February 3, 20215 yr Can somebody do some rough number crunching for me please. There has been a bit of talk lately about block walls with just external eps insulation, so wondered where it comes out U value wise. From the inside out. 12.5 plasterboard 25 mm service batten 150mm dense concrete blocks 130mm eps 100 25mm batten timber cladding. Thanks, oh clever ones.
February 3, 20215 yr https://www.uvalue-calculator.co.uk/calculator/ https://www.changeplan.co.uk/u_value_calculator.php You add the R values for each material and then 1/R = the U value.
February 3, 20215 yr i get it calculated to 0.21, you can get it to 0.19 if you use a lightweight block of R value 0.25.
February 3, 20215 yr Since the cavity (layer 5) is fully ventilated layers 5 & 6 are by convention not included but the external resistance, which is actually at the outside of layer 4, can be increased to 0.13 because the reduced average air movement increases the thickness of the external surface layer. See page 12 of attached pdf. BR_443_(2006_Edition).pdf
February 3, 20215 yr 53 minutes ago, A_L said: Since the cavity (layer 5) is fully ventilated layers 5 & 6 are by convention not included but the external resistance, which is actually at the outside of layer 4, can be increased to 0.13 because the reduced average air movement increases the thickness of the external surface layer. See page 12 of attached pdf. Cheers, that ups the U-value to 0.22. Edited February 3, 20215 yr by Moonshine
February 3, 20215 yr Another one for you with a few more facts and figures Also another config with Aircrete: Edited February 3, 20215 yr by MikeGrahamT21
Create an account or sign in to comment