1 hour ago, dpmiller said:

IIRC the iVT will throttle it's power back if the delta exceeds 10c. I can't recall- are you directly connected or is there a buffer tank involved?

Hi @dpmiller 

 

Thank you for your kind response. 

 

We have a 60 litre buffer tank. and about 85 litres in the pipework and radiators.

Having little knowledge, I assume iVT means inverter, which we have.

IIRC I had to look up ?

 

So do I ignore the temperature drop between the inlet and out let from each radiator because the temp drop will happen in the buffer tank?

But would that not mean losing high temperature heat unnecessarily through the flow return pipes?

 

Should not the water temperature in the buffer tank slowly reduce until the ASHP kicks in? I notice that the sensor for the Heating water is in the buffer tank?

 

All opinions greatly appreciated.

 

Link to comment
Share on other sites

If the buffer tank is to increase the volume of the water in the system, why is the hot from the ASHP going directly into the buffer tank instead of directly to the heat emitters (ours are radiators) before the temperature drops?

 

Why not return the cooler water in to the buffer tank and draw off for the ASHP?

 

 

Link to comment
Share on other sites

I think the answer is controls: with a buffer between source (boiler, heat pump) and heaters you demand heat from the source using buffer temperature. Simple.

With buffer on the return you'd have to use flow measurement to shut off the source when demand (=flow) reduces, but getting there means more and more struggle for the source (on both modulation and pressure). With the only benefit being lower buffer standing losses, you pick a buffer on supply side every time.

  • Like 1
Link to comment
Share on other sites

14 minutes ago, Olf said:

I think the answer is controls: with a buffer between source (boiler, heat pump) and heaters you demand heat from the source using buffer temperature. Simple.

With buffer on the return you'd have to use flow measurement to shut off the source when demand (=flow) reduces, but getting there means more and more struggle for the source (on both modulation and pressure). With the only benefit being lower buffer standing losses, you pick a buffer on supply side every time.

Thanks for this info.

 

In order to stop the flow reducing would not a bypass valve overcome this issue?

Link to comment
Share on other sites