richo106 Posted Monday at 11:03 Author Posted Monday at 11:03 1 hour ago, Nickfromwales said: Defo needs a FLIR / IR thermometer so you can see the heat pushing through the pipes (or not). Sorry, that doesn’t answer my question. The loops need to be purged one by one with cold mains. If this didn’t happen then it needs to, if you’re looking to eliminate every possible reason why this isn’t working properly. My immediate gut feeling is that you should defo have had 2x manifolds, each with their own pumps, and each with a TMV; this would allow a higher flow temp to the FF UFH and for the GF to be dialled back accordingly. You have 2 very different emitters here, BUT, if well insulated/airtight/MVHR then the requisite heat for the FF should be minimal. I’m glad, as the install in the pic is 🐕 💩. I apologies for these daft questions but i can borrow an IR gun from work, what areas should be checking with this? Just floor temps? Or the pipes also? I am going to ask the plumber if he did this, how can i do this now just to ensure there is no air lock? Is it possible to do? I have 2 x manifolds but one common pump, would turning GF off prove that another pump may help or not? Can't seem to get it above 20 deg with cold floors though, tiles feel very cold. Once i shut the doors the temp decreases through the night. I am guessing this doesn't help that i turn my heating off 4 - 7 due to high energy costs
richo106 Posted Monday at 20:12 Author Posted Monday at 20:12 Update (1) My heating come back on at 7pm (is this cost effective do you think switching it off for the 3 hours?) 7.30pm All FF manifolds flow rate approx 2 on all of them, 25 deg in and 24 out 7.30pm I turned down all GF thermostats so no call for heating. ASHP still running and pump running 7.35pm the flow indicators on my GF were still showing flow even though all call for heat was off, i turned off isolation valve on manifold. All flow rate indicators shot up to show no flow FF manifold flows rates immediately shot up all to around 3 and a couple closer to 4 8pm - flow rates still the higher values - 25 deg in and 24 deg out How long would you leave it like this to see if it actually makes a difference? Would this increased flow make a difference? I have attached a picture of my pump set up, green arrow is to GF manifold approx 4m of pipe and red arrow is FF manifold approx 9m of pipe
richo106 Posted Monday at 20:18 Author Posted Monday at 20:18 Any advice what to try next would be great or what to look out for. If i installed another pump would this improve flow rates on both manifolds? could i even do this? (apologies terrible plumbing knowledge!) Another idea is that i know i turn the heating off between 4 -7 (cosy tariff and expensive period!) could i leave FF running? Sorry all the questions just very determined to hopefully get to the bottom of it one way or another
Nickfromwales Posted Monday at 21:28 Posted Monday at 21:28 1 hour ago, richo106 said: Any advice what to try next would be great or what to look out for. If i installed another pump would this improve flow rates on both manifolds? could i even do this? (apologies terrible plumbing knowledge!) Another idea is that i know i turn the heating off between 4 -7 (cosy tariff and expensive period!) could i leave FF running? Sorry all the questions just very determined to hopefully get to the bottom of it one way or another Now sat in the Doghouse in Manchester, and determined to get to the bottom of a nice cold pint of Wingman, aka “Mother’s milk”. Been a long day so may have another…. 😋 First question, should have asked sooner, but what was the flow and return temps of the FF UFH before any (possible) heat hit it? Exactly the results I expected, so thanks for the feedback. Pump potential, when made divisible, is simply insufficient. GF UFH steals the lions share, ‘path of least resistance’, so the FF gets the scraps; issue here is, the FF UFH needs a lot more attention. This needs some surgery methinks. Firstly, as suggested previously, you can mess about with flow rates, however I think this will get you nowhere (sorry) and a few changes need to happen. Before surgery, the consultant in me needs to be pragmatic. That said, let’s see what we can gather before booking you in for the full, frontal lobotomy . First off, the differential of the FF flow and return are garbage, which suggests there’s a lot of airlocks occurring. 1°C suggests zero flow, tbf. Is there an automatic air vent on the FF UFH manifold? Pic plz if so (and does it work / is the cap open 2 turns?).
richo106 Posted Monday at 21:48 Author Posted Monday at 21:48 16 minutes ago, Nickfromwales said: Now sat in the Doghouse in Manchester, and determined to get to the bottom of a nice cold pint of Wingman, aka “Mother’s milk”. Been a long day so may have another…. 😋 First question, should have asked sooner, but what was the flow and return temps of the FF UFH before any (possible) heat hit it? Exactly the results I expected, so thanks for the feedback. Pump potential, when made divisible, is simply insufficient. GF UFH steals the lions share, ‘path of least resistance’, so the FF gets the scraps; issue here is, the FF UFH needs a lot more attention. This needs some surgery methinks. Firstly, as suggested previously, you can mess about with flow rates, however I think this will get you nowhere (sorry) and a few changes need to happen. Before surgery, the consultant in me needs to be pragmatic. That said, let’s see what we can gather before booking you in for the full, frontal lobotomy . First off, the differential of the FF flow and return are garbage, which suggests there’s a lot of airlocks occurring. 1°C suggests zero flow, tbf. Is there an automatic air vent on the FF UFH manifold? Pic plz if so (and does it work / is the cap open 2 turns?). I am not sure regarding the flow/return temps before any heat hit it sorry I have just check the flow temps again and no change just the 1 deg diff Please find attached pic of the air vent, to be honest i have to google to see what you meant by that! I have not touched it so any advice what to try I am all ears
Nickfromwales Posted Monday at 21:53 Posted Monday at 21:53 2 minutes ago, richo106 said: I am not sure regarding the flow/return temps before any heat hit it sorry I have just check the flow temps again and no change just the 1 deg diff Please find attached pic of the air vent, to be honest i have to google to see what you meant by that! I have not touched it so any advice what to try I am all ears Those caps are like the ones on your car tires. They need to be ‘loose’ to work, so give them a ‘twiddle’ and see what the situation is there plz. Close them finger tight, and then open 2 full turns 720°, if unsure. Then they’ll be able to function properly and let ‘air’ out.
richo106 Posted Monday at 21:59 Author Posted Monday at 21:59 (edited) 9 minutes ago, Nickfromwales said: Those caps are like the ones on your car tires. They need to be ‘loose’ to work, so give them a ‘twiddle’ and see what the situation is there plz. Close them finger tight, and then open 2 full turns 720°, if unsure. Then they’ll be able to function properly and let ‘air’ out. They were both quite tight I have done that, tightened them and then I have backed them off 720 deg Edited Monday at 22:03 by richo106
Nickfromwales Posted Monday at 22:04 Posted Monday at 22:04 4 minutes ago, richo106 said: They were both quite tight I have done that, tightened them and then I have backed them off 720 deg If they were tight, then they weren’t doing any venting. A box has been ticked. ✅
richo106 Posted Monday at 22:10 Author Posted Monday at 22:10 4 minutes ago, Nickfromwales said: If they were tight, then they weren’t doing any venting. A box has been ticked. ✅ Are these ok to leave ‘open’ then I am guessing. Do I need to manually purge each loop or if I have air locks will the auto air vents clear it all over a period of time?
Nickfromwales Posted Monday at 22:12 Posted Monday at 22:12 1 minute ago, richo106 said: Are these ok to leave ‘open’ then I am guessing. Do I need to manually purge each loop or if I have air locks will the auto air vents clear it all over a period of time? These should have been left open by the installer. They stay ‘open for life’ so they can look after you and let any ‘air’ out.
richo106 Posted Monday at 22:20 Author Posted Monday at 22:20 Ok that’s great thank you, guessing this isn’t going to fix all my issues though 😂😂
Nickfromwales Posted Monday at 22:41 Posted Monday at 22:41 20 minutes ago, richo106 said: Ok that’s great thank you, guessing this isn’t going to fix all my issues though 😂😂 Step 1 1
richo106 Posted Tuesday at 20:22 Author Posted Tuesday at 20:22 I thought i would unscrew all the actuators to see if that would make a difference (not expecting it to) 6.55pm - temp in and out was 21deg (heating been off 3 hours) 7.01pm - temp in was 25 and temp out 21 - also changed over temp gauge to prove working 7.05pm - 23 deg in and out 8pm - 25 deg in and out. For ref the GF manifold temp in 25 deg and and temp out 22 deg Saturday I am going to refill all FF loops just to ensure there is no air in there, once again i am not expecting this to make much difference as there is visible flow on the flow meters (which changes when GF manifold off) but just ticks another thing off
richo106 Posted Tuesday at 20:35 Author Posted Tuesday at 20:35 21 hours ago, Nickfromwales said: Step 1 @Nickfromwales I would love to know what step 2 is
Nickfromwales Posted Tuesday at 20:40 Posted Tuesday at 20:40 3 minutes ago, richo106 said: @Nickfromwales I would love to know what step 2 is FLIR camera to see if waters making its way around the FF loops most prob. Or feck off to the pub, and order a jumper on Prime whilst supping soothing cold beer. 1
richo106 Posted 5 hours ago Author Posted 5 hours ago Update I have borrowed an IR camera to check flow and return temps of the FF manifold The heating turned on at 7pm I have recorded the temps at 7.15pm and 7.45pm, please see attached picture to show my findings There is definitely heat loss but not much I have also IR camera'd the carpeted floor and can see the heat lines, this was around 8pm and the temp of the heat was around 20.2 deg and the 'cold bit' was 19.6 deg There was no of any heat lines on the tiled floor in the bathrooms yet (there is downstairs but appreciate the floor make up is different) For this shows the water is getting round the loops at least One thought i have now is to take it off weather compensation curve and set the water temp to 35 deg, this will make the GF 'bounce off' the thermostats though. I am not sure this will make enough difference on the freezing cold days upstairs though Any other thoughts/ideas on my findings today would be grateful, many thanks
richo106 Posted 3 hours ago Author Posted 3 hours ago At 9pm I upped my water temp to 35 deg At 11pm I checked the flow and return temps on my FF manifold, average in was 32deg and return 31deg. So averaging around 1 deg heat loss My bathroom tiled floor has increased from 20.5deg to 21 deg from 7pm to 11pm I am not sure where to go next
John Carroll Posted 55 minutes ago Posted 55 minutes ago To calculate any UFH output, kW = (total loops flowrate (LPM) X 60 X UFH (flowtemp-returntemp))/860. For example a UFH manifold with a total Flowrate of 15LPM with flowtemp-return dT of 1C will have a output of (15*60*1)/860, 1.05kW.