Does anyone have any views /experience on/of  the above re unstable HW outlet temperatures even with a perfectly operating thermostat which is the same length as the heating element.
My views.
With this top mounted immersion you will only heat the full immersion length of the cylinder from a fully cold cylinder.
20/25% of the HW must then be drawn off before the stat will cut back in, for example, with a stat setpoint of 60C and assuming 50C cut in, (hysteresis of 10C), and a cold mains of 15C then ~ 22% of the HW must be drawn off to enable the stat to cut in.                                                                                                                                     
If 22% of the HW is drawn off, just enough to get the the stat to start calling at 50C  then the top 78% will/can still be at 60C and the remaining 22% at 15C then the actual final HW temp will be far? higher than 60C because the vertical element will heat the cylinder without any destratification and you might end up with 78% at 70C and the remaining 22% at 25C on stat cut out. If the above cycle is then repeated can it lead to still higher temperatures even though the stat is still only sensing the average of 50C/60C cutin/cutout temperatures?, if not, then easy enough to take a few tests over a few days and set the stat appropriately to give 60C.
 
I have a 53 year old dual element top mounted immersion but only use the shorter element which heats 30L, it doesn't have the rod type stat but has a surface mounted one on top of the immersion so I can't carry out any tests, almost the full 30L has to be used before the stat cuts back in but it does give a very stable HW temperature of 65C.
 
 
Posted

Draw a few pictures.

I think I know what you are saying, but not sure.

 

If your cylinder is 53 years old, that betters my old one by 2 decades.

Posted

Photo of typical top mounted single element immersion below.

My Cylinder is only 14 years old, the original, 39 years, which I removed and installed a twin coil (Solar+oil fired) in 2011. I just removed the original immersion but the element had no limescale whatsoever so I desided to re install it in the present cylinder where it sits today.

 

image.jpeg.3134c966c098aae13f7e4991513f7dbc.jpeg

 

Posted

Similar arrangement for me but only time I use the immersion is when the HW/CH system is drained down for changes in the summer.

 

My thermostat is set to 55 Deg C it's only a fairly short element maybe 40 L but that's enough HW at 55 deg for two showers or one shallow bath (I have a tank temp display and from memory the thermostat was quite accurate v the temp sensor)

 

I can't help with re-heat set points as we heat only when (or just before) we need it so I've never noticed what hysteresis is applied

Posted

That's interesting, sometime maybe when using the immersion only, you might switch it on until it cuts out, note the displayed temperature, run off ~ 15L of HW to get it to cut in again, then again note the displayed temperature when it cuts out again.

Posted
6 hours ago, John Carroll said:

That's interesting, sometime maybe when using the immersion only, you might switch it on until it cuts out, note the displayed temperature, run off ~ 15L of HW to get it to cut in again, then again note the displayed temperature when it cuts out again.

 

I don't think that would tell you anything meaningful unfortunately

 

This is what I have on the tank (Library picture from a legionaires cycle to 61 deg C - followed by pouring a bath) the top one is looking at the top of the tank - the bottom one where the boiler tank thermostat is

 

TankTemps.thumb.jpg.82a31749445dd72472c86af598defd06.jpg

 

I'd need to put another temp probe in or move the bottom one up to roughly where the immersion element ends to get a better idea of hysterisis

Posted

This is what happens with my DHW cylinder.  It is on E7 and only uses the lower element, but you can see that there is quite a pronounced temperature gradient after switch off (5AM).

 

With a bit of extrapolation/guesswork, you could estimate that there is a 15°C DT below the element.

 

@John Carroll are you hoping to heat less water and once you have drawn of a bit, the element kicks in and extends the life of usable DHW enough for a shower?

If so, you are only putting in 2.8 kW which will only give you a small lift in temperature (does depend on shower flow rate).

 

image.png.d8e5fe40d9c47092fae464cfefb3fdd2.png

Posted (edited)

All I am interested in is the HW cylinder outlet temperature while using a top mounted vertical electric immersio

2 hours ago, marshian said:

 

I don't think that would tell you anything meaningful unfortunately

 

This is what I have on the tank (Library picture from a legionaires cycle to 61 deg C - followed by pouring a bath) the top one is looking at the top of the tank - the bottom one where the boiler tank thermostat is

 

TankTemps.thumb.jpg.82a31749445dd72472c86af598defd06.jpg

 

I'd need to put another temp probe in or move the bottom one up to roughly where the immersion element ends to get a better idea of hysterisis

I'm only interested in the HW (top) displayed temperature when using the (IF) you have a top mounted vertical immersion, this also incorporates its own thermostat,

"the bottom one where the boiler tank thermostat is", this is only used when you use the heating coil to heat the cylinder.

Edited by John Carroll
Posted
44 minutes ago, SteamyTea said:

This is what happens with my DHW cylinder.  It is on E7 and only uses the lower element, but you can see that there is quite a pronounced temperature gradient after switch off (5AM).

 

With a bit of extrapolation/guesswork, you could estimate that there is a 15°C DT below the element.

 

@John Carroll are you hoping to heat less water and once you have drawn of a bit, the element kicks in and extends the life of usable DHW enough for a shower?

If so, you are only putting in 2.8 kW which will only give you a small lift in temperature (does depend on shower flow rate).

 

image.png.d8e5fe40d9c47092fae464cfefb3fdd2.png

Again, thanks, but a horizontally mounted heating element heats the cylinder in a completely different fashion to a top mounted vertical one.

Posted
3 minutes ago, John Carroll said:

horizontally mounted heating element

Forgot that.

But my lower element is horizontal.

 

I am not sure how much difference it will make in practice, when heating, the water becomes quite turbulent. A combination of density and inertia does that.

Posted
33 minutes ago, John Carroll said:

All I am interested in is the HW cylinder outlet temperature while using a top mounted vertical electric immersio

I'm only interested in the HW (top) displayed temperature when using the (IF) you have a top mounted vertical immersion, this also incorporates its own thermostat,

"the bottom one where the boiler tank thermostat is", this is only used when you use the heating coil to heat the cylinder.

 

Oh I get that and 'it's why I might (in the interests of "science" ) move the bottom sensor up to a position on the outside of the tank level with the end of the immersion

 

It's a top mounted vertical immersion in a 115L tank and it has it's own internal thermostat just as yours does

 

Question will be at what point the internal thermostat signals re-heat and after how much water has been drawn off?

 

gut feel from how we've used it before is you can pretty much use 70% of the water before it will kick in again and try and reheat so maybe 40 litres

Posted
28 minutes ago, SteamyTea said:

Forgot that.

But my lower element is horizontal.

 

I am not sure how much difference it will make in practice, when heating, the water becomes quite turbulent. A combination of density and inertia does that.

 

I don't get a lot of turbulence with a vertical top mounted element and you certainly get a very defined stratification with minimal heat transfer to water - down side to my element is it's quite short, maybe less than 1/3 of total tank height so it really only heats about 50 litres max - just enough for two decent showers or a shallow bath

Posted (edited)
16 minutes ago, marshian said:

 

Oh I get that and 'it's why I might (in the interests of "science" ) move the bottom sensor up to a position on the outside of the tank level with the end of the immersion

 

It's a top mounted vertical immersion in a 115L tank and it has it's own internal thermostat just as yours does

 

Question will be at what point the internal thermostat signals re-heat and after how much water has been drawn off?

 

gut feel from how we've used it before is you can pretty much use 70% of the water before it will kick in again and try and reheat so maybe 40 litres

 

If you can move that as far up to the cylinder top as possible and run on the electric immersion and drain down as you say maybe 20/30L to get the stat to cut in, then wait until the stat cuts out, and repeat this test say one or ideally two more times  then that will provide the info I'm after hopefully.

Edited by John Carroll
  • 4 months later...
Posted (edited)
On 18/06/2025 at 21:18, John Carroll said:

 

If you can move that as far up to the cylinder top as possible and run on the electric immersion and drain down as you say maybe 20/30L to get the stat to cut in, then wait until the stat cuts out, and repeat this test say one or ideally two more times  then that will provide the info I'm after hopefully.

 

OK I had the system drained down to do so other work (it was planned for summer but well life gets in the way)

 

Work

 

1. London loop on the HW outlet of the tank (early days but it already seems to have reduced standing tank losses) 

2. Re-pipe the bypass so it's after the CH zone valve (it was before so when I restricted the flow thro the HW tank coil it opened the damn bypass and defeated my efforts to slow down the flow thro the coil!!!)

3. Combined 22mm Feed and vent for CH (removing the old 15mm feed) - Thank You @John Carroll it's solved all the issues with air ingress and got rid of another pipe in the cold loft

4. Generally remove a load of joints (from previous versions being adjusted) and clean up the lagging

5. Convert all the main rads to TBOE with Danfoss RAS-B2 flow control TRV bodies

 

Anyway  what I needed to say was

 

Immersion stat is set to 55 Deg C (well mid way between 50 and 60)

 

After heating it overshot by a large margin - Tank temp at the top was 60 deg C when it cut out

 

1 shower later and tank temp at the top was down to 50 and the immersion cut in again

 

Turned it up to 60 because bath night and top of the tank was nearly 70 when the immersion cut out 

 

She hadn't finished pouring the bath before the immersion fired up again top of the tank was reading 60

 

So I'm guessing the temp sensor is lower down the element.

 

Can't do any more tests because the system is now refilled and I'm back on gas and I've finished lagging what I call the plant room (Others might call it an Airing cupboard)

 

Plantroom.thumb.jpg.a4dd50798f63ae3e6766d2a83eb93211.jpg

 

Just to be clear - the water damage on the floor is legacy from previous occupants 

 

When I replace the tank I'm probably going to replace the floor as well because it's quite crusty

Edited by marshian
Spelling
Posted

That is a small cylinder when your used to seeing a heat pump cylinder.

 

Looks tidy. Nice insulation joints.

  • Like 1
Posted
11 hours ago, marshian said:

 

OK I had the system drained down to do so other work (it was planned for summer but well life gets in the way)

 

Work

 

1. London loop on the HW outlet of the tank (early days but it already seems to have reduced standing tank losses) 

2. Re-pipe the bypass so it's after the CH zone valve (it was before so when I restricted the flow thro the HW tank coil it opened the damn bypass and defeated my efforts to slow down the flow thro the coil!!!)

3. Combined 22mm Feed and vent for CH (removing the old 15mm feed) - Thank You @John Carroll it's solved all the issues with air ingress and got rid of another pipe in the cold loft

4. Generally remove a load of joints (from previous versions being adjusted) and clean up the lagging

5. Convert all the main rads to TBOE with Danfoss RAS-B2 flow control TRV bodies

 

Anyway  what I needed to say was

 

Immersion stat is set to 55 Deg C (well mid way between 50 and 60)

 

After heating it overshot by a large margin - Tank temp at the top was 60 deg C when it cut out

Are we talking about the twin element electric Immersion (only) here? No gas in use?.

Are you using the Sink element (short) or the Bath element (Long)

 

1 shower later and tank temp at the top was down to 50 and the immersion cut in again

 

Turned it up to 60 because bath night and top of the tank was nearly 70 when the immersion cut out 

Can you (sometime) leave the gas off and leave the immersion thermostat setting at whatever, say 60C, for a few days with the Bath (long) element only on for this period and monitor the very top of the cylinder temperature and see does it vary after after finishing reheating.

I'm (still) trying to establish if my theory (is correct) that the cylinder top temperature will only match the immersion stat setpoint when heating a "full" cylinder of cold water, I reckon, at all other times, the cylinder top temperature will be higher than the stat setpoint even with the stat working perfectly.

 

She hadn't finished pouring the bath before the immersion fired up again top of the tank was reading 60

 

So I'm guessing the temp sensor is lower down the element.

 

Can't do any more tests because the system is now refilled and I'm back on gas and I've finished lagging what I call the plant room (Others might call it an Airing cupboard)

 

Plantroom.thumb.jpg.a4dd50798f63ae3e6766d2a83eb93211.jpg

 

Just to be clear - the water damage on the floor is legacy from previous occupants 

 

When I replace the tank I'm probably going to replace the floor as well because it's quite crusty

 

Posted

Top immersion heaters are the work of the devil.  If yours has an old style thermostat without the new safety cutout trip then they work apart from eratic water temperature.

 

But when I was working I had no end of trouble with thermostat failure, and you can now only buy thermostats with the safety cut out, and they were notorious for spurious tripping when top mounted.

 

I would 100% replace the cylinder with a new one with side entry immersion heater.

Posted
2 hours ago, John Carroll said:

Are we talking about the twin element electric Immersion (only) here? No gas in use?.

 

Single element electric immersion - Gas boiler Off because system drained down

 

2 hours ago, John Carroll said:

Are you using the Sink element (short) or the Bath element (Long)

 

Hmmm it's not very long - 3KW draw - Tank capacity is about 114 Litres (guess based on our daily water usage - up to 4 showers at 30 L each one blended from 50 deg C HW temp to comfortable shower temp)

 

I can heat enough water with it for Mrs BC's bath night but I need to set it to 60 deg temp to ensure she doesn't run out of water mid pour

 

2 hours ago, John Carroll said:

Can you (sometime) leave the gas off and leave the immersion thermostat setting at whatever, say 60C, for a few days with the Bath (long) element only on for this period and monitor the very top of the cylinder temperature and see does it vary after after finishing reheating.

 

Won't be till next Spring when I do the adjustments to the heating circuit under my suspended ground floor - was on the list for this year but I've missed my window

 

2 hours ago, John Carroll said:

I'm (still) trying to establish if my theory (is correct) that the cylinder top temperature will only match the immersion stat setpoint when heating a "full" cylinder of cold water, I reckon, at all other times, the cylinder top temperature will be higher than the stat setpoint even with the stat working perfectly.

 

I think that would be the case for a side mounted immersion depending on where the temp is picked up from 

 

We only have the immersion for "emergencies" (boiler failure or replacement and when the system is drained) it's always been on a three pin plug (for 34 years!!!! - it's on the list to put it on a wall switch but I only ever thing about doing it when it gets used which isn't often - this is the second time in 12 mths)

Posted
2 hours ago, ProDave said:

Top immersion heaters are the work of the devil.  If yours has an old style thermostat without the new safety cutout trip then they work apart from eratic water temperature.

 

No idea - certainly it seems like it's got a pretty wide hysteresis judging from the overshoot

 

2 hours ago, ProDave said:

But when I was working I had no end of trouble with thermostat failure, and you can now only buy thermostats with the safety cut out, and they were notorious for spurious tripping when top mounted.

 

It's been in there since 2012 when the tank was replaced - previous tank was un-insulated copper tank with a puffer jacket that developed leaks after fitting a water softner.

 

2 hours ago, ProDave said:

I would 100% replace the cylinder with a new one with side entry immersion heater.

 

Tank replacement is on the list of things to do when I can justify the expense. 

Posted
3 hours ago, JohnMo said:

That is a small cylinder when your used to seeing a heat pump cylinder.

 

Yeah it's perfect for the two of us in a 4 bed detached - no need to worry about Legionaires when we pretty much deplete all the water every day

 

3 hours ago, JohnMo said:

Looks tidy. Nice insulation joints.

 

Thank you - It's a bit busy in there but I've tried to keep it neat - the insulation is decent Tubolit Polyethylene Pipe Insulation (not skimpy DIY store stuff) with almost identical OD for 15mm or 22mm so I have a tube mitre block set up for 30, 45 and 90 deg cuts

 

I pre-make 90 deg bends and glue them with off cuts (from the last time I did any insulation below the floor) and then I only have to fit bends and then measure the length between them and cut the lengths accordingly :D 

Posted (edited)
9 hours ago, ProDave said:

Top immersion heaters are the work of the devil.  If yours has an old style thermostat without the new safety cutout trip then they work apart from eratic water temperature.

 

But when I was working I had no end of trouble with thermostat failure, and you can now only buy thermostats with the safety cut out, and they were notorious for spurious tripping when top mounted.

 

I would 100% replace the cylinder with a new one with side entry immersion heater.

 

The devil is in the detail. They obviously don't make them like they used to. No pesky rod thermostat in mine, still working perfectly after exactly 53 years. Sink/Bath c/o switch conveniently on top of the Immersion.

Santon Immersion Nov 1972.jpg

Edited by John Carroll
  • Like 1

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...