Boiler short cycling with low flow temperatures

Featured Replies

@MrPotts

 

Is it possible to fit smaller jets to reduce boiler power? Not sure about gas boilers but that helped my oil boiler.

  • Replies 78
  • Views 14.7k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • In my conversions, the nefit opentherm ems converter works well, but when boilers are more closely matched to heat loss.   The Evohome system may be a problem here too. In this regard, I hav

  • That's to be expected. One zone and 10kW output stands no chance of running well. Putting bigger rads in, is unlikely to help if only that zone is allowed to call for heat. Would really try to get it

  • Sounds to me like the boiler isn't seeing enough flow to keep it happy in the initial purge and high output phase unless the flow temp is set high enough that it doesn't overshoot (most boilers initia

Posted Images

6 hours ago, Temp said:

@MrPotts

 

Is it possible to fit smaller jets to reduce boiler power? Not sure about gas boilers but that helped my oil boiler.

 

Nope not on a gas boiler but these days they modulate better than they did

  • Author
On 20/02/2025 at 15:11, marshian said:

 

Looks better

 

You can potentially avoid bigger rads by heating longer (ie 24/7 or with very minimal set backs outside of scheduled heating periods)

 

I was heating to a schedule and running 50 deg flow temps (at zero OAT) - to get the room up to temp within the schedule

 

Moved to 24/7 heating and I'm running 32 deg flow temps (at zero OAT)

 

Setbacks with recovery didn't seem to save any energy v a 24/7 heating period

 

Only proviso is the boiler needs to be happy at the lower flow temps

I'm going to give that a try for a few days and see what the gas consumption looks like - at the moment, it works quite hard from 4-5:30 every morning to lift the temperature, and whilst it's been around 5 degrees outside, we've been using 85kWh a day, which feels like a lot to me.

17 minutes ago, seanblee said:

I'm going to give that a try for a few days and see what the gas consumption looks like - at the moment, it works quite hard from 4-5:30 every morning to lift the temperature, and whilst it's been around 5 degrees outside, we've been using 85kWh a day, which feels like a lot to me.


if it feels like a lot it probably is but is house specific 

 

my daily for feb so far (4 bed detached heating 24/7 with room temps from 18 to 22)

 

the minus overnight temps are the peak days (70 kWh ish)IMG_5490.thumb.png.73b3b16f94e521e0484a4821fdff0a20.png

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.