maximum drainage run for 110mm soil pipe.

Featured Replies

I have permission for  a holiday cabin 250 from my treatment pant and I can find any details on pipe size , chamber spacing's and fall for that distance of run. (max occupancy 4 persons) I have plenty of fall but i cant find any details in building regs. Any advice appreciated. 

 

 

There is a requirement for inspection chambers at intervals so you don't end up with 10 sets of drain rods trying to rod a 250M run with no access.

I have two holiday cabins and they both have their own treatment systems. 

Is there a reason to go that distance I can see it being a pain. 

Materials to connect it will be in excess of £800, that’s without digging the trench. 

You can pick up a small plant for a £1000. 

Is there a 3m height difference between the cabin and treatment plant. 

 

I have just installed 260m of fence and I’m visualising how long your pipe run will be. 

23 minutes ago, ProDave said:

There is a requirement for inspection chambers at intervals so you don't end up with 10 sets of drain rods trying to rod a 250M run with no access.

 

Yep - we have a chamber every 9m or so as a set of rods is 10m and you have to allow for the drop into the chamber etc.. In practice I normally need 11 or 12 rods to do a proper job.

  • Author

I have no water course to outlet into nearby and ground is solid clay hence the long run.

what falls do you think work best on long runs as i am aware the solids can be left behind if its too steep.I was thinking 1:60 - 1:80

7 minutes ago, albert said:

i am aware the solids can be left behind if its too steep

 

That is not the case, it was a bit of an old wives tale and never proven.

 

Between 1:20 and 1:60 seems to work well. I assume there is a downhill slope, so I would go with this and have the drain fairly shallow all the way, providing enough cover for whatever is above. I think you can go 45m between inspection chambers and if the drain run is shallow you can use the small ones.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.