My wee house sits up on piers, varying from about 150-900mm off the ground.

I need to connect the kitchen sink to the SVP, which is at the other end of the house, about 8m or so away. This is all at the 'shallow' side of the house, where the piers are less than 300mm tall.

My original plan was to run the waste pipe through the insulated 300mm deep space within the floor (I'm using JJI joists). However I'm wondering if there is actually anything at all wrong with just running it underneath the house- this would be much easier. Will there be any sort of frost risk? In some ways it isn't really different to running pipes under a normal suspended floor, after all.

Posted

Make sure there is a GOOD fall and no sags in the pipe for stagnant water to collect and freeze. then I think you will be okay.

Not a great deal different to me having the same under the static caravan. I don't think the token bit of wooden screening around the bottom will do much to keeop the temperature under it above ambient.

Posted
Just now, Nickfromwales said:

For the few extra few bucks, run all the exposed pipe work in 110mm, reducing only after the vertical bend. 

What's the advantage to that?

Posted

I was going to support it on loops of wire stapled to the underside of the joists, so 600 centres.

I've got about a 1:40 fall available, it works out about the same whether I run the pipe within or beneath the floor.

Posted

Less likely to block, easier to maintain, more stable pipe, no flow restriction/future proof and probably performs better at 1:40 as opposed to a smaller pipe

 

+1 to 110mm

Posted

Less issues with sag, which is VERY problematic with the smaller bore pipes, but the main advantage is a near zero risk of freezing, or issues relating to partial freezing.

Another pro is the the inevitable accumulation of 'sludge / slime' in the bottom of the pipe is nowhere near as problematic in the larger pipe as it would be in 1"&1/2 and 1"&1/4 wastes. At the end of the run, instead of a bend going up use a branch and plug the open horizontal end with a rodding eye. That way you can clean / clear it in no time at all. :)

Posted

All good advice, thanks.

The pipe run will be: sink+dishwasher, then about half way along the washing machine will join, and then it will meet the main stack under the toilet (where the shower and basin feed in as well). So yeah I'm up for increasing the pipe diameter.

  • 8 years later...
Posted

Searching through the forum for advice, I found this old thread which is pretty close to my query but...maybe worth clarifying, if only for peace of mind.

 

Our build is timber frame over steel foundations and has a very similar ground profile to that mentioned by the OP.  Our design has a buried waste pipe running the length of the house (~25m) before connecting to the waste treatment plant another 10m or 15m away (yet to be precisely sited).

 

The groundwork has asked if we prefer the waste pipe to be buried, or if he could avoid the access complications of digging and filling the trench around the concrete footers for the steel founds.  If we suspend the waste pipe it will go below ground before exiting the footprint of the building.

 

The advice above seems neutral to the option, but is below ground better to avoid risk of frost, or above ground for access/maintenance or other reason?  Not a huge deal in the scheme of things, but would save me a couple of days and maybe £1k-£2k.

 

Ross.