Consumer units


vfrdave

Recommended Posts

Was chatting to a spark about some additions to a garage consumer unit which has raised some questions. He gave me a confused picture and has now gone quiet.

 

Garage consumer unit with 100A main switch and a 6A MCB light circuit and 32A MCB sockets. Upstream is only a 30A fuse.

 

Course of action would be to swap main switch with a 40A (or greater) RCD. Potential for an additional socket ring to go in.

 

Can RCD's and MCB's be mixed and matched in terms of manufacturer?  Current board is all mk and can't source any locally.

Link to comment
Share on other sites

Your post is not very clear, yes the same brand will normally install onto the board.

mcb are miniature circuit breakers 6amp 20amp 32amp etc

rcd residual current device

 

rcd in a board will normally have 4 or 5 mcb you normally have two RCD in a populated board.

 

rcbo - Residual Current Breaker with Over-Current this allows each circuit to have RCD protection without turning the other circuits off.

so if your lights have a fault and trip they won’t turn off your freezer etc.

 

I hope that helps.

 

please let the sparks do the install & mods.

Link to comment
Share on other sites

1 minute ago, Dutch said:

Your post is not very clear, yes the same brand will normally install onto the board.

mcb are miniature circuit breakers 6amp 20amp 32amp etc

rcd residual current device

 

rcd in a board will normally have 4 or 5 mcb you normally have two RCD in a populated board.

 

rcbo - Residual Current Breaker with Over-Current this allows each circuit to have RCD protection without turning the other circuits off.

so if your lights have a fault and trip they won’t turn off your freezer etc.

 

I hope that helps.

 

please let the sparks do the install & mods.

Apologies I wasn't clear.

 

Essentially the main switch needs swapping out with an RCD, currently there isnt one on the board or upstream protecting this board.

 

Can an RCD be added from a different manufacturer than that of the existing MCB's?

Link to comment
Share on other sites

Generally no, you should not mix and match.  Unfortunately although certain aspects of an MCB are defined by various standards, these do not extend to the height and size of the terminals.  So a wrong make of mch or switch the terminals may not line up with the height of the busbar.

 

It is in theory possible to mix some makes together but no electrician would admit to doing that other than for research :ph34r:

 

If it's an MK board, there should be no problem finding an MK RCD for it or alternatively individual MK rcbo's