Jump to content

Dillsue

Members
  • Posts

    1412
  • Joined

  • Last visited

  • Days Won

    1

Everything posted by Dillsue

  1. Yes, I think youre correct- I forgot you want batteries aswell. If the CT is for battery charging I think a wireless CT is fine. I think that a cabled CT is only mandatory where your export limition is part of a G99/G100 compliant system. Definitely worth checking before you commit to any scheme.
  2. Youd only need a CT if going down the route of export limitation to keep voltage in check. If running additional/upgraded power/comms cables isnt an option then choices to keep things above board seem to be- Use an inverter with voltage controlled power throttling Run DC down the SWA and have the inverter at the house rather than with the panels, subject to the 6mm/120m cable being up to it and having the correct voltage rating. Obviously lots of other solutions that may not keep things strictly above board.
  3. If the voltage goes too high it will trip the inverter which probably would be an issue. I just reread what you originally said and spotted that youve got another 50m of cable to the DNO service connection which will give you additional voltage rise over whatever your DNO is giving you. Not sure if the Solis inverter has a similar feature but Solaredge HD wave inverters have a power control function that can be voltage controlled so as the voltage rises the power generation is throttled. That would keep voltage in check. Another option could be to put in zero export limitation so the inverter will only supply battery charging and the house load and throttle generation if theres no charging or house load. That would remove any voltage rise caused by the 50m from house to service connection.
  4. We run at no load voltage of 250vac. I was told a while back our DNO runs it high to get more power through the system rather than lower us to UK spec of 230vac with increased current and the need for beefier cabling everywhere. Starting at 250vac means our original 4kw system pushes the house over 253vac and the new system way beyond that.
  5. But.... the problem, as prodave mentioned, is voltage rise and that is specific to your situation. It depends not only on your cable length/size but on the power(current) you are trying to push down the cable and the supply voltage to your house. UK supply voltage can legitimately be anywhere from 216-253vac. If you start with a high voltage you havent got to cause much of a rise to go outside those limits, but thats somewhat up to you and/or your electrician. The problem is if you get too much of a rise your inverter can trip. If you are charging batteries then thats unlikely to be a problem, but once the batteries are charged on a sunny summers day, it could be a problem. Best to get your electrician to look at things and do some calcs for you
  6. I thought you were getting a new system installed? If thats the case tell the installer not to register the system and you do it on your account, I didnt need an inverter serial number to open an installers account. When my daughters hubby registered their system, two of the optimisers had been previously registered- they were bought as NOS but clearly their serial numbers had made it on to the SE portal at some time. Over a day or so the optimisers were accepted and now show up on their system. I guess the SE portal checks to see if theres any data coming from the originally registered system and if there isnt, allows them to be assigned to a new system? My second system is using a secondhand inverter so I expect the same temporary issue once I get an internet connection to it and register the system.
  7. Register an installers account with SE?? I have a homeowners account for our original MCS system that was set up by the installer at the time. Ive opened an installers account to add our second DIY system to their portal once I get an internet connection to the inverter. My daughters hubby opened an installers account to add their DIY system to the portal. No batteries in any of those systems so I cant say what can be configured through the portal. I think once youve opened an installers account youd be able to log onto Setapp and use that to configure the charging??
  8. Maybe, but the OP is saying 4 batteries on each inverter and 4 x 48vdc wont give the recomended 300vdc the inverter is looking for. Im not up on battery tech but do know that theres "high voltage" PV batteries around which operate at several hundred volts which maybe what the OPs inverter is intended for?? Solaredge Energybanks operate at 350-450 vdc which matches the typical incoming DC from an optimised set of panels which the energybank is directly connected to. Maybe the OPs set up is similar??
  9. Look at the inverter and battery voltage- big mismatch. If the inverter is expecting a 300vdc battery you can use much smaller cables than youd expect to see on the 48vdc battery. A 10kw solaredge battery connects to its inverter with MC4 connectors and that pushes out 5kw sustained and 7kw for short bursts, all through MC4 connectors.
  10. Have a read of this as pocster seems to be able to configure SE charging quite easily- All is not well in the PW SE multi verse https://forum.buildhub.org.uk/topic/28269-all-is-not-well-in-the-pw-se-multi-verse/
  11. Renusol spec 5 mm minimum from top of tile to underside of bracket. If your brackets are the same ebay ones Ive tried, and they look the same, they flex more than the renusol ones so 5 mm is an absolute minimum. Its a tough call on how much clearance to have as the brackets push up the tile that sits on them so you have a big gap under the tile or have a big slot to cut in the tile so it sits back in place and doesn't lift the tiles around it
  12. Feeding power back into the grid is called exporting which you may or maynot get paid for- google smart export guarantee(SEG). Grid tie is whether your inverter is connected to the grid or not(off grid). If the inverter is feeding the house and the house is connected to the grid, then youve got a grid tied inverter. Your heat pump is only going to pull 10kw for a few seconds during startup and a fraction of that once its running. Unless you cook on full power, your cooker could well run lower than the 4kw you mention. If you design your PV/battery system to supply all the peak house load you could end up with a overly large and very expensive system that rarely gets used. Youd likely be better letting the grid supply the short term peaks like the heat pump startup. I think alot of EV chargers let you schedule charging time so you could charge the EV away from meal times so youve not got cooking and charging load at the same time.
  13. Your 5.7 kw of panels will only generate at that level for that small proportion of the year and anything generated over what the inverter can output doesnt get processed and is "wasted", during that shortish period of the year and for a few hours each day during peak generation. Early and late on peak summer days your oversized array will generate earlier and later in the day giving a longer spread of useful power but the generation peak will be "wasted" PVGIS gives hourly predictions so you can input your details and see how much any particular size of array will generate. I think you may need Excel to make sense of the data!!
  14. I dont know about other manufacturers, but SE allow several kw of DC input over the inverters rating. A G98 SE3680H is rated at 3.68kw but can have up to 5.7kw panel input connected. If the array is split and facing differing directions you can have more connected so long as total generation at any one time is less than 5.7kw.
  15. Putting Tigo optimisers or any individual module electronics on the roof gives just the same problem as SE optimisers if you get a failure. SE optimisers need to be connected to an SE inverter to get the safe 1 volt output feature to work, but SE produce a tool that allows the safe 1 volt feature to be disabled and I beleive their optimisers can then work with any inverter. Youll loose the monitoring but the optimisation will still work. As with everything in life if you want something that performs better then theres a price to pay which is the case with SE, but thats far from being had over a barrel. If you want the individual module monitoring and a better performing system then youve initially got to put your hand deeper in your pocket than you would with a simpler system, but thats an individual choice rather than a blanket "dont touch them"
  16. Weve recently installed 2 x SE systems on top of the 2015 FIT system we already had. A breeze to install and very easy to add/alter if you want to expand/rearrange panels. We had an optimiser fail on the FIT system a few years ago which was easily spotted with SE module level monitoring. SE diagnosed the fault remotely and sent out a replacement within a few days... I didnt have to ask. Fitting the module is DIY if youve got access to an alloy scaffold tower(own/hire/borrow) OR a ladder and rope/harness. Remember that with an SE system youre only dealing with <40 volts on the roof. Loads of advantages with an SE system that have been detailed in previous posts👍
  17. Its unlikely a 6kw inverter will be manufacturer limited to 16 amps so youll need to submit a G99 application and get approval before connection to the grid.
  18. Exactly this. "Pay back" depends on motivation for doing something, installing PV in this case. If youre doing it for green reasons then ROI may not be relevant with the reverse also being true. If you want autonomy from the grid then ROI might not matter much if atall. How you use and maintain a PV system can have a big effect on ROI if thats what your focus is, less of an effect on the environment if thats your focus
  19. Maybe Im mistaken but as understand it one of the ways to make the most of the agile tarriff is to charge batteries from PV during the day or from cheap rate eleccy overnight, then discharge to the grid in the evening peak to grab the highest export rates??
  20. I think the backup unit is an integrated inverter/charger and grid disconnect unit all in one, so there isnt a "main" inverter. Im guessing the inverter is able to run in off grid/island mode only when the disconnect device(contactor?) has isolated the house from the grid. Not sure if theyve got certification in the UK yet??
  21. For the max voltage have a look at the label on the panel or the data sheet. Ive just looked at one Ive installed recently and its 1500 volts. Youre unlikely to have problems with the voltage applied by a series of upstream panels and the max panel voltage could well be higher than the input to your inverter?? By series wiring differing panels youll limit the string current to that of the lowest current panel, so if you put a 250w in series with a 310w that strings current will be limited to 8.11A even though the 310w could push 8.52 By wiring in parallel each panel drives whatever current it can but higher voltage panels have their voltage pulled down to that of the lowest voltage panel. Not sure what system youre installing but micro inverters or optimsers do away with this problem and allow mixed size panels. On the optimised solaredge system weve just put in weve got 405w and 335w on one string and 310w and 320w on the second string. The optimisers deal with all the current/voltage regulation and the panels just feed the optimisers with whatever they are rated at. Makes later extensions a piece of cake👍
  22. You can check the inverter is listed on the ENA database, as above. If its on the database its hard to see how your DNO could refuse to accept your inverter. For your budget dont forget youll be charged VAT and/or import duty when the goods arrive in the UK.
  23. Theres a guy on ebay selling kits that is based in southampton. Search for "solar panel" then order the results by nearest first. He doesnt always include mounts so make sure you allow for these.
  24. AFAIK your options are micro inverters, Tigo optimisers or SolarEdge optimisers. There maybe other individual panel power processing systems but those seem to be the common ones. All will help with shading but wont elimnate the problem. If your array is shaded til 14.30 your not going to get much generation in the winter. Is it possible to prune the trees a little or relocate the panels?
  25. What was the driver to go for micro inverters originally?
×
×
  • Create New...