New build - cold bedroom


Littlebig

Recommended Posts

In all fairness this was the first time a someone has given such a detailed explanations about his findings. He also mentioned that instead of 8 bags of insulation material(as per specification) the used 9 so he was very confident in saying there is no problem with insufficient insulation.

I also mentioned he suggested draughts as the main issue, this was after he finished his inspection and the 2 main points of draughts was the main front door and the loft hatch and this was concluded after the thermal imaging survey and it was obvious on the pictures.

Also in the small bedroom and bathroom was noted that the loft insulation has been pulled too far back to unblock the vents and has caused an issue where cold air could penetrate the cavity and all it needs doing is to fold the loft insulation into the cavity.

(The attached picture is just an example of what I was able to see on his camera.)

But I’m not sure this is the reason for the cold air in there, so again someone knowledgable maybe will be able to say what is the cause. 

F2E1A1A5-3564-46F8-BE66-DF4BBB9EA096.png

Link to comment
Share on other sites

2 hours ago, Littlebig said:

In all fairness this was the first time a someone has given such a detailed explanations about his findings. He also mentioned that instead of 8 bags of insulation material(as per specification) the used 9 so he was very confident in saying there is no problem with insufficient insulation.

I also mentioned he suggested draughts as the main issue, this was after he finished his inspection and the 2 main points of draughts was the main front door and the loft hatch and this was concluded after the thermal imaging survey and it was obvious on the pictures.

Also in the small bedroom and bathroom was noted that the loft insulation has been pulled too far back to unblock the vents and has caused an issue where cold air could penetrate the cavity and all it needs doing is to fold the loft insulation into the cavity.

(The attached picture is just an example of what I was able to see on his camera.)

But I’m not sure this is the reason for the cold air in there, so again someone knowledgable maybe will be able to say what is the cause. 

F2E1A1A5-3564-46F8-BE66-DF4BBB9EA096.png

Thats an excellent thermal image of why dot and dab is so bad!!

 

Without ripping it all off, you could drill holes along the perimeter all way round, but only where it sounds hollow, the solid bits will be where the dots are, and inject some FM330 airtight expanding foam, but not silly amounts, this should seal the gaps up.

 

In my experience though, its slightly pointless, you would need to do top, bottom, and corners, but even then, a crack in the mortar or blockwork (very common with most traditional masonry construction methods), will again let air circulate in the cavity between plasterboard and blockwork. Its a very hard problem to solve without taking everything off and wet plastering. You may be lucky and get a parge coat which would possibly solve the cracking issue, but if its a developer house, i wouldn't expect that. Expanding foam top bottom and corners inbetween the dots may give you some resolution.

Link to comment
Share on other sites

4 hours ago, MikeGrahamT21 said:

Thats an excellent thermal image of why dot and dab is so bad!!

 

Without ripping it all off, you could drill holes along the perimeter all way round, but only where it sounds hollow, the solid bits will be where the dots are, and inject some FM330 airtight expanding foam, but not silly amounts, this should seal the gaps up.

 

In my experience though, its slightly pointless, you would need to do top, bottom, and corners, but even then, a crack in the mortar or blockwork (very common with most traditional masonry construction methods), will again let air circulate in the cavity between plasterboard and blockwork. Its a very hard problem to solve without taking everything off and wet plastering. You may be lucky and get a parge coat which would possibly solve the cracking issue, but if its a developer house, i wouldn't expect that. Expanding foam top bottom and corners inbetween the dots may give you some resolution.

I guess your explanation is confirming my first thought. The constant ribbon of adhesive along the top that should prevent airflow and thermal bypass is basically not there? Unfortunately like your saying not an easy fix and will have to contact the builder and see what their proposition will be to resolve it.

Link to comment
Share on other sites

9 hours ago, PeterW said:

Definitely not ok !!!! Should be full to the top..!!

 

installation will be warranted by the CWA (Cavity Wall Association) so they should take this up  

Are you saying I get in touch with the CWA and explain my problem so they can come and have a look and get it sorted free of charge and hopefully in a much more professional manner than the contractor/builder?

Link to comment
Share on other sites

1 hour ago, Littlebig said:

I guess your explanation is confirming my first thought. The constant ribbon of adhesive along the top that should prevent airflow and thermal bypass is basically not there? Unfortunately like your saying not an easy fix and will have to contact the builder and see what their proposition will be to resolve it.


absolutely, there should as a minimum be a continuous bead of adhesive along both top and bottom of the plasterboards, pretty sure that’s been the official guidance from PB manufacturers for a good while

Link to comment
Share on other sites

50 minutes ago, PeterW said:

Contractor has a legal responsibility to resolve if this is a new build but also CWA will hold the warranty so if not resolved then they will act.

Thank you. It is a new build (just over a year old) and I will contact the builder tomorrow and inform them of my findings. I assume they will conduct some sort of investigation but from my previous experience dealing with them I’m not optimistic.
In my opinion if there is a part of the cavity with such big gaps of no insulation I assume the whole house could be like this and will request a full cavity survey. No idea whether they will even acknowledge there could be a problem with the cavity insulation as the heat survey would suggest otherwise. I guess then I either contact the NHBC or the CWA  or both, but I wouldn’t know the name of the company that has done the insulation.

Link to comment
Share on other sites

Your thermal image appears to show a poorly sealed window trickle vent. I suspect that if you apply finger pressure to it, you'll notice a reduction of noise coming from outside. Maybe not fitted correctly, or in common with most trickle vents, just crap.

Link to comment
Share on other sites

On 27/02/2023 at 13:16, Littlebig said:

Also in the small bedroom and bathroom was noted that the loft insulation has been pulled too far back to unblock the vents and has caused an issue where cold air could penetrate the cavity and all it needs doing is to fold the loft insulation into the cavity.

This is the problem with eaves ventilation, made worse by the house not being timber frame. At least that would ensure insulation to the top of the wall and not have dot and dab plasterboard.

 

Looking at the picture, it appears that you have cold air getting behind the plasterboard at the top and the insulation ends before the end of the ceiling. The question is can you actually get it into the cavity without blocking the vents. Also if those vents were working you wouldn't;t have condensation in the roof.

 

Sealing the top of the dot and dab should be relatively easy. If you can access the top edge of it you could seal it with spray foam from there or by drilling small holes and injecting foam. It won't be perfect but should make a big difference.

 

Clearly the loft insulation has to extend to the edges also. Due to the issue with the eaves being ventilated, I wonder if cutting pieces of PIR to sit between the ceiling joists would be a better idea.

 

Looking at the pictures it also appears that despite their claims there is not enough insulation in the walls. If there was you wouldn't be able to see all those voids.

 

 

Link to comment
Share on other sites

  • 2 weeks later...

Thanks for all the replies. Currently the house is wrapped in scaffold as I’m hoping to get the roof fixed finally.

I am also diverting my attention to the front door that will highly likely need replacing.

I’m in the process of assessing the best location for a light in the loft so I can then either tuck the insulation behind or use PIR as recommended.

Either way I think I will do it all myself as chasing the builder seems like a waste of time and effort.

With regards to the voids in the cavity insulation hopefully they will send someone competent to get it all done and we feel the full benefit of a well insulated new build next winter.

Link to comment
Share on other sites

If youve got scaffolding up, can you remove/push up the first row of tiles and fix the entire perimeter of wallplate to ceiling junction and cavity to loft insulation join. I did this when we were replacing the soffits and facias. Hell of a job but worth it.  I taped and used airtight expanding foam between wall plate and plasterboard. We then added Dritherm 32 cavity batts to the cavity where it was missing as well as enough to over lap the wall plate. We used wall ties to hold the insulation tight in those areas. In the hard to insulate areas where the hip sat on the wall plate I added pir board and foamed it in. We took all the plasterboard off the external walls and used airtight paint and foam from below and overboarded the ceiling. All made a massive difference. 

Link to comment
Share on other sites

  • 1 year later...

Hi. Not sure if anyone will see this but I was searching around for this exact topic and found this so felt it my duty to respond with my findings :)

 

I have a new build (~2018), north and north/east facing rooms/bathrooms have always been cold, like ice-boxes in the winter.

 

After just making do and then going through covid, this year I'd had enough and thought this cannot be right! After reading through the replies here and asking around I was about to pay for someone to come round to inspect our wall insulation. I thought I'll just go into the roof first to see if I can see anything obvious..... well, I noticed a few gaps in the roof insulation and some insulation just randomly lose on top of another covered area. I simply "fluffed up" here and there and moved the lose bits to cover gaps. Honestly I'm amazed at the difference. I've bitten the bullet and bought a Hive thermostat and a few smart radiator valves to put into those cold rooms and to have easier control over adding heat to those rooms when needed (i.e. guests), but just simply fluffing up in the roof has already made a huge difference and I'm amazed.

 

So - if you have a new build and its passed building regs, aside from a major screw up I'd be surprised if there was anything majorly wrong with your wall insulation. If a room is north facing, and has a window on the north and east sides like mine then it will feel colder than other rooms. BUT, I would recommend checking in your roof before forking out for any inspections etc.

 

I've gone extra in going for smart heating but that is a personal choice and technically not completely required. I'm hoping though it makes putting the heating on more efficient and I will have easier control of what comes on when and to what temp.

 

That's my two pennies on this subject - hope it helps someone :)

  • Like 3
  • Thanks 1
Link to comment
Share on other sites

Similar to above post, I put alot of work into making good our new build (Taylor Wimpey) as we had similar problems in a upstairs bedroom.

Using a thermal camera image it showed the roof joists, similar to the images posted. The loft insulation was very badly thrown in and needed completely reseating.

I also foam filled the ceiling joist closest to the external wall as this was a 30mm uninsulated gap. This ran from one side of the house to the other.

Rather than poke insulation into the gap, I opted to fill it with foam, using a foam gun, that way I could air seal the edge of the ceiling plasterboard at the same time.

I also measured the loft insulation as I was under the impression it should have been 270mm for regs. I think it was under 150mm. When queried, the site foreman promptly sent round the loft insulation people and another layer was thrown in.

Once rearranged and laid in right angles to the existing rolls of insulation, the house heat loss was much less. 

Thermal imaging in the same area confirmed the work was good.

 

Worth checking if you have cavity closers fitted as you could be getting windwash up through the cavity.

That condensation needs to be addressed and shows the air leaks you have from the conditioned living space below into the loft, taking with it warm, moist air which is condensing on the cold fabric and roof joists. Will soon turn to mould and eventually rot.

Check the loft hatch closes against a seal and the hatch frame is seated flush to the ceiling. The hatch is a huge opening and should be addressed first.

Also check any ventilation from bathrooms/showers upstairs are vented outside. All of my ventilation hoses had been covered with insulation and flattened!

 

Since moved from the new build to a cold older house and starting the insulation journey once more.

Good luck with your investigation and do not believe a word the house-builders say - always fact check.

Link to comment
Share on other sites

On 03/12/2024 at 12:12, TheMikeG said:

If you have a new build and its passed building regs, aside from a major screw up I'd be surprised if there was anything majorly wrong with your wall insulation. 

I have some experience of helping people with poorly constructed  newbuilds.

I understand that some developers are thorough and have good reputations. Of course i haven't been asked to look at them.

 

Do not assume that builders are all competent, that site management is thorough or that a bco has inspected every element.

 