Jump to content

L/min set up


Recommended Posts

1 minute ago, Alexphd1 said:

Anybody know what they set up the L/pm flow on the ashp? Just looking at flow gauges.

 

 

Our 7 kW ASHP is nominally 20 l/min, and looking at the data for the others in the range, the 12 kW model is 35 l/min and the 14 kW model is 41.7 l/min.

Link to comment
Share on other sites

My 5KW LG Therma V is 15L per min.

 

Astonishingly, this vital information is not given in the installation manual. I had to seek it from their technical support (when it would not operate due to low flow)

 

Installing a flow meter I would say is absolutely essential. Some heat pumps provide a flow meter but not all.

Link to comment
Share on other sites

I didn’t bother fitting the flow meter as I didn’t have much space. So I set the pump to the lowest setting and then kept upping it till the ASHP didn’t trigger the alarm. Then did it from highest setting downwards. This gave me the range of what settings on the pump would work. I aimed for the slowest, as (to my logic - no actual facts) this used the least energy and extracted a degree or two more heat. 

  • Thanks 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...