Lets assume the DHW is dealt with by a seperate means (sunamp maybe), and UFH by a ASHP. How is it plumbed together? IS it just  flow and return directly from the ASHP to and from the UFH manifold/manifolds?

  • Like 1
Posted

In  it's simplest form yes.  Some people recommend a small buffer tank so the ASHP is not cycling on and off so much. My own ASHP drives my UFH directly.

Posted

Depends .....

 

If you get a decent ASHP with full inverter driven compressor and modulation down to a low level then you can go direct from ASHP to manifold. The issue becomes when you need something with a peak load higher than a small unit (ie need a 8/12kw unit due to higher heat requirement) that the modulation doesn’t go low enough and when the zones start shutting off and you reach within 2-3c of the blending point you may get short cycling. You can go for pure fixed flow temp from the ASHP and lose the blending sets etc entirely but this needs a decent controller that allows you to set up temperature curves. 

 

Second option is to use a small 60 litre or so buffer tank and let this smooth out the modulation and short cycling issues. 

Posted

Just bear in mind that you also need to run antifreeze in the whole system if it’s direct connect - dosing and filling is one issue if it’s direct, but a buffer increases the volume and subsequent antifreeze need and cost. 