marshian Posted 11 hours ago Author Posted 11 hours ago (edited) 15 minutes ago, John Carroll said: Even though the targettemp is remotely (weather compensated) set and presumably not jumping around, can/have you set the targettemp manually high enough to ensure the heat demand is slightly higher than the boiler's minimum output to prevent burner cut out and recycling and see does the boiler behave under these conditions, if not, then. IMO, a boiler control problem?. Can you post any trends? I tried that Weather compensation off, No Range Rating, Running a Fixed Target Flow Temp of 27 Deg C. 9.7 Deg Outside Air Temp 00:00:00 to 00:01:10 Start up and modulate down (missed initial start) Flow temp 29.1 00:01:10 to 00:03:33 Boiler modulated to min flow temp 29.1 00:03:34 Boiler ramps up to 24.8% flow temp increases to 32.1 00:05:44 Boiler starts to ramp down to 20.4% flow temp drops from 31.6 to 30.9 00:07:59 Modulation drops to 15.5% and flow temp drops to 30.4 00:08:41 Showing that the boiler has not been range rated by increasing the flow temp to 43 Deg C - Boiler ramps up rapidly to 44.2% 00:09:37 Reducing the flow temp back to 27 showing the boiler modulate down to 10.6% flow temp drops to 29.7 00:11:00 to 00:18:03 Boiler running at min modulation flow temps gradually rise from 29.7 to 31.2 Deg C 00:18:08 Settings review 00:18:33 Boiler ramps up to 15.5% flow temp rises to 31.7 00:19:39 Boiler flow temp risen to 32.7 00:20:30 Modulates down to 10.8% flow temp drops to 32.2 00:23:53 Flow temp 31.7 Modulation 10.8% 00:28:18 Boiler shuts down Edited 11 hours ago by marshian formatting mistakes
John Carroll Posted 10 hours ago Posted 10 hours ago If the heat demand is/was steady and if the boiler is not at minimum modulation then one might expect a very low target/flow temp dT of max 1 or 2C, I've often looked my daughter's Vokera and its almost allways spot on, biggest dT I've ever seen is 1C. Also, when you were decreasing the targettemp back down to 27C, (from 43C) were you keeping the dT < 5C while adjusting, otherwise the burner should have tripped?.
marshian Posted 9 hours ago Author Posted 9 hours ago 34 minutes ago, John Carroll said: If the heat demand is/was steady and if the boiler is not at minimum modulation then one might expect a very low target/flow temp dT of max 1 or 2C, I've often looked my daughter's Vokera and its almost allways spot on, biggest dT I've ever seen is 1C. Also, when you were decreasing the targettemp back down to 27C, (from 43C) were you keeping the dT < 5C while adjusting, otherwise the burner should have tripped?. No facility to adjust the DT at the boiler - in steady state running it's 5.9 Deg C (Difference between flow and return) When I demonstrated that the boiler wasn't range rated the DT obviously widened because the return temp would not have changed whilst the flow temp ramped up The target temp I changed was the boiler target flow temp so it wouldn't have tripped out on the way up - on the way down it's a possibility hence why it was a short burst up and quick reduce back down - the return temp being stable soon dragged the flow temp down to close to target once the boiler had modulated back down I hope that makes sense 1
marshian Posted 9 hours ago Author Posted 9 hours ago I'm sure I've stated this before but the window where this happens is between 5 deg C OAT and 10 Deg C OAT when running on Weather comp I occasionally see it when there is a big swing in OAT outside that window but under normal circumstances below 5 Deg OAT and above 10 Deg C it's rock solid behave totally normally - Fire up - initial purge at 50% modulation, ramp down to min 10.6 - 10.8% and then steady state running until over temp by 5 Deg.
John Carroll Posted 9 hours ago Posted 9 hours ago 10 minutes ago, marshian said: I'm sure I've stated this before but the window where this happens is between 5 deg C OAT and 10 Deg C OAT when running on Weather comp I occasionally see it when there is a big swing in OAT outside that window but under normal circumstances below 5 Deg OAT and above 10 Deg C it's rock solid behave totally normally - Fire up - initial purge at 50% modulation, ramp down to min 10.6 - 10.8% and then steady state running until over temp by 5 Deg. But if you have steady state running and the target/flow dT increases to 5C can only mean that the heat demand is lower than the boiler minimum output?
marshian Posted 8 hours ago Author Posted 8 hours ago 22 minutes ago, John Carroll said: But if you have steady state running and the target/flow dT increases to 5C can only mean that the heat demand is lower than the boiler minimum output? Maybe I'm not explaining myself very well DT between Flow and Return at the boiler is 5.9 Deg C Initially before the start the DT is 0 When the boiler fires up the DT is slightly larger as it throws 58% of max at the circuit Once it's modulated down to Min the DT stabilises and runs at 5.9 Deg C The house circuit is ~130 Litres in total and the flow thro the circuit is being pumped at 0.6 m3/Hr (10 Litres/Min) so if the rads can't get rid of all the heat then there will be some rise in the return temp. This causes the flow temp to increase because the boiler cannot modulate down any lower. During the cycle the DT remains at 5.9 Deg C until the temp limit is reached when the boiler shuts down The boiler doesn't measure the return temp - it measures just two things Flow temp (at the Hex and at the outlet - Why both I don't know but it does) and the temp of the Flue Gas
John Carroll Posted 8 hours ago Posted 8 hours ago 20 minutes ago, marshian said: Maybe I'm not explaining myself very well DT between Flow and Return at the boiler is 5.9 Deg C Initially before the start the DT is 0 When the boiler fires up the DT is slightly larger as it throws 58% of max at the circuit Once it's modulated down to Min the DT stabilises and runs at 5.9 Deg C The house circuit is ~130 Litres in total and the flow thro the circuit is being pumped at 0.6 m3/Hr (10 Litres/Min) so if the rads can't get rid of all the heat then there will be some rise in the return temp. This causes the flow temp to increase because the boiler cannot modulate down any lower. During the cycle the DT remains at 5.9 Deg C until the temp limit is reached when the boiler shuts down The boiler doesn't measure the return temp - it measures just two things Flow temp (at the Hex and at the outlet - Why both I don't know but it does) and the temp of the Flue Gas My understanding of boiler controls then is fairly radically different to the above, my understanding is that the boiler looks at the difference between the target flow temp and the actual flow temp, if the flow temp is < the target temp then the boiler will eventually fire flat out until the flow temp is the same as the target temp or slightly exceeds it, the boiler will then modulate down until the target flow temp and the actual flow temp are almost exactly the same, if the heat demand is < the minimum boiler output then the boier return temp will start increasing which in turn means that the flow temperature will increase until eventually it may exceed the target flow temp by 5C, the burner will then trip, the circ ump will continue to run and the burner will then refire when tha anticycle time has elapsed. Boilers like the Valliant do have return temperature monitoring and if the DT between the flow and return temps exceeds something like 27C/30C will pause the increase in modulation or take some action like this until the dT decreases, their fairly recent system boilers have various pump settings, one of which allows you to set the flow/return dT between 10C and 20C, it achieves this by changing the pump speed which changes the circulation flwrate but does not interfere with the target flow templ/actual flow temp control.
marshian Posted 7 hours ago Author Posted 7 hours ago 5 minutes ago, John Carroll said: My understanding of boiler controls then is fairly radically different to the above, my understanding is that the boiler looks at the difference between the target flow temp and the actual flow temp, if the flow temp is < the target temp then the boiler will eventually fire flat out until the flow temp is the same as the target temp or slightly exceeds it, Yep it does all that (unless range rated in which case it can only fire at maximum range rated setting) NB only applies once out of the initial fire up and ramp down 5 minutes ago, John Carroll said: if the heat demand is < the minimum boiler output then the boier return temp will start increasing which in turn means that the flow temperature will increase until eventually it may exceed the target flow temp by 5C, the burner will then trip, the circ ump will continue to run and the burner will then refire when tha anticycle time has elapsed. No anticycle that I am aware of - my monitoring indicates that the boiler re-fires based on flow temp being target - X Degs (It does vary depending on target Flow temp) - I'll post a table at the end 5 minutes ago, John Carroll said: Boilers like the Valliant do have return temperature monitoring and if the DT between the flow and return temps exceeds something like 27C/30C will pause the increase in modulation or take some action like this until the dT decreases, Very familiar with all the above - Had a glow worm before that did the same thing (although that had anticycle paramerters that could be tweaked) 5 minutes ago, John Carroll said: their fairly recent system boilers have various pump settings, one of which allows you to set the flow/return dT between 10C and 20C, it achieves this by changing the pump speed which changes the circulation flwrate but does not interfere with the target flow templ/actual flow temp control. The viessmann doesn't have that flexibility - very few parameters that you can play with Basically "Viessmann technical" are saying the behaviour is normal for a heat only boiler where the boiler has no control of the pump. Table of start temp and shut down temp based on WC settings
John Carroll Posted 5 hours ago Posted 5 hours ago (edited) At a OAT of 10C the Targettemp is 23C, the end temp is 29.5C, TT+ 6.5C At a OAT 0f 2C the Targettemp is 31C, the end temp is 32.7C, TT+ 1.7C At a OAT of 10C the burner shuts down at TT+6.5C, is this because its exceeded TT+5C? At a OAT of 2C the burner shuts down at TT+1.7C, why? Does the boiler (FT)ever run at the the TT??. Edited 5 hours ago by John Carroll
marshian Posted 5 hours ago Author Posted 5 hours ago 11 minutes ago, John Carroll said: At a OAT of 10C the Targettemp is 23C, the end temp is 29.5C, TT+ 6.5C At a OAT 0f 2C the Targettemp is 31C, the end temp is 32.7C, TT+ 1.7C At a OAT of 10C the burner shuts down at TT+6.5C, is this because its exceeded TT+5C? At a OAT of 2C the burner shuts down at TT+1.7C, why? Does the boiler (FT)ever run at the the TT??. I think that the start up and shut down signal temps are different as OAT changes. From collected data anyway (and it's remarkably repeatable - those aren't just one occasion but the average of multiple occasions) Yes the boiler FT does run at the target temp until it no longer can due to influence from the return temp creeping up The boiler ran for nearly 10 hrs sold when we had minus temps here in Feb 1
SimonD Posted 3 hours ago Posted 3 hours ago 3 hours ago, marshian said: Basically "Viessmann technical" are saying the behaviour is normal for a heat only boiler where the boiler has no control of the pump. Yes, the Viessmann heat only boilers are a completely different beast compared to the system boilers - no opentherm/room compensation available. Even on the system versions of the 100-W return temperature is not available to Opentherm - or at least not some Opentherm controllers where you can interrogate what information is available for control. Whether it is available to Viessmann ones would be interesting to check.