iMCaan Posted Thursday at 17:54 Posted Thursday at 17:54 Hi We have three heating zones of which groundfloor ufh is not heating up. All ufh components appear to be working fine. The boiler is working, it's heating up the water. The manifold side also appears to be working. However, the flow pipe to manifold/pump is always cold when the boiler has kicked in. So it appears the hot water is not reaching the manifold pump. The flow pipe from the boiler has 3 branches (one for each heating zones that are controlled by Danfoss motorised valves), attic (radiators), 1st floor ufh and groundfloor ufh. The motorised valves are close to the boiler. The attic and 1st floor zones work as they should. When they request the boiler comes on, the motorised valves open and the hot water starts flowing to those zones and the rooms warm up. The water is hot either side of those motorsied valves as it should be. Now the mind boggling bit. Whether the groundfloor heating zone (motorised valve) is open or closed, the flow pipe on both sides of the motorised valve are COLD but ONLY the branch part of the flow pipe, which is about a foot long. Nothing else is between motorised valve and the boiler just like other branches. The rest of the flow pipe from the boiler to the other motorised valves are hot (untouchable). The groundfloor ufh branch is the middle branch. How could it be that only the branch is cold but the rest of the flow pipe is hot? Thanks
Big Jimbo Posted Thursday at 17:57 Posted Thursday at 17:57 A knackered, stuck shut motorised valve ? That would be my guess.
JohnMo Posted Thursday at 18:07 Posted Thursday at 18:07 Few things, motorised valve not opening valve. A manual valve closed in that circuit. UFH pump not starting UFH mixing valve stuck and not sucking any new hot fluids in.
iMCaan Posted Thursday at 18:25 Author Posted Thursday at 18:25 (edited) Thanks, motorised valve is in auto position and lever can be manually moved to auto or manual position. I'm not sure how to test it at what state the valve is (open or closed). Surely, the water pipe on right towards the boiler should be hot just like the rest of flow pipe. The UFH pump is all lit up and goes off when there's no heating request. The flow pipe near UFH mixing valve is cold. It seems the hot water is not reaching to the mixing valve. When you say "manual valve", is that motorised valve in manual position you are referring to? Edited Thursday at 18:27 by iMCaan
JohnMo Posted Thursday at 20:04 Posted Thursday at 20:04 1 hour ago, iMCaan said: motorised valve is in auto position and lever can be manually moved to auto or manual position Remove actuator from valve and truly to rotate the valve with your finger. It should be easy to move. Manual valve is an isolation valve, so likely to have a handle on it. May look similar to this Do you have any drain valves upstream of the UFH but after the motorised valve. Will look like this?
iMCaan Posted 20 hours ago Author Posted 20 hours ago I had an electrician, who wired the ufh, to come out to investigate. He concluded that the flow and return pipes are wrongly connected. The flow pipe is connected to the return connection on the pump and the return pipe is connected to the flow connection. Therefore, the pump is circulating the cold water in the ufh pipe loop. On return, the pump (manifold side) is pushing the return (cooler) water back to to boiler to heat up and at the same time the boiler is pushing hot water on this same (flow) pipe towards the manifold. (hope this makes sense). This creates a conflict, which is why the heating is not working. He says the flow and return pipes need swapping on the pump. He said to contact the heating company to confirm that flow pipe and return pipes are correct. I contacted the heating company and they said that's rubbish (as in they don't make a mistake - probably typical response when one company says it's another company's fault) but they will come out next week to take a look. Yesterday, I did notice that the return pipe was more hotter than the flow pipe. This was when only when only one thermostat was requesting heating. If other thermostats kicked in the flow/return pipes got cooler, near the manifold and near the boiler.
ProDave Posted 20 hours ago Posted 20 hours ago Question. Has the downstairs UFH ever worked properly? i.e. are we trying to solve a fault (it used to work but has stopped working) or is it a new install that has never yet worked on the ground floor? Post some pictures of the ground floor UFH manifold please.
iMCaan Posted 20 hours ago Author Posted 20 hours ago It's a Danfoss motorised valve with a manual and auto setting. It's set on auto. Yes, there's a drain valve. Orange - Flow pipe from boiler Yellow Radiators - branch 1 Green Groundfloor UFH - branch 2 Blue 1st floor UFH - branch 3 Light Blue hot Water
JohnMo Posted 20 hours ago Posted 20 hours ago 28 minutes ago, iMCaan said: contacted the heating company and they said that's rubbish (as in they don't make a mistake Is this a new install? If so, tell them the UFH not working and needs to be fixed.
iMCaan Posted 20 hours ago Author Posted 20 hours ago 3 minutes ago, ProDave said: Question. Has the downstairs UFH ever worked properly? i.e. are we trying to solve a fault (it used to work but has stopped working) or is it a new install that has never yet worked on the ground floor? Post some pictures of the ground floor UFH manifold please. It's a new UFH system. I would say it has never worked properly. Nothing has changed since it was commissioned. It has heated the rooms before but we never had it on continuously as we haven't moved in yet. The photo was taken a few months back but nothing has changed in this system.
ProDave Posted 20 hours ago Posted 20 hours ago 14 minutes ago, iMCaan said: Can we have a closer / clearer picture of the jumble of pipes coming out of the floor bottom left of the photo. Following the copper pipes between the 2 manifolds, the left manifold has the hot pipe connecting to the right hand manifold cold. These are the flow and return to / from the manifold. So either one is connected with flow and return swapped (which is wrong) or they are connected in series, which I have never seen before.
iMCaan Posted 20 hours ago Author Posted 20 hours ago 1 minute ago, JohnMo said: Is this a new install? If so, tell them the UFH not working and needs to be fixed. Yes. They are coming out to take a look next week. I will ask them to fix it as they laid the flow and return pipe and connected it to the pump. The flow and return should be connected to the correct pump connection, if incorrectly connected. The heating request does work as it starts the boiler. Three companies setup the ufh system, ufh company laid out the plastic pipe and installed the manifold, electrician installed the thermostats and wired it all up to manifold, and the heating company fitted the boiler/cylinder.
iMCaan Posted 19 hours ago Author Posted 19 hours ago (edited) Have loads of old installation photos but not of the finished installation. Will share the photo later. Edited 19 hours ago by iMCaan
iMCaan Posted 17 hours ago Author Posted 17 hours ago If I turn off the UFH on both floors until the pipes are cool. Then turn the ground floor UFH on. Aim a thermal camera at the flow and return pipes (just has they come out of the concrete floor to the manifold). The pipe that heats up is the flow (hot) pipe. Does this make sense? Will it work?
iMCaan Posted 13 hours ago Author Posted 13 hours ago Here is the clearer photo of the ground floor manifold
iMCaan Posted 7 hours ago Author Posted 7 hours ago I turned off the ufh and let the flow and return pipes to cool down. Then I turned the heating on in one of the rooms. The boiler kicked in. The return pipe became hot first. Did this three times and on all three occasions the return pipe became hot before the flow pipe. When I left it on for a while, the return pipe appeared hotter than the flow pipe. The thermal camera was not useful so used tmy hands to feel the heat in the pipes. So it's clear the return and flow need swapping. Will see what the heating company says next week.