Dealing with the DPM on the outside of timber frame on passive slab


Recommended Posts

Posted

I need to now tidy up the DPM (Violet line) / DPC (Green line) on the outside of our frame. As I see it I have two options, see picture. I prefer the first (left hand) option as any splashing off the ground cannot get into the DPM/DPC as it is not accessible. Option 2 (right hand) feels more traditional but I am not sure it is as sound as the first in that the there seems to be a moisture path, by capillary action, between the two DPM/DPC layers.  

 

570203954_DPMdetail1.thumb.png.e95e770be1e0a625ae63045ff3c82047.png

 

Any thoughts gratefully accepted as ever.

Posted

Just out of interest, that 316 st/st trim...does it not form a cold bridge where it tucks up on the warm side of the 140mm insulation?

 

Could that affect the bottom edge of the 15mm OSB?

Posted
  On 17/09/2019 at 04:59, Onoff said:

Just out of interest, that 316 st/st trim...does it not form a cold bridge where it tucks up on the warm side of the 140mm insulation?

Expand  

It is 40mm insulation but there 300mm on the inside and although it fixes to the 300mm sole plate that is split by 50mm of insulation ( the greeny / yellow lump) so it is well protected cold bridge wise. I do have a condensation worry but I figured that I could expect the whole mass of the trim to move slowley temp wise but I will review it again.

Posted
  On 17/09/2019 at 05:03, MikeSharp01 said:

Thanks that is the traditional approach but I am not sure why - can you perhaps explain?

Expand  

Because option 1 has the potential to trap water against the bottom of the timber sole plate and OSB.

Posted

 

  On 17/09/2019 at 05:10, MikeSharp01 said:

It is 40mm insulation but there 300mm on the inside and although it fixes to the 300mm sole plate that is split by 50mm of insulation ( the greeny / yellow lump) so it is well protected cold bridge wise. I do have a condensation worry but I figured that I could expect the whole mass of the trim to move slowley temp wise but I will review it again.

Expand  

 

Sorry, read it as 140mm (small screen, bad eyes ? ).

Posted
  On 16/09/2019 at 21:29, MikeSharp01 said:

I need to now tidy up the DPM (Violet line) / DPC (Green line) on the outside of our frame. As I see it I have two options, see picture. I prefer the first (left hand) option as any splashing off the ground cannot get into the DPM/DPC as it is not accessible. Option 2 (right hand) feels more traditional but I am not sure it is as sound as the first in that the there seems to be a moisture path, by capillary action, between the two DPM/DPC layers.  

 

570203954_DPMdetail1.thumb.png.e95e770be1e0a625ae63045ff3c82047.png

 

Any thoughts gratefully accepted as ever.

Expand  

I had to use option 1. My B/insp wanted me to fold the membrane up and behind the breather membrane on the outside of the panelvent or the OSB sheathing in your case. My frame make up from the outside is render board, batten, breather membrane and then panel vent board and then timber frame and insulation. Hope this helps.

Posted
  On 17/09/2019 at 05:27, Ian said:

Because option 1 has the potential to trap water against the bottom of the timber sole plate and OSB.

Expand  

True if any water gets in there. If the breather membrane is outside it I am not sure how water can get there and any water that does will be dried out by the permiability of the structure will it not. As ever its the little details that frustrate. In the traditional case can water not get along between the two membranes if any splashes up there in a storm.

Posted
  On 17/09/2019 at 10:13, MikeSharp01 said:

True if any water gets in there. If the breather membrane is outside it I am not sure how water can get there and any water that does will be dried out by the permiability of the structure will it not. As ever its the little details that frustrate. In the traditional case can water not get along between the two membranes if any splashes up there in a storm.

Expand  

that SS trim will protect it from any splashes. (btw, does the trim have slots or perforations in the angled end section to allow for air ventilation up the cavity?)

  • 5 years later...