I went the max panel and inverter route.

 

Size of inverter was partly determined by desire to cover peaks without drawing from grid i.e. kettle, toaster, air fryer all on at same time.

 

This allowed for a large number of panels (24).

 

This was dictated strongly by my (carport) roof size.  I wanted to get it looking neat so fewer panels would look stupid. 24 panels filled the roof really nicely.

 

It also compensated for sub optimal angle and orientation (12 degrees and South West).

 

It also allowed reasonable generation (enough to cover daily demand) in the shoulder months as the panels are badly shaded by trees and the house.

 

All in all we have zero import for 6 months and produce about 25% of demand in deep winter.

 

The array easily saturates my export limit (a measly 3.6kw) so we have alot of potential excess in the summer.

 

One advantage of the big array and inverter in the winter is the charge rate can be really high so you can take advantage of the 2 or 3 hours of sun during an otherwise dull day.  3 hours of good sun is about all I need to top up.

 

 

@Beelbeebub  Yeah, that's pretty much what I want to do for similar reasons. Presumably you had to limit the export in software but had a much larger inverter?

Posted
22 minutes ago, Alan Ambrose said:

 

 

@Beelbeebub  Yeah, that's pretty much what I want to do for similar reasons. Presumably you had to limit the export in software but had a much larger inverter?

why are you limited to export volume?

Posted
On 06/08/2026 at 08:31, G and J said:

For us and I assume many, maxing the panels on one face of the roof was a no brainer as it saved slate (I’m not a fan of surface mount panels).  

I did look at that but was assured by builder that by the time they GRP that area there would be no savings  and possible problems over time  if not GRP below the panels 

Posted

>>> why are you limited to export volume?

 

Well the DNO will always limit, even if it's only to 17kW on single phase - it's a risk thing with local voltages apparently. And we have planning permission to cover one roof and the 'cartlodge' with panels.

Posted
2 hours ago, scottishjohn said:

why are you limited to export volume?

Are you talking about volume/quantity(kwh) or the rate(kw) of export??

 

I don't think anyone in a domestic situation gets limited on the volume they can export but everyone gets limited on the rate they can export as ultimately you'll blow your service fuse if you try and push power into the grid too fast! Most are limited way below the power that would blow their fuse though!

Posted (edited)
1 hour ago, Alan Ambrose said:

>>> why are you limited to export volume?

 

Well the DNO will always limit, even if it's only to 17kW on single phase - it's a risk thing with local voltages apparently. And we have planning permission to cover one roof and the 'cartlodge' with panels.

yes I knew that one --  unless you get a different export  permit

 16 kW per phase  is what I remember form when I got my 3 phase supply when I asked how big a system I could run 

 but it will be limited really by your invertor  size and I see 11kW at most as my invertor is 11.5kW-- But seen it a few times this summer

It just sounded like he was limited to the amount of kW he could send back per day 

 

 good days here i,ve been sending back 50-60 kW

Edited by scottishjohn
Posted
5 minutes ago, SteamyTea said:

16 (amp) x 230 (nominal voltage) = 3.68 kW (power per phase)

 

Yes, but mostly no. Technically the nominal voltage is 230V but for the vast amount of consumers the voltage at their socket is closer to 240 (likely higher).

 

The limit is set by amps to avoid any confusion here. You can export 16A whatever your local voltage.

Posted
2 minutes ago, -rick- said:

 

Yes, but mostly no. Technically the nominal voltage is 230V but for the vast amount of consumers the voltage at their socket is closer to 240 (likely higher).

 

The limit is set by amps to avoid any confusion here. You can export 16A whatever your local voltage.

16A is without consent via G98. We have 32A via a G99 but I think others have posted higher limits.

Posted
7 hours ago, Alan Ambrose said:

 

 

@Beelbeebub  Yeah, that's pretty much what I want to do for similar reasons. Presumably you had to limit the export in software but had a much larger inverter?

Yes. 8kw inverter 3.6kw export 

Posted
1 hour ago, SteamyTea said:

Correct.

 

What is slightly annoying is my inverter limits by power - which varies the amps as the voltage goes up and down.

 

My voltage is regularly high 240's so i could export about 4kw but occasionally it dips to 230 or so which is only 3.6kw

 

It would be nice if the inverter had a current limit export 