We are just at the point of commissioning the UFH and looking at the pumps on each manifold. They look pretty well, weedy. Do we need a pump to take from the thermal store to the manifolds as well as the pump on the loops? 

Posted

The pump in our old house packed up. It was some while before we actually noticed as the manifold pumps were doing a good job of circulating water from the boiler to the manifolds.  It was mainly the hot water heat up that suffered as gravity flow was limited.

 

So I would say no extra pump needed.

 

What does @Nickfromwales say?

Posted

One I did a good while back was convection circulating over 17m of pipe away from the TS which went through an underground trench between the house and the garage ( new plant room ). 

No additinal pump needed afaic, unless it's the longest, most adverse run in history.

Rememver you do need motorised 2-port zone valves ( ZV ) at the TS for each flow as otherwise you'll get them all draining heat from the TS 24/7 with convection circulation ;)  

Use the orange and grey wires of the 5-wire ZV to switch the respective manifold pump on, as that way you'll never have the pump pulling on a closed or partially open ZV. 