is it water or is it you dont get a 7.9kw heat pump? so they have said 10kw?

I forgot about the water, so a 10 kW seems about right.

would still get someone to do a proper room by room heat loss calculation.

You can download the MCS spreadsheet and have a go at it yourself.

On this page under Heat Pumps

https://mcscertified.com/standards-tools-library/

Link to comment
Share on other sites

4 minutes ago, SteamyTea said:

I forgot about the water, so a 10 kW seems about right.

would still get someone to do a proper room by room heat loss calculation.

You can download the MCS spreadsheet and have a go at it yourself.

On this page under Heat Pumps

https://mcscertified.com/standards-tools-library/

Thanks mate, i was on the phone to Grant this morning they said with a Heat loss(carried out roughly by Valliant) at 7.9 at -3.4 there 10kw unit would just about suffice as at -3 degrees there 10kw unit at 50 degrees flow rate puffs out 8.5kw heat outout. but they have said a proper heat loss needs to be carried out as valliant could of just been rough they dont know.

Link to comment
Share on other sites

21 minutes ago, Mike_scotland said:

Thanks mate, i was on the phone to Grant this morning they said with a Heat loss(carried out roughly by Valliant) at 7.9 at -3.4 there 10kw unit would just about suffice as at -3 degrees there 10kw unit at 50 degrees flow rate puffs out 8.5kw heat outout. but they have said a proper heat loss needs to be carried out as valliant could of just been rough they dont know.

Have you done a heat loss calc, using the spreadsheet on buildhub?  If you do you will know what you heat losses are.  You can then tell them they are wrong or right.  Because you seem to be round in circles.

Link to comment
Share on other sites

1 minute ago, JohnMo said:

Have you done a heat loss calc, using the spreadsheet on buildhub?  If you do you will know what you heat losses are.  You can then tell them they are wrong or right.  Because you seem to be round in circles.

can you send the heat loss calc?

Link to comment
Share on other sites

1 hour ago, Mike_scotland said:

Air changes per hour ?? is this the air tightness test?

No, air changes per hour is the number of complete complete air changes in the property or room… if volume of building is 100 cubic metres and 2 changes per hour required, then ventilation system needs to be 200 cube per hour minimum.

or you need to heat/cool 200 cube per hour to maintain temp

Edited by markc
Link to comment
Share on other sites

30 minutes ago, markc said:

No, air changes per hour is the number of complete complete air changes in the property or room… if volume of building is 100 cubic metres and 2 changes per hour required, then ventilation system needs to be 200 cube per hour minimum.

or you need to heat/cool 200 cube per hour to maintain temp

how do i find that out?