flanagaj Posted Saturday at 06:53 Posted Saturday at 06:53 I have searched the internet, but haven't discovered how you terminate a cavity tray at a door opening and get a proper seal. As we have a DPC for Radon directly below the tray which spans the cavity, any water that gets through the tray between the cavity closer and the cavity tray will potentially cause damp. The image below shows how water getting under the cavity tray will have no where to go except towards the inner leaf.
Oz07 Posted Saturday at 07:07 Posted Saturday at 07:07 If it gets as far as that joint its out the building though isn’t it? In reality I think you will leave the blockwork out at doorways so the radon / dpm will turn up the inside face of the brickwork. 1
Mike Posted Saturday at 15:27 Posted Saturday at 15:27 8 hours ago, flanagaj said: I have searched the internet, but haven't discovered how you terminate a cavity tray at a door opening and get a proper seal Often with a cavity tray stop end, like this: https://www.manthorpebp.co.uk/products/cavity-trays/horizontal-trays/horizontal-stop-ends/. Otherwise by doing some origami with the end of the DPC and tucking the fold securely into a perpend (vertical masonry joint). 1
Dave Jones Posted 2 hours ago Posted 2 hours ago the structural opening is the stop end. DPC is to stop damp climbing, it cant there is an opening. A tray is to deflect moisture falling down the cavity above, it cant there isnt one.