marshian Posted March 7 Author Posted March 7 26 minutes ago, John Carroll said: Wonder was it cycling due to the minimum boiler output being more than the rad demand or due to a roomstat switching it off when room temperature reached its SP. Former yes - Latter no TRV don’t intervene on majority of rooms - WC flow temp and elevated room targets that cannot be hit with WC flow temp and heat loss of the rooms. So cycling was down to the house/rads not getting rid of the energy in the circuit. was first warm night 8.5 deg C so boiler flow temp would have been 26-27 deg C max and heat loss of the house maybe around 1.6 kWh (so on that basis I’d expect the boiler to fire for 15mins in the hour minus temps over night and it’s firing 45 mins in the hour the 9 cycles might be a one off or I may need to tweak the curve a bit more to align (lower) the flow temps at higher OAT
John Carroll Posted March 7 Posted March 7 1 hour ago, marshian said: Former yes - Latter no TRV don’t intervene on majority of rooms - WC flow temp and elevated room targets that cannot be hit with WC flow temp and heat loss of the rooms. So cycling was down to the house/rads not getting rid of the energy in the circuit. was first warm night 8.5 deg C so boiler flow temp would have been 26-27 deg C max and heat loss of the house maybe around 1.6 kWh (so on that basis I’d expect the boiler to fire for 15mins in the hour minus temps over night and it’s firing 45 mins in the hour the 9 cycles might be a one off or I may need to tweak the curve a bit more to align (lower) the flow temps at higher OAT Do you know the total T50 rated output of those 9 rads and what room/house temp you are aiming for.
marshian Posted March 7 Author Posted March 7 (edited) 26 minutes ago, John Carroll said: Do you know the total T50 rated output of those 9 rads and what room/house temp you are aiming for. Yes I do - actually every damn rad dimensions and T50 output is in a spreadsheet I used it when I was working with the heat loss v rad output at various flow temps to work out where I needed to target the flow temp for the weather compensation at -2.4 Deg OAT Some of the individual rads I've tweaked the flow rates from where it was but overall system balance has remained the same. Front Hall, Toilet, Utility and Study remain on scheduled heating (heat loos of those rooms is a lot more because 3 external walls all on north facing side of the house All other rooms 24/7 Heat loss is overstated due to the software wanting higher ACH than I was comfortable with..... I also utterly badgered the dining room calc gave it a vaulted ceiling with no heated room above - Ooops True heat loss is absolute max 4.0kWh at -2.4 Deg C OAT (probably 3.6 kWh based on actual energy used if my monitoring is more accurate) Rooms & Rads.xlsx Edited March 7 by marshian Forgot target room temps
John Carroll Posted March 7 Posted March 7 I just used 12 rads output (ignored the ones in yellow) and calculated for a 9 rad output, I reckon that the 12 rads have a total T50 rating of ~ 17.6kW so 9 rads = 13.21kW (T50), the required max output seems to be ~ 4.77kW for those 12 rads = ~ 3.58kW for 9 rads. The required flowrate (for 9 rads) is ~ 0.475m3/hr, this then results in flowtemp/returntemp/dT/rads output. 41.55C/35.1C/6.48C/3.58kW At a (your) flowrate of 0.4m3/hr and flowtemp of 28.9C gives (my calcs) flowtemp/returntemp/dT/rads output. 28.9C/26.42C/2.48C/1.15kW Your data gave a calculated flowrate of only 0.06m3/hr (15% of 0.4m3/hr) flowtemp/returntemp/dT/rads output. 28.9C/20.4C/8.5C/0.6kW clearly something amiss somewhere? WC Rooms & Rads Mars Rev1.xlsx
marshian Posted March 11 Author Posted March 11 On 07/03/2025 at 20:45, John Carroll said: I just used 12 rads output (ignored the ones in yellow) and calculated for a 9 rad output, I reckon that the 12 rads have a total T50 rating of ~ 17.6kW so 9 rads = 13.21kW (T50), the required max output seems to be ~ 4.77kW for those 12 rads = ~ 3.58kW for 9 rads. Wrote a long reply and for some reason the forum or I had a blip and it never posted.......... Rooms/areas highlighted in are the hallway, stairwell and upstairs landings - they are all supplied by one ground floor rad I've amended the file to clarify which rads are 24/7 and which rads are scheduled (so only heated when needed) Rooms & Rads.xlsx On 07/03/2025 at 20:45, John Carroll said: The required flowrate (for 9 rads) is ~ 0.475m3/hr, this then results in flowtemp/returntemp/dT/rads output. 41.55C/35.1C/6.48C/3.58kW At a (your) flowrate of 0.4m3/hr and flowtemp of 28.9C gives (my calcs) flowtemp/returntemp/dT/rads output. 28.9C/26.42C/2.48C/1.15kW Your data gave a calculated flowrate of only 0.06m3/hr (15% of 0.4m3/hr) flowtemp/returntemp/dT/rads output. 28.9C/20.4C/8.5C/0.6kW clearly something amiss somewhere Well I'm not following that and I need to get my head round it One thing I have noticed is on PP3/6 the m3/hr number varies a lot - can be as low as 0.3 m3/hr to as much as 0.6 m3/hr which is also confusing me!!
John Carroll Posted March 11 Posted March 11 1 hour ago, marshian said: Wrote a long reply and for some reason the forum or I had a blip and it never posted.......... Rooms/areas highlighted in are the hallway, stairwell and upstairs landings - they are all supplied by one ground floor rad I've amended the file to clarify which rads are 24/7 and which rads are scheduled (so only heated when needed) Rooms & Rads.xlsx 12.37 kB · 1 download Well I'm not following that and I need to get my head round it One thing I have noticed is on PP3/6 the m3/hr number varies a lot - can be as low as 0.3 m3/hr to as much as 0.6 m3/hr which is also confusing me!! Will get back re rad outputs later. Re the pump, Are you saying that PP3 gives a flowrate of 0.3m3/hr and PP6 gives a flowrate of 0.6m3/hr? or, is the flowrate fluctuating while the setting is set on any one of the PP3 to PP6 settings?
marshian Posted March 11 Author Posted March 11 50 minutes ago, John Carroll said: Will get back re rad outputs later. Re the pump, Are you saying that PP3 gives a flowrate of 0.3m3/hr and PP6 gives a flowrate of 0.6m3/hr? or, is the flowrate fluctuating while the setting is set on any one of the PP3 to PP6 settings? On PP3 (out of 6) I've been checking pump parameters and I'm seeing variation from 0.3 m3/hr to 0.6 m3/hr on the same setting (ie unchanged) I maybe expect a smidge more flow when all rads are in circuit and maybe a smidge less flow when it's just the 24/7 rads in circuit but not that level of change....... I need to get my head round the PP element of pump control
John Carroll Posted March 11 Posted March 11 (edited) 1 hour ago, marshian said: On PP3 (out of 6) I've been checking pump parameters and I'm seeing variation from 0.3 m3/hr to 0.6 m3/hr on the same setting (ie unchanged) I maybe expect a smidge more flow when all rads are in circuit and maybe a smidge less flow when it's just the 24/7 rads in circuit but not that level of change....... I need to get my head round the PP element of pump control I think I know exactly how PP control is supposed to work. If you look at the attachments, it will become pretty clear. On the graphs, the red line shows what the actual flow&head is as the pump ramps up in speed, the blue line is the PP setting, on PP2, zero flow is 1.6M & 3.2M is 1.85m3/hr, as the pump speed ramps up the actual flow and calculated PP flow become exactly the same at only one head, where the red&blue lines intersect, you can see more definition in the calculations. On CP2 you got a flow 0.5m3/hr at @ 3M head & 15W, these all correspond to exactly the very accurate Wilo data for my 6M wilo Yonos Pico so that flow and head are quite correct IMO. On PP2, using that flow&head, 0.5m3/hr@3.0M, results in a flow/head of 0.403m3/hr@1.95M and on PP3, 0.535m3/hr@3.44M. IF the flow&head are steady in CP mode then the should also, too, be steady in any PP mode, (a gradual change will take place if say TRVs are closing in etc.) Note though that the PP2 & PP3 settings are taken from the 3 standard settings shown in the screenshot but doesn't really matter as there shouldnt be any fluctuating PP settings. Dab Evosta3 PP2 Rev 0.xlsx Dab Evosta3 PP3 Rev 0.xlsx Edited March 11 by John Carroll
John Carroll Posted March 12 Posted March 12 This Graph is based on what may be the 6 PP settings, just change the values to see the effect on the head/flow. Dab Evosta3 PP Various Rev 0.xlsx