April 20Apr 20 Hi all, Contemplating to moving to a ASHP over the summer (mainly for cooling benefit from UFH and fan coils). Doing my heat calcs I have a big difference between my calculated heat loss and real world heat loss. Hoping someone will help me understand the difference. Calculated heat loss is around 5.1kw using the freedom heat pump spreadsheet (attached). I used the same target temps as we have in real life, and the output figures match those generated from loopcad when I was using that. Real world I got data from my smart meter. I used a night in Jan that was -2, so no solar gain etc. This real world figure gave me 3.2kw. So what do I believe? I don't want to have an oversized heat pump and want to run the system on weather comp. Other info is we find we can heat the house quite nicely just running the UFH, and leave the rads off upstairs. Means downstairs is at 19.5 and upstairs at 17. Thanks 👍 😊 Heat loss calcs 20 HCR.xlsx
April 20Apr 20 7 minutes ago, mistake_not said: Real world I got data from my smart meter. I used a night in Jan that was -2, so no solar gain etc. This real world figure gave me 3.2kw. Not sure a single night will give you an exact heat loss rate, as any day time gains will still be there. Suspect your real heat loss is somewhere between the two figures. Plus the heat loss spreadsheet uses min BR U values not your real ones. But basically your ASHP model choice will depend on actually output at you min outside temp. I would understand size not over size.
April 20Apr 20 32 minutes ago, mistake_not said: So what do I believe? I don't want to have an oversized heat pump and want to run the system on weather comp. Difficult to say as there are issues with both and I wouldn't trust either of them. If you can bear the pain of re-inputting your data, you can use OpenHeatLoss.com (which I have developed) to complete a calc and design to current design standards. This also provides the ability to look at your ufh design in relation to heat loads etc. The only thing it doesn't do right now is Fan coil sizing
April 20Apr 20 Author 2 hours ago, JohnMo said: Plus the heat loss spreadsheet uses min BR U values not your real ones. Whilst it does have that deleted, it also has custom ones and I have made sure they match the as built values. 2 hours ago, JohnMo said: Not sure a single night will give you an exact heat loss rate, as any day time gains will still be there. Suspect your real heat loss is somewhere between the two figures. Seemed like a pretty steady output over that night though, and it's wasn't sunny days. But agree it's likely somewhere in the middle. My gut feeling is the ability for the heat pump to modulate will be more important to me than max value. 2 hours ago, SimonD said: If you can bear the pain of re-inputting your data, you can use OpenHeatLoss.com (which I have developed) to complete a calc and design to current design standards. This also provides the ability to look at your ufh design in relation to heat loads etc. The only thing it doesn't do right now is Fan coil sizing I had a quick play when you first posted about it. All my u-values are as built, so I'm guessing I'll end up v similar but will give it a go. Does anyone know the deal with BUS / MCS? Do they have to hit heat loss calcs exactly?
April 20Apr 20 6 minutes ago, mistake_not said: Does anyone know the deal with BUS / MCS? Do they have to hit heat loss calcs exactly? The MCS design and installation requirements are that the Heat Pump can provide all the heating/how water requirements, which does mean the unit has to be sized according to the heat loss, but that doesn't necessarily mean that your heat pump will be over-sized. Good design also makes sure that the heat pump can modulate down far enough to deal with typical temperatures without short cycling.
April 20Apr 20 43 minutes ago, mistake_not said: Does anyone know the deal with BUS / MCS? Someone the other day had a radiator system that currently runs at 45 degs, he was getting quotes circa £13500 before grant for a heat pump and some install works - utter bonkers. But generally most R290 heat pump seems to modulate well. But not all will do cooling if you need that. Example, current Grant heat pumps physically will do cooling BUT their controller does not allow this happen. Most installers are clueless about cooling, so be prepared for plenty of BS.
April 20Apr 20 Author Yeah, the one quote I have had (based around 5kw pump, no rad changes, leaving water tank, but including boiler rip out) is something like 7k after grant 😞. Tempted to see if the sparky that did my solar can do something with me so I get BUS.... I want a very simple fully open loop weather comp system, I already have PDHW and my pipework is all big enough already.
April 20Apr 20 28 minutes ago, JohnMo said: Most installers are clueless about cooling, so be prepared for plenty of BS. Here's some input from me. Maybe BS as I'm going by hunch and science, not proofs. I can't see how air source pumps work efficiently in reverse for domestic purposes. Of course they work as chillers in air conditioning systems but that is by air circulation. Expecting to use cooling by sucking heat from a floor slab or radiator cannot be the same. In heating, we warm the concrete floor or screed and it makes our feet and lower parts cosy. It then warms the adjacent, cooler air which rises to the ceiling and this continues until the whole room volume is warm. But in reverse, the screed will cool and we will have cool feet, and will slowly cool the adjacent air, but it will stay there. The warm air above will stay put. If I'm wrong on any of this please advise.
April 20Apr 20 3 minutes ago, saveasteading said: If I'm wrong on any of this please advise. You're not far off. Cooling effectiveness of ASHP isn't that great, you may get a few degrees drop during the hottest days, so it might take the house from uncomfortably hot to okay, but that's about it. If you're in a position where you need to drop time, money and resources on infrastructure for an ASHP to do cooling, you're better of just getting a split a/c unit. I made that choice.
April 20Apr 20 I know that air to air works both ways.. did it in our office... ashp outside, plenum inside then ducts and fans. If I wanted cooling I'd do that.
April 20Apr 20 29 minutes ago, saveasteading said: heating, we warm the concrete floor or screed and it makes our feet and lower parts cosy. It then warms the adjacent, cooler air which rises to the ceiling and this continues until the whole room volume is warm. But in reverse, the screed will cool and we will have cool feet, and will slowly cool the adjacent air, but it will stay there. The warm air above will stay put. If I'm wrong on any of this please advise Not really correct. UFH works on radiation (around 80-90% and 10-20% by convection) not convection alone. Our 6m high ceiling is almost the same temperature as the wall thermostat reads. No cosy feet really either, the floor is actually cooler than your body, typically only a little warmer than the room. Cooling works in just the same manner, by radiation, instead of heating it basically sucks the heat from you. So although room temps may drop by a couple of degrees the house feels way cooler and more comfortable.
April 20Apr 20 32 minutes ago, SimonD said: Cooling effectiveness of ASHP isn't that great, you may get a few degrees drop during the hottest days You can have it working exactly the same A2A with fan coils. Just flow at 6 degs and can be as cold as you want.
April 20Apr 20 25 minutes ago, JohnMo said: Cooling works in just the same manner, by radiation, But cold isn't a thing, it's a lack of heat, so can't radiate. Heat is a thing. In your explanation is heat radiating from the air into the floor? What temperature are the floor and the liquid circulating?
April 20Apr 20 40 minutes ago, saveasteading said: But cold isn't a thing, it's a lack of heat, so can't radiate. The floor becomes the cold area, so the room and more importantly you radiate heat to the floor. The water picks up the heat gain from the floor.
April 20Apr 20 Author I'm going to replace rads with fan coils upstairs. My downstairs doesn't get too hot, so a few degrees reduction via the UFH is good enough. If I get more then bonus 😄
April 20Apr 20 2 hours ago, JohnMo said: You can have it working exactly the same A2A with fan coils. Just flow at 6 degs and can be as cold as you want. Like I said: 3 hours ago, SimonD said: If you're in a position where you need to drop time, money and resources on infrastructure for an ASHP to do cooling, If you're going to run fan coils with a flow of 6C then be prepared not only for condensate drainage throughout, but also to very carefully lag all pipework through the house etc. So it's a lot of work to make sure the system is properly installed.
April 20Apr 20 2 hours ago, saveasteading said: But cold isn't a thing, it's a lack of heat, so can't radiate. Heat is a thing. In your explanation is heat radiating from the air into the floor? What temperature are the floor and the liquid circulating? For radiation you need to ignore the air (as that can actually hinder radiative heating and cooling). It's the radiation of heat between different bodies. For UFH the warm floor radiates heat to our bodies and the surrounding walls/floors which then radiate the heat back into the space. A similar thing happens with cooling. When the floor temperature is reduced, the walls and ceilings, and our bodies radiate heat toward the colder surface. Hence we feel cooler (even if the air isn't necessarily any cooler). It's the same reason intermittent heat isn't very good for comfort because it heats the air not solid bodies so when the heating is turned off, it feels cold very quickly because the surfaces draw heat away from the body through radiation. Passive cooling using radiation can be very effective but it has to be carefully designed for cooling. If you happen to have the infrastructure, like UFH and your heat pump has the necessary controls/sensors for relative humidity and dew point calculation, then of course you can use it. I've had conversations with the tech people at a couple of large and well known heat pump manufacturers who, whilst they confirm the heat pumps do cooling, it's not like aircon, it will temper the room temperature. In many circumstances this is okay. And the other side is finding the design resources to do the cooling side properly - if heating using heat pumps is difficult, just imagine trying to find the knowledge and skill for cooling. And I'd argue that if there is any risk of condensation forming on pipes, then detailing the system is even more painstaking than insulating for heating.
April 20Apr 20 4 hours ago, saveasteading said: But in reverse, the screed will cool and we will have cool feet, and will slowly cool the adjacent air, but it will stay there. The warm air above will stay put. If I'm wrong on any of this please advise. In the same way houses lose heat - "Hot always moves to cold" - like cold rooms steal heat from warm rooms, the outside steals heat from a heated house - it might not be as effective as say AC but the rule is just the same - warm room - cool floor the hot is going to go to cold.
April 21Apr 21 7 hours ago, SimonD said: And the other side is finding the design resources to do the cooling side properly - It really isn't that difficult - UFH flow at around 17 degs, job done. It's above dew point for the piping, and therefore the floor, no matter what the build up. It even works at 300mm centres. Fan coils just over size them, run at the same flow temperature as the UFH for heating and cooling. No additional pipe lagging needed for cooling and no condensation drains. A good compromise.
April 21Apr 21 Author 1 hour ago, JohnMo said: It really isn't that difficult - UFH flow at around 17 degs, job done. It's above dew point for the piping, and therefore the floor, no matter what the build up. It even works at 300mm centres. Fan coils just over size them, run at the same flow temperature as the UFH for heating and cooling. No additional pipe lagging needed for cooling and no condensation drains. A good compromise. This is my plan: avoids condensation faff / risk.
April 21Apr 21 1 hour ago, JohnMo said: It really isn't that difficult - UFH flow at around 17 degs, job done. It's above dew point for the piping, and therefore the floor, no matter what the build up. It even works at 300mm centres. Fan coils just over size them, run at the same flow temperature as the UFH for heating and cooling. No additional pipe lagging needed for cooling and no condensation drains. A good compromise. This is exactly the shifting argument I've come to expect from you. In one statement you say just run fan coils at 6C and get as cold as you want and then when it's pointed out the measure you have to take to get this working, in the next you say something is dead simple and no problem at all, but use reference temps that are wildly different at 17C. Once you then run at 17C the cooling effect is dramatically different and goes back to what I originally said was marginal cooling that may bring uncomfortable temps back to okay and not like aircon at all. The other issue is that your doing this in your own home, you're not running a company providing design and installation in other peoples' houses that may have vastly different expectations and understanding of the system, or none at all and then completely undermine the original strategy. What customers often understand as cooling is very difficult to quantify and can easily lead to big misunderstandings, because they often assume it's like aircon. Edited April 21Apr 21 by SimonD
April 21Apr 21 2 hours ago, SimonD said: cooling is very difficult to quantify and can easily lead to big misunderstandings I would have assumed there would be proper case studies by manufacturers or academics but I've not come across any. For me that's enough to suggest that it isn't an efficient process.... and many installers are just that, installers, and don't understand the heating principles let alone cooling.
April 21Apr 21 2 hours ago, SimonD said: one statement you say just run fan coils at 6C and get as cold Not really a shifting argument, different solutions to the same issue. The larger fan coils at a flow temp of 17 are not quite as good as Aircon, but in nearly every case more than adequate. Way less faff to install than flowing at 7 degs, better CoP also. 2 hours ago, SimonD said: The other issue is that your doing this in your own home, you're not running a company Give them two options, all singing all dancing, plus a few of grand in install costs covering, additional insulation, condensation drains, electronic mixing valves etc, worse CoP, and more complex commissioning or a comfortable night's sleep in hot weather and a super simple install. 95% of installs would never ask for cooling anyway.
April 21Apr 21 15 hours ago, saveasteading said: I can't see how air source pumps work efficiently in reverse for domestic purposes. Of course they work as chillers in air conditioning systems but that is by air circulation. Expecting to use cooling by sucking heat from a floor slab or radiator cannot be the same. In heating, we warm the concrete floor or screed and it makes our feet and lower parts cosy. It then warms the adjacent, cooler air which rises to the ceiling and this continues until the whole room volume is warm. But in reverse, the screed will cool and we will have cool feet, and will slowly cool the adjacent air, but it will stay there. The warm air above will stay put. If I'm wrong on any of this please advise. I can only talk about my personal experience, but we cool our downstairs slab with an ASHP during hot periods and it's remarkably effective. Coming in from outside on a hot day is like walking into a cool cave. We run a flow temp of about 16 °C and that's enough to keep the slab under about 20 °C, even in a multi-day heat wave. We do have concrete floors, which I'm sure helps a lot. I don't imagine the effect would be as powerful with, e.g., wooden floors. 15 hours ago, saveasteading said: In heating, we warm the concrete floor or screed and it makes our feet and lower parts cosy. It then warms the adjacent, cooler air which rises to the ceiling and this continues until the whole room volume is warm. I'd be careful about overstating the effects of convection in a well-insulated house using low flow temperatures. Sure downstairs gets warm, but as you walk up the stairs there's a clear temperature gradient as you move towards the downstairs ceiling. In the middle of winter, it's typically 2-3 °C cooler in the hallway upstairs (no heating upstairs) than it is downstairs, even in the central landing with open stairs and a large double height area. I suspect that hotter floors in a more poorly insulated house would increase convection.
April 21Apr 21 1 hour ago, saveasteading said: I would have assumed there would be proper case studies by manufacturers or academics but I've not come across any. For me that's enough to suggest that it isn't an efficient process.... and many installers are just that, installers, and don't understand the heating principles let alone cooling. That's the big red flag for me too. I can't find much in the way of useful reference and those references I can find from journals, the process is quite complex. But basically the standard used to calculate cooling is the same standard as is used for calculating UFH output - BS EN 1264. So the calculation goes that essentially the floor output for the same given floor depends on Mean Water - Air Temperature difference - give or take some details. If you're running heating you'll typically have a higher dT for heating than for cooling simply because you need to keep flow temps above dew point and a floor that's tool cold is uncomfortable. This means that the floor heat out (or actually input in this case) is going to be less that with heating. One way to think about this is that a thick slab is highly unlikely to reach parity with air temps during a heat wave, for example and will almost always provide some natural cooling effect due to its mass, so even when running cooler temp fluid through this the temperature difference is going to be even smaller. Then there is the effect of floor coverings and heat transfer. Add to this that heat pumps are designed and developed primarily for heating and you have a system that can do something else - a little bit of cooling, but it's questionable how much it's been developed and tested for this. So there's an optimisation question, then there's a control question because heating controls aren't really designed for cooling control. Etc. etc. Then there is the question as to whether, if you're building a new house anyway, you're better off designing passive cooling measures into the design in the first place. In our house, for example, the top floor is timber frame and it takes about 3 days during a heat wave for the heat to equalise and become uncomfortable when it's over 28C outside. Downstairs we have EWI coupled with brick/brick, brick/stone walls and this area maintains a nice cool temperature throughout heat waves. My sons always comment on this when they come home from school on hot days and how fresh the downstairs feels even after days of heat - this is where all our bedrooms are. We are just installing a smaller split aircon unit centrally upstairs for the living room which gets a lot of heat gain through large windows. There's also another element that's overlooked in effective cooling, which is dehumidification and the role that plays in our experience of heat. Aircon units dehumidify as a natural consequence of condensation. A heat pump using cooling does not, and will not do this especially if it's running safely above dew point - fan coils condensing can of course dehumidify. This is an effect that is important when we experience high humidity heat. So for me the conclusion is that in a well designed and highly efficient house, running cooler water through the UFH will have a positive effect, of course it will, but in terms of designing a whole house system that does efficient optimised heating and cooling through the same system, it is not a simple or easy thing to do. And as we know, how do you find an installer that'll do it and then properly support it? Anyone doing it just has to have a realistic expectation of what they're going to get and the scant public information out there is not massively helpful. Edited April 21Apr 21 by SimonD
Create an account or sign in to comment