Shower Discharge Pipe - 40mm or 50mm?


Dan F

Recommended Posts

What is best practice for diameter for wet-room shower discharge pipes?

 

Our architect has specified 50mm, shower drain has 50mm diameter trap and showersave is 50mm but it seems building regs only requires 40mm and plumber apparently only ever uses 40mm

 

 

Link to comment
Share on other sites

50mm every time. It’s big enough to create an air break over the discharging water / suds, whereas 40mm often won’t discharge anywhere near as free-flowing as with 50mm as the entire bore fills with water / suds and stalls. Makes a huge difference if there is even as little as 1000mm or so of horizontal run.

  • Like 1
  • Thanks 1
Link to comment
Share on other sites

@PeterW @Nickfromwales

 

Thanks.  I did talk them into using 50mm, but:

- They've used 40mm for bath.

- They've connected 50mm pipe from the shower trap to the top of the showersave with what looks like some 40mm pipe and elbows.

- They've connected bottom of showersave to SVP, again, with what looks like 40mm pipe and elbows.

 

Will the 40mm not have any real impact if it's only these connections? Or, will they negate the use of 50mm pipe from shower, or even worse create a bottleneck of some sort?

 

I thought I had a photo on my phone.. but seems not, will post one tommorowow..

Edited by Dan F
Link to comment
Share on other sites

3 minutes ago, PeterW said:

I’d ask them to pull the 40 out then and use 50 - shouldn’t take that long and should be done as requested. 

 

Will do.  More than "as requested", assume it's also what's correct/expected, especially given shower pipe/showersave are both in 50mm.

 

We actually have one showersave picking up two showers (which may occasionaly be used at the same time), so probably even more important here..

 

Thanks,

  • Like 1
Link to comment
Share on other sites

1 minute ago, Nickfromwales said:

Bath water has a lot of gravity assistance, showers need to have free-flowing discharge as they have next to no gravity to help get things gone. 
Agree, get them to pull it out and do as the MI’s suggest, even more so if two showers are on one unit :S 

 

Thanks.  We are using a local plumber and they are somewhat out of their depth with some of our non-standard requirements:

- Silient-PP

- 50mm shower drainage

- Showersave

- MLP

- Single central hot manifold next to UVC

- 12mm for basins (3 with 12mm hot return)

 

Link to comment
Share on other sites

Agree with others, if they aren’t installing as per your design, tell them to remove and replace or just replace them and deduct monies off their invoice to reflect the incompetence and for plumber 2 to take over.

 

these are the things that will annoy you later.

 

same with the spark installing 16 mm instead of 25mm 

  • Like 1
Link to comment
Share on other sites

So why use that crap 40mm solvent weld where 50mm is already fitted ..??

 

That first elbow will collect crud as the stopper shouldn’t be fitted horizontal as it creates a lip in the elbow. Also, they should all be swept elbows and not 90 degree elbows.  
 

I would have done that with 45 degree bends - smooth and fast into the heat recovery unit. 
 

Just looks like they used what was on the van

Link to comment
Share on other sites

4 minutes ago, PeterW said:

Just looks like they used what was on the van

 

Exactly!  The solvent weld stuff in itself isn't bad is it?   Rather,  it's just the way they've reduced to 40mm and the 90deg bends, right?

 

This is below:

image.png.8d67e82925670066fa2829353bfab977.png

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...