Hi all,
I'd like to ask a 'general' question about adding internal insulation to ONLY the 2 external-facing walls of a bedroom in my victorian terrace, with regard to what Building Control are likely to require of me, etc.
These 2 walls amount to precisely 49.1% of the total 4-walls area of the room. I read somewhere that if an upgrade is below 50% then B.C.don't need to be involved, and thus I wouldn't need to meet U-value requirements etc!
Or, do things need to be looked at more holistically & the whole room taken into consideration - for instance - the ceiling was, some years ago re- boarded (but not yet skimmed!) so would B.C. add this in as part of my upgrade (& thus becomes >50%)? I've no plan to add more insulation to the ceiling but there's an existing 200mm of wool atop in the loft space, brought up to Regs & without having to apply to BC !
Also, to ask opinions of folk on here about whether its worth all the 'faff' of obtaining B.C. consent for these smallish, almost DIY projects - For myself I'm keen to comply since, when I eventually sell (10+ yrs hence) I believe a search is made, for the sale documents, to ascertain if home improvements/works legitimately comply with Regs. But it seems to me the public commonly are quite blasé about the whole matter, + some tradesmen 'forget' to apply on behalf of client, on small jobs at least. This 'delinquent' attitude seems quite common to me. Am I right this comes back to bite the house-owner eventually?
Any comments much appreciated.
If it's not a building of historical interest (listed) and you are doing insulation internally and externally, not sure why anyone needs to be involved. Photograph everything good for future reference.
Only thing other than the above, if the wall is currently breathable keep it that way, so add mineral wool wood fibre etc not PIR.
13 minutes ago, Neverfinished said:
existing 200mm
I would be adding another 150mm on top of that.
'Renovation of a thermal element' is 'adding or replacing a layer'. The 50% is *of the relevant thermal element in the room you are in*, so if there are 2 external walls and you IWI them both, you have done 100%, so definitely BC approval required. Theoretically if you did 49%, 49% and 2% in separate tranches you could arguably do it 'outside the Regs'. However when questions are asked when you come to sell the purchaser or their solicitor may not understand the 'letter of the law' under which you carried out the works, and may ask for an indemnity of a Regularisation Certificate. Your walls and ceiling to unheated space would be treated separately if done at separate times, but for counting purposes the 2 external walls are 100% of the wall area and the ceiling is 100% of the ceiling area.
I always get BCO approval even for IWI of 1 external wall since, if and when I sell, I would want to be able to wave the completion cert in front of the person who was trying to find reasons to reduce the price.
200mm of wool will not reach the 0.16 U value for compliance (Edit: It might, just, if the exg 200mm was 'extra special' sheep's wool with a (lower-than-mainstream-sheep's wool) lambda of 0.035W/mK) but if it was done at a time when 200mm did 'cut the mustard' then as you are not adding a layer or replacing a layer (the pl'bd) you do not *have* to add anything. I would if I were replacing the ceiling (and of course arguably at that stage you have to stump up the £180 or whatever (may have changed since last I did one) for a Building Notice).
Edited by Redbeard
Clarific'n re roof U value
3 hours ago, Neverfinished said:
Hi all,
Or you could not bother and just crack on and fit the insulation.
How will anyone ever know?
As always, aside from cost, what will the BCO add to this simple excercise? Bear in mind, they may not agree with your proposal and you may need to do more/something different to comply. Once they know work is happening, they know. You cannot have them "unknow".
Thanks to you guys, as above - @JohnMo @Redbeard & @Roger440 for your views & input &, on balance, I think I'll bite the bullet & pay B.C. for a building notice; I'm eager to have a record of improvements done for when I ultimately sell the house. You Redbeard offered some clarity to my oversight - as of course its only those 2  exterior facing walls that'd really require upgrade in IWI (+ ceiling ideally too).
 I'll just add a little more of the story of this (small) project, to keep you in the loop - I originally registered with BC in 2020 to upgrade insulation of these 2 out-facing walls but only ever got as far as fitting 60mm wood fibre to brickwork, the intended 45+mm of hemp lime plastering being too hard to complete on my own  - & I even stupidly let the building notice expire too.
Pic. below shows current 'state' of the project;
So I'll re-apply (+pay) BC again !, complete the 'insulated plaster' work etc over the wood fibre base, with some help this time, to obtain a completion 'certificate'.
My house is a victorian mid-terrace, in red brick + lime mortar, in a conservation area but not listed.  In my original application I emphasised how I've retained the breathable fabric for vapour permeability etc across the house; BC officer who viewed 'site' at the outset seemed accommodating to the historical limitations to improving its u-value, so I'm hoping to get the same consideration again this time, & complete, without actually attaining the now even tighter u-value.
You guys perhaps already know how Approved Doc. L states some interesting 'accommodations', for example :- Vol 1, para 0.9 . . "the work should comply with standards in this approved document to the extent that it is reasonably practicable"
para 0.10 says: "traditional dwellings should be improved only if doing so will not cause long-term deterioration of the building’s fabric or fittings . ."
Here's for hoping BC will consider my new application sympathetically again now!    Cheers
If you started on the BN work then why would you need to re-apply.  It's only if you haven't started that it expires (AIUI)
Many thanks for that info mjc55; I came onto the forum now as plan getting the project going again in the next month, & these replies will assist my discussions with BC, as . . they wrote saying application cancelled because I hadn't responded to their enquiry/s 3 years into my application! Stupid of me really! So I will try to retrieve something. Cheers
So BC did visit. Have they agreed in principle your 60mm WF and hemp/lime? Did you state a U value? (I know you do not have to in a BN).
The trouble, to my eyes, with the clause which says:
"Historic and traditional dwellings
0.10 The energy efficiency of historic and traditional dwellings should be improved only if doing so will
not cause long-term deterioration of the building’s fabric or fittings. In particular, this applies to
historic and traditional buildings with a vapour permeable construction that both absorbs moisture
and readily allows moisture to evaporate. Examples include those built with wattle and daub, cob
or stone and constructions using lime render or mortar." (p.3 of Part L)
...is that it is open to debate as to what thickness of WF EWI will "cause long-term deterioration of the building’s fabric or fittings". Some say 'Let WUFI tell you', (which could mean up to 100mm on a solid 225 brick wall) and others say never go above 60mm. I always try to get WUFI to prove that 100 is OK, but the BCO does not *have* to agree. My local BCOs always have, but it may be more hit-and-miss elsewhere.
If they quibble you could substitute Diathonite for your hemp/lime.
Edited by Redbeard
It is the lack of clarity, and ultimately, the judgement of the BCO, that i would not involve then unless its unavoidable.
If BCO doesnt agree, tough on you. There is no "appeal" process even if they are wrong.
On some of the old house groups, theres been a couple of people running into quite some difficulty with BCO's that seem to be unwilling to relax standards based on it being an older building etc etc. Which the clause that Redbeard highlights specifically allows for. But if the BCO says no, then its no. To the point that one person couldnt insulate his roof to current standard, the BCO just said replace the entire roof structure so you can. All while roof is stripped.
Sadly, as the old school BCO's retire and the new breed of box tickers comes in, i cant see it getting any better.
OP, hope yours goes smoothly.
Thanks again to you good folks, @Redbeard & @Roger440 etc for your most helpful but cautionary words. Its now thrown me into a quandary whether to inform them (BC) or not!
I'd indeed prefer all were 'recorded' & certified, given the effort & £'s involved. Referring back to the initial/2020 application, an officer inspected the bare room (old plaster already hacked off) & I definitely outlined my intention of continuing with vapour open materials (with existing 9" old brick in lime mortar+repointed in lime) + I outlined the IWI to be WF + hemp lime; I maybe did or didn't specify exact inches of that insulation. U-values not mentioned. I did refer to 'not having excessive depths of build up' to avoid 'the interstitial'. Visiting officer didn't especially specify or emphasise any requirements yet seemed 'pleased' with all my referencing details of my methodology. (This project still unfinished so we can never be sure if it'd be signed off, but who knows).
Furthermore, I renovated a suspended floor 2yrs ago, under a BN, insulating 'under' using a VCL as cradle to hold 140-150mm Rockwool, +membrane 'atop'. The officer signed it off even with my honestly declaring the amount of rockwool (surely inadequate to meet Regs @ U=0.25).
I get the 'feeling' BC flexible if one pains to strive to honestly do ones best to comply . . . or am I just becoming too self assured  & a rude awakening awaits me!?
I'll post further developments from time to time.
My advice (for reasons I have stated, particularly on subsequent sale) would be to do it under BC. Re floor insulation you need your exposed perimeter/area ratio to work out the 'base case U value, from which you can work out the base-case R, then add that to the R value of your
15 minutes ago, Neverfinished said:
140-150mm Rockwool,
to get the combined R, then 1/R = U. I'm a bit concerned about the VCL cradle, which puts your VCL on the wrong side of the insulation, but maybe I have misunderstood.
Just be aware post october 23, much has been tightened up in BCO land. They do now bear at least a small amount of responsibility for what they sign off, where, previously, they didnt. You may find they now want "evidence" from a qualified professional to support your assertions, even though your proposals are pretty conventional. That means paying for reports, such as WUFI, for example.
But they might not. No way of knowing until they are involved.
I know what id do, but thats very different to Redbeard. Clearly he has encounterd sensible BCO's to date.
Do let us know how you get on though. Ill be doing similar in another year or so.
Thanks again @Redbeard , @Roger440 + all you others on Buildhub who contribute their expertise & help 'have a go' folk like me!
Yes, sorry Redbeard I wrongly outlined my suspended timber floor buildup. I actually followed the  Ecological Building Sys. video: https://www.youtube.com/watch?v=M1KzqaOgtss
for my 'build up'; yes, to be correct, I did infact use the 'blue' Solitex for the cradle & the green 'DA' as vcl atop. And BC signed it off a year ago (not 2 as I'd said) without questioning u-value or anything . (
Returning to my IWI upgrade of 2 adjoining walls - I always struggle calculating U values (on Ubakus), would anyone be happy to run a U value calc. on these walls for me ?
Build up is as follows:
                                                'vintage'/1897  Red Brick     - 225mm    - (lime mortared 'in', no cavity)
                                                Baumit Klima RK 38              - 5-10mm   - as a dubbing out + adhesive, layer
                                                wood fibre boards                - 60mm      -  (T & G 'fit')
                                                Baumit Klima RK 38              - 5mm         - adhesive layer
                                                Medium Hemp-Lime plaster - 45/50mm   One manufacturer states a value as 1.26w/m2k @30mm; another states conductivity = 0.07-0.09W/mk.
                                                Lime plaster finish coat         - 5/10mm
                   The Baumit layers being so thin presumably can be ignored?; note, this Baumit is an NHL lime. What's people's opinion re permeability of an NHL lime in this build-up ?
It would be just generally useful to know its u-value, & perhaps it'd help me decide if to go through B.C. (or not!)
The figure is sure to be short of the requirement !
I'd rather not increase the hemp-mortar thickness further, I'd worry the extra weight is likely make it 'peel away' from the WF base/backing perhaps!
Thanks all.
Assuming lambda values of 0.042 and 0.08 respectively for rigid WF and hemp-lime, and assuming an R value of 0.588m2K/W for the 'base case' wall, your U value with 60 and 45mm would be about 0.39, so yes, short of the requirement (of 0.30), but (a) I think you could argue for stopping there on 'safety' grounds (have you done a CRA for the WF and hemp/lime?) and (b) they may not even ask. Even though things seem to have tightened up in the new Regs and with the Bldg Safety Act it will depend on the individual BCO as to whether they ask the U value. I generally used 100mm of rigid WF which, on a 225 brick wall, gave about 0.34. Under the 'old regime' not only did no-one ever quibble; they never even asked. In fact I used to insist on telling them the U value I had achieved and why I had limited it. Like you, I ignored the adhesive layer (one only in my case) and the plaster layers in my calcs. And I always used RK70 for the adhesive layer, not RK38 - RK70 always felt much stickier. I used RK38 for the parge coat, though.
(The calc above is done from R values, and my calculator, not on software).
  • 1 month later...
Hi everyone. Thought I ought to return to this, my blog, & give an update on my progress re. this 'o-so-small' a job of hemp insulation to just 2 outside facing walls, details as described at the outset  in my initial blog . . & then a few more questions to you guys if I may !!
I indeed proceeded to apply to B.C. who in their own time looked at the intended job & merely listened without objections as I suggested "It'll be difficult to meet U-value regs, given that the wall/s insulation 'build-up' is somewhat governed by need to avoid condensation issues/risks", &, he didn't question or refer me to U-value requirements in any way & seemed to go happily on his way -It being an 1897 terrace in a conservation area they seem keen to support such heritage work in our town.
And this brings me to ask for your views re. my layers of build-up: From outside to in, its:- 230mm solid old red-brick; 60mm Pavatex WF (already afixed as seen in pic. above in this blog); Going forward now, I'm applying 45ish mm hemp-lime plaster, though have become concerned that with this much depth & weight it might all fall off before its set! - SO . . I've decided to create a simple timber 40mm deep 'partition wall', screwing it onto the WF (thru to the outer bricks), then apply the hemp'coarse stuff' into all the battened sections of the partition,thus providing a greater surface area too for the plaster to stick to. Then addition of 15mm wood wool boards fixed on to the partition; lime-plaster skim finish.  . . . I think this is the most likely way for success - any comments appreciated.
Also I've been on Ubakus, to get some kind of condensation analysis. (Can't afford a WUFI). Take a look at the attachment on here - but note:- I've had to substitute materials listed 'in Ubacus' to an extent, for those materials I'm actually going to use - but is an interesting outcome - it shows a serious condensation risk. By further playing with the addition of a VCL - Pro Clima Intello+ (see it greyed out in the current pic.) by 'turning this item back-on' the analysis then shows NO raindrops, ie no condensation !! So . .this suggests I ought add such a VCL into the 'build-up' - expensive but presumably worthwhile adding in a VCL as long as I can get it air tight (always difficult) . . any comments re. all this would be most helpful.
Many thanks.
U Balkus only takes a static shot of the situation at one temperature.  -5 outside (you can change this). Unless you live in Baffin Island this weather is unlightly.
If you raise the external temperature to something positive you'll see the condensation risk disappears. As long as you don't have to raise it too high, say much above 7 to 8 deg your wall will be drying for more of the year than wetting and it'll be fine.
Remember diffusion is only a tiny part of how water makes it way into the wall. Air leaks through bad airtightness are far more significant.
Pay attention to external driven rain on old buildings too. Something like a Auto Brick oil will repel water without compromising the walls ability to dry out.