Bpc ufh design!

Featured Replies

So, I asked(paid) bpc to do a design for us, thinking that it may be easier/quicker than me getting my head around loopcad. I even sent my filled version of Jeremy's heat loss spreadsheet as thought that may help. I also sent crib notes stating what we were looking for.

Suffice to say I'm not massively impressed but, could I get opinions on it please?

Standouts for me are;

  1. So many loops at 150mm centres

  2. Flow rate of 1.1!

  3. Surplus heat in every room from 147% up to 433%

Surely they can't have

BPC_BPCZ-1000001899_261124_Bpc.pdf

Quite why they have added a loop in the utility god only knows. I guess they don't count the dozen or so loops to the manifolds as having any impact. Same with the hall. 200mm centres would save loads of pipe, loops manifold and install cost. Wait for comments from others here who know far more than me and go back asking for amendments.

56 minutes ago, lizzieuk1 said:

So, I asked(paid) bpc to do a design for us, thinking that it may be easier/quicker than me getting my head around loopcad. I even sent my filled version of Jeremy's heat loss spreadsheet as thought that may help. I also sent crib notes stating what we were looking for.

Suffice to say I'm not massively impressed but, could I get opinions on it please?

Standouts for me are;

  1. So many loops at 150mm centres

  2. Flow rate of 1.1!

  3. Surplus heat in every room from 147% up to 433%

Surely they can't have

BPC_BPCZ-1000001899_261124_Bpc.pdf

It’s not hideous, no less rudimentary than every other one I’ve seen this and last year, and the ones before them.

I usually take these and adapt them on the fly, as per the last maybe dozen or so I’ve laid for MBC or MBC’s clients, it just needs some common sense.

Agree, utility loop is moot, but perhaps its safer to offer it as a zone than be asked why that room hasn’t been serviced; assume the designer worked on generic arrangement here eg the rest are insulated and would output / offer “less heat”.

Flow rates are low, but not a problem, these would be balanced and the pump set accordingly.

Just needs a few tweaks, but if you provided rudimentary spec / detail, you can’t expect anything more by return, really.

It looks a lot better than a couple of the free designs we were offered. Do their heat loss calcs roughly match what you calculated yourself?

I noticed they've set a design temp of 45c but presumably you'll run it lower?

You could ask what the heat outputs look like at 35, still very comfortable I'm sure and the design might look less over-spec'd then. I also think it would be reasonable enough (given it's a paid design) to ask whether a higher flow rate and wider spacing might work better, or why they didn't go that way? (E.g more even heat with narrower spacing)

1 hour ago, lizzieuk1 said:

I also sent crib notes stating what we were looking for

Different of course if they've just ignored these!

  • Author
22 minutes ago, torre said:

It looks a lot better than a couple of the free designs we were offered. Do their heat loss calcs roughly match what you calculated yourself?

I noticed they've set a design temp of 45c but presumably you'll run it lower?

You could ask what the heat outputs look like at 35, still very comfortable I'm sure and the design might look less over-spec'd then. I also think it would be reasonable enough (given it's a paid design) to ask whether a higher flow rate and wider spacing might work better, or why they didn't go that way? (E.g more even heat with narrower spacing)

Different of course if they've just ignored these!

I've been trying to do the design in loopcad as well but nothings ever straight forward! So far I have managed to get all rooms heated with a flow temp of 31⁰C so far less than the 45 they've used, and pipe spacings at 200/225 or 300mm. I'm a newbie to the loopcad though so not entirely sure I'm inputting everything I need to correctly!

On the JH heatloss spreadsheet I have total as 4159W, set at -3.9⁰C, it looks to me that the bpc total is 10kW!

One issue I'm concerned with is that we need to achieve whole house heat requirement from the ground floor ufh as intend to use that to satisfy the regs and for the heat pump grant. In reality we are also installing air con on ff&sf so will have heat & Cooling on those as well.

I will go back to them and see if they can revise it, I really don't understand why we have a 433% input, surely that's bonkers and we will be melting!

  • Author

@Nickfromwales I'm struggling to understand why they've made some rooms at 433% of need! Am I missing something here with the heat req/output??

Not sure I provided rudimentary spec, I asked for 200mm spacing, openloop, counterflow sprial design, use of 'through' pipes to heat the hallway & utility, low running temperature and minimum loops/manifolds. Heat to meet whole house need & provided my JH spreadsheet.

Re the utility comment, where you say the 'rest are insulated' does that mean we will need to insulate pipes running to other rooms??

3 minutes ago, lizzieuk1 said:

@Nickfromwales I'm struggling to understand why they've made some rooms at 433% of need! Am I missing something here with the heat req/output??

Not sure I provided rudimentary spec, I asked for 200mm spacing, openloop, counterflow sprial design, use of 'through' pipes to heat the hallway & utility, low running temperature and minimum loops/manifolds. Heat to meet whole house need & provided my JH spreadsheet.

Re the utility comment, where you say the 'rest are insulated' does that mean we will need to insulate pipes running to other rooms??

They’ve missed the remit entirely then.

Go back and ask them to reissue you with the design you requested.

Typically I’d not insulate these in a passive / insulated raft, a-la MBC, as you’ll be running the UFH very close to the target room temps. This means zero ‘hot spots’.

If it were a screed, and higher temps I’d be more concerned.

You can sleeve these with 25mm flexible conduit, if the concrete cover in the utility allows, and only the flows, if you’d like some control of the heat being preserved before getting to the farthest rooms, but as the heating goes on and just idles all winter it really isn’t an issue.

Rev 1 has been binned, go ask for Rev 2!

  • Author

@Nickfromwales thankyou 😊

Everything you've said is what I've been thinking so nice to know I'm not making it up!

I'm emailing them now to ask for a revision- hopefully they will read the remit this time!

My pet hate is the hallway having exactly the same pipe spacing as every other room.

I learned that in my first self build over 20 years ago when I blindly followed the designer and did just that. The hall and landing are inside areas with little or no outside walls and little or no heat loss. the thermostats never turned on and those loops never did anything.

So I would not (did not) fit them in my second new build.

BUT this is the difference between self design understanding the realities, and a contract designer playing safe. If he had decided no UFH needed in hall or landing, you could guarantee someone would build a house with a draughty front door, and complain his hallway was cold.

It's a basic design that allows massive overheats, but is basically designed to have a thermostat in every room and hall way to control it. Then your heat pump needs a buffer to cope, but they don't care.

I would balance the overheat percentage by reducing the loop length based a pro-rated calculation, but bump utility and all hall loops, just spread the pipes passing through the hall.

  • Author

So, I've asked for revisions. But, meanwhile, I've been on loopcad again, finally getting to grips with it, and done my own design as well. Was getting in a bit of a knot with making sure we meet :

a. Requirements for regs (part L) and

b. Meet requirements for BUS grant.

Am I correct in that:

  1. If I show heat output, of the gf ufh system & ashp, can meet the whole house heat loss & hot water demand, then the BUS criteria is met.

  2. If I show each room has sufficient heat input for its loss calculation, that will satisfy regs for heating. Unsure if just meeting whole house heat loss with the gf ufh would suffice for this??

    We are installing Aircon upstairs so, am using that for those rooms rather than relying on the gf ufh output as feels simpler for bc (a2a mainly being installed for cooling but thinking it can also help demonstrate compliance for heating even if, in reality, we never need the heat mode as gf ufh will provide whats needed)

8 minutes ago, lizzieuk1 said:

We are installing Aircon upstairs so

Why not fan coils, you don't need expensive ones or ones that run below dew point, then use ASHP to heat and cool, via fan coils and UFH. You are really making life difficult with two systems. Then just ask for a heating installation don't mention cooling (you will confuse the installer)

On the grant part: I don't know the BUS rules well, so put this to whoever signs off the MCS design. What I was told by someone who does know them is that the design is done room by room, with every habitable room covered by the heat pump system at the design temperature. A whole-house total from the ground floor loops alone wouldn't show that, so I'd ask them up front whether they will count air to air units upstairs at all, before you buy anything.

That's one more reason for JohnMo's fan coil idea. I run six water fan coils on my heat pump: the water sits at about 30 to 36 °C, the rooms warm quickly, and the same units cool in summer off the same heat pump. Each needs a condensate drain and insulated pipes to it, but it's one system instead of two.

On the 433%: their outputs are at 45 °C water. A floor gives roughly in proportion to how much warmer the water is than the room, so at the 31 °C you got in LoopCAD it gives only about a third of what it gives at 45 (around 8 degrees above the room instead of around 21). A room shown at 433% at 45 °C is then nearer 160%, which is why your own design works with wider spacing.

The bigger question is their 10 kW against your 4.2 kW. Ask them for each room's heat loss and what they assumed: outside temperature, air changes, U-values. A gap that size is usually one of those, and it decides how many loops you really need.

Companies also don't really care if the loops output exceed the heat loss requirement. Their argument as Johnmo mentioned above is we'll pump it with 45 degree flow blended down from high boiler temperatures and if the room gets too hot then the individual room stats will shut off the actuators. Which conveniently means they get to sell you a ton of actuators, room stats, control centres to bump up their profits. Not very efficient. Not many are up to speed with heat pumps, low flow temps, weather compensation and open loop concepts!

My first issued loop cad drawing was the same. I don't think many companies even bother to read the heat loss they just draw the room and press go on 150mm centres then move onto the next customer. Probably only get a 10min time window to get it done and emailed off.

I did try loopcad myself but it was a bit of a battle to get it to do exactly as I wanted as I wanted to break from the norms and did a 'double spiral within a spiral pattern' that needed manually drawing on loopcad. My theory is that if ever one of the loops went down for any reason the rooms 2nd loop conveniently spread across the whole floor rather than each loop doing only half a room. Prevent the screed from cracking with differing thermal expansions.

In the end I found it easier to get a pack of different coloured chalk paint marker pens and I just drew it all out on the actual floor (chalk pens worked well on the Black polythene membrane). It also Made life really easy when laying it all as I just followed my chalk paint line!

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.