Posted (edited)

We’ve had to replace some floor joists close to the bifold doors due to rot, twice this has happened, all other joists look absolutely fine. My feeling is it is related to the volume of rain that hits that area and collects. Had a few opinions and 2 quotes. 1 to aco drain all the way round to existing gulley and one just aco around the bifold and conservatory into a patio soakaway. Prices seem astronomical for 3-4 days work and fairly little and inexpensive materials bill. 5.4k and 4.8k.

 

thoughts on this and other options?

Edited by AdamD
Posted (edited)

First pic is the area in question second one is the side of house which does to gulley

the pic I couldn’t upload shows the front of conservatory. It’s essentially 2 right angles to get to the gully, approx 6-8m

Edited by AdamD
Posted
9 hours ago, Mr Punter said:

Cheeky (expletive deleted)ers.  DIY job. What ventilation is under the floor?

I thought that as well, but whenever one challenges it certainly amongst online trade forums, they get pelted for not understanding how the business works, overheads etc. no, I fully understand all of that but can’t wrap my head around when a days labour for such a task went to a grand. I appreciate life is hideously expensive, we’re all living it, in the uk,  but is a grand a day genuine value?

that said, drainage does seem to be a very lucrative market so perhaps it’s just market economics.

Posted (edited)

When you or your builder start talking about 'soakaways', be sure you are on the same wavelength. IIRC the PavingExpert site used to have a really good 'primer' re soakaways. Apart from anything I often see 'soakaways' (or reference to them) which don't comply with the rules re proximity to buildings, boundaries, neighbours and so on. Equally a shallow pit full of rubble may function as a soakaway for a while and then cease to do so. If you go the soakaway route get some good drawings and follow them.

 

Also, given that conservatories may be exempt from quite a lot of 'the regs' (and may also just not necessarily be built well) beware of excavating around something which may have very minimal footings. Do test-pits first. Given the extent (or lack of it) of the job and the price quoted, if it were mine I'd be looking at whether I could do it myself and do it carefully, prudently and in line with 'the rules'.

Edited by Redbeard
  • Like 1
Posted

So is that some green artificial grass matting outside the bifolds ?

Internal FFL looks as though it is lower than the outside ground level under the artificial grass. And which way does the ground slope, does it have a proper fall away from the bifolds ?

I might guess rain goes through the artificial grass and pools underneath unable to runaway because of lack of slope, and the presence of the artificial grass stopping it from running away or indeed evaporating.

Maybe consider lowering the outside ground level which looks like it could well be above DPC. If you are going to have to shell out then make sure it is a proper permanent fix you are going for. (Have you got an internal step up somewhere ?)

Posted
1 hour ago, Spinny said:

So is that some green artificial grass matting outside the bifolds ?

Internal FFL looks as though it is lower than the outside ground level under the artificial grass. And which way does the ground slope, does it have a proper fall away from the bifolds ?

I might guess rain goes through the artificial grass and pools underneath unable to runaway because of lack of slope, and the presence of the artificial grass stopping it from running away or indeed evaporating.

Maybe consider lowering the outside ground level which looks like it could well be above DPC. If you are going to have to shell out then make sure it is a proper permanent fix you are going for. (Have you got an internal step up somewhere ?)

Yes it’s Astro turf outside the bifolds.

It looks lower but is In fact marginally higher than outside, albeit clearly not enough.

slope - I need to run a level On it, will do

later and refer back here. Interestingly neither of the people quoting got a spirit level on it.

agree about it possibly pooling but the timber the Astro sits on seems fine which is odd.

lowering could be done but creates an issue as our main patio is level wirh the Astro, I can’t be removing 50 m square of patio and lowering it all.

no internal step up 

Posted
47 minutes ago, AdamD said:

the timber the Astro sits on seems fine

What is the makeup outside then ? Do you have a timber deck under the astro ? Then concrete or earth or something under that ? Is the astro fixed down somehow or can you peel it back ?

Maybe you have some photos of before the deck and astro were put in ? Any photos of what the rotten joists looked like ? Did you have problems before they were put in ? Any air bricks down there ? Where is the DPC because ends of timber joists should be on top of DPC/DPM ? Any mold on the bottom of the wall inside or staining outside ?

 

Presumably the joists run front to back in the room behind the bifolds ?

 

I just think you need to be as certain as humanly possible about the cause in order to specify the best fix.

Posted
2 hours ago, Spinny said:

What is the makeup outside then ? Do you have a timber deck under the astro ? Then concrete or earth or something under that ? Is the astro fixed down somehow or can you peel it back ?

Maybe you have some photos of before the deck and astro were put in ? Any photos of what the rotten joists looked like ? Did you have problems before they were put in ? Any air bricks down there ? Where is the DPC because ends of timber joists should be on top of DPC/DPM ? Any mold on the bottom of the wall inside or staining outside ?

 

Presumably the joists run front to back in the room behind the bifolds ?

 

I just think you need to be as certain as humanly possible about the cause in order to specify the best fix.

Timber frame around the perimeter for the Astro to be attached to, but can be peeled back carefully for inspection.

under Astro - sharp sand, then type one MOT compacted then earth.

Before Astro - per picture, decorative stones, on top of the type one MOT. Stones removed prior to Astro going down.

 

Rotten joist pics attached 

 

Yes I think there must have been as as you can see the joints were previously sistered, so clearly someone has attempted to fix them before we moved in but not the underlying issue.

 

no air brick

 

Cant See the dpm, render outside so isn’t obvious 

 

yep we have had damp marks inside the doors 

 

joists run left to right 

 

**joist pics to follow - even though they are under 2mb, the site won’t allow me to post as apparent they’re over so will try to convert them

IMG_1567.jpeg

Posted
26 minutes ago, AdamD said:

**joist pics to follow - even though they are under 2mb, the site won’t allow me to post as apparent they’re over so will try to convert them

@Sparrowhawk is currently on the case ironing out the file size upload wrinkle.
 

Bear with!  

  • Thanks 1

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...