinking to get ACH down to 3 will prove very difficult. As we are 'off grid' I will be using ASHP with UFH downstairs and upstairs Similar to Jay I don't know if I can now justify a full MVHR system, this will also negate the reason to have posi joists further saving money Would I now need trickle vents in all new windows and also dMEV extractors in downstairs toilet, bathrooms * 2? What about kitchen extract? I would love some opinions on this and I am now rather confused in what to do Link to comment Share on other sites More sharing options...
SteamyTea Posted September 8, 2022 Share Posted September 8, 2022 9 minutes ago, richo106 said: I would love some opinions on this and I am now rather confused in what to do Have you thermally modelled your house? You can then change things and see what is important and what is not. I find it easier to set a total target energy use for a building, then see what needs to be changed to achieve it. Using a metric like kWh.m-2.y-1 is pretty pointless as it takes no account of the buildings form. Link to comment Share on other sites More sharing options...
JohnMo Posted September 8, 2022 Share Posted September 8, 2022 Look into humidity controlled MEV and dMEV. Basically the trickle vent will open and close as required and the fans like wise. Overall a lower running cost compared to MVHR, no filters, and good energy conservation. Some bedtime reading. Atamate_SDAR+Paper+2019+(1).pdf 1 Link to comment Share on other sites More sharing options...
Radian Posted September 8, 2022 Share Posted September 8, 2022 I must fit some sort of active shutter to an extractor fan in our downstairs loo. I was puzzling over a uniform layer of dark grey dust on the lid of the toilet cistern when it dawned on me that the day before I'd been in the garden sanding a painted picnic table! 1 1 Link to comment Share on other sites More sharing options...
JohnMo Posted September 8, 2022 Share Posted September 8, 2022 (edited) MEV and dMEV run 24/7, so not sure you need a shutter. Do the same in the kitchen and cooker hood set up to recycle. Edited September 8, 2022 by JohnMo Add kitchen bit Link to comment Share on other sites More sharing options...
richo106 Posted September 8, 2022 Author Share Posted September 8, 2022 1 hour ago, SteamyTea said: Have you thermally modelled your house? You can then change things and see what is important and what is not. I find it easier to set a total target energy use for a building, then see what needs to be changed to achieve it. Using a metric like kWh.m-2.y-1 is pretty pointless as it takes no account of the buildings form. No I have not thermally modelled my house...I will work through the spreadsheet today and see what I can play with. Link to comment Share on other sites More sharing options...
Radian Posted September 8, 2022 Share Posted September 8, 2022 12 minutes ago, JohnMo said: MEV and dMEV run 24/7, so not sure you need a shutter. It'd have to be fairly powerful to keep the wind out! The actual fan is OK as is, the usual type operated by the light switch - but modified by me to use a 140mm PC case fan after going through a series of noisy expelairs! Almost imperceptible now, instead of something that sounded like a food mixer. Link to comment Share on other sites More sharing options...
richo106 Posted September 8, 2022 Author Share Posted September 8, 2022 I thought I had all this planned out....how wrong I was haha. Back to the drawing board My thoughts have now turned to saving my money on the MVHR and potentially use some of that money increase insulation I will still try to make as air tight as possible but with the original bungalow and large glass oak front section I think it will very very hard to get down to the ACH level required to make the MVHR cost effective/worthwhile Will my windows now need trickle vents in? I am looking into other ventilation options (dMEV) As i will be having an ASHP I do want it as low cost to run as possible but within reason weighing up budget etc.. Link to comment Share on other sites More sharing options...
JohnMo Posted September 8, 2022 Share Posted September 8, 2022 dMEV are silent also, not the same as a normal bathroom fan. A few watts to run each. 1 Link to comment Share on other sites More sharing options...
JohnMo Posted September 8, 2022 Share Posted September 8, 2022 (edited) You don't have to have trickle vents, things like this are also available from various manufacturers https://www.aereco.co.uk/products/air-inlets-uk/eht/ https://www.bpdstore.co.uk/glidevale-energy-saver-humidity-sensitive-trickle-ventilator/p/182 Edited September 8, 2022 by JohnMo Added second link Link to comment Share on other sites More sharing options...
richo106 Posted September 8, 2022 Author Share Posted September 8, 2022 https://www.bpcventilation.com/extractor-fans/c-mev/vent-axia Would something like this work? Thanks again Link to comment Share on other sites More sharing options...
JohnMo Posted September 8, 2022 Share Posted September 8, 2022 Would work, but Something like this would be much better or something from Duco or passivent https://www.ventilationland.co.uk/product/44535/itho-daalderop-cve-s-s-co2-optima-inside-package-hp-415-m-h-plus-build-in-rv-humidity-sensor-and-co2-sensor-plus-4-ventilation-valves-plus-auto-rf-control-perilex-plug.html Then you just demand controlled inlet and you are good to go. Link to comment Share on other sites More sharing options...
richo106 Posted September 9, 2022 Author Share Posted September 9, 2022 I have spoken to passivent and they recommended there sister company Glidevale and their fully passive iPSV system As you can tell I am new to this area of ventilation so trying to learn which would be best Thanks again Link to comment Share on other sites More sharing options...
richo106 Posted September 9, 2022 Author Share Posted September 9, 2022 On 08/09/2022 at 09:59, SteamyTea said: Have you thermally modelled your house? You can then change things and see what is important and what is not. I find it easier to set a total target energy use for a building, then see what needs to be changed to achieve it. Using a metric like kWh.m-2.y-1 is pretty pointless as it takes no account of the buildings form. I have completed the excel sheet linked (very good sheet) however I haven't got a ACH target. Speaking to a friend in the 'know' he says I could possible get to ACH 3. Is this easily achievable? Link to comment Share on other sites More sharing options...
SteamyTea Posted September 9, 2022 Share Posted September 9, 2022 Just now, richo106 said: Speaking to a friend in the 'know' he says I could possible get to ACH 3. Is this easily achievable? Achievable, but if that is easy is another matter. What you can do is play with the ACH figure and find out what sort of ventilation is worthwhile. Don't forget you can get single room heat recovery units. Link to comment Share on other sites More sharing options...
richo106 Posted September 9, 2022 Author Share Posted September 9, 2022 I have done some scenarios with MVHR at 0% and 85% and ACH at 7 and 3. Obviously a massive difference but would there be another system that would help total heat loss instead of MVHR? What other benefits do MVHR give? What are peoples thoughts of the scenarios i have done? Thanks again, really appreciate the replies Total House Heat Loss - Scenarios.docx Link to comment Share on other sites More sharing options...
SteamyTea Posted September 9, 2022 Share Posted September 9, 2022 9 minutes ago, richo106 said: would there be another system that would help total heat loss instead of MVHR Not really, it is just physics. MVHR gives you controlled ventilation, and to a certain extent, controls humidity, while also recovering energy. Mechanical ventilation does the same, but without the heat recovery. You can, if you want, just pump external air into the building and hope that there are enough, evenly spaced, leaks that the system works. I am currently improving my airtightness, in my already good house. For ventilation I will, for this winter, just open a window. Link to comment Share on other sites More sharing options...