Colink Posted September 11 Share Posted September 11 My son owns a 1980's Timber Frame bungalow . Structure is same as attached image. He is currently converting the attached garage to 2 bedrooms. The garage is already insulated, with fiberglass between the studs - same as the house. The house is unoccupied and with no furniture and he has easy access to all the walls in the house. The Northern Ireland Building Control inspector has mentioned that the insulation is probably not up to modern specification and would need to be upgraded. I believe he was correct that by adding additional internal insulation (on top of the internal plasterboard) could cause condensation to form on the plastic vapour barrier, behind the plasterboard, due to the lower temperature on the outside surface of the vapour barrier. The most effective solution is probably to add external insulation, however that will likely be more expensive and could end up with the garage part the house having a different finish to the rest of the house (not the end of the world). Is removing all internal plasterboard and the vapour then adding new insulated plasterboard a possible solution? However that means no vapour barrier - what effects would that have? Is there a better solution? The issue is further complicated by a comment from the Building Control officer that suggested there might be a requirement to upgrade the insulation for the whole building, however that would be a lot more work and cost. I am not fully clear on the reasoning for needing to upgrade the insulation of the whole house (I think it was due to him also requiring building control to upgrade the heating system). I need to call the inspector for clarification, but I want to be more clear on what is a suitable insulation solution for the garage or the whole house before I ask more questions. Any guidance on the most efficient / cost effective way to upgrade the garage or whole house insulation would be appreciated. Link to comment Share on other sites More sharing options...
Redbeard Posted September 11 Share Posted September 11 Hello, You could add IWI and still have a VCL (use an insulation board without plasterboard, tape the joints and perimeters and then pl'bd over. However I am in agreement with BC that EWI would be better. I do not know NI Regs so I cannot say whether an upgrade of the whole house is reasonable to request. In England (unless it has changed in the last 'round' or two) 'consequential improvement' requirements such as this were peculiar to non-domestic, AFAIK. Link to comment Share on other sites More sharing options...
Redbeard Posted September 11 Share Posted September 11 (edited) Post above should read 'use a *foil-backed* insulation board' (or use a separate VCL between ins and pl'bd.) If you do decide to go for EWI get an interstitial condensation risk analysis done, preferably using dynamic software such as the German WUFI. Edited September 11 by Redbeard Link to comment Share on other sites More sharing options...
Colink Posted September 12 Author Share Posted September 12 @Redbeard Thanks for your detailed reply. I note your recommendation for external insualtion and condensation risk analysis. We are still considerign external insulation. I realsie we need to get local professionsl advice on this before implementation, however your replies are helping me to be more informed and be better placed to help find the right person and to ask the right questions. One additional consideration. At the same time as this work the property may be upgrded with a heat pump + new radiators, replacing the oil heating which does not work. (No Gas option). In order to get sufficient water flow to the new radiators it is liley that new 22mm heating pipe will be needed. Assuming we want to hide this pipework as much as possible I see two possibiliries to include when the new insulation is added. 1 (See right image below - left image is what you described - I believe) Add 25mm stud to the existing plasterboard, then the new insulation (green) - tape all joints then the standard plasterboard. New 22mm pipewoek goes behind the insulation 2 (no diagram) - New insulation on top of existing plasterboard (taped joints), 25mm stud + standard insulation board. 22mm pipe between new insualtion and plasterbaord. I am assuming 2 is the better thermal solution, however I am not sure how easy or difficullt it wil be to find fixing points for the 25mm stud. Any comments from you or others would be appreciated.. Link to comment Share on other sites More sharing options...
ProDave Posted September 12 Share Posted September 12 What sort of EWI are you thinking of and what finish over it? There are on line tools that will do a condensation analysis of your proposed new make up. But if doing this, I would add new insulation direct onto your existing plasterboard, and THEN the battens for your service void and plasterboard. That keeps all services inside the (hopefully) sealed wall make up with no penetrations. Link to comment Share on other sites More sharing options...
Colink Posted September 12 Author Share Posted September 12 @ProDave Thanks for your reply and confirming insulation, battens, (service void) palsterboard would be the best solution - as I thought. I assume we can figure out where existing joists are located and mark the position so the new battens line up. We have given no thought to external insulation type or structure at this stage. I am assuming it will be more cost effective buit more costly. Any suggestions or comments would be appreciated. One more note - my son is a joiner so is capable of doing all the labour for this work, but would need to get the correct instructions to ensure that EWI is installed correctly. Link to comment Share on other sites More sharing options...
Redbeard Posted September 12 Share Posted September 12 I try to avoid 'boxing up' plasterboard in an insulation sandwich, so I would like to take off the exg plasterboard 1st, probably lose the exg VCL, and ensure a new, tight VCL on the warm side of your PIR. Yes, warm batten idea is good (what I used to use when I did PIR IWI) and just room to run your 22mm, as long as you don't use push-fit or compression fittings. I don't understand no.2 (no diagram) above. 2 hours ago, Colink said: New insulation on top of existing plasterboard (taped joints), 25mm stud + standard insulation board. So from the exg plasterboard, inwards: 'new insulation', 25mm stud and then more insulation? ('standard insulation board'). Or should that have said 'standard plasterboard'? 1 Link to comment Share on other sites More sharing options...
Colink Posted September 13 Author Share Posted September 13 @Redbeard Thanks again for your input. I had been thinking about removing existing plasterboard and VCL. Ref order of insulation and plasterboard. Original diagam was done beforeI had thought this through and before your original reply + my type regarding "standard Insulation board". I think this new diagram is what you describe (but may remove original plasterboard and VCL). If I am wrong please advise. If you have any general suggestions or links regarding using external insulation I would be keen to read. Link to comment Share on other sites More sharing options...
SteamyTea Posted September 13 Share Posted September 13 (edited) Assuming that internal space will not be compromised, just remove all the stuff, existing plasterboard, VCL and insulation. Make the sheathing as airtight as possible i.e. perfect. Then increase stud depth, reinsulate, VCL and all plumbing and wiring that needs changing. Sometimes it is just easier and cheaper to start again. Edited September 13 by SteamyTea Link to comment Share on other sites More sharing options...
Colink Posted September 13 Author Share Posted September 13 @SteamyTea Thanks for your imput. In your description where does plumbing and wiring go (in what order)? The current insulation is fiberglass. Are you suggesting increasing stud depth and adding thicker fiberglass? Do we still add foil backed insulation. Maybe it would be easier for me to understand if you listed items / materials from the sheathing out to plasterbaord? Link to comment Share on other sites More sharing options...
SteamyTea Posted September 13 Share Posted September 13 (edited) The wiring goes in 'safe zones' so check with an electrician. Plumbers tend to put pipes all over the place, so check with a plumber, though you will probably only need standard 15mm. Don't confuse the lower flow temperature with lower output, it is more complicated than that. As for insulation, basically the same build-up, but thicker. No need to use a foil backed, or insulated plasterboard, the VCL does that. A VCL (it is usually a sheet of polythene that is taped to make an airtight 'bag') is to stop moist air migrating to a colder area and condensing, it is not for improving wind tightness. Wind and airtightness need to be dealt with separately and go on the cold side. They are vapour 'open' to allow moisture to evaporate away to the outside. Basically the warm side i.e inside, is the most vapour proof, then as you go towards the cold side i.e. outside, you allow more vapour open materials. This allows any moisture to evaporate to atmosphere and not cause condensation related problems. Edited September 13 by SteamyTea Link to comment Share on other sites More sharing options...
Colink Posted September 15 Author Share Posted September 15 @SteamyTea Thanks for our input - My son has decided to keep the existing insulation and plasterboard and follow the procedure discussed in the early part of this thread @SteamyTea @ProDave @Redbeard I would appreciate your comments on this (hopefuly) final image and answer a question about Vapour Barrier The attached image shows two possible locations for pipework. My son plans to go with the second version where pipes go along the bottom of the wall along 3 bedrooms. I have noted the importance of taping the joints of the insulation to make a good vapout barrier. Buiding Control mentioned the possibility of a plastic vapour barrier (not sure if he will want to enforce this if he is happy with the taping). What are your thoughts on taping + plastic sheet vapour barrier? Any negatives of adding the plastic vapour barrier? Someone locally mentioned the possibility of condensation forming on the plastic vapour barrier, however as it will be on the inside of 50mm insulation I assume both sides of it will be close to room temperature - hence no condensation issue (if fitted) - Comments? Any other comments would be appreciated. Link to comment Share on other sites More sharing options...
Redbeard Posted September 15 Share Posted September 15 11 minutes ago, Colink said: I have noted the importance of taping the joints of the insulation to make a good vapout barrier. Buiding Control mentioned the possibility of a plastic vapour barrier (not sure if he will want to enforce this if he is happy with the taping). 11 minutes ago, Colink said: What are your thoughts on taping + plastic sheet vapour barrier? Any negatives of adding the plastic vapour barrier? Not really any negatives. If I were bring obsessive I'd do both, as well as I possibly could in each case. 11 minutes ago, Colink said: Someone locally mentioned the possibility of condensation forming on the plastic vapour barrier, however as it will be on the inside of 50mm insulation I assume both sides of it will be close to room temperature - hence no condensation issue (if fitted) - Comments? I don't think you've ever given the depth of the (??mineral wool?) insulation in the frame. If we guess at 100, and it's bog-standard mineral wool, that could have a thermal conductivity of 0.044W/mK, and PIR has 0.022, so your 50mm PIR has the same insulation value as the 100mm (guessed) mineral wool, so things are cooling quite a bit by the time you get to the interface. I would *not* put a VCL in the middle of that sandwich. (Of course if I am wrong re the 100mm the sum will change. I would *strongly* advise you to get a condensation risk assessment done. The British Standard (Glaser) method is not as good as WUFI but is at least indicative. I am not sure why you feel that ''both sides of it will be close to room temperature - hence no condensation issue''. It's keeping the heat in, so the interface will be significantly colder, or else the insulation is not doing its job. Link to comment Share on other sites More sharing options...
SteamyTea Posted September 15 Share Posted September 15 @Colink Will be here be enough room to fit pipes, and insulated them in a false cavity? Many people think that it is not worth insulting pipework unless it is also used as cooling. I disagree with that (not the cooling) as you just end up overheating an area with lower thermal resistance to outside. The whole idea of the vapour control layer is to stop warm, moist air condensing in a cold cavity. If you do get to 0 ACH, then you have a nice problem to deal with, just fit mechanical ventilation and heat recovery. Your son really will wish that he removes all the old plasterboard, increases the stud depth, fit his news central heating pipes (properly insulated, a well taped VCL and new plasterboard (possibly in resilience bars). I is very little extra work and will be a lot easier for a much better job. Link to comment Share on other sites More sharing options...
Colink Posted Monday at 22:36 Author Share Posted Monday at 22:36 @SteamyTea I have two question in this post - the remainder is sumarising what we will be doing. Thanks again for your input. I note your comments. I have passed on your recommendations about removal of existing plasterboard and insulation. For better or worse he has decided he will not be doing that and will be doin as per my new diagram attached. Subject to agreement with the plumber heating pipes will be going horizonatally along 3 bedrooms on one side of the house. Similar on the other side. Building control have told us to follow the guidance of the insulation manufacturer. The insulation manufacturer have also recommended removing existing insulation and plasterboard, but have also given their recommendations for insulating on top of the existing plasterboard. They have carried out calculations and determined there is very a low risk of condensation subject to adding a 1000 gauge polythene vapour control layer on top of the insulation. Even though @Redbeard and @ProDave (I think) suggested tapiing the joints we will need to follow the insulation manufactureers recommendations to keep building control happy. I am assuming taping the joints will be of no additional benefit - happy to be told I am wrong. QUESTIONS Q1 - what is the most cost effective sealer / adhesive to seal the vapour barrier against the new insulation? Adhesive tape sounds expensive, I assume some gun applied sealer or adhesive will be the easiest method Q2 - Should it be sealed / glued on the back against the insulation, or cut to the exact size and sealed around all four sides. Note - Given that we will probably be adding horizontal battens, including one at the very top (see image) the top edge of the vapour barrier will be sandwiched between the batten and insulation (presumably with sealer or adhesive between it and the insulation. I assume we will then trim the sides of the vapour barrier while being held by the top batten then sealer or adhesive (Q1) applied behind the edges or on top of the edges. Plus some more battens. Back to SteamyTea's response He will be using 50mm foil backed insulation + the void for the heating pipes. Taking into consideration your comments about insualtion he is aware he will be taking 100mm plus out of the room width. Link to comment Share on other sites More sharing options...
Mr Punter Posted Tuesday at 13:51 Share Posted Tuesday at 13:51 I have looked at this in ubakus and it all seems OK. U value of about 0.2 W/(m²K). I would not get too hung up on how to seal the plastic VCL to the insulation. The battens will hold it in place. Link to comment Share on other sites More sharing options...
Colink Posted 23 hours ago Author Share Posted 23 hours ago (edited) @Mr Punter Thanks for your reply (including your comments about sealing the vapour barrier” and for doing the calculations for me. i signed up to Ubakus but having difficulty recreating your table. I only see 4 rows and cannot see how to add? Maybe I cannot with a free account. ==== I am not sure exactly what Building Control will want to enforce. From my brief online reading I see numbers of 0.18 for upgrading an existing building. Assuming we are already committed to 50mm foam (some already fitted ) and need to get to 0.18, what else could we add between battens and plasterboard eg plywood (or some other sheet) vs buying insulated plasterboard? note, the batten depth is 50mm but I assume that will not be sufficient. Edited 23 hours ago by Colink Add more text Link to comment Share on other sites More sharing options...
Alan Ambrose Posted 14 hours ago Share Posted 14 hours ago FYI, there’s no problem adding more than 4 materials with the free version. Link to comment Share on other sites More sharing options...
Colink Posted 12 hours ago Author Share Posted 12 hours ago @Alan Ambrose My mistake. I was looking for a way to add rows before entering the first 4 To answer part of my own question to @Mr Punter I see that adding plywood or OSB makes little difference and does not get to 1.8. Building control were a little vague on what exactly they required for upgrading the original wall. (In a helpful way) suggesting that it might not be required in certain circumstances. I am planning to send the calculation to building control and ask if they will be ok with this 1.95 in main house but that we use 75mm or thicker in the garage conversion which brings it down to below 1,7 and 100mm+ for a future extension. Note Garage is same construction and insulation as main house. Any comments or corrections welcome Link to comment Share on other sites More sharing options...
Redbeard Posted 11 hours ago Share Posted 11 hours ago 11 hours ago, Colink said: From my brief online reading I see numbers of 0.18 for upgrading an existing building. That's for extensions. 0.3 for 'renovation of a thermal element' (= 'adding or replacing a layer'). https://assets.publishing.service.gov.uk/media/662a2e3e55e1582b6ca7e592/Approved_Document_L__Conservation_of_fuel_and_power__Volume_1_Dwellings__2021_edition_incorporating_2023_amendments.pdf Table 4.2 is for extensions and 4.3 for renovation of a thermal element And note it's 0.195 and 0.17, not 1.95 and 1.7 as per your last post. Using the latter *will* have the BCO querying! Link to comment Share on other sites More sharing options...