nod Posted January 5, 2022 Share Posted January 5, 2022 Over Christmas the controller for the UFH was switched off We didn’t notice Till we stopped using the wood burner Most zones had dropped to 16 I switched the controller back on and the floors slowly started to heat up I’ve noticed today that while 1 & 4 are showing a flame on the stat The actuators arnt lit ? Any pointers would be appreciated Link to comment Share on other sites More sharing options...
nod Posted January 5, 2022 Author Share Posted January 5, 2022 Link to comment Share on other sites More sharing options...
nod Posted January 5, 2022 Author Share Posted January 5, 2022 Link to comment Share on other sites More sharing options...
PeterW Posted January 5, 2022 Share Posted January 5, 2022 Controller isn’t seeing the stats - are they wired or wireless ..? If wireless, start by changing the batteries in the stats and check that by manually changing the status of the heating (do these show sun/moon etc..??) and see if they trigger after that. Link to comment Share on other sites More sharing options...
nod Posted January 5, 2022 Author Share Posted January 5, 2022 The stats are wire Just tried swapping two actuators But no joy Link to comment Share on other sites More sharing options...
PeterW Posted January 5, 2022 Share Posted January 5, 2022 Are these 240v actuators or 12v ..? Link to comment Share on other sites More sharing options...
nod Posted January 5, 2022 Author Share Posted January 5, 2022 1 minute ago, PeterW said: Are these 240v actuators or 12v ..? There 240 Link to comment Share on other sites More sharing options...
PeterW Posted January 5, 2022 Share Posted January 5, 2022 You can always pull the wiring and check by adding a short plug socket and wiring it direct to see if it moves 1 Link to comment Share on other sites More sharing options...
nod Posted January 5, 2022 Author Share Posted January 5, 2022 Thank you to Peter W for responding Very difficult when someone posts a picture and asks What wrong with this As you thought not a Plumbing issue Swapped the stats and actuators Nothing Left the actuators off the two effected zones Slowly stated to get some heat in the pipes Electrical then Put a tester on all the actuators The two effected had no power going out I took backplate off the two effected stats and found a live feed had snapped Half a day for me Half an hour for a good electrician Great feeling when those caps pop up on the actuators 4 Link to comment Share on other sites More sharing options...
SteamyTea Posted January 6, 2022 Share Posted January 6, 2022 14 hours ago, nod said: The two effected had no power going out I took backplate off the two effected stats and found a live feed had snapped Maybe @joe90 has a similar problem. 1 Link to comment Share on other sites More sharing options...
nod Posted January 6, 2022 Author Share Posted January 6, 2022 29 minutes ago, SteamyTea said: Maybe @joe90 has a similar problem. Great feeling when you see those little blue tops start to rise Link to comment Share on other sites More sharing options...
SteamyTea Posted January 6, 2022 Share Posted January 6, 2022 16 minutes ago, nod said: Great feeling when you see those little blue tops start to rise Misread blue tops. Down here, there is a group of female, cold water swimmers. They are called The Blue Tits. I wish the ones that park in the road, blocking in legitimately parked cars, would fail to rise. Link to comment Share on other sites More sharing options...
joe90 Posted January 6, 2022 Share Posted January 6, 2022 1 hour ago, SteamyTea said: Maybe @joe90 has a similar problem. No, I have no controlling actuators etc, zones and wot not, Luddite me! Well done Nod. Link to comment Share on other sites More sharing options...
PeterW Posted January 6, 2022 Share Posted January 6, 2022 16 hours ago, nod said: took backplate off the two effected stats and found a live feed had snapped glad you found that !! The issue with some of these Heatmiser stats is they need to bend the cables at 180 degrees to get into the connectors and they get continually flexed when the face places are installed. Link to comment Share on other sites More sharing options...
nod Posted January 6, 2022 Author Share Posted January 6, 2022 24 minutes ago, PeterW said: glad you found that !! The issue with some of these Heatmiser stats is they need to bend the cables at 180 degrees to get into the connectors and they get continually flexed when the face places are installed. Yes I found that putting the stat back in Thanks again Peter Link to comment Share on other sites More sharing options...