15 hours ago15 hr Morning,We are finally installing our A193 mesh into the raft foundation. I'm a bit worried about concrete cover though. Originally the plan was to tie the ufh to the top of the mesh but, now we've come to laying the mesh, I'm concerned we don't have enough tolerance for adequate cover. The mesh is on 40mm supports above insulation, mesh is A193 so 7mm but obv 2 bar thickness so 14mm, then we have some overlaps so, in places, that's 28mm. Pipes will be 16mm on top of that. If I'm adding correctly that means 40+14+16= 70mm over majority but 40+28+16 = 84mm! in places. Which in a 100mm slab leaves min 30mm cover to top of pipes over majority but (yikes) 16mm in the overlaps. Surely that's not enough and we have zero tolerance for any variations! Thinking we now need to put pipes directly on the insulation, which is a pita as we've placed half the mesh, have our dpm atop the insulation and the weather not great for sticking ufh pipe clips down to plastic sheet!😖😫
14 hours ago14 hr Are your pouring a foundation raft or a floor slab. If it is the former, then 100mm of concrete sounds very small. For comparison ours was 250mm, and even the garage has 150mm.If it is a floor slab , then you might be able to consider removing some of the overlap and "tying" the mesh together with pieces of rebar. This is non-professional advice and should be checked.
14 hours ago14 hr Author 24 minutes ago, BotusBuild said:Are your pouring a foundation raft or a floor slab. If it is the former, then 100mm of concrete sounds very small. For comparison ours was 250mm, and even the garage has 150mm.If it is a floor slab , then you might be able to consider removing some of the overlap and "tying" the mesh together with pieces of rebar. This is non-professional advice and should be checked.It's an insulated raft, all engineered, load bearing walls sit on 300mm of concrete (with rebar) then its 100mm everywhere else with mesh, but all one monolithic 'slab' as it were. Mesh overlaps need minimum of 300mm so no cutting/tying can be done. It's the concrete cover above the ufh pipes I'm concerned about though.
13 hours ago13 hr Your maths is right, and 16mm over the laps isn't enough. Even 30mm is tight once you allow for the tamp and any high spots, and pipes that close to the surface can show up as crazing lines in the slab later.The easy fix, without lifting the mesh you've already placed, is to run the pipe under the mesh rather than on top. With the mesh on 40mm chairs there's room to feed 16mm pipe underneath and cable tie it up to the underside of the bars every 500mm or so, so it sits snug against the mesh. No clips through the DPM and nothing to stick down in the wet. That puts the top of the pipe roughly 60mm below the finished surface everywhere, laps included.A few other things worth doing:Ask your engineer to confirm they're happy with pipe directly under the mesh, as it's their raft design, but it's a very common detail.Pressure test the loops before the pour and keep them under pressure during it, so any nick shows up straight away.Sleeve the pipes where they come up at the slab edge and through any joints.Have someone walking the pour watching for loops being dragged or lifting.Sitting a bit lower in the slab just means a slightly slower response, which doesn't matter with a heat pump running low and steady.
13 hours ago13 hr Author 6 minutes ago, JpManning said:Your maths is right, and 16mm over the laps isn't enough. Even 30mm is tight once you allow for the tamp and any high spots, and pipes that close to the surface can show up as crazing lines in the slab later.The easy fix, without lifting the mesh you've already placed, is to run the pipe under the mesh rather than on top. With the mesh on 40mm chairs there's room to feed 16mm pipe underneath and cable tie it up to the underside of the bars every 500mm or so, so it sits snug against the mesh. No clips through the DPM and nothing to stick down in the wet. That puts the top of the pipe roughly 60mm below the finished surface everywhere, laps included.A few other things worth doing:Ask your engineer to confirm they're happy with pipe directly under the mesh, as it's their raft design, but it's a very common detail.Pressure test the loops before the pour and keep them under pressure during it, so any nick shows up straight away.Sleeve the pipes where they come up at the slab edge and through any joints.Have someone walking the pour watching for loops being dragged or lifting.Sitting a bit lower in the slab just means a slightly slower response, which doesn't matter with a heat pump running low and steady.Thanks, I hadn't thought of tying it below the mesh but, not sure how easy that is in practice 🤔 or whether its easier to lift the mesh and start again. Thinking we could glue down pipe rails with the waterproof sealant stuff but, not sure if that's easier than tying pipes below the mesh.....
12 hours ago12 hr 1 hour ago, lizzieuk1 said:how easy that is in practiceIt won't be easy. UFH is not conducive to easy manipulation unfortunately.Will you be able to, or have you planned for a screed layer? If so, you could lay pipe as you plan, on top, diverting round the 4 overlap areas to keep them at the 30mm below surface, then a shallow screed layer to increase that depth. Not sure what minimum depth of screed is possible.A screed layer also provides the opportunity to correct any concrete level issues that might occur.
11 hours ago11 hr We had this exact issue on our slab under the basement. I considered attaching below the rebar but worked out it would’ve been a massive pain. We had the ceiling height to opt for a screed on top instead and so put 25mm PIR on top of the slab and fixed the ufh pipes to that and then 50mm liquid screed on top. We also did the same on the ground floor above the block and beam and slab where there was no basement underneath.Blog post here and there’s a thread of mine about attaching to the rebar somewhere on here too.
11 hours ago11 hr 4 hours ago, lizzieuk1 said:Morning,We are finally installing our A193 mesh into the raft foundation. I'm a bit worried about concrete cover though.Originally the plan was to tie the ufh to the top of the mesh but, now we've come to laying the mesh, I'm concerned we don't have enough tolerance for adequate cover.The mesh is on 40mm supports above insulation, mesh is A193 so 7mm but obv 2 bar thickness so 14mm, then we have some overlaps so, in places, that's 28mm. Pipes will be 16mm on top of that.If I'm adding correctly that means 40+14+16= 70mm over majority but 40+28+16 = 84mm! in places.Which in a 100mm slab leaves min 30mm cover to top of pipes over majority but (yikes) 16mm in the overlaps.Surely that's not enough and we have zero tolerance for any variations!Thinking we now need to put pipes directly on the insulation, which is a pita as we've placed half the mesh, have our dpm atop the insulation and the weather not great for sticking ufh pipe clips down to plastic sheet!😖😫There’s zero issue here, same on loads of jobs I’ve been on / installed UFH / down to sporadic locations with, as you say, as little as 16mm concrete cover. These slabs are so ridiculously over-engineered you have nothing to worry about. This isn’t theory, these are on live projects where I am present from concept and design, site prep (inc demolition), foundation, superstructures, and some all the way to interior fit & finish.Tiled floors over 150m2, L-shaped slabs, changes in levels, you name it I’ve done it.I don’t even entertain expansion joints at thresholds (unless it’s a floating, thin screed) and I’ve been walking on these laid finished for 12-24 months after we’ve laid them (so I am answerable and responsible for any event of them failing).Stop panicking, it’s just another slab and life will go on. Remember that you’ll likely be self levelling over this also, adding further cover, reducing any ‘concern’; you need not be concerned 😉.
11 hours ago11 hr 2 hours ago, JpManning said:Even 30mm is tight once you allow for the tamp and any high spots, and pipes that close to the surface can show up as crazing lines in the slab later.Do you mean hairline cracking? As this will occur in slabs without UFH pipes in them and 50mm cover over the mesh.
10 hours ago10 hr 4 hours ago, lizzieuk1 said:Surely that's not enoughIt's plenty. Has someone told you otherwise? It doesn't really need any cover but it's tidier and safer covered. And best to specify something like 30mm rather than be random.Every slab, bridge, nuclear power station in the world has hairline cracking and your mesh is there precisely to keep it hairline.There's lots of nonsense written about expansion joints. Concrete contracts and cracks a bit when curing, then stays there.As I often say... do not let anyone add water to the mix. That's what makes it crack too much. Tell the delivery driver that nobody can instruct it. It's a shame for the contractor if they need more effort, but that's how it is.
9 hours ago9 hr Fair question, lizzieuk1. With half the mesh already down, tying under it is fiddly rather than hard: lift the sheet edge a little, feed the pipe through and tie it up as you go. If it turns into a fight, the others are right that 30mm cover over most of the slab is fine, so you could simply divert the pipe around the laps, or only tie it under the mesh where the sheets overlap and leave the rest on top. I'd skip gluing rails to the DPM in this weather, as they tend to come loose once people start walking the pour.Nick, yes, I meant hairline cracking that can follow a pipe line where the cover is very thin. As you and saveasteading say, a slab will hairline crack anyway and the mesh keeps it that way, so it's cosmetic rather than structural, and any levelling compound on top covers it.
9 hours ago9 hr 12 minutes ago, JpManning said:lift the sheet edge a little, feed the pipe through and tie it up as you go.Please tell me it’s April 1st?!
8 hours ago8 hr 57 minutes ago, Nickfromwales said:Please tell me it’s April 1st?!I suspect @JpManning as chat bot. Feeding pipe loops under mesh sheets would not be possible.
20 minutes ago20 min Author 10 hours ago, Nickfromwales said:There’s zero issue here, same on loads of jobs I’ve been on / installed UFH / down to sporadic locations with, as you say, as little as 16mm concrete cover.These slabs are so ridiculously over-engineered you have nothing to worry about. This isn’t theory, these are on live projects where I am present from concept and design, site prep (inc demolition), foundation, superstructures, and some all the way to interior fit & finish.Tiled floors over 150m2, L-shaped slabs, changes in levels, you name it I’ve done it.I don’t even entertain expansion joints at thresholds (unless it’s a floating, thin screed) and I’ve been walking on these laid finished for 12-24 months after we’ve laid them (so I am answerable and responsible for any event of them failing).Stop panicking, it’s just another slab and life will go on. Remember that you’ll likely be self levelling over this also, adding further cover, reducing any ‘concern’; you need not be concerned 😉.Thanks Nick, it's good to hear your real world experience of the situation. I had thought we couldn't be unique in this! So, we just crack on and lay the pipe on top and not worry about any 16mm "thin" bits? We were almost ready to take the mesh off and run the pipe beneath then tie it to the underside but if we don't need to then all the better!