Clark Kent Posted August 20 Posted August 20 Had a heat loss survey with a Heat Geek, when it came to the topic of radiators the guy pooh-poohed column rads. He suggested they weren’t efficient and wants to use type 21 or 22. I’m not after using Victorian cast iron ones, just something slightly more aesthetically pleasing. I know that heat pumps run at a low temp so you have to have a decent surface area but I would have thought BTU’s were BTU’s…..
Dillsue Posted August 20 Posted August 20 You are right that BTUs are BTUs and watts are watts. No matter what the style it's the output that matters, but..... The output of the rads needed as the flow temperature drops increases quite considerably. Manufacturers supply correction factors for their rads at lower flow temps so once you have the loss for a room you can size the rad for your planned flow temp. I'm designing at 35deg C and have just finished installing the last of the replacement/additional rads and there's some big uns gone in!! Unless a room has a very low heat loss the fancy tall rads without any convectors will likely give a very low output at HP low temps. Do the calcs and see for yourself.
nod Posted August 20 Posted August 20 We have eight SS in the bedrooms landing etc We are unlikely to use them But when we have tested them They don’t run hot from a HP The same radiators ran very hot from a gas boiler on our previous build You would have to use them like UFH man’s let them heat up slowly and let the thermostat keep the temperature within a couple of degrees of what you want Our upstairs tracks the ground floor UFH by about 1 degree less Same as our previous
Clark Kent Posted August 20 Author Posted August 20 Thanks for your replies. I’ve done a fair bit of research on heat pumps and am quite aware that the rads will probably feel like they aren’t even on. We’re only putting them upstairs as we’re having UFH downstairs. So basically without the convector's the column radiator isn’t as efficient and will need to be even bigger to work with the low flow temps?
SteamyTea Posted August 20 Posted August 20 47 minutes ago, Clark Kent said: BTU’s were BTU’s 32 minutes ago, Dillsue said: You are right that BTUs are BTUs and watts are watts Watts (W) are not British Thermal Units (BTU). 1 W = 3.412141633 BTU.h-1 The h = hour (3600 s). It is a very important distinction. A BTU is an energy unit, as is a watt-hour (Wh). BTU.h-1 and watt are power units. If you hear an electrician, plumber or energy 'specialist' say killa wot per our, start to run away.
Dillsue Posted August 20 Posted August 20 1 hour ago, Clark Kent said: I’ve done a fair bit of research on heat pumps and am quite aware that the rads will probably feel like they aren’t even on. We’re only putting them upstairs as we’re having UFH downstairs. At 35deg C+ you'll know they are on but they won't feel toasty hot like a typical boiler fed rad. 1 hour ago, Clark Kent said: So basically without the convector's the column radiator isn’t as efficient and will need to be even bigger to work with the low flow temps? Do the calcs. Your heat geek calcs should give you loss per room so you know the output you need. Use the manufacturers figures to give you the adjusted output you need at low temps and you can then pick your rad/rads. Any rad without a convector is going to be less efficient than the same rad with a convector but you won't know what you need without doing the calcs 2
JamesPa Posted August 20 Posted August 20 (edited) To give an example of the calculation: Radiator output is normally (but not universally) quoted for a average deltaT (rad to room) of 50C. Convector rad output is approximately proportional to deltaT^1.3 (manufacturers do quote exponents very slightly different to 1.3, but they are almost always close to 1.3). So a convector radiator operating at ft 35 and DT (flow to return) of 5, target room temp 20, will have an average deltaT of 35-5/2-20 = 12.5. The output will therefore be (12.5/50) ^ 1.3 = 0.16 times the output at deltaT 50. Thus a radiator quoted as 1kW at deltaT 50 will emit only 160W at deltaT 12.5. You can invert this to get the 'oversize factor', in this case 1/0.16 = 6.25, the figure by which you must multiply the calculated loss to get the radiator output (at deltaT50). For any given type of radiator (unless it is very short or very tall) the oversize factor is a constant so this is a very convenient way to work out which radiator from a range you need Column radiators may have a different exponent than 1.3, or even a different basic formula (although the latter is unlikely); you need to check with the manufacturer. There is, however, a fair likelihood that the same formula will apply. Incidentally if you could pump a bit harder and reduce the DT to say 3, the oversize factor reduces to 5.25. Edited August 20 by JamesPa
marshian Posted August 20 Posted August 20 5 hours ago, Clark Kent said: Thanks for your replies. I’ve done a fair bit of research on heat pumps and am quite aware that the rads will probably feel like they aren’t even on. We’re only putting them upstairs as we’re having UFH downstairs. So basically without the convector's the column radiator isn’t as efficient and will need to be even bigger to work with the low flow temps? So size the rads to work on the same low flow temp as the UFH based on the heat loss of the upstairs rooms (allow a bigger oversize for bathrooms because ventilation losses tend to be larger - extract fans / opening windows etc)
sharpener Posted August 21 Posted August 21 16 hours ago, marshian said: So size the rads to work on the same low flow temp as the UFH based on the heat loss of the upstairs rooms (allow a bigger oversize for bathrooms because ventilation losses tend to be larger - extract fans / opening windows etc) This may well result in infeasibly big rads whatever their construction. But the fancy column radiators do not have as much emitting surface area per unit frontal area as a conventional Type 22 or Type 33. Our installers designed for a flow temp of 45 and used a (conventional) rad size uplift factor of 1.9. This is a compromise with the partial ground floor UFH set to 35C, but a mixed system is going to have very big rads indeed unless you sacrifice some efficiency. As were were migrating from an oil system we are happy enough if it costs no more to run.
marshian Posted August 21 Posted August 21 50 minutes ago, sharpener said: This may well result in infeasibly big rads whatever their construction. But the fancy column radiators do not have as much emitting surface area per unit frontal area as a conventional Type 22 or Type 33. Our installers designed for a flow temp of 45 and used a (conventional) rad size uplift factor of 1.9. This is a compromise with the partial ground floor UFH set to 35C, but a mixed system is going to have very big rads indeed unless you sacrifice some efficiency. As were were migrating from an oil system we are happy enough if it costs no more to run. Yes and Yes - very house and heat loss specific - I effectively went for same size T22 to replace T11 - only one rad needed to go from T11 to T22 and then T33 (cos it got extended) I didn’t design the system to run at 25 to 35 deg flow temps it just happens to be the range that heating 23.5/7 with WC works (30 mins for HW daily) I have 3 column rads in the house and whilst they are also an equivilent % upgrade 2 of them are single column and they really could do with being double column rather than single because they only just cope - I think the claims for heat output are based on T50 and when run at lower temps they aren’t as effective
S2D2 Posted Thursday at 21:36 Posted Thursday at 21:36 I looked at this for my install, anything without convectors just has a lower heat output so has to be much larger. I couldn't make it work without them being silly big so had T21/T22 fitted. The thing to watch out for is most of the designer radiator sites will state the output @65C without telling you they're doing so, so dont assume its @50 and make sure you know what you're actually getting at your design temp. Adam (heat geek) actually fell foul of this for the install at his own house so its easily done if you're not fact checking what the sales blurb claims.
JamesPa Posted Friday at 07:13 Posted Friday at 07:13 (edited) Perhaps this is a good point to throw in a plus for fancoils. I have one Mitsubishi ilife2 slim in a room where even convectors would have been unfeasibly large, and I love it. Smart, neat and small and of course does cooling as well. I wouldn't choose them universally but I do wish I'd fitted a couple more! There are some really swanky Italian designs (actually the Mitsubishi ones are Italian) at really swanky prices if you want a particular look. Edited Friday at 07:14 by JamesPa
Michael_S Posted Friday at 19:24 Posted Friday at 19:24 (edited) Fancoils seemed to be a lot more expensive and of course need a power supply nearby - and to me tend to look ugly... We decided a 45 flow temp was a sensible trade off between efficiency and rad size. I use da standard table of deltaT reduction factors, probably should have looked for rad brand specific ones but decided it was probably good enough. I have one rad that is claiming an improbably high BTU at deltaT 50 so I guess we will see. Edited Friday at 19:26 by Michael_S
JamesPa Posted Monday at 09:47 Posted Monday at 09:47 (edited) On 22/08/2025 at 20:24, Michael_S said: Fancoils seemed to be a lot more expensive and of course need a power supply nearby - and to me tend to look ugly... They are certainly more expensive (although not so much so compared to a large type 33) and do need a power supply (just a few watts so the cable can be small!). Im not sure convector radiators are terribly pretty! Faced (at 45C target flow temperature) with the choice of a radiator 1600mm*600mm*200mm type 33, in a space where this only just fits without obstructing a doorway, and a Mitsubishi i-life slim 937*579*131mm and which could also do cooling, the choice for me at least was clear. In place it looks very smart indeed, but of course beauty is in the eye of the beholder. I think the point to be made is that they are worth considering when the size of rads would otherwise be unwieldy and/or in rooms where cooling might be desired. Of course we all really want UFH operating at 35C or less, but in a retrofit that's not always practical. Edited Monday at 09:48 by JamesPa
Michael_S Posted Monday at 11:55 Posted Monday at 11:55 2 hours ago, JamesPa said: They are certainly more expensive (although not so much so compared to a large type 33) and do need a power supply (just a few watts so the cable can be small!). Im not sure convector radiators are terribly pretty! Faced (at 45C target flow temperature) with the choice of a radiator 1600mm*600mm*200mm type 33, in a space where this only just fits without obstructing a doorway, and a Mitsubishi i-life slim 937*579*131mm and which could also do cooling, the choice for me at least was clear. In place it looks very smart indeed, but of course beauty is in the eye of the beholder. I think the point to be made is that they are worth considering when the size of rads would otherwise be unwieldy and/or in rooms where cooling might be desired. Of course we all really want UFH operating at 35C or less, but in a retrofit that's not always practical. Thanks for replying, beauty is in the eye of the beholder I guess, to me they look like the cheap rads/night store heaters you get in a bedsit so negative connotations. I found your other thread on fan coils and one question seemed to be about condensation if used for cooling. I was thinking that the forced air flow would tend to evaporate any attempt at condensation and so the problem would remain with the pipes not the rad itself? Finally it seems a bit harder to work out what the equivalent output in watts is for a fan coil for a given flow rate. It often seems hard to fathom out what deltaT they are using for their stated output and what adjustment factor should be used for a lower flow rate? Final finally, many of the units suggest that they only activate the fan if the flow rate is 35C or over - not much use for a heat pump running weather comp nor for cooling!
Michael_S Posted Monday at 12:00 Posted Monday at 12:00 For reference, I am currently replacing some rads in preparation for a heat pump, given restrictions in my circulating pipes it seems like I can't realistically go below a 45C flow rate for the coldest day so am sizing my rads accordingly so have not had to go up to triple panel or change sizes, rather just going from type 10/11/21 to 20/21/22. However the thought that if I were to use fan coils I could also use the unit for cooling is obviously quite tempting so there are 3 or 4 west facing rooms that get the hottest where fantails (if they have the right output and are not too ugly nor noisy) would be a tempting option.
JohnMo Posted Monday at 12:12 Posted Monday at 12:12 12 minutes ago, Michael_S said: Final finally, many of the units suggest that they only activate the fan if the flow rate is 35C or over Most decent fan coil will have adjustable setting for fan activation temp with different setting for cooling or heating. 14 minutes ago, Michael_S said: equivalent output in watts is for a fan coil for a given flow rate. They are really rated in a given flow temperature. dT is depending on work done and fan speed. 15 minutes ago, Michael_S said: was thinking that the forced air flow would tend to evaporate any attempt at condensation If you start flowing water below about 12 the air being drawn in by the fan is at dew point, so cannot absorb any more water, so water just stays water. Fan coils rated for cooling have a condensation tray to catch this water
JamesPa Posted Monday at 14:03 Posted Monday at 14:03 (edited) 2 hours ago, Michael_S said: I guess, to me they look like the cheap rads/night store heaters you get in a bedsit so negative connotations. Some do for sure, but some don't. If you want to go mad there are some really swanky looking ones available in Italy, at correspondingly swanky prices. Actually the Mitsubishi ones are made in Italy and IMHO look better in 'real life' than in their publicity leaflets, because the stylistic curves have more impact. 1 hour ago, JohnMo said: Most decent fan coil will have adjustable setting for fan activation temp with different setting for cooling or heating. Thats the one niggle with the Mitsubishi model. It does have different thresholds for heating and cooling, but they are not adjustable. The cooling one is fine (18C I think) but the heating one, at 30C, is a bit high at the beginning and end of the season. For me that hasn't yet been a problem because the room its in has solar gain, so when the fancoil doesnt come on because of the threshold, the sun is heating the room anyway. However that wont be the case for everyone and, personally, I think they should allow the threshold for heating to go as low as 25. 2 hours ago, Michael_S said: and so the problem would remain with the pipes not the rad itself? You need to set the coolant temperature above the dew point. My Vaillant measures dew point and does that by default (once you have enabled cooling with their overpriced dongle, or the with the exact same dongle, but at 1% of the price, sold also for coding their gas boilers). Doubtless at least some other makes will also control for dew point. @JohnMo is of course spot on about power output. Mine and many others modulate their fan according the the settings and/or the set temperature compared to room temperature. It seems to work well. The one thing to watch is that they have essentially zero water volume, so if you have a lot of them you are likely also to need a volumiser. Edited Monday at 14:08 by JamesPa
Michael_S Posted Monday at 14:17 Posted Monday at 14:17 Sorry, meant flow temp not flow rate - eg I know a conventional rad rated 2kw at 50C deltaT will output about 41% of that at 25C deltaT (45C Flow temp). How about a 2kw rated fan coil - us it the same?
JohnMo Posted Monday at 14:30 Posted Monday at 14:30 8 minutes ago, Michael_S said: How about a 2kw rated fan coil Not the same as a radiator calculation wise. You just need to read the datasheets. Generally they are designed to run sensibly flow temps and the datasheet will give a range of flow temps in cooling and heating and output at different fan speeds. In cooling my fan coil fan will only run when water sensor sees 13.5 degs and lower (ASHP compressor is actually on) AND room temp is above set point. Fan speed then changes automatically based on how much work the fan coil has to do. 1
Dillsue Posted Monday at 16:01 Posted Monday at 16:01 3 hours ago, Michael_S said: For reference, I am currently replacing some rads in preparation for a heat pump, given restrictions in my circulating pipes it seems like I can't realistically go below a 45C flow rate for the coldest day so am sizing my rads accordingly so have not had to go up to triple panel or change sizes, rather just going from type 10/11/21 to 20/21/22. A few days ago I finished all our rad upgrades and ran up the HP for the first time using the existing mix of 10 and 8mm copper runs out to the radiators and all bar 2 of the rads with 8mm drops down walls got toasty hot with a test flow temp of 50deg C. If you want to run at 35deg C then you might find your pipework is up to it but maybe it's too late to resize your rads for 35 degrees?? Yet to investigate why 2 out of the 4 rooms with 8mm drops down the walls aren't getting flow but a second pump for those 4 rooms should get things moving if it's purely down to the small bore.
Michael_S Posted Monday at 16:41 Posted Monday at 16:41 35 minutes ago, Dillsue said: A few days ago I finished all our rad upgrades and ran up the HP for the first time using the existing mix of 10 and 8mm copper runs out to the radiators and all bar 2 of the rads with 8mm drops down walls got toasty hot with a test flow temp of 50deg C. If you want to run at 35deg C then you might find your pipework is up to it but maybe it's too late to resize your rads for 35 degrees?? Yet to investigate why 2 out of the 4 rooms with 8mm drops down the walls aren't getting flow but a second pump for those 4 rooms should get things moving if it's purely down to the small bore. How thick is your 'backbone/main loop' though - ours is rather long due to the house having bene extended and the whole upstairs is 15mm. The online tools suggest the most the upstairs rads could output is about 3.85kw at any sort of reasonable flow rate and that rate would only be achievable if you only take the total length of the circuit and ignore the corners and fittings.... On the other hand it does work with our gas weather comp boiler running at 55C at min outside temp but it takes a long time to warm up after a cool down in the furthest room, fortunately the gas boiler can modulate right down and keep the flow going rather than on/off..
JohnMo Posted Monday at 16:47 Posted Monday at 16:47 Pretty simple cheat sheet below. You really want to aim at zero hydraulic seperation. So 8mm will carry 0.75kW at a dT of 5 etc.
JohnMo Posted Monday at 16:52 Posted Monday at 16:52 7 minutes ago, Michael_S said: 3.85kw Why do you need rads doing that output with a heat pump system? If you room has that heat loss you must be living in an open shed. Flow rate just sets dT, it is the mean radiator flow temp that sets the output. 9 minutes ago, Michael_S said: takes a long time to warm up after a cool down Why would you cycle the system on and off, or do you mean something else?