  On 07/10/2024 at 12:36, lookseehear said:

Thermal Store for Heating and Hot Water
I'm considering installing a large thermal store (around 400-500L) to handle both heating and DHW while keeping the existing oil boiler.

Expand  

 

Fine, beware for DHW you're roughly halving the capacity of the store Vs an UVC. Eg a 500l TS will only deliver roughly half the amount of hot water a UVC will at the same temp. They work well with high temperature water supply though. I put a 250l Maxipod in my parents house. 

 

  On 07/10/2024 at 12:36, lookseehear said:

We’ll be installing solar PV, but likely without a battery for now. Excess solar energy can be diverted to the thermal store for heating and DHW

Expand  

 

Good idea. Water is a cheap battery. Beware you may not have quite enough solar in shoulder months to achieve the 60ish Degs a TS needs to work. An UVC meanwhile will work right down to 40 DEG. 

 

  On 07/10/2024 at 12:36, lookseehear said:

So, we can use cheap electricity to 'charge up' the thermal store overnight at roughly the same cost as heating with oil.

Expand  

 

Fine for DHW, however unlightly to do much for space heating. Beyond early morning. 

 

  On 07/10/2024 at 12:36, lookseehear said:
  • We plan to install large radiators or FCUs in the bedrooms and avoid UFH in areas without insulation.

  • Main Living Space
    In the upstairs living area, we’re thinking of large radiators, and perhaps plinth FCUs in the kitchen to provide an extra heating boost if needed.

  • Bedroom in New Extension
    For the new extension, we’ll install wet UFH. However, instead of embedding it in screed, we might use an overlay system on top of a well-insulated slab. This would allow the room to cool overnight and heat up quickly when needed, making the UFH act more like a radiator - any pros/cons here?

  • Bathrooms
    We have two downstairs bathrooms (en-suite and main bathroom) in the older part of the house. I’d like to install UFH for extra comfort underfoot.
    With 100mm of PIR insulation and 50mm of screed, head height shouldn't be too compromised. A wet overlay system over 100mm PIR might be the best option here.

Expand  

 

Rads everywhere. As large as you can fit. Simple cheap, all on the same zone. 

 

Put electric UFH mats in the bathroom on a timer for comfort. 

 

In my parents house the solid fuel cooker will often get the store to 70ish Deg + after which the rads will kick in to dissipate the excess heat. They'll be running at maybe 30deg which is far more comfortable than the regular "hot" rads you get. My point being, if you oversize your rads and run them at a low flow temperature then you'll have lots of the benefits of UFH without the complexity of integrating a new and old system. 

 

  On 07/10/2024 at 12:36, lookseehear said:

External Insulation: I’m tempted to install 150mm of EPS around the foundation downstand (about 600mm deep) to reduce heat loss through the floors over time. This wouldn’t go around the entire property but could cover about 50%.

Expand  

 

Good plan. If you were just to add 10mm of PIR under the floor though it'd make a world of difference. I did a thermal model here for someone ages ago. 

 

There's no mystery with internal insulation. Just make sure it can "DRY" more than it gets "WET". 

 

1. Eliminate bulk water. Gutters, chutes , drains leaks driven rain etc. 

 

2. Regulate internal humidity with mechanical ventilation. MVHR DCV and PIV is the hierarchy. 

 

3. Don't build layers in manner that will trap moisture with materials of very low permeability, PIR, foil, polythene etc.

 

4. Stop air taking internal moisture where it should go via air leaks. 

 

Lime and hemp is good, but over sold IMO. A mild sand cement wall parge and tapes to the windows and floor for Airtightness. A battened layer of mineral wool for insulation and plasterboard would be fine. Airtighess is the key here. 

 

 

 

 

 

 

 

  • Thanks 1
Posted

Your wife is very very right. 

 

It's a house not a branch of currys. nothing more frustrating than being unable to work the controls. It's more expensive, more lightly to break etc. 

 

Single zone heating on a timer or single thermostat. All rads no plinth heaters or fan coils or UFH.  

 

UVC for DHW only. No messing with banking heat for space heating. It doesn't really work unless you have thousands of litres. 

 

dMEV to every wet room.

 

Electric UFH in bathrooms on a switch or timer. 

 

Fastidious attention to Airtightness. 

 

As much insulation as you can fit. 

 

As much PV as you can fit. 

 

No home automation or connected nonsense. It's out of date as soon as it's installed and everyone who is not Geek hates it. 

 

 

  • Like 1
Posted
  On 08/10/2024 at 13:00, Iceverge said:

UVC for DHW only. No messing with banking heat for space heating. It doesn't really work unless you have thousands of litres. 

Expand  

Yup. For heating, via thermal storage, you can directly heat the circulating water with a big immersion and use that to bolster/reduce oil consumption (basically by it being seen as an electrical inline heater of sorts), and that will have some benefit of introducing cheap there direct electricity to space heating, but for a domestic heating scenario in a poorly insulated 2-storey home the least capacity TS I’ve installed for bulk stowage is 2600L. That was storing at 85°C to be anywhere close to being useful/effective and to have sufficient sustain.

A 300-500L storage tank heated to 85°C would be drained to a useless temp in an hour or two. 

Posted
  On 08/10/2024 at 13:59, Nickfromwales said:

A 300-500L storage tank heated to 85°C would be drained to a useless temp in an hour or two. 

Expand  

 

Yes. We have a very specific use case which is heating the bedroom rads at 0700, so before we get up but after the end of the cheap rate, the 270 litres was calculated with just that in mind.

 

The plan was to do the same before we go to bed, but now that Cosy has an extra cheap window 2200 - 2400 we don't need it so it can be re-purposed for living room rads over the 1600 - 1900 peak.

 

I think part of the OP's plan was to use the TS as somewhere to amalgamate all the various sources of heat, it is still valid for that. And also to prevent the oil boiler short cycling though I would question whether that is really necessary, ours used to fire 3 or 4 times an hour for 5-10 mins, I don't think they mind that unlike a HP. But unless a proper condensing type they object to low flow temps as any condensate will then rot the flue.

Posted
  On 08/10/2024 at 12:17, lookseehear said:

I love this! I can have a look back through your posts to see if there's anything relevant, but I'd love to hear in particular why you decided on hempcrete vs another type of insulation for the solid walls.

Expand  

 

There isn't much on here that I've posted, just a thread about TS v UVC and a thread about what to do about old stone walls and IWI. I'm not going to go the whole hog on IWI just something to help raise the temperature, a bit, of the surface of the old stone walls.

 

 

Posted
  On 08/10/2024 at 14:34, sharpener said:

And also to prevent the oil boiler short cycling though I would question whether that is really necessary, ours used to fire 3 or 4 times an hour for 5-10 mins, I don't think they mind that unlike a HP

Expand  

So say it's 3 times an hour for 5 minutes, that would be a duty cycle of 25% On, with an On time of 5 minutes.  Why do you think a heat pump would mind that?  

Posted
  On 08/10/2024 at 18:45, ReedRichards said:

On time of 5 minutes.  Why do you think a heat pump would mind that?  

Expand  

My heat pump instructions state

 

The choice of regulation is fundamental to optimise the efficiency of the system and to reduce the number of starts/hour in order to achieve the correct thermodynamic balance and the correct lubrication of the mechanical parts in the compressor, it is recommended to choose them in order to have a continuous operation of the heat pump of at least 10 minutes.

 

Found with mine, running less than about 10 minutes, result in the best part of no heat being added to the house. So it is now set to run no less than about 15 minutes.

 

Short running is likely to use lots of energy and not do much heating of the house. Especially when the heat source is located outside.

Posted
  On 08/10/2024 at 20:49, JohnMo said:

Short running is likely to use lots of energy and not do much heating of the house. Especially when the heat source is located outside.

Expand  

That sounds a bit non-physical.  If you are using lots of energy then you must be heating something, even if it's with a COP of near-one.  And if it's not inside then it must be outside.  If it's outside, as you seem to think then what is happening?  Is some motor inside the heat pump getting very hot?  Do those mechanical parts inside the compressor need more lubricant?  Your symptoms "best part of no heat added to the house" sound more like a fault than regular behaviour.

Posted
  On 09/10/2024 at 07:14, ReedRichards said:

That sounds a bit non-physical.  If you are using lots of energy then you must be heating something, even if it's with a COP of near-one.  And if it's not inside then it must be outside.  If it's outside, as you seem to think then what is happening?  Is some motor inside the heat pump getting very hot?  Do those mechanical parts inside the compressor need more lubricant?  Your symptoms "best part of no heat added to the house" sound more like a fault than regular behaviour.

Expand  

I have zero issues with the heat pump. A heat pump behaviour is different to a boiler, its output is a lot different. Most heat pumps are sub 10kW, most oil boilers are 4x the output.

 

You don't have lots of energy, a 6kW heat pump running at full load for 10 mins generates a max 1kWh of heat. Getting 60L of water from 21 deg to 28 is 0.5kWh, plus heating a bunch of pipes, a heat exchanger etc. That 1kWh is very quickly consumed, before any real useful work is done.

 

So a typical heat pump running for 10 mins looks like this

image.thumb.png.7a3192025d0c78798cabfb8791710560.png

Key points are

Compressor starts at 22.5 degs return temp

At 10 mins the flow temp has increased to 28.6 degs and return temp is up to 24.8 deg.

Actual heat output after 10 mins is only 0.852kWh, so basically heating the system, and not much heat is going into the house.

 

 

Posted
  On 09/10/2024 at 09:11, JohnMo said:

Actual heat output after 10 mins is only 0.852kWh, so basically heating the system, and not much heat is going into the house.

Expand  

 That's good data.  But after 10 minutes you have now warmed up all the water inside your house to 26.7 C average.  So even if everything was turned off at that point you would still have heat going into the house; that doesn't stop.  You will still derive benefit from all parts of the heated system that are inside the insulated fabric of the building; that energy spent heating the system was not wasted, as you seem to imply.

Posted
  On 09/10/2024 at 12:06, ReedRichards said:

You will still derive benefit from all parts of the heated system that are inside the insulated fabric of the building; that energy spent heating the system was not wasted, as you seem to imply.

Expand  

Not saying it's wasted, but it not enough to be properly useful. It better to have a slightly longer run, the remainder run time is all useful heat. Its getting the correct balance between heating stuff up and heating heating stuff up and adding heat to the house

 

a few runs at similar average outside temps, only change from first and send two runs was a slight change to compressor stop hysteresis to get a longer run. The compressor start hysteresis remained the same

 

7.8 deg OAT, short runs (10 to 15 mins duration), 9.1kWh electric 44.2kWh heat delivered - short runs (space heat CoP 4.86)

7.5 deg OAT, longer runs runs (15 mins plus duration), 5.7kWh electric 27.8kWh heat delivered - longer runs (space heat CoP 4.89)

slightly colder day at 6.8 deg OAT, again longer (35 mins plus duration) runs, 6.8kWh electric 33.8kWh heat delivered - longer runs (space heat CoP 4.97)

 

On all occasions above is run full WC mode, house remains at a stable 20.5 degs. Difference between 7.8 and 7.5 deg day is a reduction of 40% electrical use. Which is huge. CoP stays similar, CoP increase on the 6.8 deg day, is due to slightly cooler day leading to longer run times and less standby time.

 

As point to note I did find similar reductions in energy use when I optimised the gas boiler when running very low flow temps, once I added the heat meter and started to understand what was happening.

 

 

  • 2 weeks later...
Posted
  On 08/10/2024 at 12:52, Iceverge said:

Rads everywhere. As large as you can fit. Simple cheap, all on the same zone. 

Expand  

 

Let's just say for a minute that I don't want huge radiators in all the bedrooms, what would the next best option be? How oversized is oversize? While space isn't massively at a premium, I feel that placement is incredibly important if you're putting in oversized rads so as not to be in the way of furniture.

 

  On 08/10/2024 at 12:52, Iceverge said:

Put electric UFH mats in the bathroom on a timer for comfort. 

Expand  

 

My brother in law and my in-laws have this, and both have said that it doesn't work as well as they'd hoped. If you don't have a regular daily routine (our weeks can be quite varied) then a timer doesn't work, and I'm imagining that it's slow to heat up and expensive to run. What's the real life experience like of using these?

  On 08/10/2024 at 12:52, Iceverge said:

Good plan. If you were just to add 10mm of PIR under the floor though it'd make a world of difference. I did a thermal model here for someone ages ago. 

Expand  

 

I like this idea - I'll try and factor this in.

 

  On 08/10/2024 at 12:52, Iceverge said:

A mild sand cement wall parge and tapes to the windows and floor for Airtightness. A battened layer of mineral wool for insulation and plasterboard would be fine. Airtighess is the key here

Expand  

 

Can you explain in a little more detail? By parge do you mean brushed on? Do you then mean battens screwed directly to the wall, with mineral wool filling the whole gap between wall and plasterboard? If the airtight layer is the parge coat, doesn't this risk condensation behind the plasterboard on the wall?

 

If walls are already plastered and in a good state of repair I assume battens directly to this, mineral wool fill and regular plasterboard on top? This would be cheap and easy. Any issues with the original walls being painted (from a breathability perspective)?

 

Thanks for all the advice so far.

  • 1 month later...
Posted

I'm coming back to this thread after some time thinking and my current plan is a hybrid (with an eye on simplicity and flexibility):

  • Focus on insulation and airtightness, to the point where it makes sense to have MVHR
  • Put in an air to air heat pump for the main living space which is upstairs. We'll be spending 80+% of our time in there when at home and not working or asleep. It's ~65m2 living/kitchen/dining space with vaulted ceilings albeit only 3m to the ridge beam. MVHR will be continuously moving the warm air to other living spaces, so it might make sense to oversize this somewhat. Given this space is upstairs I'm very keen to have some active cooling which is a big benefit of the a2a HP. I think just using the a2a with MVHR will suffice for 75%+ of the year as the main heating and cooling of the house.
  • Retain our oil boiler and unvented cylinder, and use this as top-up heating in the winter and for DHW when there's not enough solar PV
  • Electric UFH mats/towel rails in bathrooms for comfort

The benefits of this are:

  • It's relatively simple - we'll set the temperature on the a2a in the living space, and the rest of the house will likely be a couple of degrees cooler
  • it's flexible - as much heat as we need in the winter and cooling in the summer.
  • we'll drastically reduce the amount of oil we use
  • we don't need to oversize radiators significantly - oil boilers don't appear to benefit from low flow temperatures as much as gas boilers and they will only be used to top up the heat as required.
Posted (edited)
  On 10/12/2024 at 14:23, lookseehear said:

oil boilers don't appear to benefit from low flow temperatures as much as gas boilers

Expand  

 

I think it's more a question that unless a recent model and specially designed for it you shouldn't run them in condensing mode as the combustion products (?oxides of sulphur?) in solution will rot the heat exchanger and flue.

We used to have a Kidd oil boiler and despite the min thermostat setting being 65 and it only condensing at start-up the aluminium condensate tray in the economiser section had to be replaced twice (albeit in 29 years), all the other "permanent" parts were fine.

Edited by sharpener
Posted
  On 10/12/2024 at 14:23, lookseehear said:

MVHR will be continuously moving the warm air to other living spaces

Expand  

If you have read that somewhere, they generally don't move heat about, the flow rates are too low. Oversizing to do that makes no sense, as although they recover heat, its not 100% efficient, so you are actually pumping out more heat than you should.

 

MVHR is ventilation, not heating or a make shift heat mover.

 

 

Posted
  On 10/12/2024 at 14:49, sharpener said:

 

I think it's more a question that unless a recent model and specially designed for it you shouldn't run them in condensing mode as the combustion products (?oxides of sulphur?) in solution will rot the heat exchanger and flue.

We used to have a Kidd oil boiler and despite the min thermostat setting being 65 and it only condensing at start-up the aluminium condensate tray in the economiser section had to be replaced twice (albeit in 29 years), all the other "permanent" parts were fine.

Expand  

 

Our oil boiler is only 3 years old (a Worcester Bosch external model) so I assume it is relatively efficient (as oil boilers go) but it is probably oversized (18-25kW). I didn't know about avoiding running them in condensing mode but I'll definitely be looking it up.

Posted
  On 10/12/2024 at 15:00, JohnMo said:

If you have read that somewhere, they generally don't move heat about, the flow rates are too low. Oversizing to do that makes no sense, as although they recover heat, its not 100% efficient, so you are actually pumping out more heat than you should.

 

MVHR is ventilation, not heating or a make shift heat mover.

Expand  

 

I agree, but if you take an example where you have 21 degree warm air (could be warmer than this when extracted close to the ridge of the vaulted ceiling) and 8 degree fresh air incoming, with 80% efficiency then you could reasonably expect the air being pushed to living spaces being above above 18 degrees (18.4 degrees would be 80% efficiency assuming it's linear). Bear in mind that we currently tend to have bedrooms at 17 degrees around the clock currently.

 

I'm not expecting it to 'heat' the rooms but to reduce the number of days we use the oil boiler by making those rooms more comfortable during the milder months in spring and autumn.

Posted
  On 10/12/2024 at 17:45, lookseehear said:

I'm not expecting it to 'heat' the rooms

Expand  

I am having a bad day with lightbulbs on my car, so let me relax and do a bit of arithmetic.

 

A cubic meter of air has a density of around 1.25 kg.m-3 and a specific heat capacity of 1 kJ.kg-1.K-1.

So a m3 takes 1.25 kJ of energy to be raised by 1K or °C.  That is 0.00035 kWh.

I would think that the fan moving the air would use that much energy.

 

 

Posted
  On 10/12/2024 at 18:21, SteamyTea said:

I am having a bad day with lightbulbs on my car, so let me relax and do a bit of arithmetic.

 

A cubic meter of air has a density of around 1.25 kg.m-3 and a specific heat capacity of 1 kJ.kg-1.K-1.

So a m3 takes 1.25 kJ of energy to be raised by 1K or °C.  That is 0.00035 kWh.

I would think that the fan moving the air would use that much energy.

 

 

Expand  

 

It took me a minute to see what you're getting at - I guess I didn't quite realise how low the air flow rates of MVHR systems are, but at 20-30m3/hr to a typical living space there's not really much 'redistribution' of heat going on other than keeping it within the overall thermal envelope.

 

I probably need to take a serious look at the cost and disruption of ducted MVHR vs decentralised systems with heat recovery because I had assumed one of the benefits of a centralised system is that you are putting warmer air back into living spaces.

Posted
  On 10/12/2024 at 20:02, lookseehear said:

didn't quite realise how low the air flow rates of MVHR systems are

Expand  

Less than half the volume of the house an hour, all very slow.

 

  On 10/12/2024 at 20:02, lookseehear said:

need to take a serious look at the cost and disruption of ducted MVHR vs decentralised systems

Expand  

I would really consider dMEV.

 

Greenwood CV3 or CV2, they will only do background ventilation unless needed. They are silent out the box. One in each wet room (including kitchen). No trickle vents in wet rooms. Trickle vents in dry rooms with humidity activated vent control. Undercut all doors for easy cross flow with doors closed. 4 fans cost about £4 year to run.

 

You only have enough ventilation, not over or under vented. No ducts, no filters.

  • Thanks 1
Posted
  On 10/12/2024 at 20:14, JohnMo said:

Trickle vents in dry rooms with humidity activated vent control

Expand  

 

Are these common? Do I just ask the window manufacturer for them? Not sure I follow how this works - lets say I get in the shower with the door closed (as you do) therefore the fan in the 'wet' room ramps up to maximum, but the 'dry' rooms are still dry meaning trickle vents will be closed. Where is the air coming from in this instance? Our kitchen/diner/living space is quite large (65m2) - would you put two in?

 

I'm pretty sold on this I think. It does seem a shame though when you have lovely warm air after a shower only to dump it all outside!

Posted
  On 23/10/2024 at 23:39, lookseehear said:

Can you explain in a little more detail? By parge do you mean brushed on? Do you then mean battens screwed directly to the wall, with mineral wool filling the whole gap between wall and plasterboard? If the airtight layer is the parge coat, doesn't this risk condensation behind the plasterboard on the wall?

Expand  

 

I made a poor quality video trying to explain this. 

 

 

  • Thanks 1
Posted
  On 10/12/2024 at 21:09, lookseehear said:

Where is the air coming from in this instance?

Expand  

 

We had an air change rate of 0.31 ACH and yet the calculated equivilant leaky hole in the house was still 49cm2, plenty to keep a bathroom fan satisfied. 

 

Believe me the air will come from somewhere in an old house. 

Posted
  On 10/12/2024 at 21:09, lookseehear said:

Are these common? Do I just ask the window manufacturer for them?

Expand  

You may get a blank look from the window people, they are generally clueless.

 

Do a Google search on here and you will find a few people using different ones.

 

We have MVHR it has humidity sensing and boosts as needed. No idea when it last boosted, fairly steady temps and continuously running ventilation is key. Once the house settles down the background ventilation is mostly all that's needed.

  On 10/12/2024 at 21:09, lookseehear said:

but the 'dry' rooms are still dry meaning trickle vents will be closed

Expand  

No really correct they are always partly open so room always gets some ventilation.

 

  On 10/12/2024 at 21:09, lookseehear said:

kitchen/diner/living space is quite large (65m2) - would you put two in?

Expand  

No, size is irrelevant really it's the usage, it's there for background ventilation. You will have your cooker hood as well.

 

 

  • Thanks 1