marshian Posted December 24, 2024 Posted December 24, 2024 11 minutes ago, Dee said: The second image are the style I have. I'll look into those valves...thanks for a great peice of info and advice! Not a problem - you shouldn’t need diverters for those rads (OK they are column rads by name but not in the modern sense) Just for giggles this was the view into the bottom tube of the column rad in my bathroom (first picture) So poor manufacturing tolerances meant opportunity for water to go straight thro from flow in to return out rather than be forced up the columns
Dee Posted December 26, 2024 Author Posted December 26, 2024 Marshian.....so which of the 3 valves you mentioned would you use now?
marshian Posted December 26, 2024 Posted December 26, 2024 4 hours ago, Dee said: Marshian.....so which of the 3 valves you mentioned would you use now? @Dee Use the @ before a users name to tag someone (they get a notification they’ve been mentioned) and you should get a drop down to pick from If I was doing it again I would use the flow setting (auto balancing type) by either Drayton (I use Wiser TRV’s but they work also with conventional Drayton TRV’s) good explanation here or the Danfoss equivalent Either may accept your existing TRV Heads with adaptors (not sure if they are compatible or not) good explanation of the Danfoss valves here Fundamentally they both do the same thing - allow you to set up specific flow rates to individual rads that are not affected by system pressure changes (like when TRV heads start intervening in the circuit) Both types work with the lockshield valve wide open 2
MrPotts Posted December 26, 2024 Posted December 26, 2024 I think you mean valves that are affected by system pressure changes.
marshian Posted December 26, 2024 Posted December 26, 2024 4 hours ago, MrPotts said: I think you mean valves that are affected by system pressure changes. No I don't
MrPotts Posted December 27, 2024 Posted December 27, 2024 Isn’t the idea of an auto balancing valve to be setup initially based on the required flow rate and when this changes, due to other TRV’s closing, it automatically adjusts to try and maintain the flow rate.
Nickfromwales Posted December 27, 2024 Posted December 27, 2024 So……they’re not actually auto-balancing then as they each require full mechanical (human) commissioning? I’m failing to see the benefit, sorry, and think it is much easier (for a newbie in particular) to get to the best result with balancing via the existing lock shield valve. The latter is also the obvious choice in an existing install where you have the TRV’s (regular, serviceable ones) and do not want to make any changes. @Dee, best to save your pennies and do this in one hit in the summer, as suggested above. Then you can take your time.
marshian Posted December 27, 2024 Posted December 27, 2024 1 minute ago, Nickfromwales said: So……they’re not actually auto-balancing then as they each require full mechanical (human) commissioning? I’m failing to see the benefit, sorry, and think it is much easier (for a newbie in particular) to get to the best result with balancing via the existing lock shield valve. Less effort than setting up a radiator circuit from scratch - Main difference is that each one can be set up with the correct flow rate before fitting Setting up with a lock shield depends on how good (or how much valve authority) your lock shields are (or have) Precis - Some lock shields are utter garbage very few are excellent - I looked at buying the IMI ones but the EB4 bodies with 6 settings was cheaper
MrPotts Posted December 27, 2024 Posted December 27, 2024 4 hours ago, Nickfromwales said: So……they’re not actually auto-balancing then as they each require full mechanical (human) commissioning? I’m failing to see the benefit, sorry, and think it is much easier (for a newbie in particular) to get to the best result with balancing via the existing lock shield valve. The latter is also the obvious choice in an existing install where you have the TRV’s (regular, serviceable ones) and do not want to make any changes. @Dee, best to save your pennies and do this in one hit in the summer, as suggested above. Then you can take your time. You use an app which tells you what setting to use based on the size and type of radiator. 1
Dee Posted December 28, 2024 Author Posted December 28, 2024 I've calculated that it will cost £450 to change all valves and it's too costly in one hit. I'll persevere with manual balancing as too much could go wrong with my limited knowledge! Those last two rads are about 20m from the boiler and the heat/ pressure/power just doesn't seem to be enough to get there....no oomph! Someone suggested the expansion tank might be too small??
marshian Posted December 28, 2024 Posted December 28, 2024 1 hour ago, Dee said: I've calculated that it will cost £450 to change all valves and it's too costly in one hit. I'll persevere with manual balancing as too much could go wrong with my limited knowledge! Those last two rads are about 20m from the boiler and the heat/ pressure/power just doesn't seem to be enough to get there....no oomph! Someone suggested the expansion tank might be too small?? It only takes a few rads stealing a little too much flow to starve the furthest rads - benefits of those flow setting valves is that the flow is fixed at exactly what the rooms/rads need and no more. how much do you value your time? how much grief do you get for the rooms that aren’t getting warm Fully open circuit in my house and the pump is moving 0.5 m3/hr and that’s being shared out across 13 rads in a system with a total volume of 150 Litres (excluding HW)
SteamyTea Posted December 28, 2024 Posted December 28, 2024 Would a second pump, closer to where the troublesome radiators are, solve the flow problem? Pumps are cheap, and relatively easy to fit.
Dee Posted December 29, 2024 Author Posted December 29, 2024 As tempting as it is to change the valves I think it's a step too far for me to attempt and as much as I woukd like yo try its likely to cost me more when I buggar something up! I'll keep persevering with the current tedious method!
SteamyTea Posted December 29, 2024 Posted December 29, 2024 In the days of old, when we all drove BL cars, balancing a set of SU carburettors was a challenge. One way to do it was by listening down each inlet barrel and matching the pitch. I am not sure of something similar can be done with water pipes, phones have useful sound analysis software on them these day.
joe90 Posted December 29, 2024 Posted December 29, 2024 2 hours ago, Dee said: I'll keep persevering with the current tedious method! Well done, it’s amazing how little a lockshield valve needs to be open on a rad near a boiler to heat up and steal from those furthest away.
marshian Posted December 29, 2024 Posted December 29, 2024 2 minutes ago, joe90 said: Well done, it’s amazing how little a lockshield valve needs to be open on a rad near a boiler to heat up and steal from those furthest away. And that is why even though I could balance my system pretty well on cheap DIY lockshields I made the choice to invest in flow control TRV bodies or high quality lockshield valves with very linear performance characteristics because every time a TRV intervened it upset the system balance so found myself constantly tweaking and never happy The high quality lockshields were more money than the flow control TRV bodies
joe90 Posted December 29, 2024 Posted December 29, 2024 2 hours ago, Dee said: As tempting as it is to change the valves I think it's a step too far for me to attempt and as much as I woukd like yo try its likely to cost me more when I buggar something up! It’s the OP,s choice. We can only advise.
Dee Posted January 3, 2025 Author Posted January 3, 2025 I'm down to the last rad....furthest away from the boiler (by about 40 linear meters) that will not heat up. I have tweaked, cajoled, threatened and pleaded with it but it will not yield to my will. I just get the feeling there just isn't enough 'oomph' left in the pump to get there. Does it influence anything that the flow and return ftom the boiler goes to straight upto the floor void above and that the ground floor are solid. So all the pipes drop down to the rads below.
marshian Posted January 3, 2025 Posted January 3, 2025 2 hours ago, Dee said: I'm down to the last rad....furthest away from the boiler (by about 40 linear meters) that will not heat up. I have tweaked, cajoled, threatened and pleaded with it but it will not yield to my will. I just get the feeling there just isn't enough 'oomph' left in the pump to get there. Does it influence anything that the flow and return ftom the boiler goes to straight upto the floor void above and that the ground floor are solid. So all the pipes drop down to the rads below. How open is the lockshield valve on that rad? I don't think drop legs from a flow and return circuit above will make any difference but heat will always prefer to rise Ages ago I got into a discussion with a chap who had a type of reverse return circuit for flow and return in the loft of his bungalow - all the pipes dropped down from ceiling to the rads The last radiator fed with the flow was the first on the return leg really high primary balance and all the lock shields were pretty much fully open 1
Dee Posted January 4, 2025 Author Posted January 4, 2025 The return is almost fully open on Kitchen 1 rad ( the one im struggling with). I have tried every combination....shut off rad above and it gets a tad warmer, close the rad next to it ( Kit 2) and it gets a bit warmer still but not what I woukd call hot. On kit 1 the return pipe is much hotter than flow, like their reversed? Flow is about 37⁰c and return 52⁰c and both kitchen rads are vertical column type....I'm truely stumped. How critical is the order in which I balance each rad as its a big house and some rads seem to heat up very close in time so it's tricky to be sure I'm doing it in the right order.?
Dee Posted January 6, 2025 Author Posted January 6, 2025 I'm sure you've all had enough of me but I thought I would post the list of temps. The temps on all but the furthest 2 rads in order they heat up are as follows; (I put the rad temp in there for my own curiosity) Boiler Flow 60 Rtn 50 Flow Rtn Rad 54 43 45 56 45 44 38 54* 41 44 40 45 57 45 45 45 52* 46 40 55* 40 54 40 43 54 51 50 43 29 study. 30 55 43 47 55 47 49 49 39 39 57 46 46 54 46 44 49 47 44 52 47 ?? 44 41 40 51 39 39 ?? ?? ?? ?? I can't achieve 12⁰ drop on any of them Study won't heat atall and the last two (ground floor) won't heat up either. Is there a pattern here or is it as good as it gets? * Rtn hotter than TRV Thankyou as ever
marshian Posted January 6, 2025 Posted January 6, 2025 41 minutes ago, Dee said: I'm sure you've all had enough of me but I thought I would post the list of temps. The temps on all but the furthest 2 rads in order they heat up are as follows; (I put the rad temp in there for my own curiosity) Boiler Flow 60 Rtn 50 Flow Rtn Rad 54 43 45 56 45 44 38 54* 41 44 40 45 57 45 45 45 52* 46 40 55* 40 54 40 43 54 51 50 43 29 study. 30 55 43 47 55 47 49 49 39 39 57 46 46 54 46 44 49 47 44 52 47 ?? 44 41 40 51 39 39 ?? ?? ?? ?? I can't achieve 12⁰ drop on any of them Study won't heat atall and the last two (ground floor) won't heat up either. Is there a pattern here or is it as good as it gets? * Rtn hotter than TRV Thankyou as ever Lot of data there to dissect but I'm going to start with the obvious - the TRV end might not always be the flow end Example flow of two of my rads would mean the TRV would be tucked in a corner rather than in Free Air so more likely to turn the rad off before the room has reached temp so I deliberately put the TRV on the return end So I would suggest that if you have a hotter end on the lock-shield end then that is the flow end and the TRV end is the return. Second point - how are you measuring the temps (ie with what and where are you measuring on the rad) I take 3 temp readings from every rad (all my rads are BBOE rather than the more efficient TBOE) with an hand held IR 4 of my rads are anthacite the rest are white and I get better readings from the dark rads - I did put black insulation tape on some of the white ones to improve accuracy but Mrs Marshian didn't like that approach at all. Flow inlet - ie bottom of the rad where the flow pipe enters the rad Top Middle - middle of the rad at the top Return outlet - ie bottom of the rad where the return pipe leaves the rad I take 3 measurements because depending on what the TRV is doing and what the boiler is doing often the middle top is the best guide to actual flow temp (Hot water rises so often the inlet area is actually slightly cooler) If I can format the results I'll share the readings I took from earlier this evening Bear in mind (when I share the results) that this evening I was running a boiler flow temp of 32.5 Deg C and the return to the boiler was 25.0 Deg C Even when I was running scheduled heating and 55 deg flow temps I could only get a couple of rads to beat 12 Deg C drop between flow and return and they were big 1400 x 600 T22 (Double panel double convector) rads
marshian Posted January 6, 2025 Posted January 6, 2025 1 hour ago, Dee said: I'm sure you've all had enough of me but I thought I would post the list of temps. The temps on all but the furthest 2 rads in order they heat up are as follows; (I put the rad temp in there for my own curiosity) Boiler Flow 60 Rtn 50 Flow Rtn Rad 54 43 45 56 45 44 <Snip> Thankyou as ever So from left to right it's Rad Flow temp - Rad Return Temp and Rad Temp? Rather than order they heat up in which is notoriously difficult to get - could you annotate them with Upstairs or Downstairs and Label them with the room Here's what I use
marshian Posted January 6, 2025 Posted January 6, 2025 (edited) Just to clarify - the boiler was no longer on a burn when the last radiator (Lounge) Flow and Return temps were taken and that rad has the highest flow rate of all the rads at ~1.2 Litres per min so it doesn't take long for the flow side to cool quickly Also to add Everything before Bed 1 is downstairs Circuit and after Front Hall is Upstairs Circuit - the whole house is one Zone for CH Every radiator has flow restrictions in the TRV body and lockshield wide open I have a fairly good understanding of the flows to each rad Edited January 6, 2025 by marshian
marshian Posted January 6, 2025 Posted January 6, 2025 Me trying to make sense of it (It's in the same order from top to bottom but I've fixed where flow and return were wrong and worked out the DT Normally I'd say if the DT (Difference between flow and return was small there would be too much flow thro the rad but if the rad concerned is a towel rail then all bets are off because they are terrible for getting a decent drop between flow and return (they aren't much good as a heat emitter either IMO) B. Flow 60 B. Return 50 Rad Flow Rad Ret DT Rad?? Comments 54 43 11 45 56 45 11 44 54 38 16 41 44 40 4 45 What sort of Rad? 57 45 12 45 52 45 7 46 55 40 15 40 54 40 14 43 54 51 3 50 What sort of Rad? 43 29 14 30 55 43 12 47 55 47 8 49 49 39 10 39 57 46 11 46 54 46 8 44 49 47 2 44 What sort of Rad? 52 47 5 ?? What sort of Rad? 44 41 3 40 What sort of Rad? 41 39 2 39 What sort of Rad? ?? ?? ?? ??