Air Source Heat Pump - general question

Featured Replies

3 hours ago, dpmiller said:

"single phase" there means it doesn't apply to any inverter units as they use a 3-ph compressor and slowly ramp up speed, automatically clearing down gently with no "protector" to trip out anyway...

No following the logic, unless a big ASHP the supply would be single phase.

  • Replies 58
  • Views 7.8k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • You can use a Combi in a small, medium or large house.  You can get very good flow out of a combi if it big enough and you choose the right one.  Performance varies quite a lot.

  • If your property is suitable and if the alternative is electric (resistance) heating, then ASHP may very well be a good choice.  Properly set up it should use about a third to a quarter the electricit

  • This is proving to be a question that should be asked of the manufacturer BEFORE you buy an ASHP as some are proving to have high standby power use.   My own, a 5kW LG Therma V use used 1kWh

@JohnMo yes the supply to the ASHP is singlephase, but the inverter converts it to a nice controllable voltage-, current-, and frequency- controlled 3phase.

I know that

'means it doesn't apply to any inverter units as they use a 3-ph compressor'

 

This is bit where the logic makes no sense.  The heater is just a single phase and would there whether the  compressor motor is single or three phase or even DC driven.  The heater has nothing to do with motor driving the compressor.

 

no the logic is that the startup of the compressor is controlled, and so oil and gas can be gently redistributed rather than with a switch-start 1ph machine the pump is "blocked" from starting by the liquid refrigerant

 

 

same thing applies to air compressors- a switch-start machine has a valve built into the pressure switch to "unload" the pump head until the rpms and output pressure build. Switching the compressor on at the wall instead of the airswitch results in a humming noise and a blown fuse...

The mitsubishi ASHP with higher than ideal standby electric usage are inverter driven, so I am still missing what you are trying to say.  They have a crankcase heater and a requirement to heat up prior to starting.

 

It's easy to dump air and water not so easy to dump refrigerant.  Hense the need to heat the crankcase and turn the liquid refrigerant back to a gas state.  An inverter doesn't get around the science that a liquid isn't compressible.  Nor that lube oil diluted with refrigerant is a rubbish lubricant.

2 hours ago, JohnMo said:

Nor that lube oil diluted with refrigerant is a rubbish lubricant.

Would a silicone oil get around that problem, silicone is very inert.

I think you have to use an oil that is hydroscopic to the refrigerant gas.  I know in industrial screw compressor that is the case. 

 

It's matter of clearing enough condensate to restore lubricity, you don't have to clear all of it.  And also enough condensate so the fluid can makes its way through the compressor without undue load being placed on thrust bearings.

 

As the the compressor increases pressure the refrigerant naturally phase changes back to gas. You often get operators that think they know better, and over ride the heat up timers, this does two things, accelerates bearing wear and places huge loads on thrust bearings, which gives premature failure.

8 minutes ago, dpmiller said:

some info here ST

No mention of polydimethylsiloxane, but I guess if it has not been tested, they cannot report on it.

It is a shame that the chemist I knew at university has retired, she was brilliant, even explained, in less than a minute, why CO2 causes energy to be trapped when in mixed with other gases.

Edited by SteamyTea

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.