Crustydoodle Posted September 21, 2023 Share Posted September 21, 2023 Hi all, I am new here so hopefully posting in the right place and this is OK to ask. We have recently had the following installed: Mistubishi Ecodan R32 11.2kW Mitsubishi FTC6 controller Underfloor heating throughout (Heatmiser controlled) The Mitsubishi cylinder is horizontally mounted in the loft as shown in the picture. We are seeing a behaviour which our installer said should not happen and yet Mitsubishi claim is 'normal'. Every 2-4 hours, the ASHP will activate when there is no call for hot water or heating (and no legionella cycle). The Hot water calls appear to be normal and happen as expected. We were told that the ASHP should only really come on at the moment when the hot water needs bringing back up to temp. This is clearly not the case and now the installer is backtracking following a call to Mitsubishi. I've complied a full day of hourly traces into one image (attached) that shows these spikes in the form of flow and return temperatures spiking, then gradually dropping and then triggering to spike again when it hits around 25degC. On this trace you can also see a hot water call and the cylinder temp rising to the correct level. We also tested the heating last night so you can see some activity around that. We can also hear that water is being pumped through the services in the wall on the internal side of the setup - not sure if it is requesting water or wasting water or both, but it is coming from where the mains connects into the ASHP setup and where the ASHP connects down to the UFH manifolds. As a side note, we did have an L9 error as well but this has not returned and so we think it is not related. The main issue is that the pumps and water movement in the loft is noisy enough to wake us in the night. We are very tired! I am not convinced this is normal behaviour - if it is, then we have a major issue with constant noise through the night. The 2 other Ecodan users I know do not see this happening. Any ideas or seen this behaviour before? Thanks in advance Link to comment Share on other sites More sharing options...
JohnMo Posted September 21, 2023 Share Posted September 21, 2023 My view is if you can here noise in the water system you have air in it. Are you sure something isn't calling for heat. The circulation pump should only be on if you have a call for heating or DHW. So I would guess the installer has a setting or two wrong (there will be a few ways to call for heat and various ways to operate circulation pump) Link to comment Share on other sites More sharing options...
ProDave Posted September 21, 2023 Share Posted September 21, 2023 Has it been installed properly? A self builder near me had an Ecodan system installed and it did similar things. It was about a year after the install he got me to look at it, and the call for heat from the UFH manifold had not been connected to the Ecodan controller, so when the heating was "off" it was still circulating water in the short loop from the ASHP to the UFH manifold and occasionally starting up to keep that warm. Link to comment Share on other sites More sharing options...
Andehh Posted September 21, 2023 Share Posted September 21, 2023 We had a gas boiler randomly coming on when no demand for heat, and traced it back to a failed zone valve?? Link to comment Share on other sites More sharing options...
Crustydoodle Posted September 21, 2023 Author Share Posted September 21, 2023 @ProDave Is there an easy way to check for that? We just had a slightly different symptom - I could hear the pumps working water around the system and yet the ASHP was not active according to the app - I can hear noise where the UFH loop would come down. Up in the loft by the system it is definitely not running, yet I can feel a small vibration on the return to the ASHP where that pump is and also the spitter - hard to tell where else. The noise of water moving was also loud by the ASHP itself and yet the ASHP was not actually running. Link to comment Share on other sites More sharing options...
ProDave Posted September 21, 2023 Share Posted September 21, 2023 I would just call your installer back. It would be almost impossible to diagnose remotely. Tell them they need to stay long enough to witness the phantom activation and determine what is causing it. It does sound like water is circulating somewhere all the time, go round and try and work out which pump and where is on all the time, that is another thing to point out to them Link to comment Share on other sites More sharing options...
Gary68 Posted September 21, 2023 Share Posted September 21, 2023 Is this the freeze stat function running the pumps, if you go to the service menu, the one that has a spanner on the far right, then down to page 2/4 there is a operation settings, in that menu there is the freeze stat function, there should be an ambient temperature its set to, on the right side this can be set as high as 20C, it runs the pumps every few hours. If you turn the temperature right down till it just ** then see if the issue stops. It doesn't sound like that but its easy to test overnight. 1 Link to comment Share on other sites More sharing options...
Crustydoodle Posted September 21, 2023 Author Share Posted September 21, 2023 One other thing to add - we have had the installer back twice, the second with a specialist. They thought it was resolved but as they went to leave, the ASHP was on, which they agreed shouldn't be the case. They spent a chunk of time on the phone to Mitsubishi who claim that it is normal behaviour - It does not sound like it to me from the comments so far. Link to comment Share on other sites More sharing options...
ProDave Posted September 21, 2023 Share Posted September 21, 2023 6 minutes ago, Crustydoodle said: One other thing to add - we have had the installer back twice, the second with a specialist. They thought it was resolved but as they went to leave, the ASHP was on, which they agreed shouldn't be the case. They spent a chunk of time on the phone to Mitsubishi who claim that it is normal behaviour - It does not sound like it to me from the comments so far. Before you let them fob you off with that excuse, ask for a written explanation from Ecodan describing exactly what it is doing, why it is doing it and how do you configure that aspect of it's aparently essential and normal operation? 1 Link to comment Share on other sites More sharing options...
HughF Posted September 22, 2023 Share Posted September 22, 2023 Is that a grundfos selectric bronze secondary return circulator? It looks very similar to one I have on the floor at the moment. If so, I expect that it's the call for heat from the cylinder temp sensor, as the secondary return is draining the cylinder heat away. Link to comment Share on other sites More sharing options...
Crustydoodle Posted September 22, 2023 Author Share Posted September 22, 2023 1 hour ago, HughF said: Is that a grundfos selectric bronze secondary return circulator? It looks very similar to one I have on the floor at the moment. If so, I expect that it's the call for heat from the cylinder temp sensor, as the secondary return is draining the cylinder heat away. I believe it is. That pump comes on when there is a call for hot water and circulates the tank (I think). When the random ASHP activations happen every couple of hours, it does not come on - the one that activates is the black one in this picture which is on either the in flow or return from the ASHP (although I am struggling to get to it to confirm that!). Link to comment Share on other sites More sharing options...
Crustydoodle Posted September 22, 2023 Author Share Posted September 22, 2023 16 hours ago, Gary68 said: Is this the freeze stat function running the pumps, if you go to the service menu, the one that has a spanner on the far right, then down to page 2/4 there is a operation settings, in that menu there is the freeze stat function, there should be an ambient temperature its set to, on the right side this can be set as high as 20C, it runs the pumps every few hours. If you turn the temperature right down till it just ** then see if the issue stops. It doesn't sound like that but its easy to test overnight. Thanks for this - we tried it last night but it didn't change the behaviour. I was optimistic as it definitely seems to be the drop in flow/return temps that drives the ASHP to come on - usually around 25degC. They have become more frequent with the weather cooling. Link to comment Share on other sites More sharing options...
Gary68 Posted September 22, 2023 Share Posted September 22, 2023 So can you confirm that when the heat pump is running its trying to heat the DHW? If so, assuming it doesn't actually need to heat the hot water then you can either lower the reheat threshold or just control it through the timer so that it only heats once or twice a day depending on your requirements. Link to comment Share on other sites More sharing options...
Crustydoodle Posted September 22, 2023 Author Share Posted September 22, 2023 (edited) Nope, when the heat pump is running on those activations hat happen every 2-3 hours, it is not trying to heat anything as far as we can tell. The flow and return temps rise up, but this is not affecting the DHW and the heating is off. This happens around 8 times per day. When there is a call to heat up the DHW, this also activates the ASHP and the cylinder temp rises back to 50degC - this happens around once per day. The reheat threshold is 10 degC below the 50 and that seems to be working fine. Traces of the two types of activation we see are attached - First image is a normal hot water call and you can see the red trace for the hot water temp rise. Second image is one of the random activations where the overlapping flow and return temps drop to ~30degC, then dip and rise together to ~60degC - no call for heating or DHW. Edited September 22, 2023 by Crustydoodle Link to comment Share on other sites More sharing options...
Gary68 Posted September 22, 2023 Share Posted September 22, 2023 In the random activations the temperature is getting to 60°C very quickly suggesting its heating a very small volume of water, what temperature do you have the heating flow set to does that align with the 60°C? If so then the ashp is getting a call for heat from somewhere but none of the pumps are activating hence the rapid increase in flow temp. You said the UFH is controlled by heatmiser maybe there is an issue with how that's been wired to the ecodan controller. Link to comment Share on other sites More sharing options...
Crustydoodle Posted September 22, 2023 Author Share Posted September 22, 2023 Yeah - my gut feel is that it is just heating whatever is in the loop to the ASHP, possibly something in the UFH loop, but I am very far from an expert. The legionella cycle is set to 60°C but that is on a 7 day cycle, was at 5am but now at 2pm Other temp settings from the summary: Hroom1 30°C HFlow1 55°C Croom1 20°C Cflow1 15°C HWtemp 50°C HWDRop 10°C Link to comment Share on other sites More sharing options...
JohnMo Posted September 22, 2023 Share Posted September 22, 2023 Do you have a buffer? If so a suggestion to what may be going on. Assume the heatmiser is controlling the pump the central heating side of the buffer. The heat pump circulation pump is controlled by the heat pump controller, if this is set to weather compensation mode the the heat will be managing the heat in the small loop to the buffer? Link to comment Share on other sites More sharing options...
Gary68 Posted September 22, 2023 Share Posted September 22, 2023 That all makes sense flow temp is 55°C and its hitting 60°C before shutting off its probably overshooting due to the volume of water being so small. Its not working correctly that's for sure its getting a signal from somewhere that heat is required when it isn't. If heatmiser wireless thermostats lose connection with the UH8-RF, it opens the UFH circuits for 12mins every hour, again it doesn't look like this is what's occurring but are all the zones working as they should be and turning on when thermostats call for heat? Link to comment Share on other sites More sharing options...
Crustydoodle Posted September 22, 2023 Author Share Posted September 22, 2023 As far as we can tell, every heating zone comes on when the stats call for it, but we haven't really tested how much heat is outputted yet. Might try that now. 32 minutes ago, JohnMo said: Do you have a buffer? If so a suggestion to what may be going on. Assume the heatmiser is controlling the pump the central heating side of the buffer. The heat pump circulation pump is controlled by the heat pump controller, if this is set to weather compensation mode the the heat will be managing the heat in the small loop to the buffer? I do not think we have a buffer. They are larger than an expansion tank, right? Link to comment Share on other sites More sharing options...